Old 01-16-2019, 05:16 PM   #1
Member
 
Join Date: Mar 2018
Location: Loganville
Posts: 59
Furnace ignites, goes out, ignites, out

I have searched the forum and can not find where anyone had the problem I am having with the furnace in my 2018 Eagle 293RKDS.


I turn the furnace on and the blower starts. After a few seconds the burner ignites and goes out in a second or two. The blower stays running then after about 30 seconds the burner ignites and goes out in a second or two. The blower never turns off and the gas never burns longer than two seconds. I have let it run for 15 minutes and it keeps repeating this cycle.

Propane tanks were about 1/2 full so I filled the tanks. That did not change anything. The three burners on the stove all burn blue when on at the same time, so I have good flow of propane.


The furnace has worked fine till now. Anyone had this problem? If so what was the fix. I took the wall down in storage area and found the furnace. They did not leave much room for 6'4" man to work!
__________________
2018 Jayco 293RKDS
2015 Ram 2500 6.7L
B&W Companion
Bama is offline   Reply With Quote
Old 01-16-2019, 05:19 PM   #2
Senior Member
 
Mopar_Earl's Avatar
 
Join Date: Oct 2016
Location: Saint Thomas, PA
Posts: 2,234
Thermocouple issue?


Earl
__________________
2017 Eagle 293RKDS, factory ordered, lots of mods and upgrades. More than I can list.
2018 Ram 3500 crew cab long bed SRW diesel 6spd Aisin 4wd Tradesman.
B&W Ram puck 5th wheel
Line-X premium
Mopar wheel to wheel steps
Mopar_Earl is offline   Reply With Quote
Old 01-16-2019, 05:25 PM   #3
Member
 
Join Date: Mar 2018
Location: Loganville
Posts: 59
I thought about that or flame sensor. I assume I have to remove the furnace to get to this? No access door on side of camper.
__________________
2018 Jayco 293RKDS
2015 Ram 2500 6.7L
B&W Companion
Bama is offline   Reply With Quote
Old 01-16-2019, 05:32 PM   #4
Senior Member
 
Mopar_Earl's Avatar
 
Join Date: Oct 2016
Location: Saint Thomas, PA
Posts: 2,234
If they are like the older furnaces they would still have a thermocouple. Which senses the flame is there.
I believe you have to remove the furnace to service it. I haven't worked on any late model furnaces, so I'm not much of help. The older ones could be serviced to a point without removing or had an exterior access cover. Looking at my 2017 Eagle furnace, doesn't appear to have any service access.


Earl
__________________
2017 Eagle 293RKDS, factory ordered, lots of mods and upgrades. More than I can list.
2018 Ram 3500 crew cab long bed SRW diesel 6spd Aisin 4wd Tradesman.
B&W Ram puck 5th wheel
Line-X premium
Mopar wheel to wheel steps
Mopar_Earl is offline   Reply With Quote
Old 01-16-2019, 07:58 PM   #5
Senior Member
 
Join Date: Aug 2017
Location: Rock Island
Posts: 1,073
You said you refilled the tanks, so this may not apply and points to the thermocouple, but, try this:
Turn off both tanks, disconnect to release pressure, reconnect, now SLOWLY turn tanks back on. Bleed air out through stove top burners and then try the furnace again.
I had this exact issue as you describe and it was the auto regulator that switches from empty tank to full. Mine shows green and red, and even with full tanks it was red. Had to release the pressure a couple times before it showed green and then the furnace ran fine. The key is to open tanks slowly.
Just something else quick and cheap to try.
__________________
2017 Eagle 291RSTS
2017 Chevy Silverado Duramax 2500
GHen is offline   Reply With Quote
Old 01-16-2019, 07:59 PM   #6
Senior Member
 
Join Date: Aug 2017
Location: Rock Island
Posts: 1,073
Also, my burners on the stove worked also, but looking closely they were running only ay 25%.
__________________
2017 Eagle 291RSTS
2017 Chevy Silverado Duramax 2500
GHen is offline   Reply With Quote
Old 01-17-2019, 08:52 AM   #7
Member
 
Join Date: Mar 2018
Location: Loganville
Posts: 59
Ghen, I will give that a try. My auto switch over has been green. I’ll try it this evening. Thanks.
Bama is offline   Reply With Quote
Old 01-17-2019, 09:00 AM   #8
Junior Member
 
jimr63's Avatar
 
Join Date: Nov 2018
Location: Dunkirk, MD
Posts: 14
Mine (previous trailer) would do this every year after sitting all winter. I would fix it by cleaning out the spider web or mud dauber nest from the gas tube elbow thingy at the ignitor. Every time it acted this way it was something in that tube. Worth a look...


p.s. Sometimes you could barely see the spider web but it was enough to disturb the gas flow. Seemed like that tube had to be spotless in order for the furnace to light properly.
__________________
Jim R.
Dunkirk, MD
2018 Ram 3500 MC 4x4, CTD, DRW, w/ Max Tow
2018 Jayco NorthPoint 315RLTS
jimr63 is offline   Reply With Quote
Old 01-17-2019, 09:16 AM   #9
Senior Member
 
hoppers4's Avatar
 
Join Date: Mar 2015
Location: Port Orchard
Posts: 2,064
I just had this problem recently. It was a simple matter of removing the furnace cover on the outside, disconnecting and reconnecting the circuit board and every other wire connection I could find. Fixed the problem. The thermocouple sensor is very low voltage and it wouldn't take much resistance in a poor connection for it fail.
__________________
Don
hoppers4 is offline   Reply With Quote
Old 01-17-2019, 09:18 AM   #10
Senior Member
 
hoppers4's Avatar
 
Join Date: Mar 2015
Location: Port Orchard
Posts: 2,064
Also, you have to put the cover back on with the extension tube or the burner won't stay lit. I also discovered this after a bit of troubleshooting. You don't have to put the screws back in, but just install the cover with the extension tube for a quick test.
__________________
Don
hoppers4 is offline   Reply With Quote
Old 01-18-2019, 12:15 PM   #11
Member
 
Join Date: Mar 2018
Location: Loganville
Posts: 59
I disconnected the propane for about ten minutes. Reconnected to propane tanks then very slowly opened the valves. Used stove to bleed air out of the lines. Furnace is still doing the same thing.

I looked in exhaust tube from outside the camper and do not see anything. Since Jayco did not install an outside access door for the furnace, looks like I may have to pull the furnace to check the wires and tubes inside the furnace.

Thanks for all the tips on what to check. I will report back when I find the problem.
__________________
2018 Jayco 293RKDS
2015 Ram 2500 6.7L
B&W Companion
Bama is offline   Reply With Quote
Old 01-18-2019, 12:36 PM   #12
Senior Member
 
Join Date: Sep 2017
Location: Blue Bell
Posts: 718
Isn’t this the classic symptom of a bad sail switch? Once the furnace does not sense air moving through the duct, it shuts down?

Running for 30 seconds afterwards is the normal cool down program after being in heat mode, I think.
Lowmiler is offline   Reply With Quote
Old 01-18-2019, 12:51 PM   #13
Member
 
Join Date: Mar 2018
Location: Loganville
Posts: 59
The blower is working fine. I have a lot of cold air coming out of the ducts. In fact the blower never does shut off when the flame goes out. I have let it run for 15 minutes. During this time the blower stays running but the flame goes out with in two seconds of lighting. It will continue lighting the flame every 30 seconds or so but it goes out within two seconds.
__________________
2018 Jayco 293RKDS
2015 Ram 2500 6.7L
B&W Companion
Bama is offline   Reply With Quote
Old 01-18-2019, 01:00 PM   #14
Senior Member
 
Join Date: Sep 2017
Location: Blue Bell
Posts: 718
Quote:
Originally Posted by Bama View Post
The blower is working fine. I have a lot of cold air coming out of the ducts. In fact the blower never does shut off when the flame goes out. I have let it run for 15 minutes. During this time the blower stays running but the flame goes out with in two seconds of lighting. It will continue lighting the flame every 30 seconds or so but it goes out within two seconds.
Right, with a bad sail switch the blower can blow, but the furnace doesn't sense it. The shape of the switch catches the air moving through the duct and changes position, which tells the furnace that the blower is working.

On second thought, not sure a bad sail switch would even allow the furnace to ignite. I think it has to be blown into proper position first before the furnace will light off. So if you are sure you are getting ignition, it's probably not the sail switch.
__________________

Todd
Just outside Philly
2018 377RLBH
2019 Ford F450 Platinum
Old Faithful: 2004 GMC Sierra 3500 Diesel Dually
Lowmiler is offline   Reply With Quote
Old 01-18-2019, 01:12 PM   #15
Member
 
Join Date: Mar 2018
Location: Loganville
Posts: 59
I am getting ignition. I can hear it and feel heat for two seconds at the exhaust port outside the camper. Thanks!
__________________
2018 Jayco 293RKDS
2015 Ram 2500 6.7L
B&W Companion
Bama is offline   Reply With Quote
Old 01-18-2019, 01:36 PM   #16
Senior Member
 
ALJO's Avatar
 
Join Date: Oct 2014
Location: Sparwood, BC
Posts: 2,800
Send a message via Skype™ to ALJO
It ignites but doesn't detect the flame, it means the problem is in the burner area. Since your furnace has no outside access door the furnace has to be removed for bench testing.
__________________
2014 Ram 1500 CrewCab 4x4 5.7 Hemi 3.92 Rear and Air Lift 1000
2005 Jayco Jay Feather LGT - 29Y GVWR-7000 lbs.
Dexter Axle Lift 4-9/16" - installed with sub-frame.
Pro Series 1200 lbs. WDH with Double Sway Bar.
Champion 3100/2800 watt Inverter/Generator-Onboard Solar Power
ALJO is offline   Reply With Quote
Old 01-18-2019, 06:46 PM   #17
Senior Member
 
Join Date: Jan 2018
Location: arp
Posts: 193
I had a very similar problem, it was the thermal switch.. ( looks like a diode inline to 2 connector spades close to flame hole/ circuit card... I made a jumper ( for testing only ).. jumped it then cycled my heater... worked perfectly,, went and got a new thermal switch,, been rock solid ever since. also got a spare one, to keep in the trailer for next time.
parallax is offline   Reply With Quote
Old 01-18-2019, 07:33 PM   #18
Senior Member
 
Cosmik Debris's Avatar
 
Join Date: Aug 2013
Location: Missoula, Montana
Posts: 704
Just my experience, that the exhaust back pressure is sensitive. Was camping in freezing weather and water line would freeze overnight, so, since the furnace exhaust was right next to the water input, thought I'd lean a sheet of plywood against the fifth wheel so the furnace exhaust would warm the water connection. Wrong. Furnace would fire up, shut down. Over and over. Moved plywood and all was fine.
Just wanted to tell this in case your furnace isn't exhausting clearly.
__________________
"I might be movin' to Montana soon..."

2020 Outdoors RV Glacier Peak Titanium
2013 Eagle 29.5RKS (traded in)
2013 Ford 6.7L diesel F350
Cosmik Debris is offline   Reply With Quote
Old 01-30-2019, 03:52 PM   #19
Junior Member
 
Join Date: Mar 2016
Location: Honolulu
Posts: 26
Furnace malfunction

I have a 2016 Jayco Precept 31 Ul and had the same problem it would fire for about 3 seconds and go out over and over again. We froze many nights in the mountains as we traveled . finally a 20.00 Walmart space heater worked like a charm. It took all of 2 years to solve the problem and 3 service centers and hours & hours on the phone with Jayco. They replaced the motherboard 4 times and had to actually leave it at the service e center for 4 months and to no avail. finally after 2 years they sent a new furnace and it appears to work fine now. The company that makes them changed ownership so Jayco finally warranted it along with 20 + other items.
Now the front A/C quit working and they tell me warranty is over so I need to replace it on my own so its back in service and I am waiting for the quote on replacement.
i HOPE YOUR UNDER WARRANTY
wondermn1 is offline   Reply With Quote
Old 01-30-2019, 04:08 PM   #20
Junior Member
 
Join Date: Oct 2018
Location: Rochester
Posts: 23
Quote:
Originally Posted by wondermn1 View Post
Now the front A/C quit working and they tell me warranty is over so I need to replace it on my own so its back in service and I am waiting for the quote on replacement.
i HOPE YOUR UNDER WARRANTY
just because the a/c quit working doesn't necessarily mean you must replace it. there are a lot of things to check before I would even consider replacing it
Jmac000 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 05:43 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.