Old 05-24-2016, 02:30 PM   #21
Senior Member
 
Join Date: Apr 2011
Location: AZ, SSA (Squabbling States of America)
Posts: 1,432
Quote:
Originally Posted by Jopopsy View Post
So YOU run: Post --> Cord --> Surge --> Autoformer --> EMS --> Cord --> Coach?
That's the way I would do it. Autoformers have their own surge/spike protection but, at best it is minimal. Replacing or repairing an autoformer is far more expensive than replacing a surge/spike arrestor so I makes good sense to put a sacrificial arrestor ahead of the autoformer.

The autoformer needs to be ahead of the EMS. Otherwise, the EMS would shut off the power before the autoformer would get a chance to boost low voltage. Since voltage can still goo too high or dip too low, even with an autoformer in the circuit, the EMS still needed for backup for over or under voltage protection.
__________________
Jeannie
Lady Fitzgerald is offline   Reply With Quote
Old 05-24-2016, 03:30 PM   #22
Senior Member
 
House of Harview's Avatar
 
Join Date: Apr 2016
Location: La La Land
Posts: 102
I'm good with Jeff's, Lady Fitzgerald's and Jopopsy's input in this matter and will not rule out opting for the Hugh's unit as part of my electrical protection regiment.
__________________
2017 Octane T32C TH (on order as of 04/08/2016)
TV: 2004 Dodge 2500 QC SB 4X4 CTD w/Timbrens
2007 John Deere Gator 850D Diesel UTV w/Cab
(2) Yamaha EF2000is Inverter Generators
House of Harview is offline   Reply With Quote
Old 05-24-2016, 04:33 PM   #23
Senior Member
 
Join Date: Jun 2015
Location: --
Posts: 2,392
Ah well, what's another $100 bucks in this incredibly expensive hobby right? The rig is certainly more than $100 bucks.

Post --> PI Surge --> 25' Cord --> Autoformer chained to my rear axle under coach --> ~12' Cord --> PI EMS (in electrical bay) --> Coach.
__________________
2023 Ford F-150 XLT SCREW 3.5EB (Max Tow Pkg., Black Appearance Pkg., Bed Utility Pkg.)
1727 Payload / 4150 RAWR

On the sidelines taking it all in.


Jopopsy is offline   Reply With Quote
Old 05-24-2016, 05:15 PM   #24
Senior Member
 
Join Date: Apr 2013
Location: Wauconda, IL
Posts: 113
Autoformer, EMS, Proper Order, Weather Protection

That setup will serve you well...
Attached is a pic of part of my setup. This is along the back wall of my storage area.




Sent from my iPhone using Tapatalk
__________________
Jeff, Julie, Cameron, & Taylor

2012 F-250 FX4 6.7 Powerstroke Diesel Lariat
2011 Jayco 365BHS 5'er

"Cram-A-Lot Inn"

J.Lockhart is offline   Reply With Quote
Old 05-24-2016, 05:24 PM   #25
Senior Member
 
Cosmik Debris's Avatar
 
Join Date: Aug 2013
Location: Missoula, Montana
Posts: 704
Boy do I feel educated now. My Progressive unit just shuts down when out of parameter power exists, and did have this happen once when wanting air conditioning in California, at my in laws house. I used my generator.
The EMS saw low voltage from his garage and shutdown. Now I know what would prevent that, but like I said, only that one time and I solved the problem by pouring fuel to my Honda.
Seems to not be a boring thread anymore, plenty of interest.
__________________
"I might be movin' to Montana soon..."

2020 Outdoors RV Glacier Peak Titanium
2013 Eagle 29.5RKS (traded in)
2013 Ford 6.7L diesel F350
Cosmik Debris is offline   Reply With Quote
Old 05-24-2016, 10:09 PM   #26
Senior Member
 
Join Date: Apr 2016
Location: new england
Posts: 110
Thanks for asking, i have both the auto transformer, and a ems unit.
The reason i went with the autoformer was because of low voltage in the parks. I also had to disconnect from the park power and fire up the generator for a/c cooling power.
So it seems the order is:
1. park power
2. ems
3. autoformer
4. power cord into the camper.
trashman is offline   Reply With Quote
Old 05-24-2016, 10:17 PM   #27
Senior Member
 
Join Date: Apr 2011
Location: AZ, SSA (Squabbling States of America)
Posts: 1,432
Quote:
Originally Posted by trashman View Post
Thanks for asking, i have both the auto transformer, and a ems unit.
The reason i went with the autoformer was because of low voltage in the parks. I also had to disconnect from the park power and fire up the generator for a/c cooling power.
So it seems the order is:
1. park power
2. ems
3. autoformer
4. power cord into the camper.
The way you want to connect them, the autoformer will never get a chance to boost low voltage because the EMS will shut the power off before it ever gets to the autoformer. You have to have the autoformer before the EMS. Since autoformers have only limited surge and spike protection, it is also a good idea to put additional surge and spike arrestor (NOT an EMS) before the autoformer since it is far less expensive to replace a blown arrestor than a blown autoformer.
__________________
Jeannie
Lady Fitzgerald is offline   Reply With Quote
Old 08-11-2017, 01:23 PM   #28
Senior Member
 
blujay40's Avatar
 
Join Date: May 2015
Location: Michigan
Posts: 940
An older thread but wanted to acknowledge those that contributed by bumping it.

I received the third "piece to the puzzle" today when my Hughes Autoformer arrived. I already had a PI surge protector that was an emergency backup to my portable EMS as well as a 25' extension cord so the autoformer was the only missing piece.

Sadly, I don't think I have sufficient room in our TT to install both a hard wired EMS and the autoformer inside, but will be investigating that shortly and will at least get a hardwired EMS installed to limit what is underneath and make things a little less noticeable.

So thanks to everyone for their comments, ideas and suggestions in this thread. Made my implementation a lot easier and my life a lot less stressful because I have a game plan that should work out just fine for now, but more importantly, no longer have to worry about the EMS cutting power to the RV due to low voltages during the times the DW is watching or recording her soaps!
__________________
2018 GMC Sierra 3500HD Denali 4WD LB SRW 6.6L Duramax
2017 Jayco Eagle 330RSTS
blujay40 is offline   Reply With Quote
Old 08-11-2017, 01:41 PM   #29
Senior Member
 
Join Date: Jun 2015
Location: --
Posts: 2,392
Happy to have helped !
__________________
2023 Ford F-150 XLT SCREW 3.5EB (Max Tow Pkg., Black Appearance Pkg., Bed Utility Pkg.)
1727 Payload / 4150 RAWR

On the sidelines taking it all in.


Jopopsy is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 09:05 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.