So YOU run: Post --> Cord --> Surge --> Autoformer --> EMS --> Cord --> Coach?
|
That's the way I would do it. Autoformers have their own surge/spike protection but, at best it is minimal. Replacing or repairing an autoformer is far more expensive than replacing a surge/spike arrestor so I makes good sense to put a sacrificial arrestor ahead of the autoformer.
The autoformer needs to be ahead of the EMS. Otherwise, the EMS would shut off the power before the autoformer would get a chance to boost low voltage. Since voltage can still goo too high or dip too low, even with an autoformer in the circuit, the EMS still needed for backup for over or under voltage protection.
__________________
Jeannie
|
|
|
05-24-2016, 03:30 PM
|
#22
|
Senior Member
Join Date: Apr 2016
Location: La La Land
Posts: 102
|
I'm good with Jeff's, Lady Fitzgerald's and Jopopsy's input in this matter and will not rule out opting for the Hugh's unit as part of my electrical protection regiment.
__________________
2017 Octane T32C TH (on order as of 04/08/2016)
TV: 2004 Dodge 2500 QC SB 4X4 CTD w/Timbrens
2007 John Deere Gator 850D Diesel UTV w/Cab
(2) Yamaha EF2000is Inverter Generators
|
|
|
05-24-2016, 04:33 PM
|
#23
|
Senior Member
Join Date: Jun 2015
Location: --
Posts: 2,392
|
Ah well, what's another $100 bucks in this incredibly expensive hobby right? The rig is certainly more than $100 bucks.
Post --> PI Surge --> 25' Cord --> Autoformer chained to my rear axle under coach --> ~12' Cord --> PI EMS (in electrical bay) --> Coach.
__________________
2023 Ford F-150 XLT SCREW 3.5EB (Max Tow Pkg., Black Appearance Pkg., Bed Utility Pkg.)
1727 Payload / 4150 RAWR
On the sidelines taking it all in.
|
|
|
05-24-2016, 05:15 PM
|
#24
|
Senior Member
Join Date: Apr 2013
Location: Wauconda, IL
Posts: 113
|
Autoformer, EMS, Proper Order, Weather Protection
That setup will serve you well...
Attached is a pic of part of my setup. This is along the back wall of my storage area.
Sent from my iPhone using Tapatalk
__________________
Jeff, Julie, Cameron, & Taylor
2012 F-250 FX4 6.7 Powerstroke Diesel Lariat
2011 Jayco 365BHS 5'er
"Cram-A-Lot Inn"
|
|
|
05-24-2016, 05:24 PM
|
#25
|
Senior Member
Join Date: Aug 2013
Location: Missoula, Montana
Posts: 704
|
Boy do I feel educated now. My Progressive unit just shuts down when out of parameter power exists, and did have this happen once when wanting air conditioning in California, at my in laws house. I used my generator.
The EMS saw low voltage from his garage and shutdown. Now I know what would prevent that, but like I said, only that one time and I solved the problem by pouring fuel to my Honda.
Seems to not be a boring thread anymore, plenty of interest.
__________________
"I might be movin' to Montana soon..."
2020 Outdoors RV Glacier Peak Titanium
2013 Eagle 29.5RKS (traded in)
2013 Ford 6.7L diesel F350
|
|
|
05-24-2016, 10:09 PM
|
#26
|
Senior Member
Join Date: Apr 2016
Location: new england
Posts: 110
|
Thanks for asking, i have both the auto transformer, and a ems unit.
The reason i went with the autoformer was because of low voltage in the parks. I also had to disconnect from the park power and fire up the generator for a/c cooling power.
So it seems the order is:
1. park power
2. ems
3. autoformer
4. power cord into the camper.
|
|
|
05-24-2016, 10:17 PM
|
#27
|
Senior Member
Join Date: Apr 2011
Location: AZ, SSA (Squabbling States of America)
Posts: 1,432
|
Quote:
Originally Posted by trashman
Thanks for asking, i have both the auto transformer, and a ems unit.
The reason i went with the autoformer was because of low voltage in the parks. I also had to disconnect from the park power and fire up the generator for a/c cooling power.
So it seems the order is:
1. park power
2. ems
3. autoformer
4. power cord into the camper.
|
The way you want to connect them, the autoformer will never get a chance to boost low voltage because the EMS will shut the power off before it ever gets to the autoformer. You have to have the autoformer before the EMS. Since autoformers have only limited surge and spike protection, it is also a good idea to put additional surge and spike arrestor (NOT an EMS) before the autoformer since it is far less expensive to replace a blown arrestor than a blown autoformer.
__________________
Jeannie
|
|
|
08-11-2017, 01:23 PM
|
#28
|
Senior Member
Join Date: May 2015
Location: Michigan
Posts: 940
|
An older thread but wanted to acknowledge those that contributed by bumping it.
I received the third "piece to the puzzle" today when my Hughes Autoformer arrived. I already had a PI surge protector that was an emergency backup to my portable EMS as well as a 25' extension cord so the autoformer was the only missing piece.
Sadly, I don't think I have sufficient room in our TT to install both a hard wired EMS and the autoformer inside, but will be investigating that shortly and will at least get a hardwired EMS installed to limit what is underneath and make things a little less noticeable.
So thanks to everyone for their comments, ideas and suggestions in this thread. Made my implementation a lot easier and my life a lot less stressful because I have a game plan that should work out just fine for now, but more importantly, no longer have to worry about the EMS cutting power to the RV due to low voltages during the times the DW is watching or recording her soaps!
__________________
2018 GMC Sierra 3500HD Denali 4WD LB SRW 6.6L Duramax
2017 Jayco Eagle 330RSTS
|
|
|
08-11-2017, 01:41 PM
|
#29
|
Senior Member
Join Date: Jun 2015
Location: --
Posts: 2,392
|
Happy to have helped !
__________________
2023 Ford F-150 XLT SCREW 3.5EB (Max Tow Pkg., Black Appearance Pkg., Bed Utility Pkg.)
1727 Payload / 4150 RAWR
On the sidelines taking it all in.
|
|
|
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Threads |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|