Generator for running Air Conditioner Question

Here's my problem. To power my 15k BTU Coleman A/C, I want to buy an inverter generator (because they are quieter than the others) and I don't want to buy two smaller wattage ones that can be hooked up in parallel (like the 2000 watt Hondas can be). So, I'm looking closely at the Champion 3100. Although several have said that they run their 15K A/C with this generator, Coleman says that the start-up wattage requirement can be as high as 3900 watts. So, here's my electrical question. I can run my A/C with no problem on a 30 amp electrical plug at the RV parks that I've stayed in. Since the Champion generator has the 30 amp RV plug with a 30 amp breaker, it seems to me that if I don't throw a 30 amp breaker at an RV park when my A/C kicks on, then the Champion 3100 generator should handle the particular start-up wattage or amp requirements of my A/C. I realize that if my A/C required a full 3900 watts at start-up, then it would draw about 32 amps ( 3900 watts / 120 volts = 32.5 amps) and would throw a 30 amp breaker. But since I have no problem when plugged in to a 30 amp plug at a park, then it seems that I should have no problem with the 3100 Champion generator. What am I missing or looking at incorrectly? This is kind of a big deal since once you put gas and oil into the generator you can't return them.
tld is offline   Reply With Quote
Old 03-29-2016, 07:56 AM   #2
Senior Member
 
Camper_bob's Avatar
 
Join Date: Sep 2013
Location: South Texas
Posts: 7,216
I've often wondered if those who use generators consider installing a "hard start capacitor" in their AC unit. It's definitely something I will consider before I try to run my AC off a generator.

Robot Check

Here's an example. I don't know which model you would specifically need.

I wonder what the boondocking crowd has to say?
__________________

-2018 Greyhawk 29MV
-2020 Jeep Wrangler Unlimited (JLU) (Primary Toad)
-1994 Jeep Wrangler YJ (Secondary Toad)
-2014 Jay Flight 28BHBE & Ram 2500 6.4L CC 4x4 (sold)
Camper_bob is offline   Reply With Quote
Old 03-29-2016, 08:32 AM   #3
Senior Member
 
3'senough's Avatar
 
Join Date: Sep 2010
Location: New York
Posts: 2,210
I can run mine on the the Yamaha in my sig below without issues. It has a boost which might be the difference.

You do need to watch your other draws though.
__________________

2014 375 BHFS Eagle Premier
2014 Ram 3500 Longhorn DRW CC
6.7 CTD, Aisin, 4.10's
Yamaha EF3000iSEB
3'senough is offline   Reply With Quote
Old 03-29-2016, 10:26 AM   #4
Junior Member
 
Join Date: Aug 2015
Location: Chino Hills
Posts: 7
The Champion 3100 inverter generator starts and runs my Coleman 15K BTU air conditioner without issue.
RiverRunner is offline   Reply With Quote
Old 03-29-2016, 10:54 AM   #5
Senior Member
 
Edd505's Avatar
 
Join Date: Apr 2015
Location: Elephant Butte, NM
Posts: 1,219
Quote:
Originally Posted by Camper_bob View Post
I've often wondered if those who use generators consider installing a "hard start capacitor" in their AC unit. It's definitely something I will consider before I try to run my AC off a generator.

Robot Check

Here's an example. I don't know which model you would specifically need.

I wonder what the boondocking crowd has to say?
Not being and electrician how would you wire one? I know my hot tub has one on each motor.
__________________
2015 F350 SRW 6.7 LB 4X4 Crew
2017 Durango G353KRT
2006 F350SD 6.0 LB Crew
2000 F250SD SRW 7.3 LB Extended Cab Air Bags
2002 Western Star 4900EX 500 Detroit 13sp.
2014 Eagle 30.5BHLT (sold)
Edd505 is offline   Reply With Quote
Old 03-29-2016, 11:25 AM   #6
Senior Member
 
Join Date: Dec 2011
Location: Upperco, Md.
Posts: 807
I can run a 13.5 K AC as well as our 1100 watt microwave at the same time with our 3100 Champion. I can't believe that you could have an issue with starting a 15 k generator with that unit.
Ela1948 is offline   Reply With Quote
Old 03-29-2016, 12:35 PM   #7
Senior Member
 
Camper_bob's Avatar
 
Join Date: Sep 2013
Location: South Texas
Posts: 7,216
Quote:
Originally Posted by Edd505 View Post
Not being and electrician how would you wire one? I know my hot tub has one on each motor.
Here's a video. There are other writeups around the interwebz about how to do it.

https://youtu.be/oHgXGlYNYkQ

It actually doesn't look too bad. I get a little antsy around capacitors though; I would hate to have one discharge into me. That would make for a bad day.
__________________

-2018 Greyhawk 29MV
-2020 Jeep Wrangler Unlimited (JLU) (Primary Toad)
-1994 Jeep Wrangler YJ (Secondary Toad)
-2014 Jay Flight 28BHBE & Ram 2500 6.4L CC 4x4 (sold)
Camper_bob is offline   Reply With Quote
Old 03-29-2016, 01:13 PM   #8
Senior Member
 
Edd505's Avatar
 
Join Date: Apr 2015
Location: Elephant Butte, NM
Posts: 1,219
Thanks Bob, should have known to look to you tube. Looks really simple.
__________________
2015 F350 SRW 6.7 LB 4X4 Crew
2017 Durango G353KRT
2006 F350SD 6.0 LB Crew
2000 F250SD SRW 7.3 LB Extended Cab Air Bags
2002 Western Star 4900EX 500 Detroit 13sp.
2014 Eagle 30.5BHLT (sold)
Edd505 is offline   Reply With Quote
Old 03-29-2016, 04:28 PM   #9
Senior Member
 
Join Date: Oct 2015
Location: Milford
Posts: 629
I don't see where it would be a problem. I got a 15k on the New camper and am going to see if my Yamaha 2400 will run it. In doing some searching, I found quite a few that had done the same thing successfully.
__________________
2016 Jayco Eagle HT 29.5BHDS (ordered 12/30/15, delivered 3/8/16)
2015 F-350 crew cab, short bed, 6.7L PSD, Pullrite Superglide 3300 hitch
Cdash is offline   Reply With Quote
Old 03-29-2016, 06:12 PM   #10
Junior Member
 
Join Date: Feb 2016
Location: Voorheesville
Posts: 1
New generator

Quote:
Originally Posted by tld View Post
Here's my problem. To power my 15k BTU Coleman A/C, I want to buy an inverter generator (because they are quieter than the others) and I don't want to buy two smaller wattage ones that can be hooked up in parallel (like the 2000 watt Hondas can be). So, I'm looking closely at the Champion 3100. Although several have said that they run their 15K A/C with this generator, Coleman says that the start-up wattage requirement can be as high as 3900 watts. So, here's my electrical question. I can run my A/C with no problem on a 30 amp electrical plug at the RV parks that I've stayed in. Since the Champion generator has the 30 amp RV plug with a 30 amp breaker, it seems to me that if I don't throw a 30 amp breaker at an RV park when my A/C kicks on, then the Champion 3100 generator should handle the particular start-up wattage or amp requirements of my A/C. I realize that if my A/C required a full 3900 watts at start-up, then it would draw about 32 amps ( 3900 watts / 120 volts = 32.5 amps) and would throw a 30 amp breaker. But since I have no problem when plugged in to a 30 amp plug at a park, then it seems that I should have no problem with the 3100 Champion generator. What am I missing or looking at incorrectly? This is kind of a big deal since once you put gas and oil into the generator you can't return them.
Camping World just listed a new inverter generator champion 3500 with a remote
NY383 is offline   Reply With Quote
Old 03-29-2016, 08:15 PM   #11
Senior Member
 
Join Date: Dec 2015
Location: Houston
Posts: 781
Why are you against using two generators in parallel?

Any why would you not want to leave yourself some headroom?

A blow dryer, microwave, or the water heater would all individually probably put you in overload using a 3100 inverter generator while the A/C is on.

3100/120 = 25.8 amps max, not continuous. It takes 4000 watts in generators to get 30amps continuous. Remember, the generator names are not.
__________________
2016 Jayco Eagle 330RSTS = "Madame Maxime"
Maxxis M8008 E rated Tires and 16" Wheel Upgrade
Dual A/C 15K BTU, 14K Equalizer WD hitch with SC
King Bed with Java Interior, (2X) Yamaha EF2000isV2
2012 Ram 4500, 6.7L Cummins Turbo Diesel, MegaCab = "Hagrid"
8'x12' BMCM Stake Bed, Cabin Chassis, 2WD
360 degree Virtual Tour
Fairenatic is offline   Reply With Quote
Old 03-29-2016, 08:40 PM   #12
tld
Senior Member
 
Join Date: Nov 2015
Location: Manhattan ks
Posts: 153
Fairnatic, thanks for the response. In getting specs from generator manufactures, what I have discovered is that tying two 2000 watt generators together does not give you 4000 watts. It actually gives you about 3000 watts. So, since buying two 2000 watt generators (plus the parallel connecting kit) costs more than one 3100 watt generator, I continue to lean toward trying to see if the 3100 watt gen would work. I know that running "everything" on a 3100 is not even possible. Don't want to do that. I am only wanting to be able to run the A/C with everything else turned off - except for maybe a few LED light still on.
tld is offline   Reply With Quote
Old 03-29-2016, 09:08 PM   #13
Senior Member
 
Join Date: Dec 2015
Location: Houston
Posts: 781
Quote:
Originally Posted by tld View Post
Fairnatic, thanks for the response. In getting specs from generator manufactures, what I have discovered is that tying two 2000 watt generators together does not give you 4000 watts. It actually gives you about 3000 watts. So, since buying two 2000 watt generators (plus the parallel connecting kit) costs more than one 3100 watt generator, I continue to lean toward trying to see if the 3100 watt gen would work. I know that running "everything" on a 3100 is not even possible. Don't want to do that. I am only wanting to be able to run the A/C with everything else turned off - except for maybe a few LED light still on.
Yes and no. Like I said, you will get 4000 watts, but not continuous (3200 continuous). Same with a 3100. That is its max, not continuous.

I do not think you will be happy running a 3100 alone. Not to mention, hauling around a heavier generator and being limited to A\C only, if it will start reliably. Nothing like having a generator overload and having to go outside, unplug, kill the generator, restart, replug, and hope it does not happen again when something starts up again.
__________________
2016 Jayco Eagle 330RSTS = "Madame Maxime"
Maxxis M8008 E rated Tires and 16" Wheel Upgrade
Dual A/C 15K BTU, 14K Equalizer WD hitch with SC
King Bed with Java Interior, (2X) Yamaha EF2000isV2
2012 Ram 4500, 6.7L Cummins Turbo Diesel, MegaCab = "Hagrid"
8'x12' BMCM Stake Bed, Cabin Chassis, 2WD
360 degree Virtual Tour
Fairenatic is offline   Reply With Quote
Old 03-30-2016, 06:13 AM   #14
Senior Member
 
Rock's Avatar
 
Join Date: Sep 2015
Location: Mexico Beach
Posts: 2,192
In my TT the 15k A/C would run fine on my Honda 3000i from the idle position. I installed the hard start kit on my first a/c. A/c was replaced because of a leak and Coleman told me not to install hard start on the new unit 2014 since it was designed not to be needed. I would call with your model s/n and see what they say. Very easy install you gut plus wires into terminal block
Rock
__________________
2024 Greyhawk 30Z
2023 Jeep Gladiator High Altitude Toad
2019 Ram 3500. Traded
2016 Pinnacle FBTS Traded
Rock is offline   Reply With Quote
Old 03-30-2016, 08:07 AM   #15
tld
Senior Member
 
Join Date: Nov 2015
Location: Manhattan ks
Posts: 153
I really appreciate all of the responses. Let me ask this question: I can run my 15K A/C with other electrical items in use (not the microwave though) at RV parks while plugged into the parks 30 amp electrical socket and I do not throw the parks 30 amp breaker. So, since the generator has a 30 amp breaker, and I don't throw the parks 30 amp breaker, shouldn't it be reasonable to assume that I would be okay using the generator?
tld is offline   Reply With Quote
Old 03-30-2016, 08:26 AM   #16
Senior Member
 
Join Date: Jun 2015
Location: --
Posts: 2,392
Having done way more generator research than anybody in their right mind would, for a camper w/ a 13.5k AC I would use a Honda EU3000is w/ a wheel kit. Hands down - no questions asked. Its the quietest most fuel efficient generator you can buy that can spin that A/C every time and still run some onboard systems. The second generator I'd consider is the Yamaha EF2400iSHC. It's got enough oomph to spin up a 13.5k A/C and is more portable than the Honda.

15k A/C I'd want 2 units running in parallel. I used to be a big believer in the EU2000 from Honda, but I'd look at the Yamaha 2000s as well. On trips you don't need the A/C spinning, you can bring one unit instead of two. Or if you A/C is really a heat pump, you can still run that too w/ both generators up.
__________________
2023 Ford F-150 XLT SCREW 3.5EB (Max Tow Pkg., Black Appearance Pkg., Bed Utility Pkg.)
1727 Payload / 4150 RAWR

On the sidelines taking it all in.


Jopopsy is offline   Reply With Quote
Old 03-30-2016, 08:28 AM   #17
Senior Member
 
Rock's Avatar
 
Join Date: Sep 2015
Location: Mexico Beach
Posts: 2,192
It is the starting amp draw that the genny has to deal with on initial start. Shore power does not do that. You can see this just by plugging into a wall socket a cheap volt guage. The volts go way down when the a/c kicks on when using a genny. My 2800 Yamaha would stall out from econo run mode sometimes but the Honda 3000i does not. That is why a hard start capacitor gives an extra kick. Low voltage starts can over time burn up the compressor. It is kind of a catch 22. Run on full and burn gas and make more noise or use econo mode and put more wear on the compressor.
Rock
Rock
__________________
2024 Greyhawk 30Z
2023 Jeep Gladiator High Altitude Toad
2019 Ram 3500. Traded
2016 Pinnacle FBTS Traded
Rock is offline   Reply With Quote
Old 03-30-2016, 08:54 AM   #18
tld
Senior Member
 
Join Date: Nov 2015
Location: Manhattan ks
Posts: 153
Rock, I think maybe you answered my question. When my compressor kicks on while I'm connected to shore power, there is not a drop in voltage. So, if I need 3000 watts and I'm plugged into 120 volts, then I'm going to draw 25 amps. But, if I'm using a generator, when the compressor kicks on, I may get a momentary drop in the amount of voltage from the generator. If the momentary voltage drop was, say, down to 110 volts, then my need for 3000 start-up watts to turn the compressor would cause a momentary current draw of over 27 amps, which might be just enough to throw the generator breaker.
tld is offline   Reply With Quote
Old 03-30-2016, 09:19 AM   #19
Senior Member
 
Camper_bob's Avatar
 
Join Date: Sep 2013
Location: South Texas
Posts: 7,216
Quote:
Originally Posted by Rock View Post
It is the starting amp draw that the genny has to deal with on initial start. Shore power does not do that. You can see this just by plugging into a wall socket a cheap volt guage. The volts go way down when the a/c kicks on when using a genny. My 2800 Yamaha would stall out from econo run mode sometimes but the Honda 3000i does not. That is why a hard start capacitor gives an extra kick. Low voltage starts can over time burn up the compressor. It is kind of a catch 22. Run on full and burn gas and make more noise or use econo mode and put more wear on the compressor.
Rock
Rock
Quote:
Originally Posted by tld View Post
Rock, I think maybe you answered my question. When my compressor kicks on while I'm connected to shore power, there is not a drop in voltage. So, if I need 3000 watts and I'm plugged into 120 volts, then I'm going to draw 25 amps. But, if I'm using a generator, when the compressor kicks on, I may get a momentary drop in the amount of voltage from the generator. If the momentary voltage drop was, say, down to 110 volts, then my need for 3000 start-up watts to turn the compressor would cause a momentary current draw of over 27 amps, which might be just enough to throw the generator breaker.
Hence the capacitor. It takes that initial kick out of the equation. Makes it so the genny doesn't bog down as much, and it's easier on the compressor too. Right?
__________________

-2018 Greyhawk 29MV
-2020 Jeep Wrangler Unlimited (JLU) (Primary Toad)
-1994 Jeep Wrangler YJ (Secondary Toad)
-2014 Jay Flight 28BHBE & Ram 2500 6.4L CC 4x4 (sold)
Camper_bob is offline   Reply With Quote
Old 03-30-2016, 09:19 AM   #20
Senior Member
 
Join Date: Jan 2014
Posts: 103
Thumbs down

Quote:
Originally Posted by Jopopsy View Post
Having done way more generator research than anybody in their right mind would, for a camper w/ a 13.5k AC I would use a Honda EU3000is w/ a wheel kit. Hands down - no questions asked. Its the quietest most fuel efficient generator you can buy that can spin that A/C every time and still run some onboard systems. The second generator I'd .
This may be true at lower elevations. However, I've been at 6k+ with temps in the high 80s and tried to throw the generator on just to cool the trailer off after getting back and the windows being shut and the 3000i wouldn't even run the AC. So the elevation, heat and stock jetting on the carb created enough loss that it would not start the AC.

Because of this and mainly portability, I'm looking at getting rid of the 3000i and getting two smaller units.
jackofall is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 05:16 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.