Can't speak for 50 amp but i regularly run 30 amp at 120 feet. No issues.
|
You actually have a larger drop on the 30 amp cord. Assuming 120 volts at the receptacle you would have 112.81 volts at the end. If additional cords plugs etc, your drop would be slightly larger. This is at full load of 30 amps. So not an issue, just watch your voltage..an EMS would be good as it would but power if voltage dropped to a point damage may occur.