Excessive voltage loss

Ok electrical gurus....can't figure what I am doing wrong here....

I have my camper near my barn....my well power line went bad so while they were there I had them trench a power line to my camper. I wanted 8, but all they had was 10....fine I figured it would work fine for what I am doing.

Well......

Length: ~120 feet (maybe 110) direct bury #10
Starting voltage: 114
Current: 14 amps
End voltage: 102
Voltage drop: 12 volts

By my calculations I should have no more than a 4 or 5 volt drop. I have checked and cleaned all my connections, yet I can make no improvements.

I have measured in various places and it is not in the camper...in most campgrounds, it barely drops a volt or two at that load.

I figured I was not going to get a full 30 amp...but at least wanted to run the ac on occasion when working on it or packing up. With this drop my EMS is shutting down.

Any thoughts or other suggestions?



__________________
Terry
2009 Jayco 26BH
2004 Chevy Silverado 1500
2009 JayFlight Manual Library

Want to add a signature to your posts? --> Click Here
Terry is offline   Reply With Quote
Old 08-04-2012, 01:00 PM   #2
Member
 
Join Date: May 2011
Location: North Phoenix, AZ
Posts: 70
Did you take in account its really 240 feet of drop ? Pure coper would be 0.9989 ohms per thousnand seems about right...
__________________
26RLS with Dodge RAM 1500
Flytyer is offline   Reply With Quote
Old 08-04-2012, 01:23 PM   #3
Member
 
pfin38's Avatar
 
Join Date: Aug 2011
Location: OH
Posts: 41
Normally you would have to use the next bigger sized wire for runs over 100' to combat the vd.
__________________
2012 Jayflight 28bhs
2006 Toyota Tundra
pfin38 is offline   Reply With Quote
Old 08-04-2012, 01:23 PM   #4
Senior Member
 
Terry's Avatar
 
Join Date: Feb 2011
Location: Germantown, TN
Posts: 4,923
I used several of the online voltage calculators and came back with similar results. They all ask for the length of the cable, so I didn't think you had to double it.

That just doesn't intuitively seem right to me....in a large house wired with #12 you could easily have 75 to 100 feet of wire from the breaker panel to the last circuit in the branch and you don't see nearly that kind of loss at 15 amp.....

Would not be such a big deal but I am way rural and during the really hot days my voltage overall is lower than normal. Had the power company out, but they don't seem to be able to do anything so far.



__________________
Terry
2009 Jayco 26BH
2004 Chevy Silverado 1500
2009 JayFlight Manual Library

Want to add a signature to your posts? --> Click Here
Terry is offline   Reply With Quote
Old 08-05-2012, 12:47 PM   #5
Member
 
Join Date: Feb 2012
Location: Southern NY
Posts: 77
Is 120' the entire distance from the service panel? Anything else on the circuit?
__________________
Dan in NY

2016 Jayco x213
2012 Toyota Tundra
Mainenebula is offline   Reply With Quote
Old 08-05-2012, 04:35 PM   #6
Senior Member
 
Terry's Avatar
 
Join Date: Feb 2011
Location: Germantown, TN
Posts: 4,923
Only thing. I ran it directly from the breaker panel. It enters the outbuilding where there is a junction box then out to a weatherproof 30 amp RV receptacle - so one splice is all it has and it is good and tight. 2x checked the receptacle as well an all looks good.



__________________
Terry
2009 Jayco 26BH
2004 Chevy Silverado 1500
2009 JayFlight Manual Library

Want to add a signature to your posts? --> Click Here
Terry is offline   Reply With Quote
Old 08-05-2012, 04:59 PM   #7
Senior Member
 
2edgesword's Avatar
 
Join Date: Jul 2011
Location: Long Island, NY
Posts: 1,402
I'm wondering if the buried wire is heating up (ground temperature and self-heating) causing a change (increase) in the resistance of the wire.
__________________

2018 Jayco 28RLS
2012 F-250 6.2L 3.73
Equalizer Hitch
Yamaha 2400ISHC
2edgesword is offline   Reply With Quote
Old 08-07-2012, 04:31 PM   #8
Member
 
pfin38's Avatar
 
Join Date: Aug 2011
Location: OH
Posts: 41
I still believe (NEC) code dictates larger wire size for anything over 100' just for this reason (voltage drop).
__________________
2012 Jayflight 28bhs
2006 Toyota Tundra
pfin38 is offline   Reply With Quote
Old 08-08-2012, 04:33 PM   #9
Senior Member
 
rwilley's Avatar
 
Join Date: Mar 2012
Location: Northern Cal
Posts: 409
Quote:
Originally Posted by pfin38 View Post
I still believe (NEC) code dictates larger wire size for anything over 100' just for this reason (voltage drop).
I was having the same problem at my sons house this year. The AC couldnt start we think because the wire was to long and not heavy enough.
__________________
2012 Jayco Eagle 321RLTS
2008 Dodge Cummins 3500 DW Crew Cab 4x4 6 speed Auto, Exhaust Brake
rwilley is offline   Reply With Quote
Old 08-08-2012, 05:41 PM   #10
Senior Member
 
Join Date: Oct 2011
Location: Central California
Posts: 2,283
I am learning a lot from this thread. I am learning about things I never thought I wanted or needed to know about...watch out Jeopardy :-)

Terry I hope you are able to get this figured out easily with much additional expense and/or labor.

After reading this I did a google search on Votage Drop and read several articles. Then I searched for a calculator, the first hit was from "South Wire". When I input your data from the original post, it determined #8 wire if direct buried was required to maintain <3% VD. They calculate actual VD to be ~2.32%
__________________
2020 Ram 1500 5.7L
2007 Chevy Duramax LMM/Allison (Sold)
2012 Jay Flight 29QBH (Sold)
2012 Jay Flight 26BH (Sold)
clubhouse is offline   Reply With Quote
Old 08-08-2012, 06:19 PM   #11
Senior Member
 
David472's Avatar
 
Join Date: Feb 2011
Location: SW Ontario
Posts: 1,393
Terry,
Here are some numbers from the electrical engineering book;
10 gauge wire has a resistance of 1.018 ohms per 1000 feet.
Your 120 foot run should be 0.12216 ohms for each wire, so, you are correct, there should be only a few volt drop, not 12 volt drop for a 14 amp draw.
To get that 12 volt drop, it's behaving like 14 or 16 gauge wire.
I suspect the copper wire was nicked or partly cut when buried, or does not have the circular-mil area in its cross-section that it needs to have to be true 10 gauge.
__________________
2013 Jayco Eagle 31.5RLDS
2018 Silverado 2500 HD Duramax
David472 is offline   Reply With Quote
Old 08-18-2012, 01:05 PM   #12
Senior Member
 
Join Date: Oct 2010
Location: Merrimack NH
Posts: 917
When you got the 102V reading did anything else turn on or was running like a water pump? That will effect your overall voltage. You have got to be carefull with that 102, lots of old elect gagets would run +-10% to 20 % of the rated 120, but this new electronic stuff will get hurt at anything less or more than the 10%. Sorry I don't have a fix . Larry
29BHS ECO is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 04:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.