Atwood Furnace AFMD35121A problem

Have an Atwood AFMD35121_A furnace that is inoperative at the moment. Turn thermostat to heat and hear a click. But nothing else, fuses are all good. Pulled the panel cover down and there are (4) wires on the top of the furnace with (3) connected. A Blue Thermostat + wire was capped off and not connected. Then the other three are Jayco (white to Atwood Black, Jayco Brown to Atwood Red, and Jayco Blue to Atwood Blue. Check all wire caps for loose connections, etc. Propane tank are full and tested stove. Exhaust tube is clean and no nest/webs, etc.
dcv is offline   Reply With Quote
Old 10-13-2016, 07:23 PM   #2
Senior Member
 
Join Date: Feb 2016
Posts: 201
Has your furnace worked before?
JEFF1963 is offline   Reply With Quote
Old 10-13-2016, 07:46 PM   #3
dcv
Member
 
Join Date: Jul 2016
Location: Marathon Twp
Posts: 32
Yes, when we took delivery
dcv is offline   Reply With Quote
Old 10-13-2016, 07:59 PM   #4
Senior Member
 
BuddyRay's Avatar
 
Join Date: Jan 2016
Location: Gainesville
Posts: 697
Atwood Furnace AFMD35121A problem

Have you had the gas off or a tank off to refill? If so your gas line might be full of air.

Frequently there is a lot of gas line between the tank and furnace. Sometimes you have to switch it on, let it try to start. Then switch it off (at thermostat) to reset it, then back on.

My last TT you had to do this a dozen times or more before you got all the air out of the gas line.

It's a safety thing, furnaces will usually have to be reset if they fail II light after a certain time.

If that's not the problem then the next step is probably a trip to the dealer.


Buddy Ray - Atlanta
---------------
Jayco Eagle HT 26.5RLS
Ford F150 Lariat, 3.5L V6 Ecoboost
Max Tow Pkg, 36gal tank
Reese Sidewinder and Reese Titan 16k hitch
__________________
Buddy Ray - Atlanta
---------------
Jayco 2016 Eagle HT 26.5RLS
Ford 2016 F150 Lariat, 3.5L V6 Ecoboost
Max Tow Pkg, 36gal tank
Reese Sidewinder and Reese Titan 16k hitch
BuddyRay is offline   Reply With Quote
Old 10-13-2016, 08:01 PM   #5
Senior Member
 
Join Date: Feb 2016
Posts: 201
Perhaps an inane question on my part, but was your propane on? Inasmuch as I don't really know how that furnace works and you haven't provided your rig's data (either on the Forum here or, as far as I can discern, in your Personal Profile), I don't know if the furnace is propane fueled, electric only, or both. Can you elaborate so we can assist? Looks like Buddy Ray is on top of it.
JEFF1963 is offline   Reply With Quote
Old 10-13-2016, 08:10 PM   #6
Senior Member
 
Join Date: Apr 2013
Location: Cleveland
Posts: 1,448
Atwood Furnace AFMD35121A problem

Another inane question......on you thermostat did you turn the furnace "on" with the top lever? It is very stiff/hard to move.
__________________
2013 Jayco JayFlight 26RKS
2013 Ford F150 Ecoboost FX4

2003 Coleman Bayside / 2011 Jayco Jayfeather X20E -- RIP
2012 Tacoma Sport DCSB / 2013 Tundra SR5 - RIP
Heady is offline   Reply With Quote
Old 10-13-2016, 08:15 PM   #7
Senior Member
 
BuddyRay's Avatar
 
Join Date: Jan 2016
Location: Gainesville
Posts: 697
Heady,
He mentioned that the furnace "clicked " which is usually the solenoid on the gas valve opening which would indicate he got it on.


Buddy Ray - Atlanta
---------------
Jayco Eagle HT 26.5RLS
Ford F150 Lariat, 3.5L V6 Ecoboost
Max Tow Pkg, 36gal tank
Reese Sidewinder and Reese Titan 16k hitch
__________________
Buddy Ray - Atlanta
---------------
Jayco 2016 Eagle HT 26.5RLS
Ford 2016 F150 Lariat, 3.5L V6 Ecoboost
Max Tow Pkg, 36gal tank
Reese Sidewinder and Reese Titan 16k hitch
BuddyRay is offline   Reply With Quote
Old 10-13-2016, 08:24 PM   #8
Senior Member
 
THE MEEKER's Avatar
 
Join Date: Apr 2015
Location: Western New York
Posts: 605
There might be air in the propane line which is preventing gas getting to your furnace. Try igniting your center stove burner and leave it on for about a minute or two to get all the air out of the propane line. Then try to ignite your furnace.
__________________
2015 Jayco Jayflight 27RLS
2012 Ford F-150
2001 Fleetwood Terry 28x
1996 Viking Pop-up
1979 Coleman 8 man cabin tent
1967 G.I Joe (hasbro) canvas pup tent
THE MEEKER is offline   Reply With Quote
Old 10-13-2016, 08:38 PM   #9
dcv
Member
 
Join Date: Jul 2016
Location: Marathon Twp
Posts: 32
To clarify my problem with the furnace
2015 Jayco Eagle 339flqs
1) Propane tanks both full
2) stove, oven, hot water heater on LP all work perfectly
3) The furnace, when switched on to heat, only makes a click at the furnace. NO Blower fan, No Ignition. Then I turn of the heat switch and back on same thing
4) No fuses blown and battery has been load tested to confirm
5) shore power
I have ran out of ideas on what it could be.
Thank you
dcv is offline   Reply With Quote
Old 10-13-2016, 08:41 PM   #10
dcv
Member
 
Join Date: Jul 2016
Location: Marathon Twp
Posts: 32
Thank you for the quick responses and ideas
Jeff1963
BuddyRay
Heady
The Meeker,
dcv is offline   Reply With Quote
Old 10-14-2016, 08:25 PM   #11
dcv
Member
 
Join Date: Jul 2016
Location: Marathon Twp
Posts: 32
Found the problem with the furnace. Water has manage to come in the combustible air intake tube, due to the Atwood vent being angle upward instead of downward to prevent water/moisture from entering into the furnace.
Attached Thumbnails
20161014_210225.jpg   20161014_205046.jpg   20161014_215719.jpg   20161014_215730.jpg  
dcv is offline   Reply With Quote
Old 08-15-2017, 10:26 PM   #12
Junior Member
 
Join Date: Jul 2017
Location: Edmonton
Posts: 10
Quote:
Originally Posted by dcv View Post
Found the problem with the furnace. Water has manage to come in the combustible air intake tube, due to the Atwood vent being angle upward instead of downward to prevent water/moisture from entering into the furnace.


I'm having the same issue. Did you have to replace the circuit board?


Sent from my iPhone using Tapatalk
mw5655 is offline   Reply With Quote
Old 08-16-2017, 04:41 AM   #13
dcv
Member
 
Join Date: Jul 2016
Location: Marathon Twp
Posts: 32
MW5655,
Yes replaced the circuit board and changed the furnace angle instead of tilting backwards. But i went to a local RV dealer(Atwood service center) and they called Atwood directly for a replacement at no charge. I did all of the labor tough.
dcv is offline   Reply With Quote
Old 08-16-2017, 06:10 AM   #14
Senior Member
 
Join Date: Jun 2012
Location: West Chicago
Posts: 550
Glad you got this one done, hard to diagnose.
__________________
2019 F250, gas, 4.30
2017 29RKS
wabirch is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3