07-07-2013, 09:15 AM
|
#1
|
Senior Member
Join Date: Jan 2013
Location: Elkin
Posts: 3,905
|
Electrical problem confirmation
So I've spent the better part of the morning searching topics and reading answers here on our wonderful forum and I believe I've found the answer but I wanted to get y'all's opinions and confirmation of my suspicions and/or corrections.
On our last two outings, we've been kicking the main breaker on the CG pedestal. I first noticed it 2 trips ago with the AC running and I turned on the water heater (electric). Didn't take it long at all and the main breaker tripped. Didn't think much of it and was in a hurry, so I just switched the heater to LP and went on about my business. On our most recent trip it did it again when I tried to turn the water heater on electric. Breaker tripped almost immediately, and again the AC was running. Reset breaker and tried again. As you can guess, tripped again. Set heater to LP and reset breaker.
Somewhat later in the day, DW was preparing goodies for the kiddos and using the microwave. There goes the power AGAIN. Back to the pedestal to reset. This time I took a little more time to investigate and noticed that there was a "warm" smell around the pedestal area. Felt the plug in and noticed that the plug itself was warm to the touch as well as several inches down the wire seemed to be warmer than it should be. 8 inches from the plug the wire was cool and felt as it should (at least as I guess it should feel). Turned off the pedestal breaker, unplugged, and examined the plug in. Blades were somewhat discolored and the plug appears to be slightly deformed like it was overheating and melting ever so little.
I am assuming that I need to replace the plug and/or the entire cord and that should fix my woes. Or could it also be a problem with the water heater as well? I know that I can't expect to run everything in the camper with the AC running but I should at least be able to run the AC and keep the water heater on, right?
__________________
'18 Jay Flight 33RBTS
'02 F250 Crew Cab 7.3 Powerstroke
|
|
|
07-07-2013, 09:54 AM
|
#2
|
Senior Member
Join Date: Jun 2012
Posts: 626
|
We never had problems running the electric water heater and the A/C together but not the microwave and A/C or the microwave with hair dryer
|
|
|
07-07-2013, 02:43 PM
|
#3
|
Senior Member
Join Date: Feb 2011
Location: SW Ontario
Posts: 1,393
|
If the blades on your plug are only discolored a bit, you can use sand paper to clean them up, as good as new.
A poor connection at the plug-receptacle interface can cause some of the problems you described. You can control the condition of your plug, but the receptacle state-of-repair is the responsibility of the CG. I've been at one or two CG where the receptacle really should have been replaced. We just limited our current draw at those places. A pain yes, but at least I didn't burn up my plug.
__________________
2013 Jayco Eagle 31.5RLDS
2018 Silverado 2500 HD Duramax
|
|
|
07-07-2013, 03:20 PM
|
#4
|
Senior Member
Join Date: Jun 2010
Location: Saskatoon Sask Canada
Posts: 10,726
|
Your dealing with 30 amps... A/C+waterheater or A/C+microwave PLUS the converter running is taking you over the 30A Some breakers are "touchier" than others and pop quicker.
__________________
Seann
2004 Chev Silverado Duramax optioned past the max. 2009 Jayco Eagle 308 RLS 900watts of solar, Lithium batteries (400amp hour), 2000 watt (4000 surge) whole house inverter.
145days /2023 2022/151 2021[/COLOR]
93/2020,157/2019219/2018 206/2017,215/2016, 211/2015, 196/14, 247/13, 193/12
|
|
|
07-07-2013, 04:09 PM
|
#5
|
Junior Member
Join Date: Jun 2013
Location: Tennessee
Posts: 15
|
I would check my water heater element. It's possible that the element is going bad, or already is. If the element is burned into the current can rise. Sanding the plug leads is a good idea, but you may have to eventually change it.
|
|
|
07-07-2013, 07:55 PM
|
#6
|
Member
Join Date: Feb 2012
Location: Southern NY
Posts: 77
|
Are you using a 30 amp receptacle??
__________________
Dan in NY
2016 Jayco x213
2012 Toyota Tundra
|
|
|
07-07-2013, 08:35 PM
|
#7
|
Senior Member
Join Date: Jan 2013
Location: Elkin
Posts: 3,905
|
Re: Electrical problem confirmation
Quote:
Originally Posted by Bruce and Becky
I would check my water heater element. It's possible that the element is going bad, or already is. If the element is burned into the current can rise. Sanding the plug leads is a good idea, but you may have to eventually change it.
|
Thanks for the tip. I'll check the element the first chance I get.
Quote:
Originally Posted by Mainenebula
Are you using a 30 amp receptacle??
|
And yes, it is a 30 amp plug.
__________________
'18 Jay Flight 33RBTS
'02 F250 Crew Cab 7.3 Powerstroke
|
|
|
07-07-2013, 08:39 PM
|
#8
|
Senior Member
Join Date: May 2012
Location: Boston
Posts: 664
|
I have heard about this and experienced it ourselves last week. It is a poor connection at the pedestal. Because the 30 amp plug are used more frequently, they become worn and give you a poor connection. We showed our plug to a friend (electrician) and he confirmed that poor connection was indeed the problem. A way around is to buy a 50 amp to 30 amp dog bone connector and you can plug into the 50 amp side which are used less frequently and typically less worn.
(example): http://www.amazon.com/Voltec-16-0050...+amp+to+30+amp
__________________
2013 White Hawk 28 DSBH
2011 Jay Feather X23J (traded-in)
2011 Ford F-150 XLT w/towing package
RoadMaster Active Suspension
Reese Trunnion Bar WDH w/Dual Cam sway control
|
|
|
07-08-2013, 04:40 AM
|
#9
|
Senior Member
Join Date: Jun 2012
Location: Sparta, TN
Posts: 1,174
|
FWIW, I have started using a fiber emery board (used for fingernails) and slide it into the receptacle a couple of times to clean those contacts before plugging in. If the 30 amp receptacle is very loose I use a 50 to 30 amp dog bone and use the 50 amp receptacle.
__________________
Chuck - Sparta, TN
2012 Jay Flight 22FB, 2 x Honda EU2000i
2013 GMC Yukon XL Denali AWD
EDUCATION is what you get when you read the fine print.....
EXPERIENCE is what you get when you don't.
|
|
|
07-08-2013, 05:53 AM
|
#10
|
Senior Member
Join Date: Sep 2011
Location: King George
Posts: 2,761
|
X2 on the wife's emery board. I have several of those in my RV tool box...
This is a worse case photo of the 30AMP plug which most likely started out just getting warm like you have found...
I always inspect the 30AMP Receptacle at each camp ground pedestal before plugging into them. As stated by others they get used big time at the camp grounds and will start making "loose" connection to your shore power cable. I have thought about getting a RV50A to 30AMP dogbone adapter so that I can use the 50AMP receptacle at the camp grounds. These of course are not available at alot of camp grounds we tend to go to but are usually found to be in excellent condition as I guess most users are still plugging into the 30AMP receptacles...
Also as stated by others here your high current appliances add up to more than 30AMPs which makes you keep it in the back of your mind to try not use these high current appliances at the same time.
The heavy duty 120VAC roll around vacuum usually does us in hehe... I have also tripped the breaker using the portable 120VAC OiL FILLED radiator looking type portable heaters as well. More recently we have started running a separate HD extension cord from the camp ground 20A Service at the camp ground pedestal. This is on its own circuit breaker at the pedestal and will not trip the 30AMP breaker. You might want to consider doing this as well for you portable high current items you may want to use like the vacuum, extra heaters, hair dryer, etc...
just some of my thoughts
Roy Ken
__________________
Roy and Carolyn
I claim Horse Creek Country in Southern Ill - Momabear is from North Texas
We live in King George VA
RETIRED DOD DOAF DON CONTRACTOR Electronics Tech 42YRS
"We're burning daylight" - John Wayne
2008 STARCRAFT 14RT OFF-ROAD POPUP with PD9260C and three 85AH 12VDC batteries
2010 F150 FX4 5.4 GAS with 3.73 gears - Super Cab - Towing Package - 2KW Honda EU2000i Gen
K9PHT (since 1957) 146.52Mhz
"We always have a PLAN B"
|
|
|
08-06-2015, 10:09 AM
|
#11
|
Senior Member
Join Date: Apr 2014
Location: Bella Vista, Arkansas
Posts: 171
|
RoyBraddy, that's exactly what mine looked like after a week of hot camping. Can I leave it as is and still use it? I do have dogbone, never new why it came with the camper other than if a 30 amp isn't available.
__________________
2007 29 BHS
1999 F250, RIFFRAF NAPA AIR INTAKE, MBRP 4"EXHAUST, TS6 CHIP
|
|
|
08-06-2015, 10:33 AM
|
#12
|
Senior Member
Join Date: Jan 2014
Location: Bremerton
Posts: 342
|
Quote:
Originally Posted by jdorant
|
I had the same problem, but did just the opposite to solve the problem.
my AC, electric frig, and elect WH caused the 30a pedestal bkr to trip. Due to the heat, I left the AC on, but shifted the frig and WH to gas. Later I shifted the frig back to AC, and the pedestal bkr tripped again.
I knew from my home shore power that 20a is sufficient to run the ac and the frig. Since I had a 30a to 20a dogbone and the pedestal 20a bkr was in better condition, I finished out the rest of the trip on 20a without incident. I kept the wh on gas, since the recovery is quicker.
reading all these comments, I realize that the pedestal 30a bkr was probably worn out.
|
|
|
08-06-2015, 11:24 AM
|
#13
|
Senior Member
Join Date: Apr 2014
Location: Bella Vista, Arkansas
Posts: 171
|
WOW, have you all read the post on "extending the power cord all the way out". They have a lot of concerns about using a 50 amp to 30 amp dogbone.
__________________
2007 29 BHS
1999 F250, RIFFRAF NAPA AIR INTAKE, MBRP 4"EXHAUST, TS6 CHIP
|
|
|
08-06-2015, 11:54 AM
|
#14
|
Senior Member
Join Date: Aug 2011
Location: Missouri City, The Republic of Texas
Posts: 5,063
|
Quote:
Originally Posted by Polk
WOW, have you all read the post on "extending the power cord all the way out". They have a lot of concerns about using a 50 amp to 30 amp dogbone.
|
I was a frantic reader (and I still am) of this forum prior to our first purchase and read a thread or two about pulling the cord out fully and developed that habit from day one. Most problems I have read about with regard to the power adapters are around the use of the little "brick" connectors, a "chunk" of plastic with 30 or 50A prongs on one side and 15 or 30A prongs on the other side. I've not read much at all about problems with dogbone adapters. Both "starter" kits I've gotten have included a brick adapter and I've never used one but I've always had a dogbone and use that when needed.
__________________
Cheers,
T_
2013 F-350 CC SB 2WD 6.7PS
2013 Eagle Premier 351 RLTS
-SOLD- 2012 X23B
-SOLD- 2003 Ford Expedition 5.4, Bilstein shocks
|
|
|
|