CO2 censor going off

I was out this weekend in cooler weather (Iowa) camping and had the CO2 detector go off repeatedly during the evenings. It did not go off during the day, but at night after midnight both nights it would go off.

I reset it each time and made sure that the family was OK as everyone was up from the alarm. Has anyone had this happen in the past?
slabat is offline   Reply With Quote
Old 10-20-2014, 01:28 PM   #2
Senior Member
 
RoyBraddy's Avatar
 
Join Date: Sep 2011
Location: King George
Posts: 2,761
Mine will sometimes just start doing a beep every few seconds. It has never gone into a very loud steady alarm mode.

I assume you was using your furnace when your alarm went off???

I think the occasional beep is an low voltage 'battery' alarm...

I too hate to hear any noise coming from the detector as you never really know if it for real or not...

Roy Ken
__________________
Roy and Carolyn
I claim Horse Creek Country in Southern Ill - Momabear is from North Texas
We live in King George VA
RETIRED DOD DOAF DON CONTRACTOR Electronics Tech 42YRS

"We're burning daylight" - John Wayne
2008 STARCRAFT 14RT OFF-ROAD POPUP with PD9260C and three 85AH 12VDC batteries
2010 F150 FX4 5.4 GAS with 3.73 gears - Super Cab - Towing Package - 2KW Honda EU2000i Gen
K9PHT (since 1957) 146.52Mhz
"We always have a PLAN B"
RoyBraddy is offline   Reply With Quote
Old 10-20-2014, 01:45 PM   #3
Senior Member
 
Join Date: May 2013
Location: SE Wisconsin
Posts: 3,430
Was this the first time you used your furnace?
__________________
Chuck
2013 Jayco Jayfeather X20 E (sold)
2016 Chevy Silverado LTZ 2 Z71 Crew Cab (sold, and dearly missed)
DocBrown is offline   Reply With Quote
Old 10-20-2014, 02:24 PM   #4
Senior Member
 
Join Date: Aug 2011
Location: Missouri City, The Republic of Texas
Posts: 5,063
Was the furnace running at all? When new there's some kind of coating that has to burn off that will trigger the smoke alarm. If your furnace is older perhaps there is a leak in the heat exchanger and you are getting CO inside.
Are you sure it was the CO alarm and not the propane alarm or even the smoke detector?
__________________
Cheers,
T_

2013 F-350 CC SB 2WD 6.7PS
2013 Eagle Premier 351 RLTS
-SOLD- 2012 X23B
-SOLD- 2003 Ford Expedition 5.4, Bilstein shocks
RedHorse1 is offline   Reply With Quote
Old 10-20-2014, 02:55 PM   #5
Senior Member
 
Brownie's Avatar
 
Join Date: Jan 2014
Location: Greater Grand Rapids
Posts: 1,392
I've discovered over the last few weeks that methane gas will set off the alarm, too. Mine is located right outside the bathroom door which I never close (since it's just me and the dog). It's gone off three times while using the toilet . . . I guess you guys/gals can take it from there.

I now open the vent & turn on the fan, and it hasn't gone off in a week.
__________________
2013 Eagle 266RKS
2011 Ford F-150 w/3.5L Ecoboost & H.D. Tow Package
Brownie is offline   Reply With Quote
Old 10-20-2014, 03:13 PM   #6
Senior Member
 
Join Date: May 2013
Location: SE Wisconsin
Posts: 3,430
Wow Brownie! What are you eating?!
__________________
Chuck
2013 Jayco Jayfeather X20 E (sold)
2016 Chevy Silverado LTZ 2 Z71 Crew Cab (sold, and dearly missed)
DocBrown is offline   Reply With Quote
Old 10-20-2014, 03:48 PM   #7
Site Team
 
Snake Plissken's Avatar
 
Join Date: Feb 2011
Location: DeWitt, MI
Posts: 1,212
Quote:
Originally Posted by Brownie View Post
I've discovered over the last few weeks that methane gas will set off the alarm, too. Mine is located right outside the bathroom door which I never close (since it's just me and the dog). It's gone off three times while using the toilet . . . I guess you guys/gals can take it from there.

I now open the vent & turn on the fan, and it hasn't gone off in a week.
__________________
MODERATOR

2007 Jayco Feather 19H
2008 Ford Explorer SportTrac
Snake Plissken is offline   Reply With Quote
Old 10-20-2014, 04:11 PM   #8
Senior Member
 
Roadwarrior's Avatar
 
Join Date: Sep 2014
Location: Pahrump
Posts: 159
I went in to the trailer today, and my smoke alarm started going off (not low battery chirp) and wouldn't stop. I finally had to take it off the ceiling into the house and took the battery out, put it back in and it still went off a couple of times. It's settled down now but, geez what's with these things?
__________________
2014 Jay Flight Swift SLX 185RB "Little Swift"
2022 Jay flight SLX 264BH Rocky Mountain Edition Baja

2006 Chev Silverado Z-71 5.3L H.O. w/ Trailer Pkg

Tekonsha Primus IQ Controller
Roadwarrior is offline   Reply With Quote
Old 10-20-2014, 06:55 PM   #9
Junior Member
 
Join Date: Sep 2013
Posts: 11
Yes, had the thing sounding off with a steady tone. Greyhawk is a year old. Furnace has been used a lot. Could not stop it, so I unscrewed it and cut the wire. Dealer will install a new CO detector.
Birdfan is offline   Reply With Quote
Old 10-20-2014, 08:07 PM   #10
Senior Member
 
Join Date: Feb 2012
Posts: 550
I have used my furnace alot as well. What is strange is we have used it in colder weather and it did not go off. I guess I will take it to the dealer and have everything checked out. I don't want to take a chance with it.
slabat is offline   Reply With Quote
Old 02-25-2015, 09:04 AM   #11
Member
 
Join Date: Mar 2014
Location: Hartford
Posts: 51
CO is a dangerous invisible odorless gas that will kill you if you are unaware of its presence. If your CO alarm is going off then take necessary precautions and have the area checked for the presence of CO. It may sound absurd, but call your FD and have them come and check with a real 4 gas meter for the presence of CO. At a minimum, ventilate the area (open windows / turn on fans) until the alarm resets.

I installed a second CO alarm in our x18d as a precaution. If only one goes off change the battery and reset. If both go off, ventilate and evacuate.

FYI, I have some experience with CO alarms and the medical emergencies they can cause. Don't disable an alarm without checking to make sure something is not legitimately wrong. Disabling the alarm and going back to sleep could be a fatal mistake!
__________________
"Never take life to seriously, no one gets out alive any way!"

Alicia and Glenn
Hartford (area), CT
2012 Nissan Pathfinder (V6)
2014 X18D
gvn71 is offline   Reply With Quote
Old 02-25-2015, 01:40 PM   #12
Senior Member
 
rryman's Avatar
 
Join Date: Jan 2015
Location: Loris
Posts: 253
Everthing GVN said is right on target. Don't take chances with a CO detector. Having said that, we've found out that hair spray, spray cologne, and other similar stuff can set off the CO detector. Found out that Scotch Guard will also do it, as it went off when I was spraying the carpet. It did go off after a few minutes. CO will definitely put your lights out without you even knowing it.
__________________
---------------------------------
Randy, Karen & Abby (Pom-a-Poo)
2014 Eagle HT 27.5RLTS
2015 F250 Super duty 6.2L full trailering pkg.
Loris, South Carolina.
rryman is offline   Reply With Quote
Old 02-25-2015, 03:59 PM   #13
Senior Member
 
Dagwood's Avatar
 
Join Date: May 2014
Location: Ottawa - Canada Eh
Posts: 405
When we had our Popup, the CO2 sensor was positioned in the Dinette area near the floor. It went off one night a scared the you know what out of us. Turns out, placing the Dog bed in that convenient spot also meant our Dog Abby could exhale directly on it.

__________________
Wayne, Kim, Mallory & Abby the Dog
2013 - Jayco Jayfeather - X20E
2012 - Toyota Tacoma DBLCB Sr5 with towing package
Equalizer 10k WD, Prodigy P3 Controller, TST TPMS

2012 - Jayco Sport 10 Popup - Traded
Dagwood is offline   Reply With Quote
Old 02-25-2015, 04:08 PM   #14
Senior Member
 
Join Date: Apr 2014
Location: Calgary
Posts: 885
Could it be a dirty or dusty sensor? I can't remember if CO detectors can be cleaned with compressed air or if that is just smoke alarms.

I think I will add a second monitor to our trailer so if one falses I can go back to sleep and have a good chance of waking up again!
__________________
2014 Jayco Swift 281BHS, 300W Solar!
2015 F250 XLT 4x4 Crew Cab, Short box, 6.2 gas
Subaru297 is offline   Reply With Quote
Old 03-04-2015, 07:03 AM   #15
Senior Member
 
bucko's Avatar
 
Join Date: Sep 2014
Location: In a house
Posts: 1,000
Quote:
Originally Posted by DocBrown View Post
Wow Brownie! What are you eating?!
I think he was blaming the dog....
__________________


2005 Jayco GreyHawk Class C
2007 Ford F150
bucko is offline   Reply With Quote
Old 03-04-2015, 07:56 AM   #16
Senior Member
 
Cosmik Debris's Avatar
 
Join Date: Aug 2013
Location: Missoula, Montana
Posts: 704
They go off when they go bad. I've had a couple replaced in two rigs.
Cosmik Debris is offline   Reply With Quote
Old 03-04-2015, 08:01 AM   #17
Site Team
 
norty1's Avatar
 
Join Date: Jan 2011
Location: James Island, SC
Posts: 22,772
They sometimes start going off for no reason at all times. Indicating it is time to replace. For some reason, they don't last like they used to.
I have had to replace one on each of my last 2 rigs that were only a few years old.
The sticker on the back says to replace every 5 years.
__________________
Moderator
2011- 351RLTS Eagle, MorRyde suspension/pin box,
2017- F350 6.7 PSD Lariat FX4,SRW, SB,CC
Hughes PWD SP-50A, TST TPMS
Gator roll-up bed cover
B&W Turnover ball, Companion Std hitch
Can't find what you're looking on JOF? Try Jayco Owners Forum Custom Google Search
norty1 is offline   Reply With Quote
Old 03-05-2015, 08:29 AM   #18
Senior Member
 
edatlanta's Avatar
 
Join Date: Dec 2009
Location: Maplesville - Home Base
Posts: 3,059
Every one I have had go bad started going off at 3:00am. I think their programmers have a warped since of humor.
__________________
Ed
KM4STL

2006 GMC 2500HD CCSB 4x4 Duramax/Allison, Titan 52 gallon fuel tank, Prodigy Controller, B&W Companion Hitch
2010 Jayco Designer 35RLTS, Cummins/Onan RV QG 5500 EVAP, Progressive Industries EMS-PT50X, TST Systems 507 TPMS, RV Flex Armor Roof
edatlanta is offline   Reply With Quote
Old 03-05-2015, 08:34 AM   #19
Senior Member
 
Join Date: Feb 2012
Posts: 968
Did you do any re-winterizing with antifreeze during your trip?
I've had my CO/Propane detector go off every year when I add antifreeze to the p-traps. I open the doors and windows and turn on the exhaust fan and after about 5 minutes, the alarm goes off and doesn't come back on. I think it is the initial smell of the antifreeze that does it.
dewey02 is offline   Reply With Quote
Old 03-05-2015, 11:17 AM   #20
Senior Member
 
AKGperson's Avatar
 
Join Date: Oct 2014
Location: SF Bay Area
Posts: 327
I'd suggest you purchase a separate Carbon Monoxide detector and place it in the TT while camping. If the factory installed alarms but the hand-held does not, you know you have a faulty detector. Better safe than sorry.
__________________
"We're all here because...we're not all here"

2015 White Hawk 25BHS w/Outdoor Kitchen
2015 GMC Sierra SLT 2500HD Z71 4x4 Duramax
1985 Coleman Sequoia Tent Trailer
AKGperson is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 01:20 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.