Old 06-17-2015, 02:16 PM   #21
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,837
Quote:
Originally Posted by VicS1950 View Post
Thanks for the reference.

Safe Work Practices...snip...

Be careful with portable generators. The electricity they supply can kill people just as dead as the voltage from a power grid.

vic
Amen! Brother Vic, amen.

Let's all be safe out there
__________________

__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Old 06-17-2015, 03:04 PM   #22
Senior Member
 
Filthy-Beast's Avatar
 
Join Date: May 2015
Location: Chicago
Posts: 269
Did you see this part?

Bonding and grounding are separate requirements for generators and other electrical distribution systems. Grounding means the connection, or the establishment of a connection, of an electric circuit or equipment to reference ground, which includes the generator’s frame. Bonding is the intentional connection between the grounded circuit conductor (neutral) and the grounding means for the generator, which includes the generator’s frame. Thus, effective bonding of the neutral conductor to the generator’s frame is also a concern for the safe use of the equipment. As with grounding terminal connections, proper bonding of the neutral terminal of a power receptacle may be confirmed via testing by a competent electrician with the correct equipment, and the ohmic resistance should measure near zero and must not be intermittent, which indicates a loose connection
__________________

__________________
2015 Jay Flight 31 RLDS
2015 F250, Reese straightline
Ham Lic: W4TFB
Filthy-Beast is offline   Reply With Quote
Old 06-17-2015, 03:32 PM   #23
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,837
Quote:
Originally Posted by Filthy-Beast View Post
Did you see this part?

Bonding and grounding are separate requirements for generators and other electrical distribution systems. Grounding means the connection, or the establishment of a connection, of an electric circuit or equipment to reference ground, which includes the generatorís frame. Bonding is the intentional connection between the grounded circuit conductor (neutral) and the grounding means for the generator, which includes the generatorís frame. Thus, effective bonding of the neutral conductor to the generatorís frame is also a concern for the safe use of the equipment. As with grounding terminal connections, proper bonding of the neutral terminal of a power receptacle may be confirmed via testing by a competent electrician with the correct equipment, and the ohmic resistance should measure near zero and must not be intermittent, which indicates a loose connection

Yes, and all it does is explain what bonding does and that it should be checked to see that it is set up properly.

The bulk of the text is about electrical safety around generators.

BUT THE MOST IMPORTANT PART OF ALL THIS is the electricity must have an alternate path to ground OTHER THAN PEOPLE when a tool or appliance malfunctions!
__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Old 06-17-2015, 07:30 PM   #24
Senior Member
 
Nighthawk 96's Avatar
 
Join Date: Apr 2011
Location: Columbia SC
Posts: 571
I have a wired EMS from PI. I have spoken with one of their telephone reps, who was very helpful. He suggested using the grounding plug in a portable generator.

Reason he gave was that one might forget to switch the unit back into the protect mode when not using the generator(s) My model has an external monitor with a switch to turn it off - actually to by pass it.

I am not worried about surge with inverter generators in use. Well maybe lighting could strike, but we would probably be fried anyway if the strike were that close!
__________________
2012 Toyota Tundra 5.7 Litre DoubleCab
6 speed, 4.30 Limited Slip, Tow Package
2013 Jayco White Hawk 27DSRL
2010 Jayco JayFlight 26BH sold
Yamaha EF2000is Generators (2)
1996 Honda CB750 Nighthawk
Nighthawk 96 is offline   Reply With Quote
Old 06-17-2015, 11:06 PM   #25
Senior Member
 
VicS1950's Avatar
 
Join Date: Apr 2013
Posts: 517
Quote:
Originally Posted by Filthy-Beast View Post
Did you see this part?

Bonding and grounding are separate requirements for generators and other electrical distribution systems. Grounding means the connection, or the establishment of a connection, of an electric circuit or equipment to reference ground, which includes the generatorís frame. Bonding is the intentional connection between the grounded circuit conductor (neutral) and the grounding means for the generator, which includes the generatorís frame. Thus, effective bonding of the neutral conductor to the generatorís frame is also a concern for the safe use of the equipment. As with grounding terminal connections, proper bonding of the neutral terminal of a power receptacle may be confirmed via testing by a competent electrician with the correct equipment, and the ohmic resistance should measure near zero and must not be intermittent, which indicates a loose connection
Yes.

I believe that I understand the definitions of grounding and bonding. I have applied them and worked with them for decades.

Please provide more detail as to how you feel this applies to the cheater plug under discussion improving the safety of a system.

I believe that I've shown that I'm open to discussion.

vic
VicS1950 is offline   Reply With Quote
Old 06-18-2015, 06:50 AM   #26
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,837
Hi All,


First an apology and correction; It is required that a genset have its ground and neutral bonded when used as an independent power system.


I am sorry for saying that it is unsafe to do so.


Hello. My name is Michael and I am
a loud-mouthed shnook who should
check his facts first.


When connecting a genset to a building for backup power, one must NOT bond the ground and neutral in the genset.


I sat down and reviewed the materials on what the ground lead is expected to do.


In any power system, there must be exactly ONE point of bonding between neutral and ground. It has to exist for the ground to be able to do its job as the abnormal return path.


Without a bonding point, the ground wire is floating and useless.


Having multiple points of bonding is bad because a fault in the neutral wire between the bonding points will cause the ground wire to carry normal return power.
__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Old 06-18-2015, 10:18 AM   #27
Senior Member
 
VicS1950's Avatar
 
Join Date: Apr 2013
Posts: 517
Quote:
Originally Posted by mike837go View Post
...


Hello. My name is Michael and I am
a loud-mouthed shnook who should
check his facts first.
Insert my name above sometimes too.

Quote:
Originally Posted by mike837go View Post
When connecting a genset to a building for backup power, one must NOT bond the ground and neutral in the genset.


I sat down and reviewed the materials on what the ground lead is expected to do.


In any power system, there must be exactly ONE point of bonding between neutral and ground. It has to exist for the ground to be able to do its job as the abnormal return path.


Without a bonding point, the ground wire is floating and useless.


Having multiple points of bonding is bad because a fault in the neutral wire between the bonding points will cause the ground wire to carry normal return power.
I agree that it depends upon how the generator is being used especially when feeding an existing system, and not cord connected equipment.

Bonding the neutral current carrying conductor to the electrically high and dry floating generator frame can have some benefit, but of itself it is not the answer to really safe operation.

Consider a scenario where a cord connected device (drill motor, power saw, etc.) has line side leakage to the metal frame outside parts. When a properly grounded supply is used that leakage is taken to ground by the the green wire. If the supply is an ungrounded generator frame with no neutral bond then that leakage will travel back on the green wire to the floating generator frame and elevate the frame to some voltage above ground potential. I say some voltage above ground potential because without a ground rod (the frame and generated voltage is floating) there is no set ground potential.

With the generator frame bonded to the neutral current carrying conductor the drill frame leakage as described above is combined with the neutral conductor and carried back to generator coils. The floating generator frame may still be elevated to some potential above ground.

Neither of the above situations is ideal.

To me the safe answer is to make certain that a tested GFI is always used right at the generator plug. As I have stated earlier, the GFI doesn't need a ground to do it's job. If more than 5 mA of current goes anywhere but back to the generator coils the GFI will trip.

That said, if one is going to bond the generator frame and neutral I feel it should be done by properly hard wiring the bond at the generator, not by using some cheater plug.

I still question whether a bonded neutral to an ungrounded generator frame brings devices such as the Progressive Industry unit to full protection operation.

FWIW. vic
VicS1950 is offline   Reply With Quote
Old 06-18-2015, 10:31 AM   #28
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,837
Quote:
Originally Posted by VicS1950 View Post
Insert my name above sometimes too.

... snip ...
To me the safe answer is to make certain that a tested GFI is always used right at the generator plug. As I have stated earlier, the GFI doesn't need a ground to do it's job. If more than 5 mA of current goes anywhere but back to the generator coils the GFI will trip.

That said, if one is going to bond the generator frame and neutral I feel it should be done by properly hard wiring the bond at the generator, not by using some cheater plug.

I still question whether a bonded neutral to an ungrounded generator frame brings devices such as the Progressive Industry unit to full protection operation.

FWIW. vic
Never thought of using a GFCI with a genset. Good Idea!

[That's gonna mean some really wild mods to the ol' EMXFQS 5500]

Generally, because a portable generator has a metal frame that is in contact with the physical ground, it is considered grounded. But nothing beats driving a 3 foot length of copper rod into the ground and connecting it properly to the generator's frame.

Again, a GFCI makes that even that kind of protection redundant.
__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Old 06-18-2015, 10:47 AM   #29
Senior Member
 
VicS1950's Avatar
 
Join Date: Apr 2013
Posts: 517
Quote:
Originally Posted by mike837go View Post
...

Generally, because a portable generator has a metal frame that is in contact with the physical ground, it is considered grounded. ...
Many generators sit on rubber feet to minimize noise and vibration, or on plastic wheels for portability.

As you mention, even when the painted metal frame is in direct contact with bare ground it doesn't really "ground" the frame properly.

vic
VicS1950 is offline   Reply With Quote
Old 12-27-2015, 10:13 PM   #30
Moderator Emeritus
 
Rustic Eagle's Avatar
 
Join Date: Apr 2011
Location: Michigan
Posts: 7,369
Quote:
Originally Posted by VicS1950 View Post
snip...... Are these cheater plugs commercially available? vic
A little late to the thread...., but to your question, Yes.

I ran across the following "cheater" product sold by Progressive Industries just a couple days ago....., thought you might find it interesting. Mike Sokol of the "No-Shock-Zone" (referenced earlier in this thread) states he developed the new Generator Plug product (refer to video in link).

Generator Plug: Progressive Industries RV Surge and Electrical Protection industry lea

Bob
__________________

__________________

2016 GM 2500HD 6.0L/4.10
2018 Jay Flight 24RBS
2005 Jayco Eagle 278FBS (retired)
1999 Jayco Eagle 246FB (retired)
Reese HP Dual Cam (integrated sway control)
Rustic Eagle is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia State Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -6. The time now is 05:26 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.