Don’t do it.

If you have only a 15amp breaker circuit don’t use the ac. First there is an adapter dog bone…quality?
Then an extension cord… correct one? The prongs of the adapters dog bone is a 20amp design. Make sure the extension cord is proper gauge.
Long term use WILL cause arcing burns on the prongs that will then cause increased resistance.
Then there is the chance that your not just running the ac. Don’t under power your ac your asking for trouble..burn out your ac electrical stuff.
Get a 30 amp circuit installed or get a proper generator.
Grip is offline   Reply With Quote
Old 05-19-2021, 03:17 PM   #22
Junior Member
 
Join Date: Oct 2020
Location: gouldsbore
Posts: 28
I wouldn’t put anything less than a 20 amp circuit breaker with 12 gauge wire. If the CB breaker kicks when the A/C kicks on you might need a special CB to absorb the initial surge. Went I replaced my in house vacuum. It would occasionally kick the CB during start up. I contacted SQ D and their engineer told me what CB to use. Had to order off the internet. Elect supply houses didn’t carry it or know about it.
mrpavette is offline   Reply With Quote
Old 05-19-2021, 06:36 PM   #23
Member
 
Join Date: Feb 2014
Location: Pawleys Island
Posts: 69
Quote:
Originally Posted by Route 66 Traveler View Post
What size is the AC....13.5K or 15k? The starting current most likely will trip the breaker. Once running my 15k runs uses 12 & 14 amps.

If you connected it to a 20 amp outlet and installed a SoftStart it would run all day without a problem.

https://www.softstartrv.com//rvlife/?utm_CamperReport
I often run our smaller AC (13.5btu) with a standard 20amp house outlet. I do use the heavy 50amp cord and use just 1 dogbone to plug into the outlet. I used to go back and check the cord periodically, but it has never even been warm, even after extended use. I did double check to make sure no other heavy duty appliance is on that circuit.
RKHengst is offline   Reply With Quote
Old 05-20-2021, 07:12 AM   #24
Junior Member
 
Join Date: Dec 2020
Location: Chambersburg
Posts: 1
Quote:
Originally Posted by Grumpy View Post
Plug it in and try. Worst case scenario the breaker in the house will pop.
you could melt your plug or adapter
Jim in Pa is offline   Reply With Quote
Old 05-20-2021, 07:15 AM   #25
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 17,414
Quote:
Originally Posted by Jim in Pa View Post
you could melt your plug or adapter
Unlikely.. it would melt using any power source then, the current DRAW is always the same. Heat is based on the load, not what is providing the current.
__________________
DISNEY LOVERS
Grumpy is online now   Reply With Quote
Old 05-20-2021, 10:14 AM   #26
Senior Member
 
Vicr's Avatar
 
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,886
Quote:
Originally Posted by Jim in Pa View Post
you could melt your plug or adapter

How would a 13 amp load melt an adapter rated for 20 amps??
Vicr is offline   Reply With Quote
Old 05-20-2021, 10:16 AM   #27
Senior Member
 
Vicr's Avatar
 
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,886
Quote:
Originally Posted by mrpavette View Post
I wouldn’t put anything less than a 20 amp circuit breaker with 12 gauge wire. If the CB breaker kicks when the A/C kicks on you might need a special CB to absorb the initial surge. Went I replaced my in house vacuum. It would occasionally kick the CB during start up. I contacted SQ D and their engineer told me what CB to use. Had to order off the internet. Elect supply houses didn’t carry it or know about it.

They are called HACR breakers.


HACR stands for Heating, Air-Conditioning, and Refrigeration breaker. HACR rated breakers open within a specified time curve, similar to a fuse, to protect group motor equipment (fans for combustion air, exhaust control, heated air handling, AC compressors, etc).
Vicr is offline   Reply With Quote
Old 05-20-2021, 07:12 PM   #28
Junior Member
 
Join Date: May 2021
Location: St. Andrews
Posts: 17
Generally speaking you are limited to about 80% of the circuit interrupters labeled capacity. For a 15A breaker this is 12A or 1440Watts. This is why you never see an appliance that plugs into a 15A receptacle with a higher power requirement than 1500W.
This is due to design and also how thermal magnetic interrupters work. Since heat generated in a bimetallic strip is what causes them to open, they have what is known as a "trip curve" this is a relationship between current draw, and time at a given ambient temperature. It s not linear and in fact more similar to an inverse logarithmic curve. When you just enter the trip curve (generally above 80%) you could operate for hours, or minutes depending on the curve characteristics. Eventually the heat will build up enough to open the contacts. The more current you draw the quicker the contacts will open. There is a possibility the AC will work, since it wont run at 100% duty cycle. It will cycle on and off, likely providing time for the breaker to cool and not tip. Your best bet would be to check the nameplate on the AC and see what its current draw is. It its under 12A you are good, but likely don't expect to run too much more. If you do need the extra power, you could run a heavy 12GA extension cord from a 20A kitchen counter receptacle and use a 15-30A adapter built with 12GA or larger cable. the contacts on a 15A plug will handle the current since they are the same as on a 20A just oriented differently, just make sure the cord is short enough to not cause voltage drop and conductor heating.
internalvoice is offline   Reply With Quote
Old 05-20-2021, 07:17 PM   #29
Junior Member
 
Join Date: May 2021
Location: St. Andrews
Posts: 17
Quote:
Originally Posted by Vicr View Post
They are called HACR breakers.


HACR stands for Heating, Air-Conditioning, and Refrigeration breaker. HACR rated breakers open within a specified time curve, similar to a fuse, to protect group motor equipment (fans for combustion air, exhaust control, heated air handling, AC compressors, etc).

Also known as high magnetic and often found on lighting circuits with many inductive ballasts. They typically differentiate the part numbers from the standard trip curve with an added "H"
internalvoice is offline   Reply With Quote
Old 05-20-2021, 07:57 PM   #30
RPR
Senior Member
 
Join Date: Dec 2018
Location: Owens Cross Roads
Posts: 3,471
More info
Attached Thumbnails
5E3856EC-D6E9-4178-9163-6C9FD85EA946.jpg  
RPR is online now   Reply With Quote
Old 05-22-2021, 04:11 PM   #31
Senior Member
 
Bill Johnson's Avatar
 
Join Date: Sep 2019
Location: SOUTH BELOIT
Posts: 876
Quote:
Originally Posted by Highlander73 View Post
When we have our TT home and we are plugged in to shore power can we run the AC! The TT is 30amp and we only have 15 amp outlets. Living in AZ during summer makes running the AC almost a must if we are going to be in the rig for any length of time. I’m looking into having an 30amp outlet installed but in the short term can we Run the AC?
I was up at Lake puckaway this week fishing and one of the campground guys was telling me they have a 120 volt plug with 40 amps and the wiring meets code. I don't think I'll be bringing my motorhome up there, they have one seasonal spot I could park if the ground isn't too wet at the time
Bill Johnson is offline   Reply With Quote
Old 05-22-2021, 04:51 PM   #32
RPR
Senior Member
 
Join Date: Dec 2018
Location: Owens Cross Roads
Posts: 3,471
May be 50 amp rated 120 looking receptacles
Attached Thumbnails
1143364E-E5FE-4C1D-BB44-F659FEDCA6C9.jpg  
RPR is online now   Reply With Quote
Old 05-22-2021, 06:01 PM   #33
Senior Member
 
Bill Johnson's Avatar
 
Join Date: Sep 2019
Location: SOUTH BELOIT
Posts: 876
Quote:
Originally Posted by RPR View Post
May be 50 amp rated 120 looking receptacles
I told him I had a 50 amp plug and drew him a diagram of 50 amp and 30 amp he said I would need an adapter to a regular 120 house outlet. Before the owner told me there was nowhere to park and that I would need to boondock. I asked if there was a dump station and they said you can dump it in my farm field. This place is from the early 1950s. I guess I'll just stay in a cabin that is the same from 1954. It's just ruff staying with a chain smoker for a week. I feel like burning my clothes when I get home. I think I lose 2 weeks off my life every time I go
Bill Johnson is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 09:59 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.