Quote:
Originally Posted by bdreinv View Post
I plug my 15000 ac into my dryer plug using the dog bone, its on a 30 amp breaker. I should say never tried to run both 15000 on 100 plug.
Confused.. are you saying you are using a 'Dryer' plug to power stuff? I won't get into the 240 volt discussion if that's not the case... I probably read your post wrong.
__________________

__________________
2016 27BHS Elite
2012 F-150 EcoBoost / Max Tow (Sold)
2017 'Blue Jeans' 6.2 F-250 Lariat 4.3 gears.
bansai is offline   Reply With Quote
Old 09-28-2016, 02:19 PM   #12
Site Team
 
norty1's Avatar
 
Join Date: Jan 2011
Location: Charleston, SC
Posts: 11,738
If I were you, I would not do any more experimenting until you know a little more about the electrical system.
__________________

__________________
Moderator
2011 351RLTS Eagle, Mor/Ryde suspension & pin box
06 F350 Lariat PSD, SRW, LB, CC, EGR delete kit, 16K DrawTite hitch, Timbrens, TST TPMS

Can't find what you're looking on JOF? Try:Jayco Owners Forum Custom Google Search
"It's easier to fool people than to convince them that they have been fooled." - Mark Twain
norty1 is offline   Reply With Quote
Old 09-28-2016, 02:21 PM   #13
Senior Member
 
Join Date: Mar 2013
Posts: 217
AC Problem

I would not plug anything set up for 120 V into any household dryer connection until I knew for sure it was 120 versus 240V. Being a non-electrical type, I thought all h/h dryers ran off 240V due to the high heat requirement.
mohok1 is offline   Reply With Quote
Old 09-28-2016, 02:29 PM   #14
Senior Member
 
Join Date: Oct 2014
Location: Dallas
Posts: 288
Adapting a dryer vent has burned a number of RV people.

RV 30 AMP is 110/120v where a dryer 30 AMP is 220/240.

RV 50 AMP is 220/240.

If your AC isn't working on the generator then my vote is you have an issue somewhere. Hopefully it wasn't caused by plugging into the wrong power source.
__________________
2017 Jayco Redhawk 29XK
2015 Wrangler JKU
Blue Ox Baseplate w/Avail Tow Bar & Protect-a-Tow
RViBrake2 w/TPMS
drk98 is offline   Reply With Quote
Old 09-28-2016, 02:41 PM   #15
Site Team
 
norty1's Avatar
 
Join Date: Jan 2011
Location: Charleston, SC
Posts: 11,738
RV 50a service is actually 2 separate 120v -50a feeds with a common neutral. Effectively 100a of total power available to your rv. When you use a dog bone, you are limited to the current capacity of the source breaker.

I still suggest you back off until you have more information.
__________________
Moderator
2011 351RLTS Eagle, Mor/Ryde suspension & pin box
06 F350 Lariat PSD, SRW, LB, CC, EGR delete kit, 16K DrawTite hitch, Timbrens, TST TPMS

Can't find what you're looking on JOF? Try:Jayco Owners Forum Custom Google Search
"It's easier to fool people than to convince them that they have been fooled." - Mark Twain
norty1 is offline   Reply With Quote
Old 09-28-2016, 02:46 PM   #16
Senior Member
 
Join Date: Oct 2014
Location: Dallas
Posts: 288
Quote:
Originally Posted by norty1 View Post
RV 50a service is actually 2 separate 120v -50a feeds with a common neutral. Effectively 100a of total power available to your rv. When you use a dog bone, you are limited to the current capacity of the source breaker.

I still suggest you back off until you have more information.
Correct... I should have been more specific in my 50 AMP description.

Another good reason for a EMS unit.... If you plug a 30 AMP unit and it detects 50 AMP it'll kill the flow.
__________________
2017 Jayco Redhawk 29XK
2015 Wrangler JKU
Blue Ox Baseplate w/Avail Tow Bar & Protect-a-Tow
RViBrake2 w/TPMS
drk98 is offline   Reply With Quote
Old 09-28-2016, 03:03 PM   #17
Senior Member
 
Dustdevil's Avatar
 
Join Date: Mar 2016
Location: Orange County
Posts: 589
Quote:
Originally Posted by norty1 View Post
RV 50a service is actually 2 separate 120v -50a feeds with a common neutral. Effectively 100a of total power available to your rv. When you use a dog bone, you are limited to the current capacity of the source breaker.

I still suggest you back off until you have more information.
Oh, so it's TWO X 50 amp 115 volt circuits, not two X 25amp? Geez. I also read somewhere that the two 115 volt circuits are out of phase with one another, which means you would normally measure 230 volts between them, but only 115 volts between each line and common neutral. Is this correct?
__________________
2006 Jayco Seneca 34SS
2006 Jeep Wrangler Unlimited Rubicon Toad
Dustdevil is offline   Reply With Quote
Old 09-28-2016, 03:05 PM   #18
Senior Member
 
Dustdevil's Avatar
 
Join Date: Mar 2016
Location: Orange County
Posts: 589
Sorry to hijack the thread, by the way, but I think it's germane to the OPs topic, as well as anyone using a 230v dryer outlet to power the RV.
__________________
2006 Jayco Seneca 34SS
2006 Jeep Wrangler Unlimited Rubicon Toad
Dustdevil is offline   Reply With Quote
Old 09-28-2016, 04:39 PM   #19
Senior Member
 
wags999's Avatar
 
Join Date: Jan 2015
Location: Surprise
Posts: 1,419
Quote:
Originally Posted by Dustdevil View Post
Oh, so it's TWO X 50 amp 115 volt circuits, not two X 25amp? Geez. I also read somewhere that the two 115 volt circuits are out of phase with one another, which means you would normally measure 230 volts between them, but only 115 volts between each line and common neutral. Is this correct?
Yes, same as any 240 volt circuit. If you use a dog bone and plug into a 120 volt plug you will only power a portion of your RV appliances. If you have two AC only one will have power.

As others have said, I would back off until what your situation is. A dryer is typically a 30 amp 240 circuit...
__________________
2011 Toyota Tundra double cab
2015 27RLS
wags999 is offline   Reply With Quote
Old 09-28-2016, 06:37 PM   #20
Senior Member
 
Dustdevil's Avatar
 
Join Date: Mar 2016
Location: Orange County
Posts: 589
Quote:
Originally Posted by wags999 View Post
Yes, same as any 240 volt circuit. If you use a dog bone and plug into a 120 volt plug you will only power a portion of your RV appliances. If you have two AC only one will have power.

As others have said, I would back off until what your situation is. A dryer is typically a 30 amp 240 circuit...
Oh, it wasn't me using the dryer outlet. I was told, though, that each AC unit operates from a different 115 volt line in a 50 amp RV circuit.
__________________

__________________
2006 Jayco Seneca 34SS
2006 Jeep Wrangler Unlimited Rubicon Toad
Dustdevil is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia State Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -6. The time now is 01:17 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.