50 amp only at campground

New jayco owner, can't I camp at a campgroung that only has 50 service with my 30 amp camper ? manual says no adaptors of any kind...could damage my electrical system ?
MikenKaren is offline   Reply With Quote
Old 08-01-2014, 07:22 PM   #2
Senior Member
 
Join Date: Apr 2013
Location: White Rock, BC. Canada
Posts: 374
Not sure why it would damage anything. The voltage is the same and the trailer will only draw what ever current it needs.

Every plug in your house can put out 15 amps but there's nothing wrong with plugging in an one amp appliance.

You would need an adapter plug though.
__________________
]2013 Jay Feather X213
2003 Ford Expedition
Paulx213 is offline   Reply With Quote
Old 08-01-2014, 07:23 PM   #3
Junior Member
 
Join Date: Aug 2014
Location: Danville
Posts: 18
on reserve America some of the campgrounds will list multiple service hookups, and then again some only say 50 amp...would an adapter plug or converter type adapter hurt my 30 amp rv at a 50 amp plug with the adapter ? thanks
MikenKaren is offline   Reply With Quote
Old 08-01-2014, 07:24 PM   #4
Junior Member
 
Join Date: Aug 2014
Location: Danville
Posts: 18
the owners manual says not to use one...new to this...just don't want to void the warranty
MikenKaren is offline   Reply With Quote
Old 08-01-2014, 07:32 PM   #5
Senior Member
 
tnchuck100's Avatar
 
Join Date: Jun 2012
Location: Sparta, TN
Posts: 1,174
There is NOTHING wrong with using the proper 50 amp male to 30 amp female dogbone adapter. It will NOT harm your trailer. It will NOT void your warranty. The lawyers for the manufacturer make them put that warning in the manual. It is just lawyer crap.
__________________
Chuck - Sparta, TN
2012 Jay Flight 22FB, 2 x Honda EU2000i
2013 GMC Yukon XL Denali AWD

EDUCATION is what you get when you read the fine print.....
EXPERIENCE is what you get when you don't.
tnchuck100 is offline   Reply With Quote
Old 08-01-2014, 07:37 PM   #6
Senior Member
 
Join Date: May 2014
Location: VA
Posts: 394
50 amp only campgrounds are not common around here. Matter of fact, I have never seen one.
I do believe this is the adapter you would need.
Shouldn't be an issue.
__________________
2005 Dodge Ram 1500 Quad Cab 5.7 HEMI
2̶0̶1̶4̶ ̶J̶a̶y̶ ̶F̶e̶a̶t̶h̶e̶r̶ ̶X̶1̶9̶H̶
howie is offline   Reply With Quote
Old 08-01-2014, 07:42 PM   #7
Senior Member
 
tnchuck100's Avatar
 
Join Date: Jun 2012
Location: Sparta, TN
Posts: 1,174
The dogbone type is preferable to the hockey puck type. The hockey puck type tend to overheat under heavy load.
__________________
Chuck - Sparta, TN
2012 Jay Flight 22FB, 2 x Honda EU2000i
2013 GMC Yukon XL Denali AWD

EDUCATION is what you get when you read the fine print.....
EXPERIENCE is what you get when you don't.
tnchuck100 is offline   Reply With Quote
Old 08-01-2014, 08:16 PM   #8
Senior Member
 
Join Date: Oct 2011
Location: Central California
Posts: 2,283
I've never seen a 50 Amp only CG. My experience is CG list the highest capacity, everything less is there too. Last week, the box at my campsite had 20A, 30A & 50A outlets and breakers.
__________________
2020 Ram 1500 5.7L
2007 Chevy Duramax LMM/Allison (Sold)
2012 Jay Flight 29QBH (Sold)
2012 Jay Flight 26BH (Sold)
clubhouse is offline   Reply With Quote
Old 08-01-2014, 08:21 PM   #9
Senior Member
 
RoyBraddy's Avatar
 
Join Date: Sep 2011
Location: King George
Posts: 2,761
X2 on the dogbone type. they are also available from most WALMARTS..

Will look like this google image...



As you can see from this DMBRUSS diagram only one 50A Leg is connected to your 30A trailer.


Most of us carry all the necessary ADAPTERs to get going when at the different pedestals we run into at the campgrounds. A necessary PLAN B item to have with you...

Roy Ken
__________________
Roy and Carolyn
I claim Horse Creek Country in Southern Ill - Momabear is from North Texas
We live in King George VA
RETIRED DOD DOAF DON CONTRACTOR Electronics Tech 42YRS

"We're burning daylight" - John Wayne
2008 STARCRAFT 14RT OFF-ROAD POPUP with PD9260C and three 85AH 12VDC batteries
2010 F150 FX4 5.4 GAS with 3.73 gears - Super Cab - Towing Package - 2KW Honda EU2000i Gen
K9PHT (since 1957) 146.52Mhz
"We always have a PLAN B"
RoyBraddy is offline   Reply With Quote
Old 08-01-2014, 08:22 PM   #10
Site Team
 
FPM III's Avatar
 
Join Date: Nov 2010
Location: Fayette Ridges of PA, USA
Posts: 5,252
Another reason for using a 50A socket even if 30A is Available

If the 30A socket doesn't feel "tight" when I plug into it, I'll use my 50A to 30A adapter and plug into the 50A socket because they tend to be used less often and therefore have less wear.
__________________
MODERATOR

TV: 2009 GMC Sierra 2500HD | Crew Cab | Std. Box | 4WD | Duramax/Allison
RV: 2000 Jayco Eagle 266 | FBS | TT
PREVIOUS: 1986 Coleman Laramie pop-up -- Still in the family!!!

FPM III is offline   Reply With Quote
Old 08-01-2014, 08:26 PM   #11
Senior Member
 
lx22f/c's Avatar
 
Join Date: Feb 2012
Location: Friendswood
Posts: 917
Quote:
Originally Posted by clubhouse View Post
I've never seen a 50 Amp only CG. My experience is CG list the highest capacity, everything less is there too. Last week, the box at my campsite had 20A, 30A & 50A outlets and breakers.

X2
lx22f/c is offline   Reply With Quote
Old 08-01-2014, 08:52 PM   #12
Junior Member
 
Brownjm's Avatar
 
Join Date: Jun 2014
Location: Mason, MI
Posts: 24
You can get the dog bone adapter at Menards (if there is one in your area) in the electrical department. I don't remember the cost.
__________________
2014 X23B
2008 Ford Explorer 4.6L V8
Brownjm is offline   Reply With Quote
Old 08-02-2014, 04:12 AM   #13
Senior Member
 
mcfarmall's Avatar
 
Join Date: Jun 2011
Location: Kalamazoo, West Michigan
Posts: 1,817
Quote:
Originally Posted by MikenKaren View Post
New jayco owner, can't I camp at a campgroung that only has 50 service with my 30 amp camper ? manual says no adaptors of any kind...could damage my electrical system ?
*************SARCASM WARNING***********************

For your own personal safety, you should not use your new camper.

************END OF SARCASM**************************

Gotta love the first 20 pages of any owners manual. I'm glad Bic razors don't come with an owners manual or I'd look like ZZ Top.
__________________
2006 23B Hybrid with 10k round bar WDH
2011 F150 4x4 SCREW Ecoboost, Max Tow, Integrated TBC, 3.73 LS axle, Firestone Ride Rite airbags.
mcfarmall is offline   Reply With Quote
Old 08-02-2014, 05:47 AM   #14
Senior Member
 
Join Date: May 2014
Location: VA
Posts: 394
Quote:
Originally Posted by RoyBraddy View Post
X2 on the dogbone type. they are also available from most WALMARTS..

Will look like this google image...



Roy Ken
Not at any of the Wal Marts near me.
__________________
2005 Dodge Ram 1500 Quad Cab 5.7 HEMI
2̶0̶1̶4̶ ̶J̶a̶y̶ ̶F̶e̶a̶t̶h̶e̶r̶ ̶X̶1̶9̶H̶
howie is offline   Reply With Quote
Old 08-02-2014, 08:44 AM   #15
Senior Member
 
Join Date: May 2013
Location: Dale Hollow Lake Tn/Ky
Posts: 2,525
Remember the service rating is referring to "max" amps available. Your 30A system is protected with a 30a breaker and you can't pull more than that thru your converter without popping the breaker. Plugging into a 50a service will still supply you with 110V power just like a 30a service. there is the potential for a larger amp load from a 50a service, but your system is protected and will not allow more than a 30a draw. Put another way, many CG water systems have very high PSI that would damage your internal plumbing if attached directly to the RV. You should always use a pressure restrictor to limit the pressure getting into your camper. The 30a breaker in your converter does the same thing.

Get yourself one of the dogbone addapters others have suggested and I would also suggest you get a 30a to 15a adapter so you can plug in to a standard outlet in your garage or while spending a night at a friends house.
Bassdogs is offline   Reply With Quote
Old 08-02-2014, 09:45 AM   #16
Site Team
 
norty1's Avatar
 
Join Date: Jan 2011
Location: James Island, SC
Posts: 22,843
Look in the camping section near hardware.
__________________
Moderator
2011- 351RLTS Eagle, MorRyde suspension/pin box,
2017- F350 6.7 PSD Lariat FX4,SRW, SB,CC
Hughes PWD SP-50A, TST TPMS
Gator roll-up bed cover
B&W Turnover ball, Companion Std hitch
Can't find what you're looking on JOF? Try Jayco Owners Forum Custom Google Search
norty1 is offline   Reply With Quote
Old 08-02-2014, 12:30 PM   #17
Senior Member
 
Join Date: Apr 2011
Posts: 248
Amazon can be your friend.
campingva is offline   Reply With Quote
Old 08-02-2014, 01:35 PM   #18
Senior Member
 
ChuckD37's Avatar
 
Join Date: Apr 2013
Location: Beautiful Southern Oregon
Posts: 105
Quote:
Originally Posted by FPM III View Post
If the 30A socket doesn't feel "tight" when I plug into it, I'll use my 50A to 30A adapter and plug into the 50A socket because they tend to be used less often and therefore have less wear.
That is the main reason I carry the adapter. Many 30 amp receptacles are over used and are bad connections. I have never had a problem with it.
__________________
[SIGPIC]
ChuckD
From Beautiful Southern Oregon
2017Jayco Precept
towing a 2007 Honda CR-V
ChuckD37 is offline   Reply With Quote
Old 08-02-2014, 01:51 PM   #19
Senior Member
 
Join Date: May 2012
Location: Sebastian FL
Posts: 196
When I bought my first camper 7 years ago, the dealer told me I should take the 50-30 amp adapter as part of their "free kit". He assured me that most CG's were changing over and would only have 50A service. I have never had to use it.
__________________

John & Nancy
Jay Feather 25Z 2007
Ford F-150 XLT 5.4 Triton 2008
TeamFoxy is offline   Reply With Quote
Old 08-02-2014, 03:49 PM   #20
Senior Member
 
troutslayer's Avatar
 
Join Date: Dec 2012
Location: NW AR (God's Country)
Posts: 2,051
Quote:
Originally Posted by FPM III View Post
If the 30A socket doesn't feel "tight" when I plug into it, I'll use my 50A to 30A adapter and plug into the 50A socket because they tend to be used less often and therefore have less wear.
I generally wrap a bungee cord around the plug (of my surge protector) and the post. That seems to keep it tight in the 30 amp socket. BTW, I also wrap Glad Press'N Seal around where the RV cord plugs into the surge protector because it usually hangs out of the post box and is subject to getting wet. The Press'N Seal keeps the connection dry. Just some additional "garbage info" for ya'
__________________
Skip

2012 Eagle Super Lite HT 26.5RKS
2005 GMC 2500 SLT HD D/A
troutslayer is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 04:37 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.