Solar not charging lithium batteries Seneca

The dealer installed my 1200w of solar panels and hooked them up to the AGM batteries that came with the coach. We used it for a few days and all seemed fine. Then they installed 4 re-lion Lithium batteries. My understanding is that the solar will charge the batteries but since the converter that allows the generator or shore power to charge the batteries doesn’t work on lithium batteries, I would have to make a manual setting on my MPPT controller each time I connect to shore power or want to use the generator to charge the batteries. Now that they have dropped in the lithium and have us hooked to shore power, the lithium batteries have gone from 98% to 80% in 24 hours. We’re sitting in full sun on a 90 degree day and the batteries aren’t charging. Could it be a setting on my MPPT controller? It’s a Victron Energy SmartSolar MPPT 150/85-Tr Charge Controller w/ Bluetooth.
Seek and Enjoy is offline   Reply With Quote
Old 09-15-2019, 05:45 PM   #2
Senior Member
 
Join Date: Mar 2015
Location: Odessa
Posts: 409
Maybe when they changed the batteries - a fuse may have blown or something didn’t get hooked up correctly ( a lot of possibilities ) is the monitor showing any charging amps and voltage?
You shouldn’t need to use the house charger when on shore power or generator because the 12 volt usage will be very little ( lights and maybe water pump and heater ) and you have a massive amount of solar - we have 540 watts and until we added a residential refrigerator- we never needed more charge than the solar provided - now when dry camping in cloudy weather we will have to run the generator some Les
__________________

Les & Sandy
2016 Seneca HJ - Scangauge D - Truma Comfort
560 watts solar - Blue Sky 3024iL -IPN ProRemote - Trojan T-105RE
Good Sam Life Member - FMCA Member - Passport America
Les7h is offline   Reply With Quote
Old 09-15-2019, 05:55 PM   #3
Junior Member
 
Join Date: May 2019
Location: OTR
Posts: 17
Quote:
Originally Posted by Les7h View Post
Maybe when they changed the batteries - a fuse may have blown or something didn’t get hooked up correctly ( a lot of possibilities ) is the monitor showing any charging amps and voltage?
You shouldn’t need to use the house charger when on shore power or generator because the 12 volt usage will be very little ( lights and maybe water pump and heater ) and you have a massive amount of solar - we have 540 watts and until we added a residential refrigerator- we never needed more charge than the solar provided - now when dry camping in cloudy weather we will have to run the generator some Les
Here’s a shot of what’s currently going on. Can’t figure out what’s drawing power.
Attached Thumbnails
424C82E4-592F-4AFE-A6A0-336ABCC8AA9E.jpg  
Seek and Enjoy is offline   Reply With Quote
Old 09-16-2019, 09:18 PM   #4
Senior Member
 
Join Date: Mar 2015
Location: Odessa
Posts: 409
Very strange - good voltage but everything else looks bad - I could be wrong but I don’t think that it’s possible to use enough 12 volt power to be using 1200 watts of solar and be -6 amps - is your inverter on? What are the readings after dark? Possibly a defective battery? ( it appeared to work with the AGM batteries ) the relay shows to be “ open “ ( is it supposed to be open? I would think it should be “ closed “ ) I don’t have a relay so I don’t know
I suggest you make the installer find and repair the problem
Les
__________________

Les & Sandy
2016 Seneca HJ - Scangauge D - Truma Comfort
560 watts solar - Blue Sky 3024iL -IPN ProRemote - Trojan T-105RE
Good Sam Life Member - FMCA Member - Passport America
Les7h is offline   Reply With Quote
Old 09-16-2019, 09:41 PM   #5
Senior Member
 
Screwby's Avatar
 
Join Date: Jun 2016
Location: Indiana
Posts: 1,424
Did you set your solar controller to Li Batteries? My Renogy controller has separate settings for charging Li Batteries as opposed to Flooded batteries. 6ah draw can’t be anything too big, possibly all your 12v items together equaling that. I’m assuming that reading is as you are currently using the camper and that everything isn’t shut down? If your still not charging there is an issue between the controller and batteries because the panels seem to be providing plenty of voltage.
__________________
1999 Suburban 2500 4x4
2016 Jayflight 23RB Elite, Fiberglass, Polar Package
400w Renogy RV solar kit w/ Bluetooth, 100w Renogy solar suitcase
430 amp/hr 6v battery bank
1000w Renogy hard wired inverter
2011 F350 Lariat, DWR 4x4, 6.7 turbo diesel
2017 Open Range, Mesa Ridge 374BHS
Screwby is offline   Reply With Quote
Old 09-17-2019, 07:35 PM   #6
Senior Member
 
Bullitt6283's Avatar
 
Join Date: Jul 2017
Location: New Freedom, PA
Posts: 791
The solar controller and the converter need to work properly with Li batteries.
The voltage coming out of Li batteries is higher than the voltage coming out of lead-acid batteries, and it remains high until the Li batteries are nearly dead.

The problem is, because the voltage stays high, the controller or converter don't even know that the batteries need charged.
So they don't try.

For Battle Born batteries, for the Bulk/Absorption stage charging, the ideal voltage is between 14.2v-14.6v.
__________________
Ron K3HIL Amateur Extra
Retired
2016 Greyhawk 29MV
2000 Jeep Sahara


"Any advice I give or facts I present are valid to the best of my knowledge,
but I am not responsible if you follow it and you **** your **** up."
Bullitt6283 is offline   Reply With Quote
Reply

Tags
batteries, lithium, not charging, solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 07:30 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.