Originally Posted by mikeauto2
Turned on the a/c for the first time this year and not cold at all. The compressor is on but the air coming out of the vents is not cold. 2018 32bhds with the dometic unit and the dometic digital thermostat. Any help would be appreciated.
|
Ok, what could be wrong. If you have a clamp-on amp meter & confirmed. Compressor is actually running, could be dirty condenser, low on refrigerant or a " low pumper ". If not running possible control board problem, bad wire terminal, bad capacitor, bad thermostat. I assume the fan is running so you have voltage.