Originally Posted by Bob Landry View Post
Before you tear into this unit and create more problems than you can fix, measure compressor amp draw. The amperage on the data plate is based on an ambient temp of 95 degrees. A 10 degree change in ambient temp will cause a change of 1A in compressor draw. Interpolate in between. If the data plate says 14A, and the temp is 100, then you should read 14.5A. That will tell you if the unit is properly charged. This test is valid for both R22 and R410a.
I doubt you are low on charge. These units only hold a pound or so, so any type of leak is going to blow the entire charge and then there is no cooling.

I think your time would be better spent inspecting and taping the plenum where is goes into the ceiling vents(if it is a ducted unit) and around the ceiling registers. RV AC ducting is by nature installed very sloppily and you may be dumping cold air into the ceiling area where it is going to do you no good.
Thanks Bob, I figured you would chime in.


2015 Jayco 24FBS Elite Jay Flight
2013 Chevrolet Silverado 2500HD 4X4 6.0L 3.73 Axle
HD Trailering Package with Integrated Brake Controller
Equal-i-zer Hitch 10k/1000
Camping Couple is offline   Reply With Quote

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

» Virginia State Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -6. The time now is 09:04 PM.

Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2016, vBulletin Solutions, Inc.