30AMP Service
2010 Greyhawk, 30AMP.
Are there any advantages or cautions to plugging into a 50AMP outlet with a 50 to 30 AMP adapter? I haven't heard anything either way but want to ask before I find a situation where I might have to or run the generator.
|
|
|
08-12-2018, 03:36 PM
|
#2
|
Senior Member
Join Date: Oct 2014
Location: Sparwood, BC
Posts: 2,800
|
As your current draw will be more that 30 amp the breaker on the service outlet will trip.
So stay under it. If you have to go over the 30 amp and no service available use your generator.
__________________
2014 Ram 1500 CrewCab 4x4 5.7 Hemi 3.92 Rear and Air Lift 1000
2005 Jayco Jay Feather LGT - 29Y GVWR-7000 lbs.
Dexter Axle Lift 4-9/16" - installed with sub-frame.
Pro Series 1200 lbs. WDH with Double Sway Bar.
Champion 3100/2800 watt Inverter/Generator-Onboard Solar Power
|
|
|
08-12-2018, 03:45 PM
|
#3
|
Senior Member
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,106
|
Quote:
Originally Posted by ALJO
As your current draw will be more that 30 amp the breaker on the service outlet will trip.
So stay under it. If you have to go over the 30 amp and no service available use your generator.
|
No, the coach only has 30 amp service. They want to use the 50 amp outlet.
|
|
|
08-12-2018, 03:59 PM
|
#4
|
Senior Member
Join Date: Oct 2014
Location: Sparwood, BC
Posts: 2,800
|
Oops!..... they can use the 50 amp (with adaptor) on 30 Amp, but are limited to 30 amp on the RV breaker.
__________________
2014 Ram 1500 CrewCab 4x4 5.7 Hemi 3.92 Rear and Air Lift 1000
2005 Jayco Jay Feather LGT - 29Y GVWR-7000 lbs.
Dexter Axle Lift 4-9/16" - installed with sub-frame.
Pro Series 1200 lbs. WDH with Double Sway Bar.
Champion 3100/2800 watt Inverter/Generator-Onboard Solar Power
|
|
|
08-12-2018, 04:41 PM
|
#5
|
Senior Member
Join Date: Feb 2016
Location: Lafayette, LA
Posts: 285
|
Quote:
Originally Posted by Loretta
2010 Greyhawk, 30AMP.
Are there any advantages or cautions to plugging into a 50AMP outlet with a 50 to 30 AMP adapter? I haven't heard anything either way but want to ask before I find a situation where I might have to or run the generator.
|
Hello Loretta.... There are no advantages or disadvantages in using a 30AMP to 50 AMP adapter. There may be times when you will need to do this because of the well-used well-worn 30 AMP plug on the post. I carry such an adapter for just such situations. Just make sure you purchased a reputable adapter.
__________________
Wilson Boudreaux
From Cajun Country
Jayco 2016 Grey Hawk 29MV Champagne
Toad - '16 Subaru Forester (Pearl White - manual transmission)
Blue Ox (everything) for the TOAD
|
|
|
08-12-2018, 05:14 PM
|
#6
|
Senior Member
Join Date: Jun 2016
Location: Newburgh
Posts: 6,307
|
I often choose the 50 amp outlet even though my camper is only 30 amp simply because they are on better condition many times. They are used less often so there is less wear and tear on them
__________________
2022 33RBTS
Progressive Industries EMS - Hardwired
Equalizer 4 Point WDH
2021 Ford F350 7.3
Air Lift Rear Bags w/ On Board Compressor (Pending)
2016 28BHBE - (Traded and Missed already)
|
|
|
08-12-2018, 05:21 PM
|
#7
|
Senior Member
Join Date: Aug 2013
Location: Bellingham,Wa.
Posts: 6,680
|
Quote:
Originally Posted by Marcm157
I often choose the 50 amp outlet even though my camper is only 30 amp simply because they are on better condition many times. They are used less often so there is less wear and tear on them
|
X2 and have done so for a few years now.
__________________
2010 Jayco Hybrid EXP21M
2013 Toureg TDI
|
|
|
08-12-2018, 06:00 PM
|
#8
|
Senior Member
Join Date: May 2017
Location: Kingman
Posts: 620
|
Quote:
Originally Posted by Marcm157
I often choose the 50 amp outlet even though my camper is only 30 amp simply because they are on better condition many times. They are used less often so there is less wear and tear on them
|
X2
|
|
|
08-14-2018, 05:33 AM
|
#9
|
Senior Member
Join Date: Jun 2012
Location: Long Island, NY
Posts: 675
|
The only disadvantage is your 30 amp shore line is now protected by a 50 amp breaker. If there was a short in the cord between the main breaker in your unit and the pedestal then it is possible the cord will overheat and bad stuff could happen. It is a remote possibility but is possible non the less.
__________________
Thanks,
Brian
TV = 2006 F-350 CC DRW 6.0
TT = 2018 Wildwood 31KQBTS
TT = 2007 Jayco Jay Flight 27bh - SOLD
|
|
|
08-14-2018, 06:57 AM
|
#10
|
Senior Member
Join Date: Sep 2011
Location: King George
Posts: 2,761
|
We do this ll the the time mainly because of a well worn 30A SERVICE connector on the pedestal. You can note burn and arcing marks on the 30A Service like shown in this photo.
Google image
I would not want to plug my 30A Shore Power cable into this connector. This may result in your Shore Power cable to look like this and will have to be replaced...
Google image
These are my concerns at any rate hehe...
The 50A to 30A Adapter only selects one of the 50A HOT LEGS so there is no two zones of 50A LEGS feeding your 30A Electrical setup...
Google Image
As noted above in a couple of responses about the only thing to be aware of is the 50A Circuit breaker on the pedestal is now feeding your 30A Service Breaker in your trailer. If you pull more than 30 Amps from your trailer setup it will trip your 30A trailer main breaker and not the 50A breaker on the pedestal...
I forget where this was at but I have seen at one camp ground a sign saying using the 50A to 30A Adapter Cord was not permitted.
All part my infamous PLAN Bs to use when camping trying to stay ahead of the game hehe...
Roy Ken
__________________
Roy and Carolyn
I claim Horse Creek Country in Southern Ill - Momabear is from North Texas
We live in King George VA
RETIRED DOD DOAF DON CONTRACTOR Electronics Tech 42YRS
"We're burning daylight" - John Wayne
2008 STARCRAFT 14RT OFF-ROAD POPUP with PD9260C and three 85AH 12VDC batteries
2010 F150 FX4 5.4 GAS with 3.73 gears - Super Cab - Towing Package - 2KW Honda EU2000i Gen
K9PHT (since 1957) 146.52Mhz
"We always have a PLAN B"
|
|
|
08-14-2018, 07:19 AM
|
#11
|
Senior Member
Join Date: Mar 2015
Location: Port Orchard
Posts: 2,064
|
Quote:
Originally Posted by Marcm157
I often choose the 50 amp outlet even though my camper is only 30 amp simply because they are on better condition many times. They are used less often so there is less wear and tear on them
|
X3. Another advantage is that if you accidentally draw too much current, the house breaker will trip and not the post breaker.
__________________
Don
|
|
|
08-14-2018, 07:36 AM
|
#12
|
Senior Member
Join Date: Jun 2018
Location: USA
Posts: 237
|
Quote:
Originally Posted by hoppers4
X3. Another advantage is that if you accidentally draw too much current, the house breaker will trip and not the post breaker.
|
Had this problem last time out. Kept tripping the 30AMP at the pedestal. Switched over to the 50AMP, no issues.
|
|
|
08-14-2018, 07:43 AM
|
#13
|
Senior Member
Join Date: Apr 2015
Location: Michigan
Posts: 2,650
|
Quote:
Originally Posted by Marcm157
I often choose the 50 amp outlet even though my camper is only 30 amp simply because they are on better condition many times. They are used less often so there is less wear and tear on them
|
Same here, I only plug into the 50amp outlet when available for my 30amp service.
|
|
|
08-14-2018, 09:33 PM
|
#14
|
Senior Member
Join Date: Feb 2017
Location: Kennewick
Posts: 331
|
What Roy said. A 50 amp outlet is two 30's essentially. Even in your coach, one leg is wired to the majority of your "stuff" while the other powers things like a second AC (a separate circuit). So your protection remains the same at 30 amps (or 25 if they use 25 amp breakers) x 2. Your adapter just taps one side for the 30 amp service.
I found this out converting a 220v welding plug over to a 50 amp rv plug. You are running two 110v services through two breakers. So there is no potential issues for running an good adapter off the 50 amp outlet.
__________________
2016 Jayco GreyHawk 31DS
2016 Jeep Cherokee Trailhawk Toad.
SE Washington State
|
|
|
08-14-2018, 09:40 PM
|
#15
|
Senior Member
Join Date: Jan 2015
Location: Surprise
Posts: 2,623
|
Quote:
Originally Posted by jd99336
What Roy said. A 50 amp outlet is two 30's essentially. Even in your coach, one leg is wired to the majority of your "stuff" while the other powers things like a second AC (a separate circuit). So your protection remains the same at 30 amps (or 25 if they use 25 amp breakers) x 2. Your adapter just taps one side for the 30 amp service.
I found this out converting a 220v welding plug over to a 50 amp rv plug. You are running two 110v services through two breakers. So there is no potential issues for running an good adapter off the 50 amp outlet.
|
A 30 amp service is only 120 volts, at 3600 potential watts of power. Your 50 amp service is 2 120 volt legs at 12,000 watts of power. The 50 amp is a 240 system but normally is broken down in the rv to 2 120 50 amp 6000 watt systems. Some RV's do utilize 240 for some appliances ie dryers.
The 50 amp system gives you potentially 100 amps at 120 volts or 12,000 watts. Over 3 times the power that a 30 amp system offers..
__________________
2011 Toyota Tundra double cab
2015 27RLS
|
|
|
08-14-2018, 10:04 PM
|
#16
|
Senior Member
Join Date: Jun 2018
Location: USA
Posts: 237
|
Quote:
Originally Posted by wags999
A 30 amp service is only 120 volts, at 3600 potential watts of power. Your 50 amp service is 2 120 volt legs at 12,000 watts of power. The 50 amp is a 240 system but normally is broken down in the rv to 2 120 50 amp 6000 watt systems. Some RV's do utilize 240 for some appliances ie dryers.
The 50 amp system gives you potentially 100 amps at 120 volts or 12,000 watts. Over 3 times the power that a 30 amp system offers..
|
To summarize. Ohms law still works?
|
|
|
08-18-2018, 11:52 AM
|
#17
|
Junior Member
Join Date: Jan 2014
Posts: 2
|
We do it all the time....no problems
|
|
|
08-18-2018, 12:14 PM
|
#18
|
Senior Member
Join Date: Apr 2015
Location: winnipeg
Posts: 257
|
I often run my 50 to 30 for the rv. Then a 30amp to regular plug to run an ice maker or something of that nature as to not overload the 30 amp service.
|
|
|
08-18-2018, 01:50 PM
|
#19
|
Senior Member
Join Date: Feb 2018
Location: Windsor
Posts: 322
|
I presume this doesn't pose any problem with an EMS, right?
|
|
|
08-18-2018, 01:52 PM
|
#20
|
Senior Member
Join Date: Apr 2015
Location: winnipeg
Posts: 257
|
Nope I run one.
|
|
|
|
|