Another furnace question....

Hey guys, new to the forum and I’ve been searching all day for answers, but nothing seems to match what we’re dealing with 100 percent....

We bought a ‘19 377 rlbh, and we’re having an issue in the furnace. With the thermostat set to 68, the furnace will not start up unless reset, by that I mean I turn it off for several minutes, turn back to heat, and the blower starts, runs the cycle and shuts down. No ignition. I’ve checked the magic reset switch(continuity), I’ve checked the sail switch(continuity), and voltage(12v). I haven’t check the high temp relay as I ran out of day light. Any light shed would be huge. We’re in northern nv @ 6200 feet. It’s blowing down snow and we’re here for a while. Also, if I shut down the 12 volt supply and fidget with the sail switch, I can get the furnace to operate until it reaches the desired temp but is dead in the water after
Linehand13 is offline   Reply With Quote
Old 01-24-2021, 07:54 PM   #2
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,107
Quote:
Originally Posted by Linehand13 View Post
We’re in northern nv @ 6200 feet. It’s blowing down snow and we’re here for a while.
There are numerous comments on the web about high altitude problems across many different RV brands.
__________________
DISNEY LOVERS
Grumpy is offline   Reply With Quote
Old 01-24-2021, 07:59 PM   #3
Senior Member
 
Route 66 Traveler's Avatar
 
Join Date: Mar 2017
Location: Kingman, AZ
Posts: 1,985
Make sure you have good propane flow...turn on your stove and let it run or a minute or two. If there isn’t a good flow to the furnace it will try to lite, then shut down if the burner doesn’t ignite. Also, when opening the valve on the propane tank turn it slowly; turn it too fast and the internal safety will stop the flow of propane.

Has your furnace ever worked??
__________________
Lee & Kathy, and our alarm clock Jake!
2017 Starcraft Autumn Ridge 266RKS 50 amp.
2017 Toyota Tundra Crewmax 4x4, 10-1-2021

Route 66 Traveler is offline   Reply With Quote
Old 01-24-2021, 08:07 PM   #4
Junior Member
 
Join Date: Jan 2021
Location: Soda springs
Posts: 7
We have good flow, I’ve bled the system as you stated and still no ignition. The furnace was working up until two days ago. I was intermittent and last night just up and quit on us. Like I said, I can pull the heater apart and clean the contact in the sail switch and breaker switch. And get one good heat cycle out of it then it’s back to square one....
Linehand13 is offline   Reply With Quote
Old 01-24-2021, 08:09 PM   #5
Junior Member
 
Join Date: Jan 2021
Location: Soda springs
Posts: 7
That was what I’ve been reading but it was working fine until a couple nights ago....
Linehand13 is offline   Reply With Quote
Old 01-24-2021, 08:18 PM   #6
Moderator Emeritus
 
Rustic Eagle's Avatar
 
Join Date: Apr 2011
Location: Michigan
Posts: 9,424
Assuming the sail switch, high temp switch, and LP flow are good..., it leaves the circuit board and wall thermostat

Have you checked that the furnace has good return air flow to it? Some 5th wheels have a return air vent at the bedroom/bath steps and may also have a filter...., just a thought.

Bob
__________________

2016 GM 2500HD 6.0L/4.10
2018 Jay Flight 24RBS
2002 GM 2500HD 6.0L/4:10 (retired)
2005 Jayco Eagle 278FBS (retired)
1999 Jayco Eagle 246FB (retired)
Reese HP Dual Cam (Strait-Line)
Rustic Eagle is offline   Reply With Quote
Old 01-24-2021, 08:31 PM   #7
RPR
Senior Member
 
Join Date: Dec 2018
Location: Owens Cross Roads
Posts: 3,223
Had to buy a sail switch while on the road from a dealer two years ago. Parts guy had a tech come up to the counter and he said bend the sail part of the switch just a little and switch will last longer. Catches air better.
RPR is offline   Reply With Quote
Old 01-24-2021, 08:33 PM   #8
Senior Member
 
JimD's Avatar
 
Join Date: Apr 2017
Location: Inland Empire, California
Posts: 2,006
You mentioned that there was no ignition. Does that mean there is no sparking or does it mean sparking but no flame?

If it isn't sparking the problem is in the sequence before ignition is to start or there is a problem in the sparker (gap?). If it sparks but doesn't light, the problem is in the next phase of operation which is gas valve opens and gas flows then lights.

Attached is some info from the manual.
Attached Thumbnails
Capture.JPG  
__________________


Jim

Retired electronic technician (45 years in the field)
2017 Greyhawk 29W (solar & many other mods)
wife (maybe I should have given her top billing)
JimD is offline   Reply With Quote
Old 01-24-2021, 08:51 PM   #9
Junior Member
 
Join Date: Jan 2021
Location: Soda springs
Posts: 7
You mentioned that there was no ignition. Does that mean there is no sparking or does it mean sparking but no flame?

If it isn't sparking the problem is in the sequence before ignition is to start or there is a problem in the sparker (gap?). If it sparks but doesn't light, the problem is in the next phase of operation which is gas valve opens and gas flows then lights.


If I turn the thermostat to off, then return it to heat, the blower will start and run for 15 seconds or so..... and turn off with no ignition. It won’t even try, as stated in the manual. But if I go out and completely disconnect the 12volt source, pull the sail switch and blow on it or fidget with it, reinstall, and turn power back on, turn the thermostat to heat, I get one solid heat cycle and nothing after. It’s very confusing to me
Linehand13 is offline   Reply With Quote
Old 01-24-2021, 09:13 PM   #10
RPR
Senior Member
 
Join Date: Dec 2018
Location: Owens Cross Roads
Posts: 3,223
Replace the sail switch
RPR is offline   Reply With Quote
Old 01-24-2021, 09:13 PM   #11
Senior Member
 
JimD's Avatar
 
Join Date: Apr 2017
Location: Inland Empire, California
Posts: 2,006
When you shove it back in is it possible something falls into the sail switch area preventing it from moving? Thinking outside the box.

You checked the sail switch for continuity. Was there any resistance measured when closed? Did the switch move freely? Does the sail move very freely? Any possible restriction in the air flow?

Sure sounds like the problem is in the blower sensing area. Is there any way of firing it up while looking inside for switch operation?

Love these kinds of problems that go away after you open them up only to return.
__________________


Jim

Retired electronic technician (45 years in the field)
2017 Greyhawk 29W (solar & many other mods)
wife (maybe I should have given her top billing)
JimD is offline   Reply With Quote
Old 01-24-2021, 09:26 PM   #12
Junior Member
 
Join Date: Jan 2021
Location: Soda springs
Posts: 7
The switch and in side the blower were clean, I’m hoping that I can get the switch tomorrow and we’ll be back in business.... I sure appreciate all of the input! It’s way to damn cold here to be in the predicament... lol
Linehand13 is offline   Reply With Quote
Old 01-25-2021, 03:35 PM   #13
Junior Member
 
Join Date: Jan 2021
Location: Soda springs
Posts: 7
Well, we’ve made progress and it’s trying to do the three cycle and shutting down....
Linehand13 is offline   Reply With Quote
Old 01-25-2021, 04:33 PM   #14
Senior Member
 
ALJO's Avatar
 
Join Date: Oct 2014
Location: Sparwood, BC
Posts: 2,800
Send a message via Skype™ to ALJO
The Atwood furnaces with the sail-switch at the front of the blower we had more problems on late models RV's - most solutions where bending the fan to give it better lift. In one case it was the micro-switch. The electronic board is all about timing and any error will be reported in flashes to determine which circuit did fail. If one doesn't have a clear view on the flash LED's remove the furnace and bench test.
__________________
2014 Ram 1500 CrewCab 4x4 5.7 Hemi 3.92 Rear and Air Lift 1000
2005 Jayco Jay Feather LGT - 29Y GVWR-7000 lbs.
Dexter Axle Lift 4-9/16" - installed with sub-frame.
Pro Series 1200 lbs. WDH with Double Sway Bar.
Champion 3100/2800 watt Inverter/Generator-Onboard Solar Power
ALJO is offline   Reply With Quote
Old 03-04-2021, 07:03 PM   #15
Junior Member
 
Join Date: Nov 2019
Location: Twin Falls
Posts: 9
Hello Lindhand, my furnace in a Pinnacle has similar issues, I reset switch, turn on furnace which runs fine thru one cycle then trips reset switch again. Did you find an answer?? Thanks Steve
steveajohnson is offline   Reply With Quote
Old 03-06-2021, 12:04 AM   #16
Junior Member
 
Join Date: Jan 2021
Location: Soda springs
Posts: 7
Quote:
Originally Posted by steveajohnson View Post
Hello Lindhand, my furnace in a Pinnacle has similar issues, I reset switch, turn on furnace which runs fine thru one cycle then trips reset switch again. Did you find an answer?? Thanks Steve
Hey Steve, so my situation as stated above was a ton of trial and error..... obviously same as you I’m sure, I’d fumble with the sail switch and reset and get one solid heat cycle. What it needed up being was the high temp sensor. I have a friend that is a rv tech at a local dealer here in Reno NV, and that was the last guess before a bench test. My circuit board wasn’t throwing any flashes to indicate error and the ohm test through the new and old sail switch proved to be around the same. So I’d replace the high temp sensor and see if it fixes your issue. After replacing mine, it’s work famously and my family and I are nice and warm.
Linehand13 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 07:40 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.