As far as I know, it's all copper wiring. I'm wondering if the neutral had a partial break and with full draw ( a/c water heater etc) it caused it to burn through. The electrian from the RV centre that made initial repair pulled out the entire panell and checked over everything. Couple of loose wire nuts but nothing else. Frustrated. Not sure after all these years why it would be doing this.
__________________

Bossman is offline   Reply With Quote
Old 08-02-2016, 10:17 AM   #12
BCK
Senior Member
 
Join Date: Apr 2016
Location: Nanaimo
Posts: 405
Over-tightened connections cause hot spots just like loose ones. Makes me wonder if the tech that fixed it last time was worried about loose connections and may have tightened it too much. The proper torque settings for neutral bar screws aren't all that high (usually 20-35 in.lbs depending on wire size).

Also if power was out for several hours then everyone's AC, water heaters, etc in the park and the fridges, freezers, etc on the wider grid all come on at the same time and cause the line voltage to sag. That could easily be what provided the stress to cause an already poor connection to fail.
__________________

__________________
2016 Jayflight 26BHS Elite
2014 F150 4x4 Super Crew, Eco-Boost, Max Tow
Bayliner Trophy 2002ff
BCK is offline   Reply With Quote
Old 08-02-2016, 09:20 PM   #13
Junior Member
 
Join Date: Jul 2016
Location: Winnipeg
Posts: 12
Sounds like a good place to start. Tec guy really did giver her hard on set screws. If anyone has any other information about this, I'd sure like to hear.
Bossman is offline   Reply With Quote
Old 08-02-2016, 11:13 PM   #14
BCK
Senior Member
 
Join Date: Apr 2016
Location: Nanaimo
Posts: 405
You should start by replacing the neutral bar. They are not hard to find. If it's been that hot twice it's shot and will be very hard to get good reliable connections.

Cut all of the neutral wires back to good wire including the ones that don't appear cooked and re-terminate using a torque driver. I would check to be sure on the replacement bar but normally up to #10cu wire is 20 inch-pounds and there shouldn't be any in there bigger than that on the AC power side. That's not nearly as tight as you'd think so don't be tempted to tighten by feel or you will be going down the same road again.

I think a bad connection is the likely cause of your problem and not any other internal wiring issue. A wiring issue on an internal cct would have caused heating on its own smaller wire and not the larger shore power wire. Also, wire fails where it is compromised is so unlikely damage to another spot on the cord or cord plug would have caused your problem.
BCK is offline   Reply With Quote
Old 08-03-2016, 05:16 AM   #15
Senior Member
 
RVhiker's Avatar
 
Join Date: Dec 2010
Posts: 1,226
Quote:
Originally Posted by BCK View Post
Over-tightened connections cause hot spots just like loose ones. Makes me wonder if the tech that fixed it last time was worried about loose connections and may have tightened it too much. The proper torque settings for neutral bar screws aren't all that high (usually 20-35 in.lbs depending on wire size)...
Just curious how over-tightened connections can cause hot spots. Does the wire just get smashed flat and become too thin and cause the issue, or is it something else?
__________________
There's lots of advice and information in forums... sometimes it is correct. For example, all of my posts are made by a political appointee who got the job as a reward for contributions to my diesel bill.

2011 Jayco 28.5RLS; 2008 Chevy Duramax; Pullrite Superglide Hitch

RVhiker is offline   Reply With Quote
Old 08-03-2016, 10:35 AM   #16
BCK
Senior Member
 
Join Date: Apr 2016
Location: Nanaimo
Posts: 405
Over tightening can over compress and deform the metal of the terminal & screw and/or damage the conductor. In time this actually causes the connection to fail & loosen, overheat, oxidize and further deteriorate. A termination that is failing because it was over tightened in the first place is often “loose” when discovered and the thought is to re-tighten because it was “loose”. Simply re-tightening a “loose” or hot connection without understanding why it is failing in the first place and fixing it properly has limited success. Only about 20% of “loose” connections are fixed by simply tightening – the other 80% will fail again.
__________________
2016 Jayflight 26BHS Elite
2014 F150 4x4 Super Crew, Eco-Boost, Max Tow
Bayliner Trophy 2002ff
BCK is offline   Reply With Quote
Old 08-03-2016, 11:52 AM   #17
Senior Member
 
Join Date: Jun 2012
Location: Long Island, NY
Posts: 626
Hmm. ALL the neutrals were burnt? That is unusual to say the least. This is a 30 amp trailer or a 50 with the extra A/C?

Are there by chance and MWBC's? (Multi Wire Branch Circuits) Are there any red wires on the breakers? If you have some shared neutrals on a single phase then the neutral would have to take the load of both circuits combined. Normally the neutral would only take the difference in loads. But this should only effect the single and/or surrounding neutrals, not all of them.
__________________
Thanks,
Brian

TV = 2006 F-350 CC DRW 6.0
TT = 2018 Wildwood 31KQBTS
TT = 2007 Jayco Jay Flight 27bh - SOLD
Macrosill is offline   Reply With Quote
Old 08-03-2016, 08:13 PM   #18
Junior Member
 
Join Date: Jul 2016
Location: Winnipeg
Posts: 12
No shared neutrals and no mwbc's ( red wire ).
Bossman is offline   Reply With Quote
Old 08-03-2016, 08:45 PM   #19
Senior Member
 
Join Date: Aug 2013
Location: NC
Posts: 973
If you are on a 30amp circuit number 10 wire should never melt insulation. Number 10 is rated at 30amps with only a 30deg c temp rise. A loose connection can get very hot based upon change in resistance at the contact points. The voltage drop across the connection times the current draw on the wire is the wattage (heat) that causes the melting.
A good electrician can probe the wire and bar(measure voltage in parallel with the connection) and read the voltage drop. That needs to be done to either rule out the bus bar connections or prove they are the issue.
__________________
No man has a good enough memory to be a successful liar. Abraham Lincoln

2016 36FBTS Pinnacle
2016 F350, 6.7, 4x4, DRW, long bed
B & W Companion 5th wheel Hitch
eldermike is offline   Reply With Quote
Old 08-12-2016, 07:34 AM   #20
Junior Member
 
Join Date: Jul 2016
Location: Winnipeg
Posts: 12
When I do the repair I intend to replace the neutral bus bar. Is there a paste that I can coat the wires with to prevent oxidation of the wires ?
__________________

Bossman is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia State Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -6. The time now is 07:31 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.