50 amp adapter

Ok not sure if this is the right area, but seems like a tech question.

I camp a lot at state parks in Ohio. The electrical grid in a lot of the parks is 50 plus years old. When I 1st pull in I typically trip the main breaker on the pole when the AC, water heater, a fridge all start doing their thing. Sometimes just the AC is enough to trip it.

The solution has been to plug into the 50amp socket using a 50 to 30 adapter and the problems go away. I've checked the cord and the plug and everything is cooler than when plugged into the 30 amp socket.

So here's the question, the adapter essentially uses only 1 phase of the 2 phase 50 amp service. Is it possible to power 2 campers from one 50 amp/240 volt plug? Essentially one phase for each camper? Seems like a fairly straightforward project, right?
__________________
2011 JayFlight G2 32BHDS
2003 GMC 3500HD Crew Cab Long Bed 6.6L Turbo, 100 gal auxiliary fuel tank, Brake Smart controller
1 DW, 3 kids, 2 large dogs, & assorted friends!
Chazinn is offline   Reply With Quote
Old 08-02-2013, 08:17 PM   #2
Junior Member
 
Join Date: Jul 2013
Location: North Fort Myers, FL
Posts: 16
50 amp adapter

Check out the "Buddy Box" on Camping World's web site. Probably available elsewhere as well
__________________
2012 Eagle 314BDS
2013 Dodge Ram 2500, Cummins 6.7 Turbo
:campfire:
Florida Camper is offline   Reply With Quote
Old 08-02-2013, 08:36 PM   #3
Senior Member
 
Join Date: Dec 2010
Location: North Idaho/Arizona
Posts: 5,446
I bet the 30 amp breakers are about shot from being used all the time and trip easily. I believe that half of the 50 amp service is only 25 amps. I don't think the 50 amp is a 240 V.
clutch is offline   Reply With Quote
Old 08-02-2013, 08:50 PM   #4
Member
 
Join Date: Jun 2011
Location: Central Ohio
Posts: 38
That'll work great! Thanks
__________________
2011 JayFlight G2 32BHDS
2003 GMC 3500HD Crew Cab Long Bed 6.6L Turbo, 100 gal auxiliary fuel tank, Brake Smart controller
1 DW, 3 kids, 2 large dogs, & assorted friends!
Chazinn is offline   Reply With Quote
Old 08-02-2013, 08:58 PM   #5
Member
 
Join Date: Jun 2011
Location: Central Ohio
Posts: 38
Quote:
Originally Posted by clutch View Post
I bet the 30 amp breakers are about shot from being used all the time and trip easily. I believe that half of the 50 amp service is only 25 amps. I don't think the 50 amp is a 240 V.
I'm pretty sure that there are 2 legs on a 50 rv service. That would mean 240 volts at 50 amps is available, or 100 amps of 120 volts.
__________________
2011 JayFlight G2 32BHDS
2003 GMC 3500HD Crew Cab Long Bed 6.6L Turbo, 100 gal auxiliary fuel tank, Brake Smart controller
1 DW, 3 kids, 2 large dogs, & assorted friends!
Chazinn is offline   Reply With Quote
Old 08-03-2013, 04:47 AM   #6
Senior Member
 
RoyBraddy's Avatar
 
Join Date: Sep 2011
Location: King George
Posts: 2,761
This is a drawing of the 50A-30A standard dogbone adapter which you can see only is connected to one HOT leg of the 50A service. Having the correct wiring you could use two 30A circuits from one connection. Of course my question is where are going to park the second 30A RV trailer. I have also heard alot of camp grounds are policing the use of the split cable adapters... Some are not safe to use I guess...

This is a RV50A MALE to RV30A FEMALE dogbone adapter drawing from DMBRUSS.


I do this all the time at camp ground location with my 30A trailer setup. The first thing I do is look at the condition of the Pedestal 30A Service receptacle and if it shows any signs of burned contacts etc i will use my RV50A-30A dogbone adapter and hook up to the 50A service if available.

The only drawback is the 30A Shore Power Cable will most likely have a 120VAC 50A source present on it at all times even when a 30A circuit trip has occurred in the 30A Trailer. These 30A trailer overloads will probably NOT ever trip the Camp Ground Pedestal 50A service circuit breaker. Lots of recent posts on RV NET Forum on this subject as being SAFE to do or not.

Just my 2-cents
Roy Ken
__________________
Roy and Carolyn
I claim Horse Creek Country in Southern Ill - Momabear is from North Texas
We live in King George VA
RETIRED DOD DOAF DON CONTRACTOR Electronics Tech 42YRS

"We're burning daylight" - John Wayne
2008 STARCRAFT 14RT OFF-ROAD POPUP with PD9260C and three 85AH 12VDC batteries
2010 F150 FX4 5.4 GAS with 3.73 gears - Super Cab - Towing Package - 2KW Honda EU2000i Gen
K9PHT (since 1957) 146.52Mhz
"We always have a PLAN B"
RoyBraddy is offline   Reply With Quote
Old 08-03-2013, 05:39 AM   #7
Senior Member
 
tnchuck100's Avatar
 
Join Date: Jun 2012
Location: Sparta, TN
Posts: 1,174
There should be no safety issue here. The breakers in the pedestal are not there for your protection. They are there to protect the campground equipment. The breakers in your RV are for your protection. If you have a fault or load in your RV that exceeds 30 amps the RV breaker will trip. This removes all 120V electric power in the RV. The only thing that would cause the 50 amp pedestal breaker to trip would be a fault in the RV cable up to the point it connects to the main RV breaker. The likelyhood of anyone coming in contact with the wiring connections between the cable and the RV breaker is less than that of winning the lottery 3 months in a row. There is no compromise in safety.
__________________
Chuck - Sparta, TN
2012 Jay Flight 22FB, 2 x Honda EU2000i
2013 GMC Yukon XL Denali AWD

EDUCATION is what you get when you read the fine print.....
EXPERIENCE is what you get when you don't.
tnchuck100 is offline   Reply With Quote
Old 08-03-2013, 05:57 AM   #8
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,081
Quote:
Originally Posted by Chazinn View Post
I'm pretty sure that there are 2 legs on a 50 rv service. That would mean 240 volts at 50 amps is available, or 100 amps of 120 volts.
It's still only 50 amps. Each 110 volt leg is protected by a 50 amp breaker the current rating doesn't double.
__________________
DISNEY LOVERS
Grumpy is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 12:04 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.