No power to half of inside trailer
Hey guys!
Jay flight 32 TSBH. I am currently camping and the 50 amp breaker on the power poll we are hooked up to went bad. While switching it out I forgot to turn the new one to off and it sparked while installing.
Now the trailer has power except for one side of the trailers outlets, second A/C, refrigerator, microwave and water heater do not. I have flipped the breakers, changed out the GFCI outlet in the bathroom and still can’t figure out how to fix it.
Would like to try to fix this as we are currently camping with the family. Any help would be greatly appreciated.
|
|
|
12-31-2021, 07:01 PM
|
#2
|
Senior Member
Join Date: Dec 2014
Location: Akron
Posts: 3,208
|
Quote:
Originally Posted by Jcal87
Hey guys!
Jay flight 32 TSBH. I am currently camping and the 50 amp breaker on the power poll we are hooked up to went bad. While switching it out I forgot to turn the new one to off and it sparked while installing.
Now the trailer has power except for one side of the trailers outlets, second A/C, refrigerator, microwave and water heater do not. I have flipped the breakers, changed out the GFCI outlet in the bathroom and still can’t figure out how to fix it.
Would like to try to fix this as we are currently camping with the family. Any help would be greatly appreciated.
|
You've lost a leg of your 50-amp service. Hopefully you have a meter and I would check the pedestal first making sure you have power on each of the hot legs at the outlet. If not, you've found that the problem lies somewhere at the receptacle, breaker, or the incoming lines.
If power good at pedestal you need to check your plug, cord, panel, or your 50-amp breaker. If you have a generator and an automatic transfer switch the switch could be a source of trouble also.
Do you have an EMS or surge protector? If so there could be an issue with that.
Good luck!
__________________
Rob R.
Akron, OH
2014 Seneca 37TS
Toads: 2019 Ford Edge ST or 2013 Ford Focus ST
|
|
|
12-31-2021, 07:35 PM
|
#3
|
Junior Member
Join Date: Aug 2021
Location: Dallas
Posts: 5
|
Quote:
Originally Posted by Robbbyr
You've lost a leg of your 50-amp service. Hopefully you have a meter and I would check the pedestal first making sure you have power on each of the hot legs at the outlet. If not, you've found that the problem lies somewhere at the receptacle, breaker, or the incoming lines.
If power good at pedestal you need to check your plug, cord, panel, or your 50-amp breaker. If you have a generator and an automatic transfer switch the switch could be a source of trouble also.
Do you have an EMS or surge protector? If so there could be an issue with that.
Good luck!
|
I have no power at any of the outlets on the one side. I even bypassed the GFCI and no power. I unfortunately don’t have a meter. It seems like the problem has to be between the incoming breaker the lines in between or the breakers at the fuse box. The rest of the trailer has perfect power with the number AC working fine along with slides and lights.
|
|
|
12-31-2021, 07:45 PM
|
#4
|
Senior Member
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,102
|
I have to ask the obvious. Did you reset the breaker on the post? One side may have tripped, but the handle didn't move.
__________________
DISNEY LOVERS
|
|
|
12-31-2021, 07:50 PM
|
#5
|
Senior Member
Join Date: Dec 2014
Location: Akron
Posts: 3,208
|
Quote:
Originally Posted by Jcal87
I have no power at any of the outlets on the one side. I even bypassed the GFCI and no power. I unfortunately don’t have a meter. It seems like the problem has to be between the incoming breaker the lines in between or the breakers at the fuse box. The rest of the trailer has perfect power with the number AC working fine along with slides and lights.
|
Anyone close by that maybe can help with a meter?
Have you tried forcefully cycling the pedestal breaker and your rig's main breaker off then back on? Sometimes they'll reset.
And lastly, do you have a dog bone to adapt your 50-amp cord to the 30-amp receptacle on the pedestal? That would at least tell you if your rig is okay if everything begins working again. But obviously you can't run everything off a 30-amp circuit.
__________________
Rob R.
Akron, OH
2014 Seneca 37TS
Toads: 2019 Ford Edge ST or 2013 Ford Focus ST
|
|
|
12-31-2021, 07:52 PM
|
#6
|
Senior Member
Join Date: Apr 2017
Location: Inland Empire, California
Posts: 2,005
|
All excellent troubleshooting ideas. By chance do you carry a 30 amp to 50 amp converter plug? If so you may be able to get by with a connection to the park's 30 amp outlet. This would tie all 120 volt items into one leg of the service. If everything powers up inside the rig, the problem is with the pedestal.
__________________
Jim
Retired electronic technician (45 years in the field)
2017 Greyhawk 29W (solar & many other mods)
wife (maybe I should have given her top billing)
|
|
|
12-31-2021, 08:04 PM
|
#7
|
Senior Member
Join Date: Feb 2021
Location: Clarence
Posts: 236
|
Unplug, flip pedestal breaker and tt breakers off 10 seconds, back on, turn pedestal off,plug in and flip on. Worked for me when I did that. Gfci may have popped too. I had one that did. Red led only lit while reset was pushed
__________________
2018 octane SL 222.
2021 4x4 5.3 silverado
|
|
|
12-31-2021, 08:44 PM
|
#8
|
Junior Member
Join Date: Aug 2021
Location: Dallas
Posts: 5
|
Quote:
Originally Posted by Robbbyr
Anyone close by that maybe can help with a meter?
Have you tried forcefully cycling the pedestal breaker and your rig's main breaker off then back on? Sometimes they'll reset.
And lastly, do you have a dog bone to adapt your 50-amp cord to the 30-amp receptacle on the pedestal? That would at least tell you if your rig is okay if everything begins working again. But obviously you can't run everything off a 30-amp circuit.
|
It’s a hard wired 50 amp connection to a power poll. It’s at our deer lease and not a typical RV park. I will add when I originally swapped the bad 50 amp breaker I didn’t have another 50 so I made another older 30 amp breaker work temporarily. We have done this in the past and it still powered everything fine though.
|
|
|
12-31-2021, 08:50 PM
|
#9
|
Senior Member
Join Date: Oct 2017
Location: Southwest ND
Posts: 352
|
Everyone with an RV needs a multimeter. You will use it sooner than later.
|
|
|
12-31-2021, 08:58 PM
|
#10
|
Senior Member
Join Date: Apr 2017
Location: Inland Empire, California
Posts: 2,005
|
Quote:
Originally Posted by Jcal87
It’s a hard wired 50 amp connection to a power poll. It’s at our deer lease and not a typical RV park. I will add when I originally swapped the bad 50 amp breaker I didn’t have another 50 so I made another older 30 amp breaker work temporarily. We have done this in the past and it still powered everything fine though.
|
I believe a typical 50 amp breaker would be 2 breakers connected together with a cap. That way you are forced to turn off both breakers instead of just one. If you are mixing breakers they are probably not connected together meaning that one could trip and not affect the other. Could lead to a dangerous situation.
What you did is good for a temporary fix but should be permanently fixed with a new 2 unit breaker. Not preaching, just recommending.
__________________
Jim
Retired electronic technician (45 years in the field)