Westom, yes, your explanation is in-line with my suggestion, which is, the popular surge protectors aren't what many people expect.

Progressive industries does sell a surge protector model SSP-30, which plugs into the pedistal, then you plug your RV into it. They sell for $99. I'm afraid to ask the price in Canada This item would equal the Cutler-Hamer unit you mentioned.
__________________
2013 Jayco Eagle 31.5RLDS
2018 Silverado 2500 HD Duramax
David472 is offline   Reply With Quote
Old 04-13-2011, 05:15 PM   #22
Site Team
 
Crabman's Avatar
 
Join Date: Nov 2010
Location: Virginia`s Eastern Shore
Posts: 17,091
Moving right along now, I don`t even have a surge protector yet! I may have to put one on my wish list. One of Crabman`s many wants and needs.
__________________
2017 Coachmen Catalina 283RKS
2018 Ford F250 Super Duty 6.2l CCSB
2010 Jayflight 28BHS (sold)
Crabman is offline   Reply With Quote
Old 04-13-2011, 05:17 PM   #23
Senior Member
 
Terry's Avatar
 
Join Date: Feb 2011
Location: Germantown, TN
Posts: 4,923
Great discussion and info!

So jwmmck -- hope you got your question answered - or at least a good amount of varied opinion and info so you are able to make an informed decision. You will find a lot of good discussions on these types of topics.

Be safe out there playing with electricity! Remember it is not the volts, its the amps



__________________
Terry
2009 Jayco 26BH
2004 Chevy Silverado 1500
2009 JayFlight Manual Library

Want to add a signature to your posts? --> Click Here
Terry is offline   Reply With Quote
Old 04-13-2011, 05:35 PM   #24
Senior Member
 
David472's Avatar
 
Join Date: Feb 2011
Location: SW Ontario
Posts: 1,393
First, I don't mean any ill-will,
So, in the interest of engineering accuracy, you will see in the attached thumbnail, for the V130LA20B MOV, when voltage reaches 350 volts, the MOV will be drawing about 30 amps (that much clamping action). If this event duration last for more than a few milli-seconds, which it could, this extra MOV current draw through the main breaker, will trip that breaker. Power dissipation ability of the MOV must be matched to the expected energy content (watt-seconds) of sustained over-voltage, until the main breaker opens up. The two will work in harmony. Note that, in the case of a direct lightning strike, this system is only marginally helpful. Mighty Thor has too much power available.
Attached Thumbnails
scan0001.jpg   scan0002.jpg   scan0003.jpg  
__________________
2013 Jayco Eagle 31.5RLDS
2018 Silverado 2500 HD Duramax
David472 is offline   Reply With Quote
Old 04-14-2011, 06:35 AM   #25
Senior Member
 
David472's Avatar
 
Join Date: Feb 2011
Location: SW Ontario
Posts: 1,393
Since the orginal post was about voltage regulation, here is a link to an industrial product which truly does regulate an AC supply source. That is, it will boost a steady low voltage condition, or reduce a steady over voltage condition, under load. The company is called Sola.

http://www.solahd.com/products/power...g/mcr_hard.htm

For the RV world, the AC supply protection devices typically seen, only shut down in a low voltage or over voltage situation. That approach is not regulation, but rather is protection. See Progressive Industries link.

http://www.progressiveindustries.net/ems_hw30c.htm

I think I have said enough on this topic.
__________________
2013 Jayco Eagle 31.5RLDS
2018 Silverado 2500 HD Duramax
David472 is offline   Reply With Quote
Old 04-14-2011, 05:15 PM   #26
Junior Member
 
Join Date: Apr 2011
Posts: 12
Quote:
Originally Posted by David472 View Post
So, in the interest of engineering accuracy, you will see in the attached thumbnail, for the V130LA20B MOV, when voltage reaches 350 volts, the MOV will be drawing about 30 amps (that much clamping action). If this event duration last for more than a few milli-seconds, which it could, this extra MOV current draw through the main breaker, will trip that breaker.
OK. 30 amps creating 350 volts for 20 milliseconds means the MOV is degraded on a first surge (see datasheet charts). Anything longer will probably create 'completely unacceptable' catastrophic destruction. I cannot say more because a transient that long is not even listed in those charts. Transient that long violates what MOV manufacturers intend. And may create a human safety issue.

Meanwhile, a 30 amp transient on a 20 amp circuit takes between 20 and 200 seconds to trip (numbers for various Square D 20 amp breakers). The MOV would have vaporized in flames before that circuit breaker even thought about tripping. That was my point. MOVs are not installed to trip circuit breakers or fuses.

MOVs are thermal fused. A 30 amp transient through an MOV causes an unacceptable (catastrophic) failure that endangers human life. A tiny thermal fuse would disconnect the MOV long before any fire and before any circuit breaker tripped. An effective surge protector is for transients that are hundreds or thousands of amps. And that occur in microseconds.

Surge Guard is a switch that disconnects from AC mains if prolonged AC voltage exceeds (for example) 132 volts.

MOV protector and the Surge Guard are for two completely different events. MOV based protector is for a microsecond transient. And requires a short connection to earth ground. The second is for an anomaly that may occur for seconds or hours. And does not require any earth ground.

Bottom line: Not listed are solutions for other anomalies such as power factor, frequency variation, harmonics, neutral failures, rapid power cycling, etc. For RV shore power, Surge Guard addresses a most common problem. A surge protector at the pedestal addresses a different and rare anomaly that is also so catastrophic. Two completely different solutions for two completely different problems.
westom is offline   Reply With Quote
Old 04-14-2011, 05:26 PM   #27
Senior Member
 
Terry's Avatar
 
Join Date: Feb 2011
Location: Germantown, TN
Posts: 4,923
Man...I am a pretty technical person, but you guys are taxing my brain lol!

I am going to stick with my Flux Capacitor. If my camper ever hits 88, watch out!



__________________
Terry
2009 Jayco 26BH
2004 Chevy Silverado 1500
2009 JayFlight Manual Library

Want to add a signature to your posts? --> Click Here
Terry is offline   Reply With Quote
Old 04-14-2011, 06:10 PM   #28
Member
 
Join Date: Jan 2011
Location: Carteret, N.J.
Posts: 30
Thanks to all

for the input.... Think I'll grab one of these...


http://www.campingworld.com/shopping...egulators/7507
__________________
2010 Eagle Superlite 314BDS

2008 Ford F-250 Crew Cab
6.4 Turbo Diesel 4:10 rear
Reese Dual Cam
Tekonsha Prodigy
jwmmck is offline   Reply With Quote
Old 04-14-2011, 06:14 PM   #29
Member
 
Join Date: Jan 2011
Location: Carteret, N.J.
Posts: 30
And....

maybe one of these.............................



http://www.campingworld.com/shopping...rge-guard/2279
__________________
2010 Eagle Superlite 314BDS

2008 Ford F-250 Crew Cab
6.4 Turbo Diesel 4:10 rear
Reese Dual Cam
Tekonsha Prodigy
jwmmck is offline   Reply With Quote
Old 04-14-2011, 06:30 PM   #30
Senior Member
 
bertscampers's Avatar
 
Join Date: Mar 2011
Location: Southwestern Ontario, Canada
Posts: 119
I am really trying to follow these posts but am struggling. I am picking up my RV in a week. I am not sure what I need to get to protect my trailer. Surge guard or surge protector. If I get nothing what then? I am just trying to understand.

Thanks for all the help.
bertscampers is offline   Reply With Quote
Old 04-14-2011, 08:12 PM   #31
Senior Member
 
Join Date: Oct 2010
Posts: 414
Quote:
Originally Posted by bertscampers View Post
I am really trying to follow these posts but am struggling. I am picking up my RV in a week. I am not sure what I need to get to protect my trailer. Surge guard or surge protector. If I get nothing what then? I am just trying to understand. Thanks for all the help.
I know what you mean. re: Too much details is more confusing then staying high-level.

For my TT setup (and if getting a new trailer next week as well), I would:

A - Purchase 30A RV voltage Monitor / Management system. Progressive has an affordable system at: http://www.dyersonline.com/progressi...nt-system.html

Note: I love "hard wire" devices because once installed, they are a "leave it and read it" usage device. And, lower risk of someone illegally removing it. Especially when installed inside the TT.

If wondering, this device monitors "too low" and "too high" of electrical current. If current is outside normal range, it then "switches off" the main power. And, keeps the switch off - until the AC unit has time to decompress itself. And, this device has "some" built in MOV surge protection as well. And, it has a nice display. Which, allows the person to easily read its numbers.

B - Where possible (re: on LCD TV outlet, rear fridge outlet, Coffee Pot outlet, your DVD/CD/Media Player outlet), I'd install a low cost "outlet" MOV surge protection device. If a power spike snuck past the Main Panel device, the "outlet" level device might lower the spike. For example: http://sales.buysmrt.com/Monster+Cab...rge+Suppressor

Note: Do shop around. I've seen this same device for as low as $15. Buy a few each year and in 3 years, all TT "electronic" sensitive outlets are protected.

If wondering, Main Panel and wall Outlet surge protection is called a 2 tier system. Double layers of protection. Some RV devices cannot have a 2nd tier (re: Ceiling mount AC unit, behind the walls Microwave, electric Hot Water tank, outside 110/120V outlet, bathroom GFCI outlet) but installing a 2nd tier surge protection "were possible" is a good idea.

If one's Progressive Monitor/ Management system is always "cutting off / switching off" the main power because the main power line is consistantly too low (re: under 103V), then install a Voltage Regulator. Many Voltage Regulator units boost (increase) main power. For example, increase from 102V to perhaps 109V (which stops the Progressive Management device from switching OFF - because its main power is now above 103V).

If wondering, I may have to install a future Voltage Regulator at my seasonal camp site. When all TT AC units "on the same electrical grid" are ON, my TT's volts drops down to 101-103 range. And, my Surge Guard device sometimes cuts off its main power. I may have to install a voltage regulator to "boost" power above its current lower 103 Volt limit. Only time will tell...

Hope this helps in your research....

.
Spike99 is offline   Reply With Quote
Old 04-14-2011, 08:23 PM   #32
Senior Member
 
RVhiker's Avatar
 
Join Date: Dec 2010
Posts: 1,643
Quote:
I am really trying to follow these posts but am struggling. I am picking up my RV in a week. I am not sure what I need to get to protect my trailer. Surge guard or surge protector. If I get nothing what then? I am just trying to understand.
Most of us do not use any device to test the AC coming into our RV. I didn't until recently. The deal is that under or over voltage on the AC supply can hurt your trailer. Bad wiring at the pedestal can hurt your trailer and maybe you. Surges - that is very short over voltages - can hurt your electronic devices in your trailer, like your converter, the refrigerator controls, etc.

For the bad wiring at the pedestal, you can buy a simple outlet tester at a home supply store. It checks for bad grounds, and backwards wired hot and neutral supply.

For surges, you can't do much cheaply.

For under and over voltage supply, you could buy an AC voltmeter and check the supply- of course, that only tells you it's condition then, and not in the afternoon at 90 degrees when everybody has their AC cranked up.

You could buy one of these or similar http://www.progressiveindustries.net/ssp_30.htm

You could do nothing special. That's what I did for 10 years, and nothing happened. I did use a polarity tester when I first hook up.
__________________
There's lots of advice and information in forums... sometimes it is correct. For example, all of my posts are made by a political appointee who got the job as a reward for contributions to my diesel bill.

2011 Jayco 28.5RLS; 2021 Chevy Duramax; Pullrite Superglide Hitch

RVhiker is offline   Reply With Quote
Old 04-14-2011, 08:27 PM   #33
Senior Member
 
Terry's Avatar
 
Join Date: Feb 2011
Location: Germantown, TN
Posts: 4,923
Quote:
Originally Posted by bertscampers View Post
If I get nothing what then? I am just trying to understand.

Thanks for all the help.
The honest answer is probably nothing. I am just guessing, but I would say 95% of trailers do not have protection. I have a Progressive Industries EMS, but didnt have one for a while. I just like the piece of mind it gives me. Before that, I checked the pedestal before I plugged in and make sure it was the correct voltage and wired properly - and I also had a volt meter in the camper so I could keep an eye if it dropped too low when everyone had AC turned on.

I personally think of it more as insurance - you just have to choose if you want to live without it or not but I dont think you should worry if you go out the door without it.



__________________
Terry
2009 Jayco 26BH
2004 Chevy Silverado 1500
2009 JayFlight Manual Library

Want to add a signature to your posts? --> Click Here
Terry is offline   Reply With Quote
Old 04-16-2011, 06:18 AM   #34
Senior Member
 
David472's Avatar
 
Join Date: Feb 2011
Location: SW Ontario
Posts: 1,393
Quote:
Originally Posted by westom View Post
Bottom line: Not listed are solutions for other anomalies such as power factor, frequency variation, harmonics, neutral failures, rapid power cycling, etc. For RV shore power, Surge Guard addresses a most common problem. A surge protector at the pedestal addresses a different and rare anomaly that is also so catastrophic. Two completely different solutions for two completely different problems.
I agree totally.
There is a small chance of a surge protector going up in smoke, or a small chance of it going to a short circuit. Thus, pedistal location is best place for a surge protector.
__________________
2013 Jayco Eagle 31.5RLDS
2018 Silverado 2500 HD Duramax
David472 is offline   Reply With Quote
Old 04-16-2011, 06:23 AM   #35
Senior Member
 
David472's Avatar
 
Join Date: Feb 2011
Location: SW Ontario
Posts: 1,393
Quote:
Originally Posted by tafische View Post
The honest answer is probably nothing. I am just guessing, but I would say 95% of trailers do not have protection. I have a Progressive Industries EMS, but didnt have one for a while. I just like the piece of mind it gives me. Before that, I checked the pedestal before I plugged in and make sure it was the correct voltage and wired properly - and I also had a volt meter in the camper so I could keep an eye if it dropped too low when everyone had AC turned on.

I personally think of it more as insurance - you just have to choose if you want to live without it or not but I dont think you should worry if you go out the door without it.
Yes, the chances of having problems when you use nothing, is very low. You would probably win the lottery first.
__________________
2013 Jayco Eagle 31.5RLDS
2018 Silverado 2500 HD Duramax
David472 is offline   Reply With Quote
Old 04-16-2011, 08:21 AM   #36
Senior Member
 
bertscampers's Avatar
 
Join Date: Mar 2011
Location: Southwestern Ontario, Canada
Posts: 119
Thanks for all the advice. My train of thought was if it was a serious issue wouldn't the trailer companies have them installed? Thanks once again.

Cheers
bertscampers is offline   Reply With Quote
Old 04-16-2011, 08:22 AM   #37
Senior Member
 
Join Date: Oct 2010
Location: Merrimack NH
Posts: 917
Generac makes an expensive ac volt meter (on line 20.00+-)it plugs in and has an outlet on the face so you don't loose the outlet. I saw it work when I pluged in my son's truck block heater and the voltage went from 120v to 115v due to voltage drop(200' distance form the elect panel to the truck and 16ga wire in the cord)besides the numerical scale it also has a color change ie green, yellow & red to alert you of low voltage.
__________________
Larry & Rachel Demers 2013 F150 Eco Boost Super Cab 6.5 bed 6 sp. 3.31 4x4 White Hawk 28DSBH
29BHS ECO is offline   Reply With Quote
Old 04-16-2011, 08:23 AM   #38
Senior Member
 
Join Date: Oct 2010
Location: Merrimack NH
Posts: 917
Sorry, I meant to say INexpensive
__________________
Larry & Rachel Demers 2013 F150 Eco Boost Super Cab 6.5 bed 6 sp. 3.31 4x4 White Hawk 28DSBH
29BHS ECO is offline   Reply With Quote
Old 04-16-2011, 10:26 AM   #39
Senior Member
 
David472's Avatar
 
Join Date: Feb 2011
Location: SW Ontario
Posts: 1,393
Quote:
Originally Posted by 19H F250 View Post
Generac makes an in-expensive ac volt meter (on line 20.00+-)it plugs in and has an outlet on the face so you don't loose the outlet. I saw it work when I pluged in my son's truck block heater and the voltage went from 120v to 115v due to voltage drop(200' distance form the elect panel to the truck and 16ga wire in the cord)besides the numerical scale it also has a color change ie green, yellow & red to alert you of low voltage.
Yes, and here is another low cost product to monitor for "brown-out" conditions, if you like to do that.

http://www.mfjenterprises.com/Produc...uctid=MFJ-850B
__________________
2013 Jayco Eagle 31.5RLDS
2018 Silverado 2500 HD Duramax
David472 is offline   Reply With Quote
Old 04-16-2011, 10:31 AM   #40
Site Team
 
Crabman's Avatar
 
Join Date: Nov 2010
Location: Virginia`s Eastern Shore
Posts: 17,091
Quote:
Originally Posted by David472 View Post
Yes, and here is another low cost product to monitor for "brown-out" conditions, if you like to do that.

http://www.mfjenterprises.com/Produc...uctid=MFJ-850B
Now that one I have!
__________________
2017 Coachmen Catalina 283RKS
2018 Ford F250 Super Duty 6.2l CCSB
2010 Jayflight 28BHS (sold)
Crabman is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 04:47 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.