Old 06-15-2015, 05:59 AM   #1
Member
 
Join Date: Jun 2013
Posts: 50
Coiled Electrical Cable

Hi all

For ease of use I leave the electrical cable coiled in the back of my X17Z and use an extension cable to connect my trailer to the campsite's hydro box.

Can anyone tell me if thus coiled cable could produce some sort of electrical or magnetic field while plugged in? If so, could extended use be harmful?

Thanks.

Bob
OttawaBob is offline   Reply With Quote
Old 06-15-2015, 06:44 AM   #2
Site Team
 
norty1's Avatar
 
Join Date: Jan 2011
Location: James Island, SC
Posts: 22,772
I have read all type horror stories about heat buildup and induced fields but I have had 3 campers with the power cord stuffed in the rat hole and never pulled out any more than I needed. Never had any indication of a problem.
__________________
Moderator
2011- 351RLTS Eagle, MorRyde suspension/pin box,
2017- F350 6.7 PSD Lariat FX4,SRW, SB,CC
Hughes PWD SP-50A, TST TPMS
Gator roll-up bed cover
B&W Turnover ball, Companion Std hitch
Can't find what you're looking on JOF? Try Jayco Owners Forum Custom Google Search
norty1 is offline   Reply With Quote
Old 06-15-2015, 06:47 AM   #3
Senior Member
 
BrentB's Avatar
 
Join Date: Mar 2013
Location: Central
Posts: 219
From my owner's manual:

The power cord must be fully extended
when in use and not left coiled in the
electrical compartment or on the ground. If
the power cord is left coiled, it may
potentially create enough heat to melt its
protective casing.

And:

Do not connect the power cord to an
extension cord. Use of an improper
extension cord will cause overheating
of the cord as well as potentially
causing premature failure of the AC
equipment.
BrentB is offline   Reply With Quote
Old 06-15-2015, 06:51 AM   #4
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,835
Technically, yes. You have heat and stronger magnetic fields on a bunched up cord than a stretched out one.


However, these cords are 12ga wire and capable of carrying much more power than a small camper can possibly use.


Leaving the cord crumpled inside will have no ill effects on the cord, the trailer, users of the trailer or the environment.


Bear in mind though, that the cord you actually use may only be 14ga or (gasp) 16ga wire and will not carry the power your trailer needs without significant loss.


Have you considered cutting the cord and converting over to a power inlet?
__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Old 06-15-2015, 07:10 AM   #5
Site Team
 
norty1's Avatar
 
Join Date: Jan 2011
Location: James Island, SC
Posts: 22,772
Also remember that the legal department clears all these statements!
__________________
Moderator
2011- 351RLTS Eagle, MorRyde suspension/pin box,
2017- F350 6.7 PSD Lariat FX4,SRW, SB,CC
Hughes PWD SP-50A, TST TPMS
Gator roll-up bed cover
B&W Turnover ball, Companion Std hitch
Can't find what you're looking on JOF? Try Jayco Owners Forum Custom Google Search
norty1 is offline   Reply With Quote
Old 06-15-2015, 07:31 AM   #6
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,835
Quote:
Originally Posted by norty1 View Post
Also remember that the legal department clears all these statements!
What? Mealy-mouthed, uncommitted double-talk isn't good enough?
__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Old 06-15-2015, 08:18 AM   #7
Member
 
Swardy's Avatar
 
Join Date: May 2015
Location: Winnipeg
Posts: 50
A full draw of 30A @ 120V through a 12AWG cable that is 25 feet long results in about a 2% voltage drop (about 2.5 volts) That "missing" voltage turns into heat. Your cable needs to dissipate that heat and it can't do that effectively when it's in a tight coil. In worst case situation, the outer jacket of the wire melts and all the bad stuff happens.

However:
The likelihood of that happening is pretty miniscule. The 2% voltage drop is very small - and that's based on max draw - something my trailer has never seen and unlikely yours as well.

In a wound coil, AC magnetic fields come into play that can change the above math, but not to any seriously significant way. Loosely stacked / crammed in the rat hole is not going to cause any issues.

All the above said, manual says stretch it out, I say stretch it out.

Not that it applies here, but a high output DC circuit (like a welder output) has to be run out. The magnetic flux in that situation can cause erratic low output and will certainly overheat when left coiled.
Swardy is offline   Reply With Quote
Old 06-15-2015, 08:40 AM   #8
Senior Member
 
Jagiven's Avatar
 
Join Date: May 2012
Location: Minnesota
Posts: 9,740
I would be more concerned about what you use for an extension cord. I commonly only pull out a bit more than what I really need, and leave the rest in the hole. When I have used the AC a lot, the plug is warm, and so is the cable near the plug. The more you use the big black cord the softer it gets, so the easier it is to pull out and push in.

Personally, unless you are using a heavy duty extension cord, I would not use the AC and keep the use of microwave and coffee maker like devices to a minimum.

With that said, my HTT is kept at home. I run a 25’ 14 gage extension cord from the garage to the HTT. I pull out a few feet of power cord and pull the cords together. Been doing this for years, no issues, no heat buildup that I have noticed. At home, about the only thing running is the on board battery charger, and the frig a for a few days before a trip. At a campsite, there would be a lot more current pull.
__________________

2012 Jayco X23B
2020 Ram Laramie 3500 SRW Air ride 50Gal fuel tank.
2007 Dodge Dakota Quad Cab (sold)
Equal-I-zer 4-Point Sway Control
Jagiven is offline   Reply With Quote
Old 06-15-2015, 08:54 AM   #9
Senior Member
 
tnchuck100's Avatar
 
Join Date: Jun 2012
Location: Sparta, TN
Posts: 1,174
This is one of those issues where theory is interpreted incorrectly when applied to the real world situations.

The biggest problem encountered is the possible poor connection from a worn campground receptacle than a coiled service cable.

Magnetic field? Insignificant.
Extension cord? Use the appropriate one and there will be no problem.

As with most electrical issues understanding is key.
__________________
Chuck - Sparta, TN
2012 Jay Flight 22FB, 2 x Honda EU2000i
2013 GMC Yukon XL Denali AWD

EDUCATION is what you get when you read the fine print.....
EXPERIENCE is what you get when you don't.
tnchuck100 is offline   Reply With Quote
Old 06-15-2015, 09:57 AM   #10
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,835
Quote:
Originally Posted by tnchuck100 View Post
...snip...

The biggest problem encountered is the possible poor connection from a worn campground receptacle ...
Regardless of too long/short/coiled/stretched ^^^THAT^^^ is a huge problem!
__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Old 06-15-2015, 10:13 AM   #11
Senior Member
 
VicS1950's Avatar
 
Join Date: Apr 2013
Posts: 517
As a practical matter I agree that leaving the cord coiled in the rabbit hole will have no problems with magnetic fields or even overheating. As has been mentioned already the warnings are based upon legal issues more than practical usage.

That said, there is a practical reason for pulling the cord out all the way once in a while. Many of the OEM cords are not very flexible and over time can take a set when the cord stays curved in the same places. In lower ambient temperatures that can be a problem when it is necessary to pull the cord out to the full length. The issue can be minimized by pulling the cord out to full extension once in a while.

Although not uncommon for connectors to get a bit warm, it is best when they stay cooler. Cleaning the connector prongs with a Scotchbrite pad followed by a light coating of dielectric grease or simply common Vaseline will help to keep the contacts in better condition for carrying the load.

FWIW. vic
VicS1950 is offline   Reply With Quote
Old 06-16-2015, 06:22 AM   #12
Senior Member
 
Join Date: Jul 2012
Location: CT
Posts: 361
There are far more sources of unhealthy amounts of electro-magetic energy flying all around you everyday, then you could ever possibly get from the coiled up camper power cord. Cell phones, computers, TV's Microwaves, power lines, cell towers, unseen radio waves traveling through the air, etc. All of which you can get from just hanging out at home.
Regarding the use of an extension cord, sometimes you have to use one, just make sure you purchase one that can handle the full 30 amp load and you should be fine.
__________________
Model X19H Expandable
GMC Sierra Pick up

Been a camper since I was a kid, and that was a long time ago :)
From pup tents with no floors, to tents with floors and flies, to a pop up, to the expandable.
chuckworkb is offline   Reply With Quote
Old 06-16-2015, 06:37 AM   #13
Senior Member
 
Join Date: Oct 2014
Location: oneonta ny
Posts: 534
Quote:
Originally Posted by mike837go View Post


However, these cords are 12ga wire
shouldnt it be 10 gauge for 30 amp?
rick danger is offline   Reply With Quote
Old 06-16-2015, 06:48 AM   #14
Senior Member
 
Join Date: Jul 2012
Location: CT
Posts: 361
Yep.
__________________
Model X19H Expandable
GMC Sierra Pick up

Been a camper since I was a kid, and that was a long time ago :)
From pup tents with no floors, to tents with floors and flies, to a pop up, to the expandable.
chuckworkb is offline   Reply With Quote
Old 06-16-2015, 09:21 AM   #15
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,835
Quote:
Originally Posted by rick danger View Post
shouldnt it be 10 gauge for 30 amp?
Whups, my bad. Haven't kept that chart in my head for years.
__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 12:52 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.