Old 08-13-2022, 08:22 AM   #21
Senior Member
 
kirkelli's Avatar
 
Join Date: Aug 2018
Location: ridgecrest
Posts: 1,196
Quote:
Originally Posted by Josparkz View Post
I am wondering if the 30 A to 50 A adapter is what's tripping the GFI.
With this added info, yes it is possible the 30 to 50A dogbone adapter could trip the GFI.. Some of the cheap China made Dogbones dont jumper the hot lead on the 50A side and you'll lose voltage on one side. You need to check your main panels to make sure you have equal voltage on each side of the the 50 Amp panel. if you don't chuck that adapter and get a good Cameco. Also, GFI's are always the first circuit in a series circuit and there should only be one in series.
below is a picture showing how a 30 amp to 50 amp doggone shoed be wired
Attached Thumbnails
30_to_50_amp_dogbone.jpg  
kirkelli is offline   Reply With Quote
Old 08-13-2022, 06:07 PM   #22
Senior Member
 
Join Date: Jun 2022
Location: delta
Posts: 101
Quote:
Originally Posted by kirkelli View Post
With this added info, yes it is possible the 30 to 50A dogbone adapter could trip the GFI.. Some of the cheap China made Dogbones dont jumper the hot lead on the 50A side and you'll lose voltage on one side. You need to check your main panels to make sure you have equal voltage on each side of the the 50 Amp panel. if you don't chuck that adapter and get a good Cameco. Also, GFI's are always the first circuit in a series circuit and there should only be one in series.
below is a picture showing how a 30 amp to 50 amp doggone shoed be wired
Nice picture. Thanks. I should checkout their website.
I rang out the adapter initially and that's how it's wired.
Pretty hard to find anything not made in China anymore. Breaks my heart.
__________________
2022 28.5 rsts
One Ton Dodge
Josparkz is offline   Reply With Quote
Old 08-13-2022, 06:27 PM   #23
Senior Member
 
Join Date: Jan 2022
Location: Baton Rouge
Posts: 1,048
Quote:
Originally Posted by Vicr View Post
OK, to the answer. And the OP had it in post #14 in his last sentence. The grounding and the bonded neutral in an RV will cause a current flow difference between the hot and the neutral which trips the GFCI. A bunch of posters here need to study up on how a GFCI works before posting. Google "how a GFCI breaker works".
not sure what going on here...but the ground and neutral are not and should not be bonded in the RV panel.
__________________
2022 Jayco Pinnacle 32RLTS, Onan 5500, 380 Watts
Solar, GoPower MPPT, Four 6 Volt batteries, EMS-HW50C, Hughes Hardwired Autoformer, Disc brakes and 17.5" tires

2017 Ram Cummins 3500, 4x4, Dually Aisin, 3.73
B&W hitch
Learjet is offline   Reply With Quote
Old 08-14-2022, 11:31 AM   #24
Senior Member
 
Vicr's Avatar
 
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,862
Quote:
Originally Posted by Learjet View Post
not sure what going on here...but the ground and neutral are not and should not be bonded in the RV panel.
Tell that to the RV "electricians".
Vicr is offline   Reply With Quote
Old 08-14-2022, 03:56 PM   #25
Senior Member
 
Join Date: Jun 2022
Location: delta
Posts: 101
Quote:
Originally Posted by Vicr View Post
Tell that to the RV "electricians".
That might be what keeps them in business <LOL>
__________________
2022 28.5 rsts
One Ton Dodge
Josparkz is offline   Reply With Quote
Old 08-17-2022, 12:19 PM   #26
Junior Member
 
Join Date: Nov 2021
Location: Kempner
Posts: 1
Quote:
Originally Posted by kirkelli View Post
switch out your GFI plug at the house to a non-GFI and you'll be fine. Running two GFI's in series will trip themselves.
What he said you cannot run an RV off a GFI plug it will trip them every time. RV's are not grounded like a house or building so you will almost always trip them.
mvanderhoff is offline   Reply With Quote
Old 08-17-2022, 12:27 PM   #27
Junior Member
 
Join Date: Aug 2011
Posts: 5
Your RV panel probably has the neural jumper in place. That will trip the GFI.
thumper111 is offline   Reply With Quote
Old 08-17-2022, 01:11 PM   #28
Senior Member
 
Join Date: Dec 2010
Location: Wheatfield, New York
Posts: 1,069
Quote:
Originally Posted by Learjet View Post
not sure what going on here...but the ground and neutral are not and should not be bonded in the RV panel.
I had a brand new pop-up camper that kept triggering a GFI receptacle at a campground. I took a look inside the panel and sure enough, the neutral was bonded to the ground. This will trip a GFI every time; all I had to do was remove that wire in the panel and all was fine.

The only time that bonding jumper should be in place is if the trailer is a "point of service". This would be if you had your own meter at a campground that was wired directly into your camper panel.
__________________
2009 Jayco Jay Feather 17C 130W Solar, 2021 F150 2.7L Eco Boost, 2021 Toyota Highlander
Isaacs is offline   Reply With Quote
Old 08-17-2022, 02:19 PM   #29
Member
 
Join Date: Aug 2015
Location: West Hurley
Posts: 61
If plugged into a gfi my moho will trip a gfi if I use the fridge on electric. Ok on propane.
saarf is offline   Reply With Quote
Old 08-17-2022, 06:41 PM   #30
Senior Member
 
Join Date: Apr 2019
Location: Northern, Ontario
Posts: 110
Quote:
Originally Posted by Isaacs View Post
I had a brand new pop-up camper that kept triggering a GFI receptacle at a campground. I took a look inside the panel and sure enough, the neutral was bonded to the ground. This will trip a GFI every time; all I had to do was remove that wire in the panel and all was fine.

The only time that bonding jumper should be in place is if the trailer is a "point of service". This would be if you had your own meter at a campground that was wired directly into your camper panel.
I was at a Michigan state park last week and connected to a 30 amp pedestal, protected by a 30 amp GFI breaker

The neutral and the ground is touching

Example neutral screw on plug could be touching metal box.

The white wire in the trailer panel should not be touching a ground


The fact that the GFI is tripping confirms that. With a clamp on amp meter, you can confirm it.
MPD56 is offline   Reply With Quote
Old 08-17-2022, 11:45 PM   #31
Senior Member
 
Join Date: Jun 2022
Location: delta
Posts: 101
Quote:
Originally Posted by MPD56 View Post
I was at a Michigan state park last week and connected to a 30 amp pedestal, protected by a 30 amp GFI breaker

The neutral and the ground is touching

Example neutral screw on plug could be touching metal box.

The white wire in the trailer panel should not be touching a ground


The fact that the GFI is tripping confirms that. With a clamp on amp meter, you can confirm it.
Tell me please how you would do that with a clamp on meter. Thanks.
__________________
2022 28.5 rsts
One Ton Dodge
Josparkz is offline   Reply With Quote
Old 08-18-2022, 04:25 AM   #32
Senior Member
 
Join Date: Apr 2019
Location: Northern, Ontario
Posts: 110
Plug in the trailer to a non-GFI and measure the current going through the ground

Only reason I'm posting this, is your an Electrician. I wouldn't want anyone else trying this. The safe way would be with a ohm meter. Neutral to ground
MPD56 is offline   Reply With Quote
Old 08-18-2022, 05:07 AM   #33
Senior Member
 
Join Date: Jun 2022
Location: delta
Posts: 101
Quote:
Originally Posted by MPD56 View Post
Plug in the trailer to a non-GFI and measure the current going through the ground

Only reason I'm posting this, is your an Electrician. I wouldn't want anyone else trying this. The safe way would be with a ohm meter. Neutral to ground
I have a dandy clamp on meter I just got. Icould break the cable out and see if there is a ground flow. I disconnected the GFI function of the breaker so this made it's way down on the list of priorities for a bit. Thanks
__________________
2022 28.5 rsts
One Ton Dodge
Josparkz is offline   Reply With Quote
Old 08-18-2022, 09:18 AM   #34
Senior Member
 
Join Date: Apr 2019
Location: Northern, Ontario
Posts: 110
Quote:
Originally Posted by Josparkz View Post
I have a dandy clamp on meter I just got. Icould break the cable out and see if there is a ground flow. I disconnected the GFI function of the breaker so this made it's way down on the list of priorities for a bit. Thanks


If it is easier. Clamp on to the neutral and then the hot.

If they are not equal, then the difference is flowing through the ground
MPD56 is offline   Reply With Quote
Old 08-18-2022, 10:53 AM   #35
Senior Member
 
craigav's Avatar
 
Join Date: Mar 2017
Location: North Texas
Posts: 3,573
Quote:
Originally Posted by MPD56 View Post
If it is easier. Clamp on to the neutral and then the hot.

If they are not equal, then the difference is flowing through the ground
While you are correct, the difference in current to trip a gfi starts as low as 4 milliamps which is so little that many if not most amp meters would not measure this low of a difference. Also, keep in mind that if the RV does have current leakage, that the current could simply be flowing through the stabilizer jacks instead of the ground conductor. ~CA
__________________
2010 GreyHawk 31SS
craigav is online now   Reply With Quote
Old 08-19-2022, 09:33 PM   #36
Senior Member
 
Join Date: Apr 2019
Location: Northern, Ontario
Posts: 110
Quote:
Originally Posted by craigav View Post
While you are correct, the difference in current to trip a gfi starts as low as 4 milliamps which is so little that many if not most amp meters would not measure this low of a difference. Also, keep in mind that if the RV does have current leakage, that the current could simply be flowing through the stabilizer jacks instead of the ground conductor. ~CA
Yes.
When I'm troubleshooting, I don't assume anything. The resistance should be less going through the ground wire then the sablilizer (the path of least resistance). If the trailer is plugged into a GFI and tripping the ground current must be above 4 milliamps. Although I do have a milliamp meter, when troubleshooting you have to start somewhere. With the trailer tripping a GFI, their is a potential to have a dangerous situation. This is why I have concerns posting on a forum, I and coworkers have knowledge and experience working on Ground Detection Circuits with fault currents in the 100,000's of amps and 115,000 volts. If I, myself couldn't verify the problem I would shut off the power till I got someone that could.
MPD56 is offline   Reply With Quote
Old 08-19-2022, 10:32 PM   #37
Senior Member
 
SloPoke's Avatar
 
Join Date: Apr 2016
Location: Kingman AZ and where our Seneca is today.
Posts: 3,118
I need more popcorn....
__________________
Steve & Stacy with Jasper (Australian Cattle dog)
2015 Seneca 36FK
Custom 27' flatbed trailer hauling:
07 Toyota FJC & Yamaha Kodiak 400 ATV

SloPoke is offline   Reply With Quote
Old 08-20-2022, 03:04 AM   #38
Senior Member
 
Join Date: Jun 2022
Location: delta
Posts: 101
Quote:
Originally Posted by MPD56 View Post
Yes.
When I'm troubleshooting, I don't assume anything. The resistance should be less going through the ground wire then the sablilizer (the path of least resistance). If the trailer is plugged into a GFI and tripping the ground current must be above 4 milliamps. Although I do have a milliamp meter, when troubleshooting you have to start somewhere. With the trailer tripping a GFI, their is a potential to have a dangerous situation. This is why I have concerns posting on a forum, I and coworkers have knowledge and experience working on Ground Detection Circuits with fault currents in the 100,000's of amps and 115,000 volts. If I, myself couldn't verify the problem I would shut off the power till I got someone that could.
The potential is their but not quite to the same amplitude. Are you working in a substation or something?
__________________
2022 28.5 rsts
One Ton Dodge
Josparkz is offline   Reply With Quote
Old 08-20-2022, 03:09 AM   #39
Senior Member
 
Join Date: Jun 2022
Location: delta
Posts: 101
Quote:
Originally Posted by SloPoke View Post
I need more popcorn....
Microwave, stovetop, or campfire? Perhaps just Tesla style. Maybe just a full Edison.
__________________
2022 28.5 rsts
One Ton Dodge
Josparkz is offline   Reply With Quote
Old 08-20-2022, 07:27 AM   #40
Senior Member
 
Join Date: Apr 2019
Location: Northern, Ontario
Posts: 110
Quote:
Originally Posted by Josparkz View Post
The potential is their but not quite to the same amplitude. Are you working in a substation or something?
I'm blessed to work in a place I can learn every day

If it has wire to it, I'm suppose to know how to install or troubleshoot and repair it.

We consume over 100 megawatts per hour and in a short time we are going to double that.

We have over a dozen Substations from 250kv to 11.5kv. Below that we just call them load centers.

Anyway my popcorn is done

I will say 120 volt ac is harder to troubleshoot, when 11.5kv and up has problems, there is a big boom and a light show.

As for ground detection, last week we had a 14,000 HP 11.5KV motor trip on Ground Fault. It ended up being a bad card in a SAF drive. No boom, no light show told me that it wasn't a high voltage problem.
MPD56 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 08:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.