Quote:
Originally Posted by ALJO View Post
In short I will explain how the electronic operated Atwood furnace works.

The thermostat (TH) turned up and switch on the TH in ON position calls for heat; which in turn tells the furnace to fire up (high limit ON)
The fan will start and blows cold air. The same fan is hooked also to the combustion fan which in turn clears the burning chamber from any gasses out through the flu pipe (is called purge cycle). After approx. 60 sec. when all the electronics switches are in line it will tell the gas valve to open and ignite on the same time.

If there is air in the lines the furnace will trip and you have to reset the TH switch to of and then the above cycle will repeat. In order to speed up this process; after you turn on the LPG at the bottle (do this slow) then light first your stove burners. Turn the burners off after there is a normal flame. After this in most cases the furnace will start after the first try.

When you feel the heat coming from the registers the furnace will trip the high limit switch which turn off the furnace burner. If the TH still calls for heat the furnace burner may come on even if the blower fan is still running.
If you think your furnace is cycling too much you have to adjust your TH (follow the instructions manual from the TH)

The furnace has usual 4 discharge outlets (4 x 12 sq.in = 48 sq.in) Return air is minimum 65 sq.in and recommended is 80 sq.in) (8516 and 8520) Check for pinched discharge hoses this can be a cause of overheating and trip the furnace operation in to fault code. The blower fan has its own cycle switch.

I would recommend to read the manual if you have troubles. If you donít have one; download one from Atwood.

That is a good discription of the operation of the furnace. And a couple of good troubleshooting tips.

The thermostat I have is a hot/cold electronic with NO delay adjustment. What you are referring to is an adjustment in mechanical thermostats that adjust the cycle time. The furnace can run longer less frequently or shorter more frequently. Helps adjust the large temp swings you get in a small under insulated trailer.

However only under the most extream temp conditions will the thermostat call a shutdown, and then recall a startup in less than 1 - 2 mins causing the burner cycle but no fan stoppage.

In the case of my furnace it is NOT the thermostat making the call. The dealership confirmed it and even replaced my stat. They agree its not getting proper airflow, they change the ducting arround and then put the grill back on crimping the duct hose in half. I am sure that I am not the only person with this problem and the others describe the exact same thing. If you have anything less than (2) 4" unobstructed ducts with NO 90 degree bends you are not getting proper air flow AS PER MANUAL! Adding a few 90s may still work but will degrade the life of your $850+ dollar furnace by years!
__________________

firestorm128d is offline   Reply With Quote
Old 11-24-2014, 05:38 PM   #32
Member
 
Join Date: Nov 2014
Location: Yakima
Posts: 37
New update... I was suppose to receive a call from the Dealership today with answers..... Days come and gone, and no call... Big shock!
__________________

firestorm128d is offline   Reply With Quote
Old 11-25-2014, 12:48 PM   #33
Junior Member
 
MPH9's Avatar
 
Join Date: Dec 2013
Location: Cottonwood Az
Posts: 28
Furnaces in RVs are noisy gas hogs. I had a 40ft mh. A fatalistic heater does the job nicely with low gas consumption and no noise and battrey drain
They also have an auto shut off . I now have a 19 Jayco and use a small cat/ heater
On low it keeps rig comfortable at nite
__________________
Using Tapatalk
MPH9 is offline   Reply With Quote
Old 11-25-2014, 01:15 PM   #34
Lost in the Woods
 
Join Date: Jan 2014
Location: N/A
Posts: 567
Quote:
Originally Posted by Grumpy View Post
There may not be a duct as such, but there may be a hole cut into the metal duct work. They also rely on the radiated heat from the metal duct to help warm the underbelly.
I may be wrong about your unit, but my 338 rlts furnace does not have visable duct work per say coming off the furnace. One end of the very bottom of the unit hooks up to a plenum that can not be seen easily. This plenum provides air to the duct work under the floor for the through the floor heat through out the unit as well as the heated underbelly. My floor gets warm in the kitchen area where the furnace is blowing hot air into the heated underbelly area when the furnace is operating. I tell everyone that my top of the line TT even has heated floors.
wwsmith111 is offline   Reply With Quote
Old 11-25-2014, 03:57 PM   #35
Member
 
Join Date: Nov 2014
Location: Yakima
Posts: 37
So Jayco... Why did you change the design of the 23mb? My unit is 4 months old. And the brand new units have the furnace and converter in different locations. And the ducting on the furnace is correct on the one I am sitting in down at a Portland dealership??? I'm guessing you know why you changed the design less than 6months into a model year!!!! This just about takes the cake!!!!!
firestorm128d is offline   Reply With Quote
Old 12-01-2014, 11:59 AM   #36
Member
 
Join Date: Nov 2014
Location: Yakima
Posts: 37
I have attempted to detail these pictures with some notes. I finally spoke to a customer service agent at Jayco, last Wednesday. She confirmed to me that she had NO notes listed on my trailer(IE, The dealership has never called them, no authorized the first hack repair that didn't solve anything). Nor had they authorized the second attempt that i have scheduled for today- that the service technician claimed he had spoken to them about.

I could not get an immediate response as to why Jayco changed the design less than 4 months into a production year. But i think its pretty obvious!!!
Attached Thumbnails
Resampled_2014-11-26_10-23-20_628.jpg   photo 2.jpg   photo 1.jpg   photo 3.jpg   Untitled.jpg  

firestorm128d is offline   Reply With Quote
Old 12-01-2014, 12:16 PM   #37
Senior Member
 
tnchuck100's Avatar
 
Join Date: Jun 2012
Location: Sparta, TN
Posts: 1,174
After seeing this I would be suspicious there may be much more shoddy workmanship in that unit you cannot see. If it were me I would push hard for a new trailer. This is NOT an inadvertent mistake. SOMEONE knew when they did it it was not right.

Can't say much for your dealer either. Obviously your dealer prefers lying to you over dealing with Jayco.

If Jayco fails to make this right I would spread these pictures far and wide.
__________________
Chuck - Sparta, TN
2012 Jay Flight 22FB, 2 x Honda EU2000i
2013 GMC Yukon XL Denali AWD

EDUCATION is what you get when you read the fine print.....
EXPERIENCE is what you get when you don't.
tnchuck100 is offline   Reply With Quote
Old 12-01-2014, 01:14 PM   #38
Member
 
Join Date: Nov 2014
Location: Yakima
Posts: 37
That post in picture #2 that is behind the duct hose. I imagine was an after thought. It is holding up the furnace unit, the engineer that designed the cabinetry didn't resize the hole, and the guy who installed that without saying anything should be fired! But I have been in manufacturing for 10 years. I bet he did say something and was told to "shut up- toe the line and if his team didn't crank out 10 of thees rigs by end of week they weren't going to get their bonuses!"

The rest of it is just plain crap engineering! Obviously Jayco changed the design! I'm going to call them out on it! I was assured I would get a call today from someone.... It's already 2:00 east coast- not really reassuring!!
firestorm128d is offline   Reply With Quote
Old 12-01-2014, 01:26 PM   #39
Member
 
Join Date: Nov 2014
Location: Yakima
Posts: 37
There is one major flaw to this layout configuration. The cold air intake is now less than 2' from a discharge vent. Which i assume was the reason Jayco originally located the furnace under the range in my trailer. But since that ended up causing the host of problems I now have. I would assume that they compromised and moved it over under the Fridge. Both locations violate the installation and operation requirements set forth clearly in the manual from Atwood.
Attached Thumbnails
September 23MB.jpg  
firestorm128d is offline   Reply With Quote
Old 12-01-2014, 06:36 PM   #40
Member
 
Join Date: Nov 2014
Location: Yakima
Posts: 37
So....... Of course No body called me back today from Jayco.
However after my 3rd call in, i was connected with a 2nd tier technician. He says he talked to the service rep at the dealership and was told I have an appointment for the 12th of December. This was news to me since I had an appointment for TODAY!!! - Anyhow other than telling me that all repairs and service "Must be preformed by a Jayco service center" - it was a total waste of time. No help! And it started to go even further south when I asked why they changed the design? He all but called me ignorant and made some comment about trailers all being different as they come off the lines. Supposedly a manager is going to call me back at some point. (Yeah Right) So back to square one!

I shortly thereafter called the other dealership in the town about 32 miles from here. It is owned by the same fella. And which up until this point I have always thought this dealership to be pretty good! Both of them. Anyhow I called looking for the owner of the company as I have talked to him before and I know he is usually at one or the other location. Not sure the position of the gentleman who answered the phone is in, but asked me to tell him what was going on. After letting me know that Mr. XXXXXXX was out of the office.

I told him every detail - and he was very sympathetic to my situation. He was going to try and get a hold of Mr. Owner. But surprisingly enough his service manager called me back... I was shocked, as this is the first time in this whole ordeal that someone called me! - Anyway he was eager to solve the problem of a broken furnace and was willing to change it out tomorrow morning for me. Encouraged by his enthusiasm I thanked him for the call and gesture, and explained the real problems to him. I now have an AM appointment with them to bring the trailer (32 miles over a mountain pass in 15 degree weather). I am not going to hold my breath but its the first real open dialog i have had thus-far that sounds like it might go somewhere.

He also has a September manufactured 23MB on the line and he was going to go take a poke around in it and see how it was assembled. But he believed it to have Furnace under fridge.
__________________

firestorm128d is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia State Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -6. The time now is 05:21 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.