Originally Posted by Shokyle1 View Post
Here is a good way of thinking about it in my breaker panel at home I have a total of 450 amps of breakers with a 200 amp panel. I could be within my amperage draw for the breakers but overload the feed. Should the builder put in a 500 amp main feed just in case.
Sure, if you regularly exceed 200 amp draw when all your normal appliances are running. Do you pull over 200 amps on a regular basis?

I have 100 amps of breakers in my rig with a 30 amp service. I can easily pull 40 - 50 amps if I use all the systems as installed.
RetiredOne is offline   Reply With Quote
Old 06-01-2020, 02:38 PM   #22
Senior Member
 
Vicr's Avatar
 
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,863
Quote:
Originally Posted by RetiredOne View Post
It would be helpful if you could post specifically how that pertains to a 30 amp rating.



In a nutshell: (1) HVAC unit (AC) a 30 amp service is required, that's bare minimum code so they wouldn't electively install a 50 amp service. UNLESS, and the code doesn't cover this YET, there is an electric fireplace. Which technically falls under the NEC article if you read the wording of the article carefully. But since there are no electrical inspections done on RVs there is no "Authority Having Jurisdiction" so there is no one to tell the RV manufacturer that they must indeed install a 50 amp service because they interpret the code to read, inferred, that an AC and an electric fireplace are two "HVAC" devices.
A bit wordy but that's my summation of what our present situation is with RV's and the NEC requirements and jurisdictional short comings of the code being interpreted and enforced.
Vicr is offline   Reply With Quote
Old 06-01-2020, 02:41 PM   #23
Lost in the Woods
 
Join Date: Apr 2019
Location: Ocean County
Posts: 2,807
Quote:
Originally Posted by JimD View Post
Hey, we need to make some consolations, after all we are technically "roughing it". If you feel the need to use every electrical appliance at once you might as well stay home.

I am perfectly happy with my 30 amp service and do not mind managing what I have turned on at the same time. I can run my 2 air conditioners without any problem. If I want to run the microwave, coffee pot, electric skillet, or whatever, I just either shut down the rear air or let the power management system handle it.
That was my point. You, I and a bunch more understand power loads, and turn on and off fixtures to stay in range of the 30 amp. But, we also have a ton on newbies who don't understand it. So, I believe, it's very possible for someone to exceed the 30 amp service, and not even know it.

Heck, just running the A/C, water heater, converter and fridge comes in at like 38 amps, 25% over the rating, before turning anything else on. How often are those 4 items running at the same time?
RetiredOne is offline   Reply With Quote
Old 06-01-2020, 02:45 PM   #24
Lost in the Woods
 
Join Date: Apr 2019
Location: Ocean County
Posts: 2,807
Quote:
Originally Posted by Vicr View Post
In a nutshell: (1) HVAC unit (AC) a 30 amp service is required, that's bare minimum code so they wouldn't electively install a 50 amp service.
I think that's it, more than reality and function. "Bare Minimum".... that fits just about everything they do to these rigs...
RetiredOne is offline   Reply With Quote
Old 06-01-2020, 02:51 PM   #25
Lost in the Woods
 
Join Date: Apr 2019
Location: Ocean County
Posts: 2,807
Quote:
Originally Posted by JimD View Post
Having 50 amp service in a rig would also require a much larger generator at increased cost. Great if you need it but if you don't, why have it.
That's an interesting point, too. My rig has a 4kW generator, instead of a smaller one, so they built in some additional capacity with genny versus shore power.[/QUOTE]

Quote:
Lastly, some campgrounds charge more for 50 amp service over 30 and may have limited 50 amp spaces.
I've seen that, but it's not much of an upcharge. How many have limited 50 amp spaces due to the age of the campground and many of the old rigs only having 30 amp service, so that was the majority of what was built/installed. Aren't the majority of TTs 30 amp?
RetiredOne is offline   Reply With Quote
Old 06-01-2020, 09:35 PM   #26
Senior Member
 
Join Date: Jun 2016
Location: Denver
Posts: 4,249
Quote:
Originally Posted by Jagiven View Post
Also there would be a fair up charge for the camp grounds to add another conductor.



I think this is the key point here.


I'm a new RV'er - only a half dozen years.
But it looks like the ratio of 30A to 50A pedestals in many campgrounds is 6 to 1.


There would be a lot of unhappy camp ground owners if they had to turn away their class c market.
__________________
2016 Greyhawk 31FK
pconroy is offline   Reply With Quote
Old 06-02-2020, 06:19 AM   #27
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,107
Quote:
Originally Posted by RetiredOne View Post
That's an interesting point, too. My rig has a 4kW generator, instead of a smaller one, so they built in some additional capacity with genny versus shore power.
Except your geny only has a 30 amp breaker. That is also the case with most generators up to the 8000 Quiet Diesel.
__________________
DISNEY LOVERS
Grumpy is offline   Reply With Quote
Old 06-02-2020, 06:24 AM   #28
Senior Member
 
Join Date: Apr 2016
Location: Morganton
Posts: 724
We go by the Green Acres method you can not use number 2 with number 5
che57vy is offline   Reply With Quote
Old 06-02-2020, 08:29 AM   #29
Senior Member
 
Join Date: Jun 2016
Location: Denver
Posts: 4,249
Quote:
Originally Posted by che57vy View Post
We go by the Green Acres method you can not use number 2 with number 5



Ha! I remember that!
__________________
2016 Greyhawk 31FK
pconroy is offline   Reply With Quote
Old 06-02-2020, 09:20 AM   #30
Senior Member
 
Jagiven's Avatar
 
Join Date: May 2012
Location: Minnesota
Posts: 9,782
Quote:
Originally Posted by pconroy View Post
But it looks like the ratio of 30A to 50A pedestals in many campgrounds is 6 to 1.
We do not visit many private CG's. Around here, very little of the state parks have 50 amp. In reality, I only know of one campsite in one SP that has a 50 amps at a campsite.
__________________

2012 Jayco X23B
2020 Ram Laramie 3500 SRW Air ride 50Gal fuel tank.
2007 Dodge Dakota Quad Cab (sold)
Equal-I-zer 4-Point Sway Control
Jagiven is offline   Reply With Quote
Old 06-02-2020, 10:08 AM   #31
Senior Member
 
EA37TS's Avatar
 
Join Date: Sep 2019
Location: Longs
Posts: 1,484
Quote:
Originally Posted by pconroy View Post
I think this is the key point here.


I'm a new RV'er - only a half dozen years.
But it looks like the ratio of 30A to 50A pedestals in many campgrounds is 6 to 1.


There would be a lot of unhappy camp ground owners if they had to turn away their class c market.
I believe that the ratio is based on where you are and what you are looking for. The majority of private campgrounds we have been to over the last 7 years or so have had 20, 30 and 50 amp at the pedestals. Also, in those campgrounds that had done or the other the 50 amp pedestals tend to be at the sites used by larger rigs in the greater than 30 foot range. Not sure about an up charge for 50 amp because most sites are listed as 30/50 full hookup pull thru or 30/50 full hookup back in.

One fact is true and 30 amp class c owner can usually run everything in their coach off a 50 amp pedestal using a dogbone however a 50 amp owner cannot run everything in their coach from a 30 amp pedestal with adapter.
__________________
Dave
US Army (Ret)
2020 Entegra Accolade 37TS
2019 Jeep Grand Cherokee Trailhawk TOAD
EA37TS is offline   Reply With Quote
Old 06-02-2020, 11:11 AM   #32
Senior Member
 
Join Date: Aug 2015
Location: Ottawa, ON
Posts: 1,966
Always amused by these posts "why don't the mfg's just add more..."

Ignores that there is a very small handful of mfg's who do build very good RV's with "beyond code" requirements. For some reason they never find a lot of buyers willing to shell out the $$ required to build that kind of product. It is a niche market, but if you look for it, you can find it. Just be prepared to pay for that kind of quality build.

I look at my RV as an education in how to upgrade all of the systems in a very basic home. I have learned tons about both doing it right and doing it light at the same time.
__________________
2011 Jayco X19H (purchased 2015)
2008 Jayco 1007 PUP (purchased new, traded for the X19)
2018 Nissan Titan Midnight Ed.
bankr63 is offline   Reply With Quote
Old 06-02-2020, 11:14 AM   #33
Senior Member
 
JimD's Avatar
 
Join Date: Apr 2017
Location: Inland Empire, California
Posts: 2,006
Quote:
Originally Posted by EA37TS View Post
I believe that the ratio is based on where you are and what you are looking for. The majority of private campgrounds we have been to over the last 7 years or so have had 20, 30 and 50 amp at the pedestals. Also, in those campgrounds that had done or the other the 50 amp pedestals tend to be at the sites used by larger rigs in the greater than 30 foot range. Not sure about an up charge for 50 amp because most sites are listed as 30/50 full hookup pull thru or 30/50 full hookup back in.

One fact is true and 30 amp class c owner can usually run everything in their coach off a 50 amp pedestal using a dogbone however a 50 amp owner cannot run everything in their coach from a 30 amp pedestal with adapter.
Yes and no. You can hook up to a 50 amp service easily BUT your internal circuit breaker is still only 30 amp and will be your limiting factor.
__________________


Jim

Retired electronic technician (45 years in the field)
2017 Greyhawk 29W (solar & many other mods)
wife (maybe I should have given her top billing)
JimD is offline   Reply With Quote
Old 06-03-2020, 10:05 AM   #34
Senior Member
 
SloPoke's Avatar
 
Join Date: Apr 2016
Location: Kingman AZ and where our Seneca is today.
Posts: 3,120
Quote:
Originally Posted by Vicr View Post
NEC Article 551.42(C) explains what constitutes the 30a rating for an RV.
Quote:
Originally Posted by Vicr View Post
The RV industry as a whole has chosen to build to the bare minimum code as far as service circuit size. Post #6 sources the code if anyone would like to read it.
Not to mention that the code does change over the years... I've been carrying a code book in my truck since I was an apprentice in the 70's, and later on as a contractor.

for grins... here is what the 1971 code was - vs the code in 1999
Attached Thumbnails
20200603_095923.jpg   20200603_094357.jpg   20200603_094716.jpg  
__________________
Steve & Stacy with Jasper (Australian Cattle dog)
2015 Seneca 36FK
Custom 27' flatbed trailer hauling:
07 Toyota FJC & Yamaha Kodiak 400 ATV

SloPoke is offline   Reply With Quote
Old 06-06-2020, 12:41 PM   #35
Junior Member
 
Join Date: Jun 2017
Location: Palacios
Posts: 23
JPurvis

Generally the smaller units have one A/C and many of the bigger units have 2 A/C’s. Thus 50 amps. Hair dryers will trip 30’s especially in Texas and other warm places in the hotter climes. Have had two shore powers to click off with hair dryers.
jpurvis is offline   Reply With Quote
Old 06-06-2020, 12:41 PM   #36
Member
 
Picinisco's Avatar
 
Join Date: Jun 2017
Location: Gilbert, AZ
Posts: 76
Kitchen has 1 outlet with 2 sockets. If I boil the kettle or have the coffemaker on and make toast while the water heater us on, popped breaker. Have to be diligent and switch the water heater off while making toast and coffee at the same time.
__________________
TV - 2005 Dodge Ram 3500 Diesel Dually
TT - 2007 Jay Flight M-28.5 RLS
Picinisco is offline   Reply With Quote
Old 06-06-2020, 01:01 PM   #37
Member
 
Join Date: Mar 2020
Location: San Antonio
Posts: 95
Alante 29f

Our coach has 2 ac’s and 30amp service. At first I was worried about it because our 5er had 2 ac’s and 50amp service. So far no problem.
russellmania01 is offline   Reply With Quote
Old 06-06-2020, 01:19 PM   #38
Senior Member
 
Cavie's Avatar
 
Join Date: Apr 2020
Location: Port Charlotte FL/Hinsdale MA.
Posts: 1,070
Quote:
Originally Posted by RetiredOne View Post
Trying to figure out why shorter rigs have a 30 amp service (and some TT), while bigger rigs have 50 amp service. For the most part, they have the same fixtures and appliances, except the longer rigs can have a second A/C unit.

But when I add up the potential equipment that can be turned on at the same time, the 30 amp falls far short of providing enough power... Here's a list:

Turn on the A/C, 14 amps; Water heater cycles, 14 amps; turn on Coffee maker, 7 amps; Cook some bacon in microwave, 12 amps; Wifey blow drys hair, 12 amps; Converter kicks on, 6 amps; Fridge cycles, 3 amps; TV on, 2 amps...

So, with normal activities, the 30 amp supply can easily get overloaded if it's not monitored. So, based on these possibilities, why didn't Jayco put a 50 amp service (actually 100 amps, 50 amp in each leg) in the shorter rigs too?
$$$$$$$$$ It's not just Jayco. Plus most of your amperage are high. And yes, you need to learn Energy Management. Put WH on gas and your problems will go away.
__________________
Retired Master Electrician and Building Inspector.

2011 Keystone Sprinter 323 BH
Cavie is offline   Reply With Quote
Old 06-06-2020, 01:20 PM   #39
Senior Member
 
Shokyle1's Avatar
 
Join Date: Oct 2018
Location: Cheyenne
Posts: 807
If enough people complain to their congressmen maybe the rv manafacturers will be forced to follow residential building codes. Then no one will be able to afford them.
__________________
2018 eagle ht 29.5 bhds
2016 f350 Lariat 6.7 powerstroke
Shokyle1 is offline   Reply With Quote
Old 06-06-2020, 01:22 PM   #40
Junior Member
 
Join Date: Jun 2019
Location: Lincoln
Posts: 19
30 amp

1 ac - 30 amp

2 ac - 50 amp
RRRRRRJ is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 03:17 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.