05-15-2018, 07:21 AM
|
#1
|
Junior Member
Join Date: May 2018
Location: Mechanicsville
Posts: 25
|
Extrension Cord from 50A to house outlet - ‘18 JF 32BHDS
Good morning all,
We have our first trip planned for Friday and we were trying to plug our 50A shoreline cord (w/15A dog bone) in to our house but the chord won’t reach. Can I use an extension chord without damaging anything? Thanks in advance.
Roy
|
|
|
05-15-2018, 07:27 AM
|
#2
|
Junior Member
Join Date: May 2015
Location: Sibley
Posts: 13
|
Yes you can use an extension cord from the dogbone to your house. I myself have a 10ga 50' extension cord for that express purpose. I went with 10ga to ensure there is little voltage drop and if the outlet you are plugged into has a higher rated breaker you might also be able to run the AC for short periods of time if needed.
|
|
|
05-15-2018, 07:32 AM
|
#3
|
Junior Member
Join Date: May 2018
Location: Mechanicsville
Posts: 25
|
Thanks for the quick response. I’m not sure what gage this extentenion chord is. It says 16/3? Is that ok to use?
|
|
|
05-15-2018, 07:44 AM
|
#4
|
Senior Member
Join Date: Oct 2014
Location: Sparwood, BC
Posts: 2,800
|
Not recommended, buy a 10 ga for your RV (Pay me now or pay me later by damage)
__________________
2014 Ram 1500 CrewCab 4x4 5.7 Hemi 3.92 Rear and Air Lift 1000
2005 Jayco Jay Feather LGT - 29Y GVWR-7000 lbs.
Dexter Axle Lift 4-9/16" - installed with sub-frame.
Pro Series 1200 lbs. WDH with Double Sway Bar.
Champion 3100/2800 watt Inverter/Generator-Onboard Solar Power
|
|
|
05-15-2018, 07:46 AM
|
#5
|
Senior Member
Join Date: Apr 2015
Location: Lancaster
Posts: 806
|
Quote:
Originally Posted by MiddleClassHero
Thanks for the quick response. I’m not sure what gage this extentenion chord is. It says 16/3? Is that ok to use?
|
That means it's a 16 gauge wire. 50 amp service requires much heavier cable, 10 gauge or more (lower numbers are thicker cable). Not only that, but your house wiring requires 12 gauge for 20-amp service, or 14-gauge for 15 amp service. An 16 gauge extension cord (chords are for music, not electricity) plugged into a home outlet in order to supply your RV will be overloaded and could easily overheat, potentially causing a fire, without blowing the circuit breakers that protect the circuit.
For safety's sake you should use an extension cord with at least 12 gauge wire. 16 gauge creates a very unsafe situation.
Good luck!
Roger
__________________
TV 2010 Ford F-150 Supercab
TT 2016 Jay Feather 23RLSW
|
|
|
05-16-2018, 01:06 PM
|
#6
|
Junior Member
Join Date: May 2018
Location: Mechanicsville
Posts: 25
|
Thanks everyone for the help! Much appreciated. This is no kidding one of the most useful forums I’ve ever been a part of...especially for a newbie. Thanks again.
|
|
|
05-16-2018, 01:33 PM
|
#7
|
Senior Member
Join Date: May 2012
Location: Minnesota
Posts: 9,782
|
Ideally use as short of an extension cord as possible, and as heavy as possible.
With that said, I use a 25 foot 16 gauge extension cord for many years, without issues. I only keep the battery charged, run the frig lights as needed. We never turn on any other equipment.
|
|
|
05-16-2018, 06:00 PM
|
#8
|
Senior Member
Join Date: Sep 2012
Location: West Central Wisconsin
Posts: 274
|
I bought a 50a to 20a dogbone and then run my extension cord into the garage. It’s much easier to handle than the 50a cable and a 50a extension. I have the twist on power cord.
__________________
2018 Jayco Eagle HT 29.5BHOK
2016 Ford F-350 Super Duty SB CC PSD 4x4
|
|
|
05-16-2018, 09:53 PM
|
#9
|
Senior Member
Join Date: Apr 2012
Location: Flower Mound, TX
Posts: 126
|
Just fyi that Camping World has the short adapter from 50A to 110 15A plug on clearance for 22 or 27 bucks last weekend.
Bought one and made myself a exact lenth 12ga extension cord. I am lucky I have an outlet close to the corner where my RV connection is.
__________________
Greg D.
Flower Mound, TX
gdecker715@gmail.com
The old- 2001 Jayco Qwest
The new- 2018 Jayco Eagle 324BHTS
2018 F-150 Ecoboost
|
|
|
05-17-2018, 05:22 AM
|
#10
|
Junior Member
Join Date: May 2018
Location: Mechanicsville
Posts: 25
|
Thanks for the heads uo
__________________
Cheers,
Roy
|
|
|
05-17-2018, 05:29 AM
|
#11
|
Senior Member
Join Date: Apr 2018
Location: Indianapolis
Posts: 137
|
Keep in mind, the OP doesn't need a 50amp capable extension cord if he is plugging into a 15 or 20 amp standard outlet.
If it's 20amp, I'd use a 12/3 extension cord. 15 amp I'd use 14/3. That matches the much longer wires in the house and the outlet/breaker. For a short run and only running the TV a 16/3 will be fine.
Just keep in mind with the dog bone, you won't be able to run much in the RV without popping the breaker in the house.
All that said, I carry a 50 amp extension cable in the trailer because I've been places that I needed one, so it doesn't hurt to have it.
__________________
2013 Silverado 2500HD Duramax/Allison
2018 Jayco White Hawk 31BH
|
|
|
05-17-2018, 06:04 AM
|
#12
|
Junior Member
Join Date: May 2018
Location: Mechanicsville
Posts: 25
|
Thanks. I actually ended up buying a 50s extension. Wasn’t happy about how much it was but I’m sure it will come in handy
__________________
Cheers,
Roy
|
|
|
05-17-2018, 08:01 AM
|
#13
|
Senior Member
Join Date: Apr 2015
Location: Lancaster
Posts: 806
|
Quote:
Originally Posted by Dave.H
Keep in mind, the OP doesn't need a 50amp capable extension cord if he is plugging into a 15 or 20 amp standard outlet.
If it's 20amp, I'd use a 12/3 extension cord. 15 amp I'd use 14/3. That matches the much longer wires in the house and the outlet/breaker. For a short run and only running the TV a 16/3 will be fine.
|
You do what you want, but a 16/3 extension cord in a 20-amp circuit means you can overload and overheat the extension cord long before the 20-amp circuit breaker will "pop". Especially when you have a potential load at the RV that can exceed the 20-amp rating of the circuit.
And yes, you can control the load by running minimal stuff in the RV to keep the load down. You still have a potential fire on your hands, with no protection. It only takes one mistake.
Plugging your 50-amp RV into a 20-amp circuit? Use 12/3 for your extension cord, please.
Be safe!
Roger
__________________
TV 2010 Ford F-150 Supercab
TT 2016 Jay Feather 23RLSW
|
|
|
05-17-2018, 09:01 AM
|
#14
|
Senior Member
Join Date: Dec 2015
Location: Arizona
Posts: 2,324
|
We have same problem here, first tried GFI plugs would blow GFI. Moved extension cord to clothes dryer plug works OK! Thanks
|
|
|
05-17-2018, 09:36 AM
|
#15
|
Senior Member
Join Date: Apr 2018
Location: Indianapolis
Posts: 137
|
Quote:
Originally Posted by rkresge
You do what you want, but a 16/3 extension cord in a 20-amp circuit means you can overload and overheat the extension cord long before the 20-amp circuit breaker will "pop". Especially when you have a potential load at the RV that can exceed the 20-amp rating of the circuit.
And yes, you can control the load by running minimal stuff in the RV to keep the load down. You still have a potential fire on your hands, with no protection. It only takes one mistake.
Plugging your 50-amp RV into a 20-amp circuit? Use 12/3 for your extension cord, please.
Be safe!
Roger
|
I don't disagree with you. I had a 30 amp outlet placed in my garage when I built the house for this exact reason.
My point was more that a 50 amp extension ($$) provides no benefit on a 15 or 20 amp circuit. You are absolutely correct about the 16/3 extension cord.
__________________
2013 Silverado 2500HD Duramax/Allison
2018 Jayco White Hawk 31BH
|
|
|
05-17-2018, 09:36 AM
|
#16
|
Senior Member
Join Date: Apr 2018
Location: Indianapolis
Posts: 137
|
Quote:
Originally Posted by bdreinv
We have same problem here, first tried GFI plugs would blow GFI. Moved extension cord to clothes dryer plug works OK! Thanks
|
Um.... I hope this is a gas drier plug you connected to and not a 220 volt electric outlet
__________________
2013 Silverado 2500HD Duramax/Allison
2018 Jayco White Hawk 31BH
|
|
|
05-17-2018, 09:40 AM
|
#17
|
Senior Member
Join Date: Dec 2015
Location: Arizona
Posts: 2,324
|
Whoops should have said clothes washer outlet! Thanks
|
|
|
05-17-2018, 09:42 AM
|
#18
|
Senior Member
Join Date: Apr 2018
Location: Indianapolis
Posts: 137
|
Quote:
Originally Posted by bdreinv
Whoops should have said clothes washer outlet! Thanks
|
There you go!
__________________
2013 Silverado 2500HD Duramax/Allison
2018 Jayco White Hawk 31BH
|
|
|
05-18-2018, 08:37 AM
|
#19
|
Senior Member
Join Date: Mar 2017
Location: Lubbock, TX
Posts: 360
|
great info in this thread, as I have wondered about type/size of extension cord when plugging into my house before a trip. mainly to cool the frig.
I have about 40 ft to go from my power cord to house. I have a 30amp RV power cord, use an adapter to fit into extension cord.
so, in theory, you want the house breaker to trip before extension cord is overloaded? correct? so extension cord should have higher amp rating than house breaker that governs the outlet you are using???
__________________
2013 198RD
|
|
|
05-18-2018, 08:50 AM
|
#20
|
Site Team
Join Date: Jan 2011
Location: James Island, SC
Posts: 22,859
|
Yes unless you want the extension cord to act as a breaker? Anytime I use an extension cord, I have a habit of feeling the cord and connectors oin each end checking for heat.
It it is to warm to my hand, then it is to small a cord or a bad connection somewhere.
__________________
Moderator
2011- 351RLTS Eagle, MorRyde suspension/pin box,
2017- F350 6.7 PSD Lariat FX4,SRW, SB,CC
Hughes PWD SP-50A, TST TPMS
Gator roll-up bed cover
B&W Turnover ball, Companion Std hitch
Can't find what you're looking on JOF? Try Jayco Owners Forum Custom Google Search
|
|
|
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Threads |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|