What is the service voltage?

My 2021 eagle mlok has a 4 prong when connected to 50 A, so is the camper 240v when this is 50A? The box has a double throw so it makes me believe it is.

Reason I'm asking is my new home has a 220 welders outlet accessible.

Thanks!!
Camperdude is offline   Reply With Quote
Old 08-04-2024, 09:24 PM   #2
Senior Member
 
craigav's Avatar
 
Join Date: Mar 2017
Location: North Texas
Posts: 4,058
There is 240V potential with a RV 50A connection. However, it is not used as 240V and instead is used as two 120V legs. Your welder outlet may or may not work for you depending on if it has 4 wires running to it. A 240V welder likely doesn't need a neutral like your RV requires, and therefore the outlet may not have a neutral which means it wouldn't work for you. Even if there are 4 contacts in the plug, I would check it all with a meter and make sure you have a neutral and a ground along with two hots. ~CA
__________________
2010 GreyHawk 31SS
craigav is online now   Reply With Quote
Old 08-04-2024, 09:27 PM   #3
Junior Member
 
Slippy's Avatar
 
Join Date: Apr 2023
Location: Around
Posts: 15
Home 220 is generally not wired the same as RV 50 amp. If you are thinking of plugging in, have an electrician familiar with home RV connections look at it first, or you could blow the electrical system on your RV.
__________________
2010 Jayco JayFeather X17Z
2008 Jeep Grand Cherokee Limited
1999 GeorgieBoy Cruise Master 3515

Navigator (Wife)
Flight Crew (Cocker Spaniels)
Slippy is offline   Reply With Quote
Old 08-05-2024, 12:10 AM   #4
Senior Member
 
Edutron's Avatar
 
Join Date: Aug 2019
Location: Rapid City
Posts: 266
Welding 220v outlets are wired slightly different than a 220v Rv outlet plug. Youtube is an easy reference. I had an electrician run 220v wires to an outlet in the back of my garage for a welder plugin, but decided to turn that into an RV outlet to have shore power while at home. Need to buy a different outlet (female) plug and wire it. Pretty easy.
__________________
2020 GMC 3500 Dually Denali
2020 Jayco Pinnacle 32 RLTS
----------------------------------
Edutron is offline   Reply With Quote
Old 08-05-2024, 01:28 AM   #5
Senior Member
 
Join Date: Nov 2021
Location: Troy
Posts: 1,761
Quote:
Originally Posted by Camperdude View Post
My 2021 eagle mlok has a 4 prong when connected to 50 A, so is the camper 240v when this is 50A? The box has a double throw so it makes me believe it is.

Reason I'm asking is my new home has a 220 welders outlet accessible.

Thanks!!
You are getting some wild and some vague answers.
Residential services in the US are a 120/240 volt single phase 3 wire with ground.
That is exactly what a 50 amp receptacle supplies for your RV. No, it’s not two 120 volts that add together. It is 240 volts that is divided in half by connection of a neutral conductor in the center of all the windings.
You must check the welder outlet to see if it has 120 volts. Many DIY people install the same receptacle as the ones at the campgrounds are and even connect the neutral. So, from hot to hot is 240 volts, from either hot to neutral is 120 volts, and from either hot to ground is 120 volts. As Craig said, there is typically no 240 volt appliances in a RV. There are a very few exceptions.
So, if you find you have a neutral and get 120 volts, verify that you have a minimum #8 copper or better #6 copper branch circuit conductors and they are connected to a 50 amp 2 pole circuit breaker.
If not, let us know what you find.
Kevin Cooper is offline   Reply With Quote
Old 08-05-2024, 04:13 AM   #6
Junior Member
 
Join Date: Jun 2024
Location: New England
Posts: 23
The voltage is 2 120 volt legs off the 240 volt feed, Most RVs do not use the 50 amp 240 volt supply as 240 v0lts they split the voltage into 2 120 volt legs. See the example below.



Tadsher is offline   Reply With Quote
Old 08-05-2024, 05:35 AM   #7
Senior Member
 
Join Date: Nov 2021
Location: Kaufman
Posts: 108
Quote:
Originally Posted by Camperdude View Post
My 2021 eagle mlok has a 4 prong when connected to 50 A, so is the camper 240v when this is 50A? The box has a double throw so it makes me believe it is.

Reason I'm asking is my new home has a 220 welders outlet accessible.

Thanks!!
You probably have something that looks like this currently installed. 240V Welders typically have two hots (120V each leg) and a ground. Your trailer needs a Neutral wire in order to work correctly so the cable feeding the outlet would need to be changed to 6/3 with ground and the correct, 4 wire outlet.
Attached Thumbnails
51ZgWJqqGFL._AC_UL480_FMwebp_QL65_.jpg  
__________________

2021 Northpoint 373 BHOK
2022 GMC Sierra 3500 Denali DRW
Rodney27405 is offline   Reply With Quote
Old 08-06-2024, 10:36 AM   #8
Member
 
Join Date: Mar 2021
Location: Omaha
Posts: 90
50A service

Testing the 3 prong outlet at the house yields 120 each side and 240 from one hot to the other. Looks like they tied the ground to the neutral. I have an adapter that goes from 3 prong to the outlet needed for my shore line. Testing it on the camper end of the shore line I get 120 each side.


Quote:
Originally Posted by Kevin Cooper View Post
You are getting some wild and some vague answers.
Residential services in the US are a 120/240 volt single phase 3 wire with ground.
That is exactly what a 50 amp receptacle supplies for your RV. No, it’s not two 120 volts that add together. It is 240 volts that is divided in half by connection of a neutral conductor in the center of all the windings.
You must check the welder outlet to see if it has 120 volts. Many DIY people install the same receptacle as the ones at the campgrounds are and even connect the neutral. So, from hot to hot is 240 volts, from either hot to neutral is 120 volts, and from either hot to ground is 120 volts. As Craig said, there is typically no 240 volt appliances in a RV. There are a very few exceptions.
So, if you find you have a neutral and get 120 volts, verify that you have a minimum #8 copper or better #6 copper branch circuit conductors and they are connected to a 50 amp 2 pole circuit breaker.
If not, let us know what you find.
Camperdude is offline   Reply With Quote
Old 08-06-2024, 10:59 AM   #9
Senior Member
 
Join Date: Jan 2022
Location: Baton Rouge
Posts: 1,216
is the neutral wire properly sized? It must be 6awg or bigger for 50 amp service.

Using a undersized ground wire for a neutral can cause you to have high and low voltage and create a fire hazard.
__________________
2022 Jayco Pinnacle 32RLTS, Onan 5500, 380 Watts
Solar, GoPower MPPT, Four 6 Volt batteries, EMS-HW50C, Hughes Hardwired Autoformer, Disc brakes and 17.5" tires

2017 Ram Cummins 3500, 4x4, Dually Aisin, 3.73
B&W hitch
Learjet is offline   Reply With Quote
Old 08-06-2024, 11:03 AM   #10
Senior Member
 
craigav's Avatar
 
Join Date: Mar 2017
Location: North Texas
Posts: 4,058
Quote:
Originally Posted by Camperdude View Post
Testing the 3 prong outlet at the house yields 120 each side and 240 from one hot to the other. Looks like they tied the ground to the neutral. I have an adapter that goes from 3 prong to the outlet needed for my shore line. Testing it on the camper end of the shore line I get 120 each side.
It sounds as if you have two hots (L1 and L2) and a ground, is that correct? If so, don't use that for your RV.

More information: While there is always a neutral to ground bond at the service panel when properly installed as that is required by code and even without code that is required for any level of safety for every outlet that the panel's breakers feed into (the main breaker panel neutral to ground bond). The ground wire itself (which is what exists on a 3 wire 240v outlet) should never carry any current and is often not even sized large enough to do so (the ground is undersized with the understanding that a proper connection would trip the breaker if there was a short to ground, therefore the ground wouldn't carry current except for a moment or two which is why it is often undersized). Point being, even though you are measuring 120v to ground (x2), that is to be expected but the outlet should not be used for your RV unless it has 2 hots, 1 Neutral, and 1 Ground. The risks are very high to do otherwise, not just to the RV, but to the wiring in the house, fire potential, and an electrocution hazard. ~CA
__________________
2010 GreyHawk 31SS
craigav is online now   Reply With Quote
Old 08-06-2024, 11:43 AM   #11
Senior Member
 
Join Date: Nov 2021
Location: Troy
Posts: 1,761
Quote:
Originally Posted by Camperdude View Post
Testing the 3 prong outlet at the house yields 120 each side and 240 from one hot to the other. Looks like they tied the ground to the neutral. I have an adapter that goes from 3 prong to the outlet needed for my shore line. Testing it on the camper end of the shore line I get 120 each side.
Craig is absolutely correct! A three prong has only ground, not neutral. The smaller, probably bare “equipment ground” is not supposed to be a current carrying conductor. If you insist on using it as is, will it work? It will seem to be working, but in reality, as Craig said, you will be putting anyone that comes in contact with that RV at risk of shock and yes possibly electrocution, (that means death). Also, since it was mentioned that the ground is smaller, and bare, if enough amps are flowing, that bare conductor in your RV will be getting very hot. So hot, that it can cause a fire before it shorts out to the hot because it melted the insulation. If you are still not convinced, let us know.
Always practice safety! The life you save may just be your own!
Kevin Cooper is offline   Reply With Quote
Old 08-06-2024, 11:50 AM   #12
Junior Member
 
Join Date: Jun 2024
Location: New England
Posts: 23
Quote:
Originally Posted by craigav View Post
It sounds as if you have two hots (L1 and L2) and a ground, is that correct? If so, don't use that for your RV.

More information: While there is always a neutral to ground bond at the service panel when properly installed as that is required by code and even without code that is required for any level of safety for every outlet that the panel's breakers feed into (the main breaker panel neutral to ground bond). The ground wire itself (which is what exists on a 3 wire 240v outlet) should never carry any current and is often not even sized large enough to do so (the ground is undersized with the understanding that a proper connection would trip the breaker if there was a short to ground, therefore the ground wouldn't carry current except for a moment or two which is why it is often undersized). Point being, even though you are measuring 120v to ground (x2), that is to be expected but the outlet should not be used for your RV unless it has 2 hots, 1 Neutral, and 1 Ground. The risks are very high to do otherwise, not just to the RV, but to the wiring in the house, fire potential, and an electrocution hazard. ~CA

Agree 100% what craigav and Kevin Cooper said
Tadsher is offline   Reply With Quote
Old 08-06-2024, 02:52 PM   #13
Member
 
Join Date: Mar 2021
Location: Omaha
Posts: 90
Quote:
Originally Posted by Tadsher View Post
Agree 100% what craigav and Kevin Cooper said


I'm going to run a ground wire from the box to the outlet and put a 4 prong plug in. Figured might as well do it right.
Camperdude is offline   Reply With Quote
Old 08-06-2024, 03:44 PM   #14
Senior Member
 
Join Date: Nov 2021
Location: Troy
Posts: 1,761
Quote:
Originally Posted by Camperdude View Post
I'm going to run a ground wire from the box to the outlet and put a 4 prong plug in. Figured might as well do it right.
You need to run a white neutral that is the same size as the hot conductors. You already have a ground.
Kevin Cooper is offline   Reply With Quote
Old 08-06-2024, 06:50 PM   #15
Senior Member
 
Join Date: Jan 2022
Location: Baton Rouge
Posts: 1,216
Quote:
Originally Posted by Kevin Cooper View Post
You need to run a white neutral that is the same size as the hot conductors. You already have a ground.
Like I said above ^^^^^^^^^^^
__________________
2022 Jayco Pinnacle 32RLTS, Onan 5500, 380 Watts
Solar, GoPower MPPT, Four 6 Volt batteries, EMS-HW50C, Hughes Hardwired Autoformer, Disc brakes and 17.5" tires

2017 Ram Cummins 3500, 4x4, Dually Aisin, 3.73
B&W hitch
Learjet is offline   Reply With Quote
Old 08-06-2024, 07:55 PM   #16
Senior Member
 
Join Date: Nov 2021
Location: Troy
Posts: 1,761
I’ve seen videos of people running #10 copper on 30 amp breakers to a 50a receptacle for a small wire feed welder.
Kevin Cooper is offline   Reply With Quote
Old 08-07-2024, 07:26 PM   #17
Member
 
Join Date: Mar 2021
Location: Omaha
Posts: 90
Quote:
Originally Posted by Kevin Cooper View Post
Craig is absolutely correct! A three prong has only ground, not neutral. The smaller, probably bare “equipment ground” is not supposed to be a current carrying conductor. If you insist on using it as is, will it work? It will seem to be working, but in reality, as Craig said, you will be putting anyone that comes in contact with that RV at risk of shock and yes possibly electrocution, (that means death). Also, since it was mentioned that the ground is smaller, and bare, if enough amps are flowing, that bare conductor in your RV will be getting very hot. So hot, that it can cause a fire before it shorts out to the hot because it melted the insulation. If you are still not convinced, let us know.
Always practice safety! The life you save may just be your own!
I noticed the camper outlet is only 3 prong. Does this mean they tired the neutral and ground together?

It's 4 prong to the power but only three prong at the camper.
Camperdude is offline   Reply With Quote
Old 08-07-2024, 07:39 PM   #18
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 17,092
Quote:
Originally Posted by Camperdude View Post
I noticed the camper outlet is only 3 prong. Does this mean they tired the neutral and ground together?

It's 4 prong to the power but only three prong at the camper.
Which is 4 the outlet or the cord? Which is 3?
__________________
DISNEY LOVERS
Grumpy is online now   Reply With Quote
Old 08-07-2024, 08:18 PM   #19
Senior Member
 
Join Date: Nov 2021
Location: Troy
Posts: 1,761
Quote:
Originally Posted by Camperdude View Post
I noticed the camper outlet is only 3 prong. Does this mean they tired the neutral and ground together?

It's 4 prong to the power but only three prong at the camper.
Ok, let’s start all over. If you open the door on your electrical panel, what is the amps of the largest breaker in the panel? 30 amp or 50 amp.
You comments are contradicting each other.
Kevin Cooper is offline   Reply With Quote
Old 08-07-2024, 08:41 PM   #20
Senior Member
 
Join Date: Jan 2022
Location: Baton Rouge
Posts: 1,216
Probably sees the three twist lock connectors and doesn't see the outside ground terminal on the twist lock connector.
__________________
2022 Jayco Pinnacle 32RLTS, Onan 5500, 380 Watts
Solar, GoPower MPPT, Four 6 Volt batteries, EMS-HW50C, Hughes Hardwired Autoformer, Disc brakes and 17.5" tires

2017 Ram Cummins 3500, 4x4, Dually Aisin, 3.73
B&W hitch
Learjet is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 08:16 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.