Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
Jayco RV Owners Forum
 


Reply
 
Thread Tools Search this Thread Display Modes
 
Old 07-08-2015, 03:55 PM   #41
Member
 
Join Date: Mar 2015
Location: Sierra Vista
Posts: 79
To clarify, the ONLY place there could be a short that would allow 50A and not trip the 30A in the unit, is the cable, as that is the only thing between the two breakers. Again, if you develop a direct short in the cable, it will trip a 50!
Tim L is offline   Reply With Quote
Old 07-08-2015, 04:07 PM   #42
Senior Member
 
Join Date: Apr 2015
Location: Elizabethtown, PA
Posts: 1,560
Tim Although I agree with some of what you are saying. A CB is designed to protect the equipment on the circuit and also to protect the wires. And you are correct about the 30 AMP breaker should trip when a overload happens. But even the Code states you do not protect a lower rated device with a higher rated CB so using a 50 amp CB to protect a 30 amp cord is not advisable. And what would happen if the 30 AMP breaker in the RV shorted out then you have to depend on the 50 AMP breaker to trip. We all do things that shouldn't be done and most of the time we are lucky and get away with it. But over 45 years as a maintenance electrician tells me not to protect a lower rated device with a higher rated device. And using a 30 amp cord on a 50 amp service should not be done. You may get lucky but you are tempting fate.


Also this is part of the reason for the MFG to put a label on the side of the camper to state what the RV is rated for and why the plug is designed to be plugged into a 30 AMP receptacle.
__________________
2004 Jay Feather 25E
2001 Ford Expedition 4X4 EB 5.4 3.55 rear
2004 Ford Expedition 4X4 EB 5.4 3.73 rear
bedrck46 is offline   Reply With Quote
Old 07-08-2015, 06:01 PM   #43
Senior Member
 
Join Date: Apr 2015
Location: Elizabethtown, PA
Posts: 1,560
Quote:
Originally Posted by Tim L View Post
Hooking your 30A to a 50A with the adapter is fine. The adapter only uses one leg of the 50A service, so you are back to 120V, and although the service is limited to 50A at the power pole breaker, your cord will only see the current demanded by your rig, and your rig is limited by a 30A main breaker, so the cord won't see over 30A. I do this often, as many 30A female plugs, at campgrounds, are worn out and loose, where the less used 50A plugs are still in good shape.
The following was copied from the State of Illinois and I am certain other states and even the National Electric Code has similar rules



RV Electrical Safety
for Campers
Printed by the Authority of the State of Illinois
One last tip on cords, do not use a power cord adapter that converts a low power cord
for use with a higher power receptacle. For example if you have a 20 ampere cord,
do not use an adapter and plug into a 30 ampere receptacle.
__________________
2004 Jay Feather 25E
2001 Ford Expedition 4X4 EB 5.4 3.55 rear
2004 Ford Expedition 4X4 EB 5.4 3.73 rear
bedrck46 is offline   Reply With Quote
Old 07-09-2015, 09:22 AM   #44
Senior Member
 
Join Date: Jun 2015
Location: Nashville
Posts: 470
Using an adapter to connect a 30A RV to a 50A pedestal does carry some risk. Is in violation of the NEC and most local electrical codes. In my opinion it is ill advised. However, the risk is minimal and each person needs to decide if they are willing to accept that risk.

If you don't have enough knowledge to make the assessment you should probably not use an adapter. If you do have enough knowledge to make the assessment you probably won't use an adapter. Now an adapter with a built in 30A breaker might be ok but I've never seen one of those.

I've never looked but I can't imagine the commercially available adapters carry a UL approval.
Hohenwald48 is offline   Reply With Quote
Old 07-09-2015, 12:47 PM   #45
Member
 
Join Date: Mar 2015
Location: Sierra Vista
Posts: 79
With all due respect, I for one, have a B.S. in Engineering, and the understanding of risk involved, and I will continue using my adapter. I do understand that a short in the cord could happen upstream of my 30A breaker, but I also know that I could be killed driving to the campground, or get struck by lightning while I am there. I also know that I could take my dog bone, plug it into a 50A service, take my 30A to 15A adapter, and plug it into my dog bone, then plug in a 15 A lamp cord, with bare ends, short out the 14 ga lamp cord bare ends, and the 50A breaker would trip.

As far as code and legality, in our litigious, nanny state society, with this "disaster waiting to happen" product, which I can pick up at every RV store in the country, not to mention Wal Marts etc., or order from a plethora of online stores, like Amazon, and is made by large companies with deep pockets like Camco and Progressive, and Nada. With all of our social media and online content, I can't find one lawsuit, fire, or disaster story related to the adapter...
Tim L is offline   Reply With Quote
Old 07-09-2015, 12:57 PM   #46
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,835
Quote:
Originally Posted by Tim L View Post
...14 ga lamp cord bare ends, and the 50A breaker would trip. ....
Nope.

The shorted 14ga lamp cord will smoke, catch fire and glow bright red.

Depending on many factors, the 50A breaker might trip before some portion the copper wire melts and opens the circuit.

Try it sometime where you can limit the damage. I wish camcorders were affordable when I did it against a 20A breaker.


It is fairly likely that the 10ga wire inside an RV 30A cable will hold 50A until the breaker trips, but why take that kind of risk?

The cord will be ruined. And the RV will still be on fire.
__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Old 07-09-2015, 01:03 PM   #47
Senior Member
 
Join Date: Apr 2015
Location: Elizabethtown, PA
Posts: 1,560
Well I would say that with a BS in engineering that you would have a better outlook on the negatives But then if and when you do have a fire caused by your use of a adaptor that you so well put that you will continue to use. I hope when you put a claim into the insurance that you tell them you were using that adaptor. Lets see how fast they walk away and tell you that a BS in Engineering should have known better. As I said before we all do tings that we get lucky and walk away from By why be foolish and tempt fate. Also having a BS doesn't mean you have common sense. But then again with so many that have said not to use the adaptor and you with the BS say to use it we all must be wrong and you must be correct`.
__________________
2004 Jay Feather 25E
2001 Ford Expedition 4X4 EB 5.4 3.55 rear
2004 Ford Expedition 4X4 EB 5.4 3.73 rear
bedrck46 is offline   Reply With Quote
Old 07-09-2015, 01:05 PM   #48
Senior Member
 
Join Date: Apr 2015
Location: Elizabethtown, PA
Posts: 1,560
and with all that is said HOPEFULL A MODERATOR WILL END THIS THREAD BEFORE IT GETS OUT OF HAND.
__________________
2004 Jay Feather 25E
2001 Ford Expedition 4X4 EB 5.4 3.55 rear
2004 Ford Expedition 4X4 EB 5.4 3.73 rear
bedrck46 is offline   Reply With Quote
Old 07-09-2015, 01:36 PM   #49
Senior Member
 
wags999's Avatar
 
Join Date: Jan 2015
Location: Surprise
Posts: 2,623
For the record, a 12 ga wire will carry a whole house...when putting in new services, we would jump the meter with 12 ga solid wire, until it was inspected and the electric company would install the new meter. BUT the wire was stripped and in open air (inside the meter cabinet)...running higher amperage than a wire is designed to carry can cause heat to build up, since it was in open air and only for a few days, it was capable of carrying the load. Keeping your cord rolled up in your TT and extending only a small portion to connect to the pedestal can cause the heat to build up in the cord and caused issues, before 30 amps is reached and the breaker trips.


Best to pull your cord completely out so as to mitigate this potential issue in my opinion.


It is also always best to plug your cord into the correct receptacle...ie 20 to 20, 30 to 30 and 50 to 50.. Many things can be used in an emergency, but it doesn't make it right.. If it made no difference, then mfg could wire all units with a 50 amp plug and only use one leg on the 30 amp rigs.... as stated above you never want to use a higher rated breaker on a lower rated cord...your asking for issues...like so many things, you may get away with it 1000 times....but the 1001 you get banged....not worth it.


If a plug is bad, let the campground know, it's a 10 minute job to replace a plug....tho if the campground is doing it's job, they should be checking the receptacles between campers as part of their on going Preventative maintenance.


Happy Camping
__________________
2011 Toyota Tundra double cab
2015 27RLS


wags999 is offline   Reply With Quote
Old 07-09-2015, 01:40 PM   #50
Senior Member
 
Join Date: Jun 2015
Location: --
Posts: 2,392
So for those of us who take the whole cord out, how do you dissuade the ants from making that conga line into your camper?

I always spray my tires, around my tires, the sewer hose, water hose, and electrical line w/ some 12 month bug barrier/killer you can pick up at Depot. I can't stop them from climbing onto my wires and hoses, but my thinking is I can kill them before they get too far.
Jopopsy is offline   Reply With Quote
Old 07-09-2015, 01:59 PM   #51
Senior Member
 
wags999's Avatar
 
Join Date: Jan 2015
Location: Surprise
Posts: 2,623
I keep mine off the ground, by attaching it to the ladder. Never have had an issue with ants or other creepy crawlers. Lucky I guess..
__________________
2011 Toyota Tundra double cab
2015 27RLS


wags999 is offline   Reply With Quote
Old 07-09-2015, 03:02 PM   #52
Member
 
Join Date: Mar 2015
Location: Sierra Vista
Posts: 79
No need for a moderator. Pretty much everyone is being respectful in their disagreements on the subject. There is only one person who is insulting and degrading others, but hey, I've been married 35+ years, I've been insulted worse...
Tim L is offline   Reply With Quote
Old 07-09-2015, 03:25 PM   #53
Senior Member
 
Join Date: Apr 2015
Location: Elizabethtown, PA
Posts: 1,560
Well nothing was meant to insult you or degrade you But when someone says they have a BS in engineering and makes a statement like you did that it is ok to use a under-rated device and protect it with a higher rated device does not show very good common sense. And to be honest even though you feel your are safe there are others that may read this forum and get the impression by your statement that it is perfectly ok to do something that most people say not to do And that would be the person that has something go wrong and cost him his RV because his insurance refuses to cover the damage due to his neglect and you giving the OK to do it.
As stated before being you have a BS and I don't that you must be correct and the rest of us are wrong.


And by the way what does marriage have to do with this.


What you can't stand is for someone to tell you that you were/are wrong
__________________
2004 Jay Feather 25E
2001 Ford Expedition 4X4 EB 5.4 3.55 rear
2004 Ford Expedition 4X4 EB 5.4 3.73 rear
bedrck46 is offline   Reply With Quote
Old 07-09-2015, 03:58 PM   #54
Senior Member
 
The Logans's Avatar
 
Join Date: May 2014
Location: North Western West Virginia
Posts: 671
Interesting...

I never thought about pulling out the entire cord. I just take out what I need to reach the outlet... is this a problem? The rest of the cord stays coiled in it's galvanized steel box. Several of the units we looked at even have cord winders built in to the motorhomes, and they advertise only pulling out as much as is needed.

It's very confusing...
__________________
The Logan's
2018 Jayco Alante 31v
Me, Dear Wife,
2 Bluetick Hounds
1 Newfoundland
1 Newfoundland / Black Lab Mix
1 Cairn Terrier
The Logans is offline   Reply With Quote
Old 07-09-2015, 03:59 PM   #55
Senior Member
 
Join Date: Jun 2015
Location: --
Posts: 2,392
I agree. I'm confused now too. Heck I leave the Autoformer in the compartment b/c I don't want anybody walking away with it. Now I'm thinking that might be folly too.
Jopopsy is offline   Reply With Quote
Old 07-09-2015, 04:05 PM   #56
Senior Member
 
The Logans's Avatar
 
Join Date: May 2014
Location: North Western West Virginia
Posts: 671
Good point Jopopsy,

I'd never leave the surge protector out... it would grow legs and walk off before I could get back from my nap! :-)
__________________
The Logan's
2018 Jayco Alante 31v
Me, Dear Wife,
2 Bluetick Hounds
1 Newfoundland
1 Newfoundland / Black Lab Mix
1 Cairn Terrier
The Logans is offline   Reply With Quote
Old 07-09-2015, 04:07 PM   #57
Senior Member
 
Join Date: Jun 2015
Location: --
Posts: 2,392
I have a surge protector too, but I have one of those plastic lock hasps with a combo lock on it. Minimal protection I know, but enough to make somebody spend time to rip me off.

I run pedestal --> surge --> camper power cord --> Autoformer --> 5' power cord from Autoformer install kit --> RV
Jopopsy is offline   Reply With Quote
Old 07-09-2015, 04:18 PM   #58
Member
 
Join Date: Mar 2015
Location: Sierra Vista
Posts: 79
No worries Bedrck. Dozens of companies manufacture them, and thousands of companies sell them, and have for 30+ years. And, the ONLY INTENDED PURPOSE is for adapting 50A to 30A exactly as we are discussing. As far as I can find, there have been zero issues. No insurance company would ever deny a claim for using a product EXACTLY as it was intended. A short in the cord would trip the 50, and anything beyond that is protected by the 30 in the unit. Is there a 1 in 10 million chance there could be some partial short that only drew 49 amps, and caught my cord on fire? Sure, but if that is your big worry, perhaps you shouldn't leave your house. It's a dangerous world out there...
Tim L is offline   Reply With Quote
Old 07-09-2015, 04:31 PM   #59
Senior Member
 
wags999's Avatar
 
Join Date: Jan 2015
Location: Surprise
Posts: 2,623
Actually Tim I have seen issues, but your right, MOST of the time it's not a problem. But I doubt anyone would recommend to use a dog bone as a regular normal procedure.. Also most campgrounds will have more people using 50 to 30 amp dog bones rather than 30to 50...50 amp hook ups are always in demand, so when they are not available a big rig will use the dog bone to connect to a lower amp receptacle...which presents no problem to the cord or plug...but does to using everything in the rig.
__________________
2011 Toyota Tundra double cab
2015 27RLS


wags999 is offline   Reply With Quote
Old 07-09-2015, 05:09 PM   #60
Member
 
Join Date: Mar 2015
Location: Sierra Vista
Posts: 79
I would agree with that Wags999. I don't always use it. If I plug in the 30, and it falls out, I go to the adapter. I have yet to do this and find a worn out 50. I feel it is better, and SAFER to do this than use the worn out 30A, as with the poor connection, I am sure there is lower than optimal Voltage for my AC compressor etc, and I feel safer knowing there is a solid ground connection. Ironically, when searching the web for issues, the ONLY one I found was a fire in a cord compartment when a 30A to 50A was used in a large MH. I do NOT understand how that happened at all. It sounded to me like they used a 30A cord, and then had the adapter to their 50A shore cord in the compartment, and it shorted. But again, with the 30A CB on the pedestal, I don't get it???
Tim L is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 09:37 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.