50 amp to 30 amp adapter?

Does anyone have experience with an adapter that lets you plug a 30 amp cord into a 50 amp receptacle? Are they safe?

We're stopping at a location that only has 50 amp service available, and we have 30 amp service. I'll buy an adapter if they are safe, but I have a portable generator I can use if the adapters cause problems.

Thanks in advance.
__________________

OnTheGo is offline   Reply With Quote
Old 03-21-2014, 07:29 PM   #2
Senior Member
 
Join Date: Jan 2014
Location: Aurora CO
Posts: 2,336
I wouldn't

The other way makes sense, where the maximum current from the source is fused at 30 amps, going through a 50 amp rated wire, but I would never allow a potential of 50 amp draw run through a 30 amp wire.

That has fire hazard written all over it.
__________________

__________________
Jim & Kim from Colorado

2014 Eagle 30.5 RLS
2015 Dodge 3500HD SRW 6.7L
Click on my profile for Mods and notes
Jmooney is offline   Reply With Quote
Old 03-21-2014, 07:31 PM   #3
Senior Member
 
Join Date: Jan 2014
Location: Aurora CO
Posts: 2,336
Usually , when the CG says 50 amp service, the electrical box has all three: 50, 30 and 20 amp receptacles


I've never seen a connection that only has a 50 amp plug
__________________
Jim & Kim from Colorado

2014 Eagle 30.5 RLS
2015 Dodge 3500HD SRW 6.7L
Click on my profile for Mods and notes
Jmooney is offline   Reply With Quote
Old 03-21-2014, 07:36 PM   #4
Senior Member
 
Join Date: May 2012
Location: Boston
Posts: 664
I have one like this:
http://www.amazon.com/Voltec-16-0050...amp+rv+adapter

Some people like to plug into the 50amp service because they are usually less worn than the 30amp receptacles. I have only connected that way once, and I think it was for 4 nights with the AC running and had no issues.
__________________

2013 White Hawk 28 DSBH
2011 Jay Feather X23J (traded-in)
2011 Ford F-150 XLT w/towing package
RoadMaster Active Suspension
Reese Trunnion Bar WDH w/Dual Cam sway control
jdorant is offline   Reply With Quote
Old 03-21-2014, 08:10 PM   #5
Senior Member
 
dalenoel's Avatar
 
Join Date: Nov 2010
Location: SE, MI
Posts: 3,517
You'll find many newer or upgraded campgrounds that can supply this for you. Your TT will have breakers that will limit how much you draw so they will trip first before you exceed the amount of current your main cable can stand.
__________________
2008 Jayco 322FKS, Hemi, Hensley, Oreo the Malshi, DW and I

Tracking campgrounds with Ultimate Campground Log
dalenoel is offline   Reply With Quote
Old 03-21-2014, 08:25 PM   #6
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 5,041
Quote:
Originally Posted by dalenoel View Post
You'll find many newer or upgraded campgrounds that can supply this for you. Your TT will have breakers that will limit how much you draw so they will trip first before you exceed the amount of current your main cable can stand.
X2 You will not overload your cord. We used a 50 to 30 adapter for years when we had a 30 amp rig.
__________________
DISNEY LOVERS
PINNACLE 2015 38FLSA. aka: "Roam Sweet Home"
Grumpy is offline   Reply With Quote
Old 03-21-2014, 08:31 PM   #7
Senior Member
 
mcfarmall's Avatar
 
Join Date: Jun 2011
Location: Kalamazoo, West Michigan
Posts: 1,814
Quote:
Originally Posted by Jmooney View Post
I wouldn't

The other way makes sense, where the maximum current from the source is fused at 30 amps, going through a 50 amp rated wire, but I would never allow a potential of 50 amp draw run through a 30 amp wire.

That has fire hazard written all over it.
I would.

Your trailer has a 30 amp main breaker at the converter doesn't it? If the load inside your trailer exceeds 30 amps it will trip protecting the downstream (load) and the upstream (line) wire. If your 30 amp cord is plugged into a 50 amp receptacle and a tree branch falls on your shore power cord shorting the hot to ground or neutral the breaker will trip once again protecting the wire.

The 18 gauge wire on your table lamp in the living room is plugged into a 15 or 20 amp circuit that far exceeds the ampacity of the lamp cord but you have been living that way for how many years?
__________________
2006 23B Hybrid with 10k round bar WDH
2011 F150 4x4 SCREW Ecoboost, Max Tow, Integrated TBC, 3.73 LS axle, Firestone Ride Rite airbags.
mcfarmall is offline   Reply With Quote
Old 03-21-2014, 09:20 PM   #8
Senior Member
 
Jagiven's Avatar
 
Join Date: May 2012
Location: Minnesota
Posts: 4,114
I own an adapter but have never used it. In my opinion it is not as safe as using the proper socket. Some say you are protected, because you have a 30 amp breaker in the tt. I disagree, as the cord between the tt breaker panel and the electrical post has the potential of 50 amps power draw and it is not rated for that much current. In reality the the only issue would be from a short in the power cord not tripping the breaker soon enough to protect you from a potential fire.
Jagiven is offline   Reply With Quote
Old 03-21-2014, 11:07 PM   #9
Senior Member
 
Join Date: Jan 2014
Location: Aurora CO
Posts: 2,336
Quote:
Originally Posted by mcfarmall View Post
I would.

Your trailer has a 30 amp main breaker at the converter doesn't it? If the load inside your trailer exceeds 30 amps it will trip protecting the downstream (load) and the upstream (line) wire. If your 30 amp cord is plugged into a 50 amp receptacle and a tree branch falls on your shore power cord shorting the hot to ground or neutral the breaker will trip once again protecting the wire.

The 18 gauge wire on your table lamp in the living room is plugged into a 15 or 20 amp circuit that far exceeds the ampacity of the lamp cord but you have been living that way for how many years?

Interesting. Hadn't thought about it that way. The lamp itself only draws an amp or so, but it's the same principle: smaller gauge downstream from higher possible supply

Still makes me cringe a bit
__________________
Jim & Kim from Colorado

2014 Eagle 30.5 RLS
2015 Dodge 3500HD SRW 6.7L
Click on my profile for Mods and notes
Jmooney is offline   Reply With Quote
Old 03-22-2014, 12:16 AM   #10
Senior Member
 
Join Date: Jul 2013
Location: Renton
Posts: 516
I have one from Amazon. They are safe. What would not be safe is what other people have done which is they don't want to pay for or store a 50 amp cord so they use a 50 to 30 amp adapter to run a 30 amp extension cord then a 30 amp to 50 amp adapter. This is unsafe because you are actually drawing 50 amps (single phase) through a 30 amp cord. Since you have a 30 amp RV you can only pull 30 amps through the load center. It doesn't matter what you are plugged into as long as it is the correct voltage.
__________________

__________________
Michael
Old setup:
2004 Chevrolet Silverado 3500 LT with a 2004 Jayco JayFlight 29BHS
2014 Greyhawk 31FS with a 2007 Tahoe toad
New setup:
2014 Thor Palazzo 33.3 with a 2007 Tahoe toad
msturtz is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off