Old 05-12-2018, 09:48 AM   #21
Senior Member
 
Join Date: Jan 2018
Location: SW
Posts: 513
Quote:
Originally Posted by CoCanCarv View Post
You do not have a combined current of a 100amps on a 50 amp breaker. Each phase of that breaker will not exceed 50 amps for more then six seconds overload and .01 seconds of over current.
That's not what I said.

Quote:

Each of these [two] phases are capable of supplying 50 amps of current (6k watts) at 120 volts AC, for a combined total current of 100 amps (or 12k watts) at 120 volts AC. That's why there are two 50 amp breakers (one for each phase or leg) on an RV 50 amp power panel and/or pedestal.

In other words, you have access to a combined total current of 100 amps inside an RV with 50 amp service---with one caveat---no one, single load can exceed 50 amps. Yes, I could have stated this, but I thought it was understood by deduction. But, maybe not.

Hope this clarifies it for you.
CampNow is offline   Reply With Quote
Old 05-12-2018, 09:57 AM   #22
Senior Member
 
Vicr's Avatar
 
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,862
[QUOTE=CampNow;638455]That's not what I said.

Quote:

Each of these [two] phases are capable of supplying 50 amps of current (6k watts) at 120 volts AC, for a combined total current of 100 amps (or 12k watts) at 120 volts AC. That's why there are two 50 amp breakers (one for each phase or leg) on an RV 50 amp power panel and/or pedestal.

Two 50amp breakers would be a code violation. There is a 50 amp 2pole breaker. As long as people want to try and be exact let's do that. Yes, I'm an electrician. Only for the last 35 years though.
Vicr is offline   Reply With Quote
Old 05-12-2018, 10:05 AM   #23
Senior Member
 
wags999's Avatar
 
Join Date: Jan 2015
Location: Surprise
Posts: 2,623
[QUOTE=Vicr;638461]
Quote:
Originally Posted by CampNow View Post
That's not what I said.

Quote:

Each of these [two] phases are capable of supplying 50 amps of current (6k watts) at 120 volts AC, for a combined total current of 100 amps (or 12k watts) at 120 volts AC. That's why there are two 50 amp breakers (one for each phase or leg) on an RV 50 amp power panel and/or pedestal.

Two 50amp breakers would be a code violation. There is a 50 amp 2pole breaker. As long as people want to try and be exact let's do that. Yes, I'm an electrician. Only for the last 35 years though.
I think what he was saying, once inside the RV the power is typically utilized as 2 50 amp 120 volt circuits. Which is true. Were all saying the same thing just terminology. You know in fact, a double pole breaker is no different than two single pole breakers of the same amperage, they are merely connected together so if 1 trips they both trip. It also ensures correct phasing.

Happy Camping..
__________________
2011 Toyota Tundra double cab
2015 27RLS


wags999 is offline   Reply With Quote
Old 05-12-2018, 11:13 AM   #24
Site Team
 
norty1's Avatar
 
Join Date: Jan 2011
Location: James Island, SC
Posts: 22,767
I went back and reviewed the last sentence of post#3.
__________________
Moderator
2011- 351RLTS Eagle, MorRyde suspension/pin box,
2017- F350 6.7 PSD Lariat FX4,SRW, SB,CC
Hughes PWD SP-50A, TST TPMS
Gator roll-up bed cover
B&W Turnover ball, Companion Std hitch
Can't find what you're looking on JOF? Try Jayco Owners Forum Custom Google Search
norty1 is offline   Reply With Quote
Old 05-12-2018, 01:14 PM   #25
Senior Member
 
Join Date: Jan 2018
Location: SW
Posts: 513
Quote:
Originally Posted by Vicr View Post
Two 50amp breakers would be a code violation. There is a 50 amp 2pole breaker. As long as people want to try and be exact let's do that. Yes, I'm an electrician. Only for the last 35 years though.
Yes, I agree code compliance is important. However, the fact remains, a "50 amp 2-pole breaker" is comprised of two, electrically discrete, 50 amp breakers, mechanically ganged together. This mechanical linkage forces both breakers to trip/open together at the same time when an over-current condition arises on either circuit.

The fact they are mechanically ganged together has no bearing on how they operate, electrically, under normal conditions---it only becomes an issue when an over-current situation occurs. As far as I know we're not discussing over-current scenarios---just normal operation.

However, if you feel the need to address an over-current scenario, please feel free to elaborate further.
CampNow is offline   Reply With Quote
Old 05-12-2018, 07:11 PM   #26
Senior Member
 
Join Date: Dec 2012
Location: Southern Indiana
Posts: 3,203
I know virtually nothing about electricity because for some reason I can't grasp the whole concept of the ''neutral'' thing. The biggest thing I've ever done was wire in a dimmer switch that controlled 2 lights and didn't kill myself. I like these threads because I can actually learn something but they usually get the ax. Thx for education so far.
__________________
2012 Eagle 320 RLDS
2017 Ford F-250 FX4 Crew STX 6.2l
3.73 E-locker
TCNashville is offline   Reply With Quote
Old 05-12-2018, 07:26 PM   #27
Senior Member
 
Bookemdanno's Avatar
 
Join Date: Jan 2015
Location: DFW
Posts: 3,493
I went to High Voltage school a couple of weeks ago...just don't touch a neutral & a hot at the same time and all will be good!
__________________
Dan
'24 GMC 2500 AT4X AEV Edition
Bookemdanno is offline   Reply With Quote
Old 05-12-2018, 08:11 PM   #28
Senior Member
 
Join Date: Dec 2012
Location: Southern Indiana
Posts: 3,203
Quote:
Originally Posted by Bookemdanno View Post
I went to High Voltage school a couple of weeks ago...just don't touch a neutral & a hot at the same time and all will be good!
Thanks Dan! So a neutral is the same thing as a ground, right? Or not. I'll figure it out someday, or not.
__________________
2012 Eagle 320 RLDS
2017 Ford F-250 FX4 Crew STX 6.2l
3.73 E-locker
TCNashville is offline   Reply With Quote
Old 05-12-2018, 08:47 PM   #29
Senior Member
 
Bookemdanno's Avatar
 
Join Date: Jan 2015
Location: DFW
Posts: 3,493
Quote:
Originally Posted by TCNashville View Post
Thanks Dan! So a neutral is the same thing as a ground, right? Or not. I'll figure it out someday, or not.
Sort of...not necessarily the same thing, but the ground "typically" can tie into the neutral...but not always??? I know it makes NO sense. The videos I attached are what they used at the school I attended...It's about 9 minutes each, but let me warn you they're OLD, but very basic! It basically explains A/C power (power from plugging into the grid) & D/C power (power from a battery). Below are the 2 videos that I thought gave the best/basic information and I think might be applicable to you.



Hope they help you out.
__________________
Dan
'24 GMC 2500 AT4X AEV Edition
Bookemdanno is offline   Reply With Quote
Old 05-13-2018, 05:41 AM   #30
Senior Member
 
Join Date: May 2017
Location: Brunswick
Posts: 491
Quote:
Originally Posted by Fr8Train View Post
My 5er is a 50 amp, is it 120 or 240? My plug has 2 blue led sometimes only one is on and other both are on. Am curious as to if the leds are showing one or two legs.
We have the same plug on our Bungalow. According to the cord, no LEDs on means no power, one LED on means one leg is powered. Both LEDs on means both legs are powered.

-Michael
michael.g is offline   Reply With Quote
Old 05-13-2018, 06:43 AM   #31
Senior Member
 
Join Date: Oct 2016
Location: McCalla, AL
Posts: 1,228
Everyone should have a EMS. Especially with a 50 amp RV. You can have major damage if you lose a neutral. The cost of potential damage is way more than the cost of a EMS.
2naEagle is offline   Reply With Quote
Old 05-13-2018, 06:44 AM   #32
Site Team
 
norty1's Avatar
 
Join Date: Jan 2011
Location: James Island, SC
Posts: 22,767
One of my favorite memories from Basic electronics school at Biloxi AFB was touching the terminals of a charged capacitor.

That's a lesson you never forget!
__________________
Moderator
2011- 351RLTS Eagle, MorRyde suspension/pin box,
2017- F350 6.7 PSD Lariat FX4,SRW, SB,CC
Hughes PWD SP-50A, TST TPMS
Gator roll-up bed cover
B&W Turnover ball, Companion Std hitch
Can't find what you're looking on JOF? Try Jayco Owners Forum Custom Google Search
norty1 is offline   Reply With Quote
Old 05-13-2018, 07:29 AM   #33
Senior Member
 
WinnieView's Avatar
 
Join Date: Nov 2017
Location: anytown
Posts: 1,751
Quote:
Originally Posted by norty1 View Post
One of my favorite memories from Basic electronics school at Biloxi AFB was touching the terminals of a charged capacitor.

That's a lesson you never forget!
DeVry Institute electronics technician program in the mid-80s first day of lab learning how make a solder ladder.
WinnieView is offline   Reply With Quote
Old 05-13-2018, 09:23 AM   #34
Senior Member
 
Join Date: Jan 2018
Location: SW
Posts: 513
Quote:
Originally Posted by norty1 View Post
One of my favorite memories from Basic electronics school at Biloxi AFB was touching the terminals of a charged capacitor.

That's a lesson you never forget!
You, too?! I was at Biloxi (many, many years ago--lol!) for the same school. I remember a few folks (myself included) inadvertently discharging a few caps with a probe, or a hand. The big power supply caps are the ones that really get your attention!
CampNow is offline   Reply With Quote
Old 05-30-2018, 01:20 PM   #35
Junior Member
 
Join Date: Sep 2016
Location: Eustis
Posts: 5
50 amp power

Quote:
Originally Posted by wags999 View Post
Duh. Yes you only see a 240 volt line in 3 phase.. where you have two 120 volt lines and one 240 volt lines.. used commercially only.

If your powering your dryer with 240 line it does mean you have 2 120 volt PHASED lines coming to it. That IS the definition of a 240 volt system. If you check across the two 120 volt lines you will get 240 volts because it's phased. Even commercial dryers are wired exactly the same. Some industrial equipment, like the sander and edgebanders I had uses 3 phase and yes one of the lines IS 240 volt.
240 AC is not 3 phase power. 3 phase power normally reads 208 volts on each leg if I remember correctly. However, most comments were correct about 240 at the pedestal. Inside the RV, there are no 240 circuits. One comment was that with 2 AC's, each is on a separate leg, receiving 120 volts. This is correct. When you plug a 50 amp RV into a 30 amp circuit, both RV legs are shorted together to provide 120 volts to each side of the fuse box in the RV. The RV site at my brothers house is just a single 50 amp line running to a 50 amp receptacle, with the two hot terminals shorted together. Works fine. Technically speaking, a properly wired 50 amp pedestal is actually providing 100 amps; 50 amps to each 120 volt leg.
NickMurabito is offline   Reply With Quote
Old 05-30-2018, 01:28 PM   #36
Junior Member
 
Join Date: Sep 2016
Location: Eustis
Posts: 5
I remember when I was in High School, attending an Electronics Tech program. We would toss a charged capacitor to a new student. It did get there attention. My electronics training came from the US Navy. One year in ET A school at Great Lakes Naval Training Center, and later, a second year of ET B school at the Treasure Island Naval Training Center located in the San Fransisco Bay, CA. Loved it.
NickMurabito is offline   Reply With Quote
Old 05-30-2018, 01:53 PM   #37
Site Team
 
norty1's Avatar
 
Join Date: Jan 2011
Location: James Island, SC
Posts: 22,767
Quote:
Originally Posted by CampNow View Post
You, too?! I was at Biloxi (many, many years ago--lol!) for the same school. I remember a few folks (myself included) inadvertently discharging a few caps with a probe, or a hand. The big power supply caps are the ones that really get your attention!
Yep, I spent a year there in 1961, ATC Radar Repair.
__________________
Moderator
2011- 351RLTS Eagle, MorRyde suspension/pin box,
2017- F350 6.7 PSD Lariat FX4,SRW, SB,CC
Hughes PWD SP-50A, TST TPMS
Gator roll-up bed cover
B&W Turnover ball, Companion Std hitch
Can't find what you're looking on JOF? Try Jayco Owners Forum Custom Google Search
norty1 is offline   Reply With Quote
Old 05-30-2018, 06:52 PM   #38
Junior Member
 
tom0329's Avatar
 
Join Date: Apr 2018
Location: Bowling Green
Posts: 5
2 120 legs 2 30 amp breakers = 50 amp 240. Measure it at your transfer switche
tom0329 is offline   Reply With Quote
Old 05-30-2018, 06:57 PM   #39
Senior Member
 
wags999's Avatar
 
Join Date: Jan 2015
Location: Surprise
Posts: 2,623
Quote:
Originally Posted by tom0329 View Post
2 120 legs 2 30 amp breakers = 50 amp 240. Measure it at your transfer switche
No that would get you 30 amp 240 volts... 2 50 amp breakers will give you 50 amps at 240 volts. But RV 30 amp power is a single leg 30 amps at 120 volts. RV 50 amp service is 2 50 amps at 120 volts or 100 amps total. Better way to tell how much power you have available is 30 amp service gives you 3600 watts of power at 120 volts... (Less amps as voltage drops). While 50 amp service gives you 12,000 watts of power at 120 volts.
__________________
2011 Toyota Tundra double cab
2015 27RLS


wags999 is offline   Reply With Quote
Old 05-30-2018, 10:05 PM   #40
Junior Member
 
Join Date: Aug 2017
Location: BUFFALO
Posts: 6
50 Amp question

An RV can have 240 volts at the plug. That means you have two wires which have 120V on each wire. If you measure across both wires you will read 240 volts. If you read one wire to your ground wire you will read 120 Volts. The power (hot) wires are normally located at the top or bottom of your RV electrical panel. Very few RV's have a 240V appliance. However like mentioned earlier the RV could have a 240 V dryer, but most are 120V.

Regarding power spikes these are extremely rare as they would come from the service that comes from the power company. What you will see more commonly is a power sag. That could be from a bad neutral. If the service is Underground and a gopher has eaten into it the neutral could be gone and that would cause a voltage sag when you turned on an electrical appliance such as an AC unit.

talking about 3 phase is irrelevant as no RV's that I have ever seen have 3 phase.

Not a genius electrician just a 40 year veteran in the electrical trade.
Scott1956 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 03:34 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.