Main breaker poped
When running the air and microwave at the same time it popped the main breaker, you think this normal?
|
|
|
06-25-2014, 10:57 AM
|
#2
|
Senior Member
Join Date: Jun 2011
Location: Kalamazoo, West Michigan
Posts: 1,817
|
More info needed. What is your main breaker rating? 30A? What is the amp draw on your A/C and the microwave? The sum of the two should be less than the rating on the main. The main breaker could be getting weak and tripping at a lower current load or one or more of your appliances could be drawing excessive current.
Some quality time with a clamp-on amp meter would be in order.
__________________
2006 23B Hybrid with 10k round bar WDH
2011 F150 4x4 SCREW Ecoboost, Max Tow, Integrated TBC, 3.73 LS axle, Firestone Ride Rite airbags.
|
|
|
06-25-2014, 11:16 AM
|
#3
|
Moderator Emeritus
Join Date: Apr 2011
Location: Michigan
Posts: 9,424
|
Mine will do the same thing with my micro and 13.5K A/C ......, everything in my TT checks out ok.
Bob
__________________
2016 GM 2500HD 6.0L/4.10
2018 Jay Flight 24RBS
2002 GM 2500HD 6.0L/4:10 (retired)
2005 Jayco Eagle 278FBS (retired)
1999 Jayco Eagle 246FB (retired)
Reese HP Dual Cam (Strait-Line)
|
|
|
06-25-2014, 11:36 AM
|
#4
|
Senior Member
Join Date: Sep 2011
Location: King George
Posts: 2,761
|
I have the same situation here when running my 13,500 BTU Air Conditioner. If I turn on the Microwave at the same time it usually trips my main 30A breaker in the trailer.
Sometimes it doesn't so it is right on the edge I suspect.
I'm sure some other somewhat high wattage appliances must be 'ON' as well as I have never killed everything except the Air Conditioner and the Microwave to see if they would work together or not.
When I was adding both 120VAC and 12VDC things up one time for doing a BATTERY LOAD SURVEY I did notice all of my 120VAC Appliances added up to more than 30AMPs...
I guess the manf is aware of this and just thinks that everyone will not turn everything on at the same time...
During the winter months this is the reason I always run an extension cord out to the 20AMP service receptacle when I am running my oil-filled Electric Heaters.
Roy Ken
__________________
Roy and Carolyn
I claim Horse Creek Country in Southern Ill - Momabear is from North Texas
We live in King George VA
RETIRED DOD DOAF DON CONTRACTOR Electronics Tech 42YRS
"We're burning daylight" - John Wayne
2008 STARCRAFT 14RT OFF-ROAD POPUP with PD9260C and three 85AH 12VDC batteries
2010 F150 FX4 5.4 GAS with 3.73 gears - Super Cab - Towing Package - 2KW Honda EU2000i Gen
K9PHT (since 1957) 146.52Mhz
"We always have a PLAN B"
|
|
|
06-25-2014, 12:14 PM
|
#5
|
Senior Member
Join Date: Jan 2014
Location: Black River Falls, Wi
Posts: 1,154
|
Not unheard of. Are we talking the breaker at the CG post or inside the trailer? Was the water heater on also ?
I can pop the 30 amp on the post if the AC or microwave comes on with the TV on and the HW heater recovering from morning showers
__________________
2019 Pinnacle 36 FBTS
2016 Silverado 3500 CC SRW DuraMax/Allison
1975 Corvette for the sunny days n dry roads
2017 RZR for the rainy days n muddy roads
|
|
|
06-25-2014, 12:30 PM
|
#6
|
Senior Member
Join Date: Aug 2013
Location: NC
Posts: 974
|
When I was camping with 30amp I learned to switch the hot water heater over to propane when the wife was using the microwave or even a coffee pot with a hot plate on it. That solved the issue for me.
__________________
No man has a good enough memory to be a successful liar. Abraham Lincoln
2016 36FBTS Pinnacle
2016 F350, 6.7, 4x4, DRW, long bed
B & W Companion 5th wheel Hitch
|
|
|
06-25-2014, 02:45 PM
|
#7
|
Senior Member
Join Date: May 2012
Location: Minnesota
Posts: 9,768
|
But as Mcfarmall said, a little more info could be helpful. What size breaker do you have? 30 or 50 amp? It is fairly common with the 30 amp TT, not sure on the 50 amp TT. I just run one major appliance at a time. Typically just turn off the AC until we are done with the microwave.
|
|
|
06-25-2014, 02:49 PM
|
#8
|
Senior Member
Join Date: Apr 2014
Location: Bella Vista, Arkansas
Posts: 171
|
Yes it is 30. Amp. It's an 07 29bhs. We have just been turning off ac while we run the microwave.
|
|
|
06-25-2014, 07:58 PM
|
#9
|
Senior Member
Join Date: Apr 2011
Location: Columbia SC
Posts: 572
|
I have popped a 30 amp CG breaker under similar circumstances but never my own.
__________________
2012 Toyota Tundra 5.7 Litre DoubleCab
6 speed, 4.30 Limited Slip, Tow Package
2013 Jayco White Hawk 27DSRL
2010 Jayco JayFlight 26BH sold
Yamaha EF2000is Generators (2)
1996 Honda CB750 Nighthawk
|
|
|
06-25-2014, 09:18 PM
|
#10
|
Senior Member
Join Date: Dec 2010
Location: North Idaho/Arizona
Posts: 5,446
|
With a 30 amp system you may be right on the edge with big power drawing appliances running at the same time.
__________________
2011 Eagle 330RLTS with just about every option.
2017 Silverado 1500 4x4 5.3 with tow package. (no, we don't tow the Jayco with it.)
2018 Surveyor 265RLDS well equipped.
Life in the slow lane is still life.
|
|
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Threads |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|