Insufficient Heater air flow to back of 5th wheel

We have a Jayco Eagle Super Lite 31.5 BHDS

Heater works fine but we cannot seem to get enough air to flow to the floor registers in the bedroom area in the back of the 5th wheel. And in the front of the 5th wheel it gets really hot. Any suggestions?
__________________
2008 Jayco Eagle Super Lite 31.5 BHDS
2007 GMC Sierra 3500 SRW CC/LB Duramax
j4nash is offline   Reply With Quote
Old 07-05-2011, 11:57 AM   #2
Senior Member
 
OurJayco's Avatar
 
Join Date: Nov 2009
Location: East Bethel, Minnesota
Posts: 732
Can you close or cover the registers up front and see how the air flow is in back? You should be able to feel an increase in air flow.
There may be something in the vent that fell in there during build.
If you have a flashlight and a couple of mirrors, take the registers off and shine the light on one end and use a small mirror on the other end. You should be able to see the light (if the duct work is straight).
__________________
HAPPY CAMPING!! :D

Daryl and Sandy
2013 Eagle 314BDS
2014 Ford F150 Platinum, 4 x 4 Crew Cab with Ecoboost
Equal-i-zer Hitch
OurJayco is offline   Reply With Quote
Old 07-06-2011, 10:28 PM   #3
Junior Member
 
Join Date: Jul 2011
Location: Pocatello,Id
Posts: 2
I was talking to a fellow that owns a Open Range and had a problem with to much heat forward and not enough in the rear. His solution? He put dampers between the furnace and the tubing and was able to adjust heat where he needed it. I believe the furnace had 4" outlets.
pokyjoe48 is offline   Reply With Quote
Old 07-07-2011, 07:05 AM   #4
Senior Member
 
Join Date: Jun 2011
Posts: 124
You may want to check if the ductwork came loose where it connects to the furnace. I had one run that became undone. The ductwork connects to a metal piece that attaches to the furnace. I reconnected and put a pop rivit in to hold
bad99ram is offline   Reply With Quote
Old 07-07-2011, 07:13 AM   #5
Senior Member
 
barrelslime's Avatar
 
Join Date: May 2010
Location: Highland, IL
Posts: 318
? Are you wanting heat or AC?? The AC doesnt come thru the floor vents in my super lite Eagle. Only furnace heat comes thru floor vents. Im just curious cause its July and Im wondering why you are running the furnace.
__________________
" Let us endeavor so to live, that when we come to die, even the undertaker will be sorry." Mark Twain
barrelslime is offline   Reply With Quote
Old 07-07-2011, 12:08 PM   #6
Junior Member
 
Join Date: Nov 2010
Posts: 29
We were just camping up in the mountains and it was in the 40's at night. I know it sounds funny that someone would use their furnace in July.

I just talked to Jayco and they said i could switch a few of the outlets on the heater around and that the vent on the top of the heater is suppose to blow more hot air then the lower vent. So i think i will switch them around and also check for leeks this weekend.

Jayco said not to close off any of the vents as it could cause the heater to overheat. but when i talked to the dealer they told me that i might want to take silver Duck tape and close off part of the vents off the heater.
__________________
2008 Jayco Eagle Super Lite 31.5 BHDS
2007 GMC Sierra 3500 SRW CC/LB Duramax
j4nash is offline   Reply With Quote
Old 07-07-2011, 02:55 PM   #7
Junior Member
 
Join Date: Jul 2011
Location: Burnsville, NC
Posts: 17
We had a mouse cut a hole and build a nest on our duct hose between the furnace and the rear ducts. The odor along with the low air flow gave it away.

-Scott
__________________
****************
:Flag:
J. Scott Moncrief
Burnsville, NC

2007 Eagle 314BHDS
Rivermaster is offline   Reply With Quote
Old 07-09-2011, 06:53 PM   #8
Senior Member
 
Join Date: Dec 2009
Location: Peotone IL
Posts: 214
We had the same problem with ours, no heat in bedroom. Problem solved the flex duct was off at furance.
__________________
Wayne & Marti ....Yogi the spoiled Dog
2012 Ford Lariat 4WD PSD Dually LB, Aux Tank 50 gal
2010 Designer 37 RLQS, 5th Airbourne w/Sidewinder
Http://yogi154.blogspot.com/
yogi154 is offline   Reply With Quote
Old 12-22-2012, 02:45 PM   #9
Junior Member
 
Join Date: Nov 2010
Posts: 29
We we fixed the heat flow problem there was two places that had a T that just dumped to the underbelly we closed those off and now have a lot more flow to the back bunk.
__________________
2008 Jayco Eagle Super Lite 31.5 BHDS
2007 GMC Sierra 3500 SRW CC/LB Duramax
j4nash is offline   Reply With Quote
Old 12-22-2012, 07:38 PM   #10
Senior Member
 
chipper's Avatar
 
Join Date: Nov 2012
Location: Louisiana (southeastern)
Posts: 468
Glad to hear your problem is fixed.

I had a Rockwood 5er with a air flow problem. I removed the under-belly and found one of the ducts disconnected. It was flowing hot air into the under-belly. Once I reconnected the duct, all worked well.
__________________
Chipper

2006 Chevy Silverado 2500HD Duramax LBZ, CC, 4X4
2005 Jayco Talon ZX24-E Toy Hauler(SOLD).
2017 Forest River Hyper Lite XLR
Prodigy P2 Brake Control
12K Husky Straight Line WD Hitch
chipper is offline   Reply With Quote
Old 12-24-2012, 07:15 AM   #11
Member
 
matt1946's Avatar
 
Join Date: Aug 2011
Location: Williamstown NJ
Posts: 48
Too much heat in 30.5 RLS bedroom

We had too much heat in the bedroom so I installed a louvered vent which I can either close or limit the amount of heat coming from it
__________________
2012 Eagle Super Lite 30.5 RLS
2008 Silverado HD LTZ 6.0\Tow Package 3.79 Rear
16,000 lb Pull-Rite Slider
matt1946 is offline   Reply With Quote
Old 12-27-2012, 01:16 PM   #12
Junior Member
 
Join Date: Feb 2012
Posts: 26
Quote:
Originally Posted by matt1946 View Post
We had too much heat in the bedroom so I installed a louvered vent which I can either close or limit the amount of heat coming from it
If you talk to Jayco they will discourage this. I work in residential HVAC and it's not a lot different than RV HVAC, RV HVAC is just smaller versions. If you use an adjustable vent you run the risk of overheating the furnace heat exchanger which will damage it and shorten it's life. If the overheating situation burns a hole in the heat exchanger you can introduce carbonmonoxide into the air stream which can kill.
__________________
2010 Jayco Eagle Super Lite 315RLDS
2013 GMC Sierra 2500HD 6.6L Duramax
2010 Pit Bull Terrier (Jake)
2010 Camping Nights 45
2011 Camping Nights 70
2012 Camping Nights 144
2013 Camping Nights 49
allen8106 is offline   Reply With Quote
Old 12-27-2012, 04:42 PM   #13
Site Team
 
norty1's Avatar
 
Join Date: Jan 2011
Location: James Island, SC
Posts: 22,857
Quote:
Originally Posted by j4nash View Post
We we fixed the heat flow problem there was two places that had a T that just dumped to the underbelly we closed those off and now have a lot more flow to the back bunk.
On many rigs, that is how they keep the holding tanks from freezing. Closing all heat to the area may cause some problems if you are in sub freezing weather with the tanks.
__________________
Moderator
2011- 351RLTS Eagle, MorRyde suspension/pin box,
2017- F350 6.7 PSD Lariat FX4,SRW, SB,CC
Hughes PWD SP-50A, TST TPMS
Gator roll-up bed cover
B&W Turnover ball, Companion Std hitch
Can't find what you're looking on JOF? Try Jayco Owners Forum Custom Google Search
norty1 is offline   Reply With Quote
Old 12-27-2012, 05:32 PM   #14
Senior Member
 
SmokerBill's Avatar
 
Join Date: Sep 2010
Location: PNW
Posts: 5,195
If you use a small 12 volt (or 120 VAC) fan in your rv to circulate the air, I think it would make a big difference in heat distribution, without playing around with trying to adjust the airflow from the furnace registers. A fan will also help with window condensation.
__________________
Bill
2011 Dodge Ram 1500 HEMI Quad Cab
2011 Jay Flight 26BH
SmokerBill is offline   Reply With Quote
Old 12-28-2012, 10:36 AM   #15
Senior Member
 
Seann45's Avatar
 
Join Date: Jun 2010
Location: Saskatoon Sask Canada
Posts: 10,726
I had the same problem on my TT... dealer could not find a reason for it... blocked the bedroom vents but that did not help at all... finally said "to heck with it" and got a Big buddy heater. I never turn the furnace on now...
__________________
Seann
2004 Chev Silverado Duramax optioned past the max. 2009 Jayco Eagle 308 RLS 900watts of solar, Lithium batteries (400amp hour), 2000 watt (4000 surge) whole house inverter.
145days /2023 2022/151 2021[/COLOR]
93/2020,157/2019219/2018 206/2017,215/2016, 211/2015, 196/14, 247/13, 193/12

Seann45 is offline   Reply With Quote
Old 12-28-2012, 11:05 AM   #16
Senior Member
 
SmokerBill's Avatar
 
Join Date: Sep 2010
Location: PNW
Posts: 5,195
Quote:
Originally Posted by Seann45 View Post
I had the same problem on my TT... dealer could not find a reason for it... blocked the bedroom vents but that did not help at all... finally said "to heck with it" and got a Big buddy heater. I never turn the furnace on now...
Seann, I have a Big Buddy heater, but it's in storage near Seattle right now, darn it. I'm curious, how much ventilation do you have to provide? I think I read in the manual that you're supposed to leave a window or two cracked open a bit for indoor use.
__________________
Bill
2011 Dodge Ram 1500 HEMI Quad Cab
2011 Jay Flight 26BH
SmokerBill is offline   Reply With Quote
Old 12-28-2012, 02:19 PM   #17
Junior Member
 
Join Date: Mar 2011
Posts: 25
We had the same problem - our dealer was familiar with it.

He had us bring it in as a warranty repair, and he PARTIALLY covered the vents to the underbelly in order to direct more air to the rear of the unit. Our unit has a front bedroom - rear living.

He also advised against closing the front vents.

I did buy & install louvered vents for the bedroom & bath - but on his advice know NOT to fully close them. I had wanted to add another duct & register at the rear of the living area, and he advised against that also.
SouthRider is offline   Reply With Quote
Old 12-29-2012, 08:50 AM   #18
Senior Member
 
Seann45's Avatar
 
Join Date: Jun 2010
Location: Saskatoon Sask Canada
Posts: 10,726
Quote:
Originally Posted by allen8106 View Post
If you talk to Jayco they will discourage this. I work in residential HVAC and it's not a lot different than RV HVAC, RV HVAC is just smaller versions. If you use an adjustable vent you run the risk of overheating the furnace heat exchanger which will damage it and shorten it's life. If the overheating situation burns a hole in the heat exchanger you can introduce carbonmonoxide into the air stream which can kill.
Jayco sent me louvered vents that can be closed as a way to deal with the no heat in the living room problem.
__________________
Seann
2004 Chev Silverado Duramax optioned past the max. 2009 Jayco Eagle 308 RLS 900watts of solar, Lithium batteries (400amp hour), 2000 watt (4000 surge) whole house inverter.
145days /2023 2022/151 2021[/COLOR]
93/2020,157/2019219/2018 206/2017,215/2016, 211/2015, 196/14, 247/13, 193/12

Seann45 is offline   Reply With Quote
Old 01-01-2013, 03:31 PM   #19
Senior Member
 
Join Date: Apr 2012
Location: Mississauga, Ontario
Posts: 121
We had the same problem in our 30.5 RLS, dealer couldn't do or suggest anything and Jayco never responded to my email request. In speaking with someone familiar with RV's he said the problem is the supply to the underbelly to keep the holding tanks from freezing and the long run from furnace to duct and only the one duct. We also added a small portable elctric heater to assist in the rear. Because we have rear living area I am going to add an electric fireplace to the entertainment area to supply heat. Design flaw in my mind needs more supply to rear.
__________________
Barry and Lisa
with 2 Tollers!

2016 F350 PSD
2010 Jayco 30.5 RLS
Bearles is offline   Reply With Quote
Old 01-01-2013, 04:21 PM   #20
Senior Member
 
Seann45's Avatar
 
Join Date: Jun 2010
Location: Saskatoon Sask Canada
Posts: 10,726
Quote:
Originally Posted by SmokerBill View Post
Seann, I have a Big Buddy heater, but it's in storage near Seattle right now, darn it. I'm curious, how much ventilation do you have to provide? I think I read in the manual that you're supposed to leave a window or two cracked open a bit for indoor use.
I crack my bathroom vent open less than 1/2".. the big buddy has a low O2 sensor and will shut itself off if needed.
__________________
Seann
2004 Chev Silverado Duramax optioned past the max. 2009 Jayco Eagle 308 RLS 900watts of solar, Lithium batteries (400amp hour), 2000 watt (4000 surge) whole house inverter.
145days /2023 2022/151 2021[/COLOR]
93/2020,157/2019219/2018 206/2017,215/2016, 211/2015, 196/14, 247/13, 193/12

Seann45 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 10:20 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.