Quote:
Originally Posted by Quantum View Post
Personally (because I'm an electrician), I would not do it. You answered your own question when you said that you have a 15AMP receptacle on a 20A breaker.

Either, change out that breaker to a 15A, or buy yourself a 20A GFI receptacle to install in place of the 15A receptacle that you currently have. (only if you have 12 gauge wire from your panel to your receptacle. If it is 14 gauge, then you need to run a new wire, or install a 15A breaker MAX.

Checking to see if the receptacle is getting hot is a terrible idea. You can only see the face of the receptacle. You can't see the terminals where the wire is attached. You also can't see the inside of the receptacle. The last thing you want is a fire due to over loading a 15A receptacle that is on a 20A breaker.

If you were "only" running 5-10 Amps, I would be more likely to do it, but when you are running your AC, which you know is drawing 10-13 amps, and closer to 20A at start up, I would not be using the the setup you currently have.

Play safe.
Quantum - glad to know we have an electrician here! Here is what I have always understood regarding 15 and 20 amp outlets and circuits. Based on what you said, there is a flaw in my understanding. Let me know where I am wrong -- I really want to understand this properly.

I had researched and determined that 15 amp plugs are actually rated for 20 amp pass through and can actually handle 20 amps through the socket, but the plugs (5-15) are designed for devices that pull a max of 15 amps thus the two straight prongs.

I also understood that 20 amp plugs have the sideways blade, and NEC calls for them to have their own dedicated breaker.

If you look at any house around here, all the plug circuits are 20 amps 12-2 with standard 15 amp sockets.

Again - my understanding was that the 15 amp designation was for the device that was being plugged in and not the actual limit of the plug.

Anyway - where did I go wrong?
__________________

__________________
Terry
2009 Jayco 26BH
2004 Chevy Silverado 1500
2009 JayFlight Manual Library

Want to add a signature to your posts? --> Click Here
Terry is offline   Reply With Quote
Old 07-18-2011, 02:05 AM   #12
Senior Member
 
Join Date: May 2011
Location: Aldergrove British Columbia
Posts: 815
My first mod was running 10gauge wire to the front of my house from the panel. 30 feet cost me about 75 dollars. I was in shock. The price of copper has really gone up. To me it was worth the time and money to do this. Nice to have the AC when working in the trailer.
__________________

__________________
Richard
2011 Jay Feather Select 28U
2007 Silverado Crewcab LT 6.0L
Happily married and father of
two university students.
Cancer survivor
Murphie is offline   Reply With Quote
Old 07-18-2011, 01:10 PM   #13
Senior Member
 
Double Eagle's Avatar
 
Join Date: Apr 2011
Location: Central Texas
Posts: 107
Quote:
Originally Posted by tafische View Post
Quantum - glad to know we have an electrician here! Here is what I have always understood regarding 15 and 20 amp outlets and circuits. Based on what you said, there is a flaw in my understanding. Let me know where I am wrong -- I really want to understand this properly.

I had researched and determined that 15 amp plugs are actually rated for 20 amp pass through and can actually handle 20 amps through the socket, but the plugs (5-15) are designed for devices that pull a max of 15 amps thus the two straight prongs.

I also understood that 20 amp plugs have the sideways blade, and NEC calls for them to have their own dedicated breaker.

If you look at any house around here, all the plug circuits are 20 amps 12-2 with standard 15 amp sockets.

Again - my understanding was that the 15 amp designation was for the device that was being plugged in and not the actual limit of the plug.

Anyway - where did I go wrong?

This is what I thought too; I am not an electrician and know little about it though other than you don'y play with as it can kill you.
__________________
2011 Jayco Eagle Super Lite 31.5 FBHS
2002 Ford F-250 Super Duty CC 7.3 Liter Powerstroke Diesel
Double Eagle is offline   Reply With Quote
Old 07-18-2011, 02:57 PM   #14
Senior Member
 
OurJayco's Avatar
 
Join Date: Nov 2009
Location: East Bethel, Minnesota
Posts: 659
As a former electrician, you guys are correct for the most part. Here is a website I hope will help you and others understand a bit more about outlets, current and confirgurations.

http://www.frentzandsons.com/Hardwar...nfiguratio.htm


The rules that apply to installation of a GFCI outlet receptacle on a 15 or / and 20 amp rated circuit breaker are the same as the ones that apply to a regular outlet receptacle. Additionally, there may be some regulations applicable only to a particular area this GFCI is going to be installed, or your local jurisdiction requirements.

The wires (electrical conductors) between the 20 amp rated circuit breaker and this GFCI outlet receptacle (or any outlet receptacle) must be at least 20 amp rated (gauge 12). It doesn’t matter if the end device is 15 or 20 amps rated.
15 amps outlet receptacles are rated for 20 amps feed-through. In other words, they supposed to withstand the loads of a 20A rated device.


I know this is rather simple and not very informative, but good information.
Not all 15 amp outlets in a house have 15 amp breakers. The sockets themselves are capable of handling 20 amps, but designed for 15 amp products (Hair dryer, toasters, lamps, TV's, stereos etc.....).
__________________
HAPPY CAMPING!! :D

Daryl and Sandy
2013 Eagle 314BDS
2012 Ford F150 Platinum, 4 x 4 Crew Cab with Ecoboost
Equal-i-zer Hitch
OurJayco is offline   Reply With Quote
Old 07-18-2011, 03:48 PM   #15
Senior Member
 
Terry's Avatar
 
Join Date: Feb 2011
Location: Germantown, TN
Posts: 4,923
Thanks OurJayco!

So what is your opinion on running A/C on a standard 20 amp circuit / 15 amp outlet? Is that something you would recommend against as well?

In theory (and I know not everything operates that way!) - my brain was thinking that if the circuit was rated for 20 amp and the plug could handle 20 amps - then there would be no issue. If the trailer decided it needed more than 20 amps, the breaker would simply blow (Not something you want to be doing all the time obviously). In theory I thought the wire run should be capable of handling 20 amps and maintaining the proper voltage. IF you use the right adapters, and go right to the trailer my thought was that you would be ok. My comment about heat was just as a secondary check -- if anything is heating up then you have a problem somewhere such as a bad connection, too small of wire, bad plug, etc.

Again - I want to understand if my assumptions are correct or where I am wrong. This is great discussion -- glad we have some knowledgeable folks here on this subject.
__________________
Terry
2009 Jayco 26BH
2004 Chevy Silverado 1500
2009 JayFlight Manual Library

Want to add a signature to your posts? --> Click Here
Terry is offline   Reply With Quote
Old 07-18-2011, 08:03 PM   #16
Senior Member
 
Join Date: Apr 2011
Location: Niagara on the Lake
Posts: 212
When I understand feed through, it refers to the terminal screws on the back of the receptacle. Meaning, the contacts on the back of the receptacle can handle 20A.

Canadian Electrical Code (CEC) which is very similar to NEC, states that a 15A receptacle is good for 15A continuous load. Your local Home Depot sells 20A GFCI receptacles, just replace your 15A with the 20A, then you know you have a properly rated receptacle.

This is just my interpretation of the code and how I would do something for a customer. You can never be too safe when it comes to electrical...as you can't easily see problems with electricity.
__________________
2015 Jayco WhiteHawk 28BHKS Summit Edition
2016 Ford F-150, 4x4, 3.5L ECOBOOST, MaxTow, Supercrew, 6.5FT, 3.55 axle
Quantum is offline   Reply With Quote
Old 07-18-2011, 08:30 PM   #17
Senior Member
 
David472's Avatar
 
Join Date: Feb 2011
Location: SW Ontario
Posts: 1,393
Don't forget the part about 12 gauge wire feeding the 20 amp recepticle, to safely handle the 20 amp draw.

Also, if the "run" current draw is less than 15 amp, but the starting surge is over 15 amp.......this is a marginal arrangement.
__________________
Jayco Eagle 31.5RLDS
GMC Sierra 2500 HD
David472 is offline   Reply With Quote
Old 07-19-2011, 06:32 AM   #18
Senior Member
 
Double Eagle's Avatar
 
Join Date: Apr 2011
Location: Central Texas
Posts: 107
If I am understanding correctly my best bet since I have a 20 AMP braker is to change to a 20 amp plug and I should be safe as long as my wire is at least 12 guage. Is this a safe assumption?

Thanks to all who replied for your help.
__________________
2011 Jayco Eagle Super Lite 31.5 FBHS
2002 Ford F-250 Super Duty CC 7.3 Liter Powerstroke Diesel
Double Eagle is offline   Reply With Quote
Old 07-19-2011, 08:33 AM   #19
Senior Member
 
Join Date: Jul 2011
Location: Iowa
Posts: 107
I ran a dedicated 30amp circuit from my breaker box to an RV style 30amp outlet. I used 10g wire for it. 10 is hard to work with, maybe a little overkill, but, wanted it heavy duty.
It is mounted on the side of my house. I have not had any problems with it tripping. I don't always run my air but my fridge is always on and battery is charged.
__________________

2011 Jayco Jayflight 22FB
2004 Ford F-150 5.4 Triton, K&N FIPK, Magna-flow muffler
Big Jim is offline   Reply With Quote
Old 07-19-2011, 08:45 AM   #20
Senior Member
 
Join Date: May 2010
Posts: 552
The starting surge for a compressor is going to be well above 20A, however, the duration of that surge is measured in milliseconds and is not long enough to even begin to cause overheating or for a circuit breaker, either 15A or 20A to detect. The pass-through capability of the outlet being the same for both ratings, if it is fed with 12ga wire and protected by a 20A breaker, it is perfectly safe to run an AC on that outlet. If the AC tries to draw more than 20A, the C/B will trip. Also, using an outlet rated for 15A is not going to reduce the amount of voltage available to that outlet. A 30A circuit would be better ust in case you wanted to run something else with the AC.
I install Marine AC equipment all the time using a 20A circuit and the 16K BTU units do fine on it, both at startup and normal running. The entire boat is protected by double pole 30A breakers, but the AC runs on 20.
__________________

__________________
2010 22FB(Ret)
2013 F250 XLT
I now have a Keystone Outback, but I try to help when I can.
---------------------
Bitter Gun Owner
Bitter Clinger
Armed Infidel
Bob Landry is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia State Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -6. The time now is 07:07 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.