Quote:
Originally Posted by lefoster
so, in theory, you want the house breaker to trip before extension cord is overloaded? correct? so extension cord should have higher amp rating than house breaker that governs the outlet you are using???
|
That's not a bad theory!
Regarding extension cords, unless you have an actual RV 30-amp outlet, your house outlets are almost certainly either 20- or 15-amp. You only need the minimum gauge wire for the level of service at your circuit breaker box. A 15-amp circuit requires minimum 14 gauge wire, while a 20-amp circuit requires a minimum of 12-gauge wire. No need to get cords rated for higher current than the circuit breaker.
OTOH, if you have a 30-amp RV outlet then you should use 10 gauge wire for an extension cord. HOWEVER, when you exceed about 25-30' you start seeing a noticeable voltage drop. In a 30-amp circuit with 10 gauge wire, you're going to lose about 2.2 volts at 30 feet. At 50' you lose 3.6 volts, and you lose 7.2 volts at 100'.
Think about that. Suppose the supply at the pedestal is 110 volts. With a 50' extension cord of 10 gauge wire, you wind up with just over 106 volts at the other end. This can be a problem for starting up air conditioner compressors, for example. If you need a run longer than about 25' it might be worth it to drop the wire gauge down a step, to maybe 8 gauge wire.
Good luck. Hope that's not too much detail!
Roger