Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
Jayco RV Owners Forum
 


Reply
 
Thread Tools Search this Thread Display Modes
 
Old 04-26-2011, 02:14 PM   #1
Junior Member
 
Join Date: Apr 2011
Posts: 2
Electrical Fire WARNING

We have a 2004 JAYCO Legacy. Last week we awoke to the smell of burning insulation. The fire alarm did NOT go off. I located the smell at the hot water heater and when I moved the blue cable, sparks flew. I imeadiately turned off the electric switch and circuit breaker. The circuit breaker did NOT trip. To investigate the problem I removed the black plastic cover, with dificulty, to see what had happened. The electrical wires were balled up together, one wire nut had completely burned up, 6 inches of the 115V white wire burned up, and BOTH of the screws on the electric heating element were so loose that the wires fell off. The difficulty I had with removing the box was due to the ground wire to the thermal switch being only 3 inches long. I have no idea how JAYCO got this hooked up. I ohmed the element and switch. They checked good, so after cleaning up, extending wires, and electrical taping wire nuts, I reinstalled. Everything works fine.

There is some controversy on taping wire nuts. On my rv.net post some said yes & some no. One person said it was a RVIA requirement to tape wire nuts, but I could not confirm. Non in my JAYCO are taped & I tape as I find them.

I notified JAYCO of the problem and received no response.

I was concered about the circuit breaker and discovered that a regular circuit breaker may or may not trip. There are new circuit breakers that came out around 2000 that have a "Arc Fault" that takes care of the problem, but they are expensive. I was also concerned about the fire detector and learned that there are 2 types: 1. "Ionization" cheapest, and 2. "Photo Electric" best. JAYCO is cheapest and I am replacing.

I contacted the National Fire Prevention Association, NFPA, that regulates fire standards for RVs. They had an interesting RV Fire Report for 2003-2006. These are annual averages: 1,960 RV Fires, 22 Deaths, 58 Injuries, 13.7 Million Cost. Origination of fires: 15% refrigerator, 13% electrical distribution, 11% heating.

Be safe out there and I hope that this may help someone. At 68 I am too young to die in an RV fire.
navyjim is offline   Reply With Quote
Old 04-26-2011, 02:41 PM   #2
Senior Member
 
Join Date: Oct 2010
Posts: 414
Thanks for your warning...

Yes. I once see a fire at an electrical outlet where its upstream breaker did NOT flip. Its rare but can happen - even within a normal home running a 110/120V sump pump.

Your post reminds me that I "need" to buy a simple normal stick house 9V battery smoke detector. Then, install it within my Jayco - on its ceiling. Thus, having 1 factory smoke detector and one modernized (indpentant powered) smoke detector. Double the safety.

Not too sure if taping wire nuts are mandatory on TTs or automobiles. However... I think dipping each wire connector in some liquid electrical tape (re: http://ecx.images-amazon.com/images/...500_AA300_.gif ) while TT is traveling down its assembly line is a great idea. Thus, sealing its connection from natrual moisture and reducing the risk of its connector from un-screwing (from normal road bounce). Hope the higher authorizes read your warning and make liquid electrical tape mandatory. A simple $1 improvement could save many future lives.

Many thanks for sharing your electrical fire warning...

.
Spike99 is offline   Reply With Quote
Old 04-26-2011, 02:58 PM   #3
Moderator Emeritus
 
Rustic Eagle's Avatar
 
Join Date: Apr 2011
Location: Michigan
Posts: 9,424
Quote:
Originally Posted by navyjim View Post
snip........I was also concerned about the fire detector and learned that there are 2 types: 1. "Ionization" cheapest, and 2. "Photo Electric" best. JAYCO is cheapest and I am replacing.

I contacted the National Fire Prevention Association, NFPA, that regulates fire standards for RVs. They had an interesting RV Fire Report for 2003-2006. These are annual averages: 1,960 RV Fires, 22 Deaths, 58 Injuries, 13.7 Million Cost. Origination of fires: 15% refrigerator, 13% electrical distribution, 11% heating.

Be safe out there and I hope that this may help someone. At 68 I am too young to die in an RV fire.
Navyjim,

Sounds like you were very fortunate to catch it the way you did, and the RV fire statistics are alarming to say the least.

One thing for sure, looks like I'll be investing in another smoke detector!

Bob
__________________

2016 GM 2500HD 6.0L/4.10
2018 Jay Flight 24RBS
2002 GM 2500HD 6.0L/4:10 (retired)
2005 Jayco Eagle 278FBS (retired)
1999 Jayco Eagle 246FB (retired)
Reese HP Dual Cam (Strait-Line)
Rustic Eagle is offline   Reply With Quote
Old 08-05-2019, 01:56 PM   #4
Junior Member
 
Join Date: Aug 2017
Location: browndale pa
Posts: 28
wires burned

was out last weak camping with our 377rlbh when getting out of shower smelled electrical wires burning did some investigating and found same thing wires at water heater burnt found by black cover having burn hole and seeing orange glow from wires turned of breaker and repaired checked element was good just a bad connection wire nut completely burnt I would consider myself lucky because we were leaving to go out for day
roughing it is offline   Reply With Quote
Old 08-05-2019, 02:11 PM   #5
Senior Member
 
wags999's Avatar
 
Join Date: Jan 2015
Location: Surprise
Posts: 2,623
I stopped using wire nuts a few years back. Use the push in connectors. Much less prone to lessening than a wire nuts.
__________________
2011 Toyota Tundra double cab
2015 27RLS


wags999 is offline   Reply With Quote
Old 08-05-2019, 04:57 PM   #6
Lost in the Woods
 
Join Date: Apr 2019
Location: Ocean County
Posts: 2,807
One thing to realize with wire nuts, they are not there to CONNECT the wires, but just to COVER the wires.

The most important part is the mechanical connection of the wires. The wires need to be twisted well together and twisted tight. Then, the wire nut goes on, just to cover/insulate the connection.

Many people just place the wires side by side, then twist on the nut, thinking that's adequate. This is incorrect, and leads to loose connections.
RetiredOne is offline   Reply With Quote
Old 08-05-2019, 06:05 PM   #7
Senior Member
 
Witt74's Avatar
 
Join Date: Jul 2014
Location: Picayune
Posts: 1,970
Thumbs up

Quote:
Originally Posted by RetiredOne View Post
One thing to realize with wire nuts, they are not there to CONNECT the wires, but just to COVER the wires.

The most important part is the mechanical connection of the wires. The wires need to be twisted well together and twisted tight. Then, the wire nut goes on, just to cover/insulate the connection.

Many people just place the wires side by side, then twist on the nut, thinking that's adequate. This is incorrect, and leads to loose connections.

X2!!
__________________

Charlie & Lizzie the Mini Dachshunds
2008 Jayco Eagle Super Lite 30.5 RLS
2015 F350 Lariet Crew Cab Long Bed 6.7 Diesel B&W Companion Hitch
24 hours in a day, 24 beers in a case. Coincidence? I think not.
Witt74 is offline   Reply With Quote
Old 08-06-2019, 07:14 AM   #8
Senior Member
 
AKRUEBBE's Avatar
 
Join Date: Apr 2018
Location: Natalbany Creek Campground, Amite City, LA
Posts: 3,244
Quote:
Originally Posted by RetiredOne View Post
One thing to realize with wire nuts, they are not there to CONNECT the wires, but just to COVER the wires.The most important part is the mechanical connection of the wires. The wires need to be twisted well together and twisted tight. Then, the wire nut goes on, just to cover/insulate the connection.Many people just place the wires side by side, then twist on the nut, thinking that's adequate. This is incorrect, and leads to loose connections.
I think these are a great tool for using wire nuts. really gets them snug.

https://www.amazon.com/Rack-Tiers-72...gateway&sr=8-7
__________________
AL & JANET KRUEBBE
2019 PINNACLE 37RLWS
2018 NORTH POINT 315RLTS (TRADED)
2017 RAM 3500 DRW DIESEL/AISIN 4.10 AIR BAGS
B&W COMPANION TURN OVER BALL HITCH
Formerly from Sequim, WA
AKRUEBBE is offline   Reply With Quote
Old 08-06-2019, 10:28 AM   #9
Senior Member
 
Vicr's Avatar
 
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,862
Bad information on wirenuts posted here. Here are the instructions from Ideal on how to use wirenuts:


Wire-Nut®Wire Connector InstructionsWARNINGSHOCKHAZZARDContact withelectricity can cause electrical fires,seriousinjury or death.Shut off power tothecircuitor remove fusebefore using this product.SAFETY NOTICEImproperly installed electrical wiring can be dangerous and cause electrical fires. The connector chosen must be sized tothe wires being used. Consult local building codes before doing any electrical wire and to determine installationrequirements. For assistance, refer to aninstructionalbook forelectrical installations or consult a qualified electrician.To be sold only with installation instructions.Installation Instructions1.Turn off power before removing or installing connectors.2.Strip connectors to the correct strip length per the chart below:ConnectorStrip length71B®*Stripsolid wires ¼(6mm)Strip stranded wires 5/16”(8mm)72B®*Strip wires 3/8”(9.5 mm)Strip wires #16 and smaller ½”(13mm)73B®**Strip wires 5/16”(8mm)Strip wires #16 and smallerstrip 3/8”(9.5 mm)74B®**Strip wires 3/8”(9.5 mm)Strip #16 and smaller 7/16”(11mm)76B®**Strip wires#14 and larger 7/16”(11mm)Strip wires #16 and smaller½”(13mm)59B®**Strip wires 1/2"(13 mm)3.Straighten and align frayed strands.4.Hold wires together with ends even. Lead stranded wires slightly ahead of solid wires.5.Pre-twisting acceptable, but not required. For pre-twisting;strip wires long, hold wires togetherwith insulation even,twist wire ends together, trim to recommended strip length.6.Insert bundle into connector and twist clockwise until tight
Vicr is offline   Reply With Quote
Old 08-06-2019, 10:45 AM   #10
Senior Member
 
Vicr's Avatar
 
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,862
Again from 3M.3M Wire Connector Instructions.pdf
Vicr is offline   Reply With Quote
Old 08-06-2019, 12:13 PM   #11
Senior Member
 
wags999's Avatar
 
Join Date: Jan 2015
Location: Surprise
Posts: 2,623
Quote:
Originally Posted by RetiredOne View Post
One thing to realize with wire nuts, they are not there to CONNECT the wires, but just to COVER the wires.

The most important part is the mechanical connection of the wires. The wires need to be twisted well together and twisted tight. Then, the wire nut goes on, just to cover/insulate the connection.

Many people just place the wires side by side, then twist on the nut, thinking that's adequate. This is incorrect, and leads to loose connections.
https://www.bing.com/videos/search?q...il&FORM=VIREHT

Actually that is not correct. This is just one of many videos and articles on how to use wire nuts. And it's also how I was taught when I became an electrician. This is from the wire nut Mfg on how to correctly use wire nuts on solid and solid and stranded wires.

Good Luck..

I still like the wiring push blocks as it's much easier to wire multiple wires together and they rarely if ever vibrate loose.
__________________
2011 Toyota Tundra double cab
2015 27RLS


wags999 is offline   Reply With Quote
Old 08-06-2019, 12:51 PM   #12
Lost in the Woods
 
Join Date: Apr 2019
Location: Ocean County
Posts: 2,807
Quote:
Originally Posted by wags999 View Post

Actually that is not correct. This is just one of many videos and articles on how to use wire nuts. And it's also how I was taught when I became an electrician. This is from the wire nut Mfg on how to correctly use wire nuts on solid and solid and stranded wires.
Hmmm, did you notice the next video after yours by Ideal (wire nut manufacturer) says to pre-twist the wire before putting on the wire nut?

https://www.bing.com/videos/search?q...6&&FORM=VRDGAR
RetiredOne is offline   Reply With Quote
Old 08-06-2019, 01:03 PM   #13
Senior Member
 
Vicr's Avatar
 
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,862
You pre-twist the strands in stranded wire because when you strip stranded wire the strands straiten out and twisting solid wire is not a requirement because the wirenut is designed to twist the wires as you tighten the wirenut. You're trying to argue your point with two electricians. I don't know about Wags999 but I have personally or supervised the installation of over a million splices using wire nuts. I have also used the push-in connectors manufactured by Wago and have used other brands.
Vicr is offline   Reply With Quote
Old 08-06-2019, 01:07 PM   #14
Lost in the Woods
 
Join Date: Apr 2019
Location: Ocean County
Posts: 2,807
Your own post further up says "pre-twisting acceptable".

Quote:
Pre-twisting acceptable, but not required. For pre-twisting;strip wires long, hold wires togetherwith insulation even,twist wire ends together, trim to recommended strip length.6.Insert bundle into connector and twist clockwise until tight
RetiredOne is offline   Reply With Quote
Old 08-06-2019, 01:19 PM   #15
Senior Member
 
Vicr's Avatar
 
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,862
...but not required. Most resi guys will pre-twist solid wires but they seldom splice any thing larger than #12 AWG. On commercial projects we are using wirenuts to splice up to #6 AWG with wirenuts and other connectors. Just about no one on a commercial job will pre-twist wires. The point is wirenuts are designed, manufactured and UL approved to splice wires, not just to "cover up" a splice.
Vicr is offline   Reply With Quote
Old 08-06-2019, 01:34 PM   #16
Senior Member
 
wags999's Avatar
 
Join Date: Jan 2015
Location: Surprise
Posts: 2,623
Quote:
Originally Posted by Vicr View Post
...but not required. Most resi guys will pre-twist solid wires but they seldom splice any thing larger than #12 AWG. On commercial projects we are using wirenuts to splice up to #6 AWG with wirenuts and other connectors. Just about no one on a commercial job will pre-twist wires. The point is wirenuts are designed, manufactured and UL approved to splice wires, not just to "cover up" a splice.
X2
__________________
2011 Toyota Tundra double cab
2015 27RLS


wags999 is offline   Reply With Quote
Old 08-06-2019, 03:49 PM   #17
Lost in the Woods
 
Join Date: Apr 2019
Location: Ocean County
Posts: 2,807
Quote:
Originally Posted by Vicr View Post
...but not required.
Where did I say "required"?
RetiredOne is offline   Reply With Quote
Old 08-06-2019, 03:56 PM   #18
Senior Member
 
Vicr's Avatar
 
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,862
Pre-twisting acceptable, but not required. For pre-twisting;strip wires long, hold wires togetherwith insulation even,twist wire ends together, trim to recommended strip length.6.Insert bundle into connector and twist clockwise until tight




Quote:
Originally Posted by RetiredOne View Post
Where did I say "required"?

You didn't it was in the installation instructions.
Vicr is offline   Reply With Quote
Old 08-06-2019, 08:22 PM   #19
Senior Member
 
TnHiker's Avatar
 
Join Date: Nov 2017
Location: Athens
Posts: 239
In my 40 + years of electrical work, installation, and inspection I have never seen a properly sized and installed wire nut fail. The nut has to be correct for the wire size and it has to be installed correctly, if done correctly you're good to go. I only tape or recommend taping in a bad environment where corrosion is possible. I have owned 6 RV's and all of them had the scariest wiring you will ever find. The wiring in an RV would never pass in a residential, commercial, or industrial inspection. I have experience in all three area's. The first thing I do when I get an RV is inspect every inch of wiring that is accessible making corrections and upgrades as I go and pray for the wiring that I can't see. The best wiring and actually the best quality overall was the 98 HitchHiker I owned. I guess that's why they are out of business. We wouldn't pay for the details and cost of that quality. I always add extra smoke detectors in my campers. Mine has 3 detectors in it now. Good luck out there and be safe.
__________________
TnHiker
2018 Jayco Eagle HT 29.5 FBDS: GY Tire Upgrade, Sani-Con, 2 AC's, Tankless WH, Auto level, One Control, RV-CO Port-A-Step
2010 Jayco Eagle Super Lite 30.5 DBSA (Sold 2018)
1998 HitchHiker II 31 RLBG (Sold 2012)
2002 Ford F350 7.3L Turbo, Crew Cab, DRW, 4:10 (Mint, Garage Queen)
TnHiker is offline   Reply With Quote
Old 08-06-2019, 08:56 PM   #20
Senior Member
 
Cannon's Avatar
 
Join Date: Feb 2018
Location: Palmetto
Posts: 1,057
When I purchased mine I installed a hardwired 50A ems behind the main distribution panel. I found three loose wires from factory, one neutral that had not been tighten at all. I went in basement and removed wall and check one's that I could get to. While I had wall out I added smoke detector behind basement wall and then added another one in bedroom.
__________________
2017 Jayco 377rlbh (sold)
2021 Grand Design 351MR
Cannon is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 01:48 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.