Quote:
Originally Posted by PapaGNO
So I hot wired the wires to bypass the hi limit switch and the furnace light first try. Is there a reset for that switch or does it mean you have to replace the switch. Also if i'm to replace the switch from what I can see I would have to remove the furnace to replace. is this the case or can the switch be removed easier? thanks again everyone for your help.
|
There should be two screws that hold the limits switch in place.
yes you can reset the limit switch but they're only $15-$20,but before you replaced check your furnace filter, fresh air intake filter if you have them. usually dirty furnace filter or obstruction to the fresh air intake will make the high limit switch to stay open.