Old 06-19-2014, 08:20 AM   #1
Junior Member
 
Join Date: Jun 2014
Location: Red Deer
Posts: 6
trailer GFCI works on genny but not shorepower

We have a new-to-us 07 328 RLS TT.

We had it out for the first time a couple weeks ago and the GFCI circuits all went out the second day and wouldn't reset. I figured maybe it was a bad GFCI. When we got home I parked the unit on my driveway and replaced the GFCI. No go -- it still would trip and then not reset when the breaker was ON. (This was using shore power.) So, as a test, I powered up the trailer from my generator (a Kippor 3000 inverter generator) and voila -- the GFCI works fine!

The fact that the GFCI did work at first on shore power at the campground is what has me confused. When plugged into shore power, all the other non-GFCI AC plugs and appliances (refer, AC, etc.) still work fine.

My thots thus far:
- the new GFCI I installed is faulty -- perhaps overly sensitive to mA drop?
- because the generator has a floating neutral the GFCI "sees" it differently?
- could the 30 to 20 amp adapter on the shoreline cord cause the problem?
- is the transfer switch in the TT's inverter/converter to blame?

I'm comfortable working with AC electronics so will tear into whatever I need to -- I just need to be pointed in the right direction!
wheelerd is offline   Reply With Quote
Old 06-19-2014, 08:24 AM   #2
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,107
Check all your incoming SP connections in the transfer switch and make sure they are tight. A wire have come loose (ground or neutral)
__________________
DISNEY LOVERS
Grumpy is offline   Reply With Quote
Old 06-19-2014, 08:33 AM   #3
Junior Member
 
Join Date: Jun 2014
Location: Red Deer
Posts: 6
Thanks. I was thinking I should have a look at that. I'm assuming it's on the backside of the converter/inverter and will be easily identifiable? (ie. main power supply running to it.)

Still don't understand why GFCI would work with generator but not shore power. I do realize from working with computer equipment that there is "clean" and "dirty" power.
wheelerd is offline   Reply With Quote
Old 06-19-2014, 02:17 PM   #4
Junior Member
 
Join Date: Jun 2014
Location: Red Deer
Posts: 6
Pulled the load center out and took a look -- its the IOTA 3045. No transfer switch, at least none that I can see. Since I don't have an on-board generator, would/should there even be one?

Also, I used a continuity tester to check all the outlets:
- on SP, everything is fine (except for the GFCI which will not reset)
- on genny, GFCI resets but all outlets show Hot/Neu Rev

What gives?
wheelerd is offline   Reply With Quote
Old 06-19-2014, 04:00 PM   #5
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,107
It may be a loose wire on one of the GFI receptacles. I didn't read your whole post and thought you had an onboard genny. Not sure if a GFI willl trip when using the port gen.
__________________
DISNEY LOVERS
Grumpy is offline   Reply With Quote
Old 06-21-2014, 07:05 PM   #6
Senior Member
 
us71na's Avatar
 
Join Date: Jun 2013
Location: McKean, PA
Posts: 1,073
For $10 get a GFCI outlet tester Plug it in to the outlet and check for ground and polarity. The most common error installing GFCI's is to connect the hot to the load side of the receptacle. If the GFCI outlet is wired backwards (hot on load side load on hot side) it will not reset.

If your generator isn't tied in to the main panel how are you getting power from it into your system? Based on your comment "GFCI resets but all outlets show Hot/Neu Rev" It sounds to me like you are feeding the gen power in through another receptacle on the same line as the GFCI which would put the hot lead on the proper side of the GFCI if it is wired backwards so it will reset. It also sounds like your gen is providing power on the neutral side of our system which is dangerous.
__________________
2011 Skylark 21FKV
us71na is offline   Reply With Quote
Old 06-22-2014, 10:30 PM   #7
Junior Member
 
Join Date: Jun 2014
Location: Red Deer
Posts: 6
Yes, I do have a continuity tester with the GFCI check.
My gen is external. I plug my regular SL cord into it.
I've done further searching on the web and it appears that it's not uncommon for continuity testers to show what seems to be an error code because many (including mine) have a floating neutral; there is no ground to earth.
wheelerd is offline   Reply With Quote
Old 06-23-2014, 04:45 PM   #8
Senior Member
 
us71na's Avatar
 
Join Date: Jun 2013
Location: McKean, PA
Posts: 1,073
Did you check the wiring on your GFCI?
__________________
2011 Skylark 21FKV
us71na is offline   Reply With Quote
Old 06-23-2014, 06:04 PM   #9
Senior Member
 
tnchuck100's Avatar
 
Join Date: Jun 2012
Location: Sparta, TN
Posts: 1,174
You have HOT/Neutral reversed issues either at the converter or the GFCI outlet. Stay on shore power and check the polarity of EVERY outlet including the one you are getting shore power FROM.

You say the GFCI works on the generator? I think you will find that the GFCI is actually preforming properly on shore power and provides no protection on the generator.

Once you correct the HOT/Neutral reversal issues it should be fine.
__________________
Chuck - Sparta, TN
2012 Jay Flight 22FB, 2 x Honda EU2000i
2013 GMC Yukon XL Denali AWD

EDUCATION is what you get when you read the fine print.....
EXPERIENCE is what you get when you don't.
tnchuck100 is offline   Reply With Quote
Old 06-24-2014, 01:26 AM   #10
Junior Member
 
Join Date: Jun 2014
Location: Red Deer
Posts: 6
The "new" GFCI I had installed was faulty. Installed a different new one and now everything is fine.
wheelerd is offline   Reply With Quote
Old 06-25-2014, 09:38 PM   #11
Senior Member
 
Join Date: Dec 2010
Location: North Idaho/Arizona
Posts: 5,446
This has been an interesting read. Glad to hear the problem is solved.
__________________
2011 Eagle 330RLTS with just about every option.
2017 Silverado 1500 4x4 5.3 with tow package. (no, we don't tow the Jayco with it.)
2018 Surveyor 265RLDS well equipped.
Life in the slow lane is still life.
clutch is offline   Reply With Quote
Old 06-25-2014, 11:12 PM   #12
Junior Member
 
Join Date: Jun 2014
Location: Red Deer
Posts: 6
In the process, Jayco Customer Service was helpful in sending me both the 120V and 12V wiring diagrams for my unit. They responded to my email in less than a day!

I also learned more about the difference between shore power and gen power than I ever knew existed!
wheelerd is offline   Reply With Quote
Old 06-26-2014, 07:06 AM   #13
Senior Member
 
Join Date: May 2014
Location: VA
Posts: 394
Quote:
Originally Posted by wheelerd View Post
In the process, Jayco Customer Service was helpful in sending me both the 120V and 12V wiring diagrams for my unit. They responded to my email in less than a day!

I also learned more about the difference between shore power and gen power than I ever knew existed!
Glad they responded to your e-mails. They NEVER responded to mine. I did get a quick answer once I called.
Glad your issue is resolved!
__________________
2005 Dodge Ram 1500 Quad Cab 5.7 HEMI
2̶0̶1̶4̶ ̶J̶a̶y̶ ̶F̶e̶a̶t̶h̶e̶r̶ ̶X̶1̶9̶H̶
howie is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 09:53 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.