Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
Jayco RV Owners Forum
 

Go Back   Jayco RV Owners Forum > Trailers, 5th Wheels, and Motorhomes > Jayco Toy Haulers
Click Here to Login

Reply
 
Thread Tools Search this Thread Display Modes
 
Old 10-09-2020, 09:11 AM   #21
Senior Member
 
Camper_bob's Avatar
 
Join Date: Sep 2013
Location: South Texas
Posts: 7,216
Yup.

And I'd be checking the wiring between the AC circuit breaker in the main panel and the AC unit itself (including the circuit breaker itself).

Have you tried bypassing the ATS by connecting generator output directly to the main panel?

You stated that the AC unit runs fine on shore power? Are you getting excessive heat at any of the junctions between shore power and AC unit?

There's a video on Youtube of how to check the various components in the AC unit (start capacitor, run capacitor, etc) with a volt meter and an amp meter.

https://youtu.be/3VckFAXg1CY

But given that the AC unit works fine on shore power, I'm wondering if you're going to find anything there...



Also, how long does the generator "try" to fire up the AC before it shuts down? Is it instant? Or does it bog down for a few seconds, then give up?
__________________

-2018 Greyhawk 29MV
-2020 Jeep Wrangler Unlimited (JLU) (Primary Toad)
-1994 Jeep Wrangler YJ (Secondary Toad)
-2014 Jay Flight 28BHBE & Ram 2500 6.4L CC 4x4 (sold)
Camper_bob is offline   Reply With Quote
Old 10-09-2020, 09:22 AM   #22
Senior Member
 
Cavie's Avatar
 
Join Date: Apr 2020
Location: Port Charlotte FL/Hinsdale MA.
Posts: 1,070
Quote:
Originally Posted by Camper_bob View Post
Yup.

And I'd be checking the wiring between the AC circuit breaker in the main panel and the AC unit itself (including the circuit breaker itself).

Have you tried bypassing the ATS by connecting generator output directly to the main panel?

You stated that the AC unit runs fine on shore power? Are you getting excessive heat at any of the junctions between shore power and AC unit?

There's a video on Youtube of how to check the various components in the AC unit (start capacitor, run capacitor, etc) with a volt meter and an amp meter.

https://youtu.be/3VckFAXg1CY

But given that the AC unit works fine on shore power, I'm wondering if you're going to find anything there...



Also, how long does the generator "try" to fire up the AC before it shuts down? Is it instant? Or does it bog down for a few seconds, then give up?
If it works on shore power as stated then there is no point in doing that.
__________________
Retired Master Electrician and Building Inspector.

2011 Keystone Sprinter 323 BH
Cavie is offline   Reply With Quote
Old 10-09-2020, 12:40 PM   #23
Senior Member
 
Camper_bob's Avatar
 
Join Date: Sep 2013
Location: South Texas
Posts: 7,216
Quote:
Originally Posted by Cavie View Post
If it works on shore power as stated then there is no point in doing that.
I'll defer to your electrical expertise here.

But a question: Could the AC unit work on shore power even with a loose connection in the line somewhere, and you might not notice as much until you start seeing smoke coming from the wires? Whereas the generator will "see" the voltage drop due to increased resistance and cut it off and throw a code?

That's an honest question.
__________________

-2018 Greyhawk 29MV
-2020 Jeep Wrangler Unlimited (JLU) (Primary Toad)
-1994 Jeep Wrangler YJ (Secondary Toad)
-2014 Jay Flight 28BHBE & Ram 2500 6.4L CC 4x4 (sold)
Camper_bob is offline   Reply With Quote
Old 10-09-2020, 02:37 PM   #24
Senior Member
 
JimD's Avatar
 
Join Date: Apr 2017
Location: Inland Empire, California
Posts: 2,005
Quote:
Originally Posted by Camper_bob View Post
I'll defer to your electrical expertise here.

But a question: Could the AC unit work on shore power even with a loose connection in the line somewhere, and you might not notice as much until you start seeing smoke coming from the wires? Whereas the generator will "see" the voltage drop due to increased resistance and cut it off and throw a code?

That's an honest question.
If there is resistance in the line the voltage drop would appear across the resistance and not at the generator. Say the generator was putting out 120 volts at 20 amps but that power was not reaching the AC unit because of the resistance. If you have only 2 ohms of resistance you would have a voltage drop of 40 volts across that resistance (I x R or current x resistance).

If the generator is seeing a voltage drop and throwing an error code because of it, I would suspect the resistance, if present, would be internal to the generator. That could be tested by monitoring its output voltage and adding in multiple loads and watching if the voltage drops off. The voltage should be farely constant up to the generator's capacity.
__________________


Jim

Retired electronic technician (45 years in the field)
2017 Greyhawk 29W (solar & many other mods)
wife (maybe I should have given her top billing)
JimD is offline   Reply With Quote
Old 10-09-2020, 02:57 PM   #25
Senior Member
 
2edgesword's Avatar
 
Join Date: Jul 2011
Location: Long Island, NY
Posts: 1,402
My thinking is if the A/C works on shore power and everything but the A/C works on generator power the issue is the A/C overloading the generator. The fact that everything is working via some power source pretty much rules out loose connections..
__________________

2018 Jayco 28RLS
2012 F-250 6.2L 3.73
Equalizer Hitch
Yamaha 2400ISHC
2edgesword is offline   Reply With Quote
Old 10-11-2020, 09:13 AM   #26
Junior Member
 
Join Date: Oct 2020
Location: New Caney
Posts: 17
Quote:
Originally Posted by Camper_bob View Post
Yup.

And I'd be checking the wiring between the AC circuit breaker in the main panel and the AC unit itself (including the circuit breaker itself).

Have you tried bypassing the ATS by connecting generator output directly to the main panel?

You stated that the AC unit runs fine on shore power? Are you getting excessive heat at any of the junctions between shore power and AC unit?

There's a video on Youtube of how to check the various components in the AC unit (start capacitor, run capacitor, etc) with a volt meter and an amp meter.

https://youtu.be/3VckFAXg1CY

But given that the AC unit works fine on shore power, I'm wondering if you're going to find anything there...



Also, how long does the generator "try" to fire up the AC before it shuts down? Is it instant? Or does it bog down for a few seconds, then give up?

it seems that it wants to try and cycle, but then the generator shuts down
Taylor O. is offline   Reply With Quote
Old 10-14-2020, 12:44 PM   #27
Junior Member
 
Join Date: Mar 2020
Location: Saint Amable
Posts: 15
https://www.microair.net/products/ea...nt=30176048267
Dan50 is offline   Reply With Quote
Old 10-14-2020, 01:41 PM   #28
Junior Member
 
LexGator's Avatar
 
Join Date: Sep 2020
Location: Lexington
Posts: 9
Install and ezstart - works like a charm

Quote:
Originally Posted by Taylor O. View Post
I need help, if anyone has experienced this, I would greatly appreciate a reply.
I have a 2012 Jayco ZX24 Octane Toy hauler with an Onan 4k generator. My current issue is when on Generator power, I start the A/C, when the compressor starts, it will kill the generator.
What I have done so far. The generator is running on fresh, non-ethanol fuel, the spark plug and air filter have been replaced, oil level is correct. A Hard Start Capacitor has been installed on the Coleman Mach Series, 15,000btu (a starting booster).
The ATS (automatic transfer switch) engages on generator, 120v reading. The electrical panel has had all of the circuit breakers turned off, leaving only the a/c breaker active. No electrical draws present. The generator is run to warm up, engage the blower to apply some load to the generator, after 2 minutes, engage the compressor, ATS begins clicking and the generator shuts down.
I have also started the generator, put a full electrical load on the system, all lights on, refrigerator, exhaust fans, microwave, TV, fans, the generator runs flawlessly.
Tested the ATS, when on generator power, 120v registered, on Shore Power 120v. When turning on the Generator, the ATS is a 120v until engaging the A/C, then the power drops to 6v and shuts off.
If on shore power, the a/c system works as designed, cools the camper to ice cold. Everything works as designed.
The generator restarts every time with no delay on restart.
If anyone has any input, I would be greatly appreciate any input

Taylor
I had the same issue - installed an ezstart - problem solved. Wish they put them on at the factory since this is a known issue.
LexGator is offline   Reply With Quote
Old 10-14-2020, 01:42 PM   #29
Member
 
Join Date: Sep 2020
Location: Anchorage
Posts: 36
as stated, you need to find out what the current draw is on startup. if it is higher than expected, the AC is at fault. if it is within spec, the generator is tripping too soon. bear in mind that shore power has unlimited current available at a stable regulated voltage. it is only limited by the circuit breaker. and thermal CBs (not magnetic) can take a momentary overload like excessive start current and not pop off
dogmeat is offline   Reply With Quote
Old 10-14-2020, 01:52 PM   #30
Junior Member
 
Join Date: Oct 2020
Location: New Caney
Posts: 17
Latest update

Checked the amp draw on the a/c system. While on shore power, a/c system draw was between 10.1-10.7 on 4 different test.
On generator power, tested between 10.5-11.2 on start up draw. A/c system tested within normal parameters For a Coleman Mach 15k unit
Taylor O. is offline   Reply With Quote
Old 10-14-2020, 01:55 PM   #31
Junior Member
 
Join Date: Oct 2020
Location: New Caney
Posts: 17
Generator is currently at Cummins for professional opinion starting at $175.00. I can’t wait to find out what I don’t know.
Taylor O. is offline   Reply With Quote
Old 10-14-2020, 02:55 PM   #32
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,098
Quote:
Originally Posted by Taylor O. View Post
Generator is currently at Cummins for professional opinion starting at $175.00. I can’t wait to find out what I don’t know.
We're all waiting with you.....
__________________
DISNEY LOVERS
Grumpy is online now   Reply With Quote
Old 10-14-2020, 03:12 PM   #33
Senior Member
 
Join Date: Oct 2018
Location: Out there somewhere
Posts: 1,620
[QUOTE=Taylor O.;904780]13, under voltage from what I can find.[/

Yes, please keep us “posted”!
Johnynorthland is offline   Reply With Quote
Old 10-14-2020, 04:18 PM   #34
Member
 
Join Date: Nov 2018
Location: Avonlea
Posts: 49
I think there is a safely on the generator if it draws too many watts it will shut down. We had that happen a few time if we had other electrical Items that happened to be on at the same time and it was drawing to many watts.
royphillips is offline   Reply With Quote
Old 10-14-2020, 04:59 PM   #35
Member
 
Join Date: Sep 2020
Location: Anchorage
Posts: 36
the math says he's drawing 1344 watts at start so a 1500 watt genset should be OK with that. of course the 11.2 amp reading mentioned in post 29 depends on if it was taken with a meter that is fast enough to capture the true max inrush current. once the compressor motor starts to turn the current will decrease
dogmeat is offline   Reply With Quote
Old 10-14-2020, 05:24 PM   #36
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,098
Quote:
Originally Posted by dogmeat View Post
the math says he's drawing 1344 watts at start so a 1500 watt genset should be OK with that.
It's a 4000 watt geny.
__________________
DISNEY LOVERS
Grumpy is online now   Reply With Quote
Old 10-14-2020, 05:43 PM   #37
Member
 
Join Date: Sep 2020
Location: Anchorage
Posts: 36
yep, and 1500 is all you need
dogmeat is offline   Reply With Quote
Old 10-14-2020, 06:11 PM   #38
Senior Member
 
2edgesword's Avatar
 
Join Date: Jul 2011
Location: Long Island, NY
Posts: 1,402
Quote:
Originally Posted by dogmeat View Post
the math says he's drawing 1344 watts at start so a 1500 watt genset should be OK with that. of course the 11.2 amp reading mentioned in post 29 depends on if it was taken with a meter that is fast enough to capture the true max inrush current. once the compressor motor starts to turn the current will decrease
I'm not sure how you calculate 1344 watts at startup but I'm 99% sure that can't be accurate. A 1344 watt startup means an 11.2A current draw. The running current may be 11.2A but starting current is going to be much higher. One estimate I read for a 15K A/C was 3500 watts which at 120V would be 29A, a more realistic based on the numbers I've seen with my 13.5K btu A/C. That 29A would be for a new A/C. As the A/C gets older the power to start it increases. Couple that with the fact that as generators age they become less efficient and my feeling is still that the A/C startup is knocking the generator into overload mode.
2edgesword is offline   Reply With Quote
Old 10-14-2020, 06:34 PM   #39
Member
 
Join Date: Sep 2020
Location: Anchorage
Posts: 36
well... post #30 he says the start draw was tested and 11.2 was the highest, and within specs. I can't tell you if thats true because I didn't check it. also, as I noted, you need to test with a meter that has a fast enough processor time to read the inrush accurately.

and I agree... that inrush number sounds low.
dogmeat is offline   Reply With Quote
Old 10-15-2020, 07:49 AM   #40
Senior Member
 
Camper_bob's Avatar
 
Join Date: Sep 2013
Location: South Texas
Posts: 7,216
There's no way the startup amperage is that low, that's going to be running amps. The "locked rotor amperage" on a Coleman 15K unit is 61A.

That's why I was wondering if OP could start his microwave and maybe a hair dryer at the same time while on genny power. If you could replicate the startup amperage the AC unit requires, you might be able to prove out that it's the generator and not something else.

I'm wondering if the generator "hiccups" when lesser draws are applied, and how severe that hiccup is? Mine is in good running condition, and will run both of my ACs just fine (1x11,000 and 1x13,500 HE). And you can hear the generator "hiccup" when I turn on the microwave (I don't do that with both ACs running usually).

OP also mentioned he installed a start capacitor in the AC unit. That SHOULD be helping with locked rotor amperage required at startup.

On shore power, it should be able to pull as much amperage as it needs to start up. At least momentarily, before it opens a breaker. In the case of a generator, the sudden amp draw has to be compensated for with the engine, and it may just not be healthy enough to overcome that sudden kick. Hence why it "tries" for a few seconds and then gives up (so it doesn't cause more damage to the generator or the compressor).

An example from my own experience is my generator was running hot one day. My AC went to kick on, and the generator couldn't supply the required startup amperage, and so it bogged down the generator and the AC compressor. The AC tried to startup, and the generator engine tried to rev up to provide the power, but just couldn't make it. I hopped up like a jack rabbit and cut the AC off as fast as I could to limit damage from an undervolt condition.

This was from a generator that was WELL more than big enough to run my entire trailer in normal circumstances. But since it was borderline overheating, when the AC kicked on, it couldn't supply the required juice. Shore power would not have that problem.

I'm thinking there's something wrong with the generator in this case. Could be as simple as not enough ventilation (which is a common problem), a gummed up carb, a faulty/failing fuel pump, a clogged fuel filter... Or worst case scenario, something in the windings or stator inside the generator...

I'll be interested to read what OP discovers.
__________________

-2018 Greyhawk 29MV
-2020 Jeep Wrangler Unlimited (JLU) (Primary Toad)
-1994 Jeep Wrangler YJ (Secondary Toad)
-2014 Jay Flight 28BHBE & Ram 2500 6.4L CC 4x4 (sold)
Camper_bob is offline   Reply With Quote
Reply

Tags
a/c, generator shuts


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 03:17 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.