Quote:
Originally Posted by Cp50
Generator works fine
|
That is major information. Since the generator works normally you can basically eliminate everything inside the rig (so to speak).
You have 2 power feeds to the rig - shore power and generator power. They come together in the transfer switch which selects the power source to use. So, the output from the transfer switch is good since it passes the generator on through. The question is why isn't the shore power making it through cleanly.
The dealer said your power cord had a "short". That is a stupid term used for things that go wrong in electrical systems. True "shorts" will trip breakers, burn wires, and can get a lot worse. What you are dealing with is an intermittent "open" and not any sort of short.
Since the power cord was replaced that should have eliminated any problem that may have existed in the power cord plug which have been known to fail due to poor connections. If your power cord connects directly to the transfer switch, that should eliminate loose connections inside there also. If it doesn't connect directly then the transfer switch could still have a loose connection where the shore power comes in.
Going on the assumption the cord does connect to directly to the transfer switch, the only thing that hasn't been addressed is the actual shore power. The outlet could have loose connections, the circuit breaker protecting it could be bad. I can attest personally to a bad breaker causing electrical problems. As a field tech I once installed a piece of equipment that pulled about 8 amps on a standard 120 volt line. It would come up to power in steps and when it came completely on, the power line would drop out temporarily causing our equipment to "reboot" and start up the power up sequence again. I observed the breaker arcing when hit with 8 amps of current draw. Enough of my reminiscing.
Is there a way of plugging into a different outlet? If so, that would be something to try. You could even use an adapter to plug into a 20 amp (or even a 15 amp) line and see if there is any power delays. You probably could fire up 1 air conditioner on a 15 amp line but nothing else. I assume you have 2 air conditioners that both run under 30 amps. That is what I have. One unit should be OK on 15 amps for a bit.
I think you are getting closer to the source of your problem. Please keep us in the loop. We are all ears and have a lot of opinions.