Quote:
Originally Posted by mjlaupp
...When the the EMS restores power to the RV, the A/C circulation fan starts immediately and the compressor starts after the 3 minute thermostat delay. I don't see how the additional EMS 136 second delay would provide any additional protection. ...
|
You're digital T-Stat runs of DC power. So if you only lose AC power, your T-Stat is still getting power from the RV Battery. Therefore, when AC power is restored, you won't get the 3 minute delay at the T-Stat because it never lost power.
So, if the A/C was running when you had a short intermittent AC power failure, the T-Stat would command the A/C to run immediately when power is restored and you could get into an overload condition.
The 3 minute delay at the T-Stat is to protect from toggling the A/C on & off rapidly at the T-Stat.
A simple test to confirm this would be:
Test 1. Run your A/C for a little bit, turn the T-Stat A/C off and then A/C back on, there'll be ~3 min delay before the A/C compressor comes back on.
Test 2. Run your A/C for a little bit, then turn AC power off (by either toggling the breaker in the control panel or at the power post) then turn AC power back on. The A/C compressor will come back on as soon as AC power is turned back on.
Caution on Test 2, DO NOT do this if the A/C has been running a long time.
Only do it when the A/C hasn't been run and DO NOT have the A/C running long before cycling A/C power. Only run the A/C a short time, 30 sec to less then 1 minute before cycling A/C power so the A/C unit doesn't achieve full pressurization.