Furnace Intermitant Burn

2015 Jayflight 32TSBH
The furnace comes on an lights as normal but will only burn for 30 seconds at most. The burner will then cut off and the fan stays running. The burner will then reignite and go through the same cycle. The camper is being heated it just takes a long time. Shouldn't the burner stay lit the entire time?
Longhorn1998 is offline   Reply With Quote
Old 03-20-2016, 07:26 AM   #2
Senior Member
 
Join Date: Apr 2015
Location: Elizabethtown, PA
Posts: 1,560
What temp do you have the T/Stat set for
__________________
2004 Jay Feather 25E
2001 Ford Expedition 4X4 EB 5.4 3.55 rear
2004 Ford Expedition 4X4 EB 5.4 3.73 rear
bedrck46 is offline   Reply With Quote
Old 03-20-2016, 07:28 AM   #3
Senior Member
 
ALJO's Avatar
 
Join Date: Oct 2014
Location: Sparwood, BC
Posts: 2,800
Send a message via Skype™ to ALJO
Check for a flattened hose or blocking there seems not to be enough airflow.
Also check for blocking of the return air.
__________________
2014 Ram 1500 CrewCab 4x4 5.7 Hemi 3.92 Rear and Air Lift 1000
2005 Jayco Jay Feather LGT - 29Y GVWR-7000 lbs.
Dexter Axle Lift 4-9/16" - installed with sub-frame.
Pro Series 1200 lbs. WDH with Double Sway Bar.
Champion 3100/2800 watt Inverter/Generator-Onboard Solar Power
ALJO is offline   Reply With Quote
Old 03-20-2016, 07:42 AM   #4
Senior Member
 
Join Date: Feb 2012
Posts: 550
You should check for a blockage in the exhaust airflow. I had the same issue with mine, I brought it in and their was a part of the tube that had collapsed.
slabat is offline   Reply With Quote
Old 03-20-2016, 08:19 AM   #5
Senior Member
 
oldmanAZ's Avatar
 
Join Date: Dec 2014
Location: FL
Posts: 11,281
Quote:
Originally Posted by Longhorn1998 View Post
2015 Jayflight 32TSBH
The furnace comes on an lights as normal but will only burn for 30 seconds at most. The burner will then cut off and the fan stays running. The burner will then reignite and go through the same cycle. The camper is being heated it just takes a long time. Shouldn't the burner stay lit the entire time?
Welcome to the JOF.

Is this the first time you've used the furnace?

Of course, if it's still under warranty, you should have the dealer check it out.
__________________
Sherm & Terry w/rescue Eydie (min Schnauzer) & Charley (std Poodle)
SOLD:2015 Jay Flight 27RLS, GY Endurance (E), Days: 102 '15, 90 '16, 80 '17, 161 '18, 365+ '20
SOLD: 2006 Ford F350 PSD, 4WD, CC, LB, SRW, Camper pkg., 375,000mi
Full timing: Some will think you're crazy, some will be envious, just enjoy the freedom!
oldmanAZ is offline   Reply With Quote
Old 03-20-2016, 08:23 AM   #6
Senior Member
 
Join Date: May 2011
Location: Columbus Ohio
Posts: 148
It could be a bad thermostat, turn it to 90 and see if it stays on, & also said check the duct work.

Buckeyejim
Columbus OH
buckeyejim is offline   Reply With Quote
Old 03-20-2016, 09:12 AM   #7
Senior Member
 
ROC-REQS's Avatar
 
Join Date: May 2014
Location: WNY
Posts: 458
Hi Longhorn,

Welcome to the JOF

Quote:
Originally Posted by Longhorn1998 View Post
2015 Shouldn't the burner stay lit the entire time?
The blower will run for 15 seconds before the furnace burn is ignited.
Then once the burner turns off, the blower will continue to run for 1min 30sec.
This is standard operation of the furnace.
So the normal sequence for a furnace from turn on to turn off is:
Furance turns on.
15 sec - Blower only
xx time - Burner & Blower
1min 30sec - Blower only
Furnace turns off.

I'm having a similar problem with our furnace - see this post if you're interested: http://www.jaycoowners.com/forums/f3...urn-31600.html

If you have access to your furnace and can see the control board there's an diagnostic LED on the board that may give you some indications if your problem is due to the furnace issue.
How often the LED flashes is associated with an error code:
Single Flash = Sail Switch is bad
2 Flashes = Bad Electrode
3 Flashes = Bad Circuit Board
We got this info from an Atwood tech when trying to isolate the cause of our furnace problem.

Does the furnace shoot off completely (i.e., bower off)?
How long is the furnace off before it starts again.

Do you have a digital or analog (i.e., slide) T-Stat?
A Digital will give you ~+/- 2 Degree swing.
An Analog will give you ~+/- 6 Degree swing
Between controlling the furnace on & off.

Have you set a house thermometer near the T-Stat to see what temp reading it gives?

Where is the T-Stat located? Could it be getting any drafts around it or from inside the wall?

Maybe cover up the T-Stat with a clear Tupperware container to block any airflow and see if the burn time is the same.

Hope this is of some help.
Good luck
__________________
2015 Jayco Eagle Premier 361REQS
2014 GMC Sierra 3500HD 4x4 CC D/A
ROC-REQS is offline   Reply With Quote
Old 03-20-2016, 10:36 AM   #8
Junior Member
 
Join Date: Mar 2016
Location: Pearland
Posts: 28
Thanks for all the replies. I've tried setting the tstat at 90. That didn't change anything. I'll try the other suggestions and report back.
Longhorn1998 is offline   Reply With Quote
Old 04-09-2016, 08:41 AM   #9
Member
 
Join Date: Mar 2016
Location: Douglasville
Posts: 57
My furnace had water on the board. Dealer replaced board. The furnace acted very similar to yours.
edfgrf is offline   Reply With Quote
Reply

Tags
atwood, furnace

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 04:05 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.