Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
Jayco RV Owners Forum
 


Reply
 
Thread Tools Search this Thread Display Modes
 
Old 07-03-2018, 08:47 AM   #1
Senior Member
 
Join Date: Mar 2017
Location: Lubbock, TX
Posts: 360
A/C and Generator

Question........if I am using my generator and it runs out of gas while my A/C is running, does that hurt anything. Obviously the A/C will stop, but wondering if that damages anything.
__________________
2013 198RD
lefoster is offline   Reply With Quote
Old 07-03-2018, 08:56 AM   #2
Junior Member
 
Join Date: Mar 2018
Location: Tremonton
Posts: 24
No, I did that camping in Moab, UT we left to go on a white water rafting trip for 5-6 hours and needed the camper to stay cool for my dog. It ran most of 5-6 hours because it was dead when we got back and the camper was still cool.
2018SLXBAJA is offline   Reply With Quote
Old 07-03-2018, 09:32 AM   #3
Senior Member
 
2edgesword's Avatar
 
Join Date: Jul 2011
Location: Long Island, NY
Posts: 1,402
Anytime a generator starts or shuts down voltage spikes occur that can damage sensitive electronics. As a normal practice you want the loads disconnected from the generator before starting it up or shutting it down. The start-up/shutdown procedure for many generators includes...

"Never start or stop the generator with electrical devices plugged in or turned on."
__________________

2018 Jayco 28RLS
2012 F-250 6.2L 3.73
Equalizer Hitch
Yamaha 2400ISHC
2edgesword is offline   Reply With Quote
Old 07-03-2018, 09:37 AM   #4
Senior Member
 
Camper_bob's Avatar
 
Join Date: Sep 2013
Location: South Texas
Posts: 7,216
The problem is that when the generator runs out of fuel, it doesn't just shut off suddenly. It will surge as it starts to suck the last bit of fuel to keep going. This surging causes wild fluctuations in the energy coming out of the genny. Those fluctuations (especially the low voltage ones) are a big problem for things like air conditioners, and can potentially cause damage. I would try to avoid a situation like that.
__________________

-2018 Greyhawk 29MV
-2020 Jeep Wrangler Unlimited (JLU) (Primary Toad)
-1994 Jeep Wrangler YJ (Secondary Toad)
-2014 Jay Flight 28BHBE & Ram 2500 6.4L CC 4x4 (sold)
Camper_bob is offline   Reply With Quote
Old 07-03-2018, 10:11 AM   #5
Senior Member
 
ALJO's Avatar
 
Join Date: Oct 2014
Location: Sparwood, BC
Posts: 2,800
Send a message via Skype™ to ALJO
The generator/converter will kick the bucket when under heavy load like an A/C, my son in-law went through 3 of them (hard learner). A normal generator doesn't but it isn't good for electronics present in RV's.
__________________
2014 Ram 1500 CrewCab 4x4 5.7 Hemi 3.92 Rear and Air Lift 1000
2005 Jayco Jay Feather LGT - 29Y GVWR-7000 lbs.
Dexter Axle Lift 4-9/16" - installed with sub-frame.
Pro Series 1200 lbs. WDH with Double Sway Bar.
Champion 3100/2800 watt Inverter/Generator-Onboard Solar Power
ALJO is offline   Reply With Quote
Old 07-03-2018, 12:04 PM   #6
Senior Member
 
Join Date: Mar 2017
Location: Lubbock, TX
Posts: 360
thank you all for the replies. surges and spikes were my concern. the time it happened, we had gone to sleep with it running and it ran out sometime in the night. guess it would be best to cool things down and then shut it off before going to bed?
__________________
2013 198RD
lefoster is offline   Reply With Quote
Old 07-03-2018, 12:48 PM   #7
Senior Member
 
ifallsguy's Avatar
 
Join Date: Mar 2017
Location: In the gnat capital of the world, Tifton, GA
Posts: 555
With a hard wired EMS in place, as soon as it sees a voltage drop, surge, etc, it should cut off power. That's what it's designed to do. As long as it is set to prevent power past it for at least 2 minutes, I think you wouldn't harm anything in the trailer. The AC needs 2 minutes for pressures to equalize before restarting.

As for damage to the inverter, I think the fact the EMS would cut off any demand would put it in a no load situation and it shouldn't be damaged.

Just my opinion.
ifallsguy is offline   Reply With Quote
Old 07-03-2018, 12:53 PM   #8
Senior Member
 
2edgesword's Avatar
 
Join Date: Jul 2011
Location: Long Island, NY
Posts: 1,402
Quote:
Originally Posted by ifallsguy View Post
With a hard wired EMS in place, as soon as it sees a voltage drop, surge, etc, it should cut off power. That's what it's designed to do. As long as it is set to prevent power past it for at least 2 minutes, I think you wouldn't harm anything in the trailer. The AC needs 2 minutes for pressures to equalize before restarting.

As for damage to the inverter, I think the fact the EMS would cut off any demand would put it in a no load situation and it shouldn't be damaged.

Just my opinion.
This type of surge protection between the generator and RV would be a safeguard against electrical damage should the generator shut off unexpectedly.
__________________

2018 Jayco 28RLS
2012 F-250 6.2L 3.73
Equalizer Hitch
Yamaha 2400ISHC
2edgesword is offline   Reply With Quote
Old 07-03-2018, 01:26 PM   #9
Senior Member
 
ifallsguy's Avatar
 
Join Date: Mar 2017
Location: In the gnat capital of the world, Tifton, GA
Posts: 555
Quote:
Originally Posted by 2edgesword View Post
This type of surge protection between the generator and RV would be a safeguard against electrical damage should the generator shut off unexpectedly.
Thanks for adding that information. Forgot to put that into my comments.

Also the EMS would help protect against issues with shore power.
ifallsguy is offline   Reply With Quote
Old 07-03-2018, 02:52 PM   #10
Senior Member
 
Join Date: Dec 2015
Location: Arizona
Posts: 2,324
We ran out of gas twice on this trip still running, but will keep a closer eye on gas level! Thanks
bdreinv is offline   Reply With Quote
Old 07-03-2018, 03:42 PM   #11
Senior Member
 
Camper_bob's Avatar
 
Join Date: Sep 2013
Location: South Texas
Posts: 7,216
Absolutely, an EMS is a great idea for LOTS of other reasons. AND it would protect your equipment in this particular situation.

Something like this happened to us out on the road once. It was our first time overnighting at a WM on a long journey. I thought I could fire up the generator in the back of the pickup if I just opened one third of the tonneau cover. Turns out that wasn't enough ventilation and just about the time my head hit the pillow, the genny started overheating and surging. I could hear the A/C fluctuating and jumped out of bed and turned it off before any damage happened luckily. I was able to fully open the tonneau cover and drop the tailgate and the genny ran flawlessly for the rest of the night and the trip.

In our new MH, the tags were covering one of the vents on the generator, and caused it to overheat and begin surging in the same manner. Again, I popped up and turned off the AC units. I was able to clear that one up too and haven't had a problem since.

I really need to get my EMS before I break something!
__________________

-2018 Greyhawk 29MV
-2020 Jeep Wrangler Unlimited (JLU) (Primary Toad)
-1994 Jeep Wrangler YJ (Secondary Toad)
-2014 Jay Flight 28BHBE & Ram 2500 6.4L CC 4x4 (sold)
Camper_bob is offline   Reply With Quote
Old 07-03-2018, 04:55 PM   #12
Senior Member
 
Join Date: Jan 2018
Location: SW
Posts: 513
IMO . . . a non-inverter (typical open-frame) generator is much more likely (than an inverter generator) to introduce voltage and/or frequency deviations while the engine powers down down from a lack of fuel. I say that because an inverter generator's inverter circuitry is constantly monitoring/adjusting voltage, frequency, and checking the load at all times---purposely changing engine RPMs to accommodate changing loads. It's not unreasonable to expect an inverter generator's inverter circuitry to shutdown all output when it's unable to maintain proper voltage and frequency levels due to insufficient engine RPM. On the other hand, a non-inverter (open-frame) generator's voltage and frequency output is mechanically dependent on engine RPM--any change in engine RPM (i.e., surging and floundering while running out of fuel) instantly results in a change in voltage and frequency---not good.

As ifallsguy and Camper_bob also mentioned, an EMS should provide good protection. FYI, a "simple" RV surge protector, that typically costs $75-$125, offers little to no protection when a generator shuts down from a lack of fuel. A "simple" surge protector only provides protection from significant voltage spikes (a few milliseconds long) that result from lightning strikes or switching transients.

FWIW, we've run a Champion 3100 inverter generator out of fuel while powering some of our trailers with the a/c unit on many times---with and without an EMS. Never had any issues. Take this comment for what it's worth---a dime, maybe a quarter at most--lol! Don't know if we've been very lucky, or the inverter circuitry is actually doing an excellent job of blocking any voltage or frequency deviations from entering the trailer while the engine shuts down.
CampNow is offline   Reply With Quote
Old 07-05-2018, 08:01 AM   #13
Senior Member
 
Camper_bob's Avatar
 
Join Date: Sep 2013
Location: South Texas
Posts: 7,216
Quote:
Originally Posted by CampNow View Post
IMO . . . a non-inverter (typical open-frame) generator is much more likely (than an inverter generator) to introduce voltage and/or frequency deviations while the engine powers down down from a lack of fuel. I say that because an inverter generator's inverter circuitry is constantly monitoring/adjusting voltage, frequency, and checking the load at all times---purposely changing engine RPMs to accommodate changing loads. It's not unreasonable to expect an inverter generator's inverter circuitry to shutdown all output when it's unable to maintain proper voltage and frequency levels due to insufficient engine RPM. On the other hand, a non-inverter (open-frame) generator's voltage and frequency output is mechanically dependent on engine RPM--any change in engine RPM (i.e., surging and floundering while running out of fuel) instantly results in a change in voltage and frequency---not good.

As ifallsguy and Camper_bob also mentioned, an EMS should provide good protection. FYI, a "simple" RV surge protector, that typically costs $75-$125, offers little to no protection when a generator shuts down from a lack of fuel. A "simple" surge protector only provides protection from significant voltage spikes (a few milliseconds long) that result from lightning strikes or switching transients.

FWIW, we've run a Champion 3100 inverter generator out of fuel while powering some of our trailers with the a/c unit on many times---with and without an EMS. Never had any issues. Take this comment for what it's worth---a dime, maybe a quarter at most--lol! Don't know if we've been very lucky, or the inverter circuitry is actually doing an excellent job of blocking any voltage or frequency deviations from entering the trailer while the engine shuts down.
Good point. The generator I used with the TT was a Champion open frame generator. The one in the motorhome is an Onan 4kw; I'm guessing it's not an inverter generator. When it went into overheating, there were definite fluctuations in the power.
__________________

-2018 Greyhawk 29MV
-2020 Jeep Wrangler Unlimited (JLU) (Primary Toad)
-1994 Jeep Wrangler YJ (Secondary Toad)
-2014 Jay Flight 28BHBE & Ram 2500 6.4L CC 4x4 (sold)
Camper_bob is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 06:41 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.