Old 05-24-2016, 03:03 PM   #1
Junior Member
 
Join Date: May 2016
Location: Fruitland
Posts: 4
Furnace problem

I have a 2012 jayflight 32tsbh. Whenever I turn the propane on the furnace comes on and won't shut off. Doesn't matter if the thermostat is on or off or what the temp is set to. Any help would be great
rustysheros is offline   Reply With Quote
Old 05-24-2016, 03:17 PM   #2
Senior Member
 
oldmanAZ's Avatar
 
Join Date: Dec 2014
Location: FL
Posts: 11,281
Welcome to the forum.

Sounds like it might be a thermostat problem. If you carefully remove the thermostat and then turn on the propane, you'd know if the thermostat was causing the problem.
__________________
Sherm & Terry w/rescue Eydie (min Schnauzer) & Charley (std Poodle)
SOLD:2015 Jay Flight 27RLS, GY Endurance (E), Days: 102 '15, 90 '16, 80 '17, 161 '18, 365+ '20
SOLD: 2006 Ford F350 PSD, 4WD, CC, LB, SRW, Camper pkg., 375,000mi
Full timing: Some will think you're crazy, some will be envious, just enjoy the freedom!
oldmanAZ is offline   Reply With Quote
Old 05-24-2016, 03:20 PM   #3
Junior Member
 
Join Date: May 2016
Location: Fruitland
Posts: 4
The thermostat runs the air fine so I didn't think it would be a thermostat problem. But I'll try the next time I'm in it
rustysheros is offline   Reply With Quote
Old 05-24-2016, 11:04 PM   #4
ODH
Junior Member
 
Join Date: Dec 2015
Location: Riverside
Posts: 27
Different wires from the thermostat controls the furnace and the air. It sounds like you have a short in the system which is always applying 12v to the furnace relay. With a volt meter check to see if you have a constant 12v signal to the furnace while turning the thermostat heat on and off. If this is the case then you need to locate the short.
ODH is offline   Reply With Quote
Old 05-25-2016, 06:11 AM   #5
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,835
Along the shorted circuit theory...


Check the connections at the furnace. Bare wires under screws are a short circuit waiting to happen! There should be 2 or 3 separate wires.
__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Old 05-25-2016, 09:14 AM   #6
Senior Member
 
Join Date: Jun 2015
Location: Nashville
Posts: 470
Quote:
Originally Posted by rustysheros View Post
I have a 2012 jayflight 32tsbh. Whenever I turn the propane on the furnace comes on and won't shut off. Doesn't matter if the thermostat is on or off or what the temp is set to. Any help would be great
Regardless of any problems in the thermostat, I can't figure out how turning the propane valve on causes the furnace to come on. Can some one explain how that can happen?
Hohenwald48 is offline   Reply With Quote
Old 05-25-2016, 01:50 PM   #7
Senior Member
 
SmokerBill's Avatar
 
Join Date: Sep 2010
Location: PNW
Posts: 5,195
Quote:
Originally Posted by Hohenwald48 View Post
Regardless of any problems in the thermostat, I can't figure out how turning the propane valve on causes the furnace to come on. Can some one explain how that can happen?
I agree with you. I just don't see how that could be possible. Maybe in an alternate universe...
__________________
Bill
2011 Dodge Ram 1500 HEMI Quad Cab
2011 Jay Flight 26BH
SmokerBill is offline   Reply With Quote
Old 05-25-2016, 04:52 PM   #8
Senior Member
 
Join Date: Mar 2016
Location: Exeter
Posts: 151
The furnace needs two things fuel and a signal calling for heat to turn on (the same circuit that is shorted. See, this universe.
__________________
2015 Nissan Frontier SV CC 4WD
2014 Jayco Sport 8
Levinehikeski is offline   Reply With Quote
Old 05-25-2016, 05:47 PM   #9
Senior Member
 
Join Date: Jun 2015
Location: Nashville
Posts: 470
The OP stated that when he/she turns on the propane the furnace comes on. Now I've turned my propane off and on thousands of times on a dozen or more RVs and never once did the furnace come on when I turned on the valve.

Of course there needs to be propane at the furnace for it to operate but that's not what the OP said. I'm just trying to get some clarification as I don't see any connection between the tank valve and the furnace thermostat. Not in any universe.
Hohenwald48 is offline   Reply With Quote
Old 05-25-2016, 06:19 PM   #10
Senior Member
 
Dustdevil's Avatar
 
Join Date: Mar 2016
Location: Orange County
Posts: 644
The control valve for the propane line to the burner has to see constant pressure from the supply tank before it will allow the valve to open, remain open, or continue to supply gas to the burner(s). If not, it likely won't allow the blower to start either. If you turn off the tank outlet valve, pressure eventually bleeds down, and the control valve shuts off. Turn it back on again, with the theoretical short circuit showing a demand to start, and it will start up again. That's why a short circuit will cause this, just as if you had turned on the thermostat and set the temp high enough to turn the system on.
__________________
2006 Jayco Seneca 34SS
2006 Jeep Wrangler Unlimited Rubicon Toad
Dustdevil is offline   Reply With Quote
Old 05-26-2016, 02:32 PM   #11
Senior Member
 
Join Date: Jun 2015
Location: Nashville
Posts: 470
Makes sense. I think I'll give that a try sometime when I got nothing better to do. Right now it's about 90 outside so I doubt I could even get the heat to kick on. For now I'll take your word for it cause it seems logical. Thanks.
Hohenwald48 is offline   Reply With Quote
Old 05-26-2016, 03:30 PM   #12
Senior Member
 
SmokerBill's Avatar
 
Join Date: Sep 2010
Location: PNW
Posts: 5,195
Quote:
Originally Posted by Dustdevil View Post
The control valve for the propane line to the burner has to see constant pressure from the supply tank before it will allow the valve to open, remain open, or continue to supply gas to the burner(s). If not, it likely won't allow the blower to start either. If you turn off the tank outlet valve, pressure eventually bleeds down, and the control valve shuts off. Turn it back on again, with the theoretical short circuit showing a demand to start, and it will start up again. That's why a short circuit will cause this, just as if you had turned on the thermostat and set the temp high enough to turn the system on.
The opening and closing of the gas valve is controlled by voltage from the circuit board, which actuates the solenoid. Whether there's gas pressure or not wouldn't affect the state of the valve. It would be opened or closed depending on the presence of a control voltage. And if the control circuit is working properly, the valve would only open if the fan is running, and the sail switch has been actuated for a specific period of time.

A lack of propane pressure wouldn't "tell" the furnace control circuit anything. The only way the furnace would "know" there was no propane would be a case where the ignitor was actuated, and no heat was sensed by the flame sensor.

And if the flame sensor hasn't proven a flame after the ignition cycle, the control circuit will shut off the gas valve, requiring a reset (off/on) before the furnace is able to operate again.

I still see no way that propane, flowing through an already opened gas valve (which shouldn't be the case in a non-running furnace) could cause the blower to engage and the ignitor to activate.
__________________
Bill
2011 Dodge Ram 1500 HEMI Quad Cab
2011 Jay Flight 26BH
SmokerBill is offline   Reply With Quote
Old 05-26-2016, 03:43 PM   #13
Senior Member
 
ALJO's Avatar
 
Join Date: Oct 2014
Location: Sparwood, BC
Posts: 2,800
Send a message via Skype™ to ALJO
Well said SmokerBill. If there's no flame and even if the igniter is working the furnace has to be reset at the thermostat. The Atwood furnace are very safe and simple in operation.
__________________
2014 Ram 1500 CrewCab 4x4 5.7 Hemi 3.92 Rear and Air Lift 1000
2005 Jayco Jay Feather LGT - 29Y GVWR-7000 lbs.
Dexter Axle Lift 4-9/16" - installed with sub-frame.
Pro Series 1200 lbs. WDH with Double Sway Bar.
Champion 3100/2800 watt Inverter/Generator-Onboard Solar Power
ALJO is offline   Reply With Quote
Old 06-01-2016, 01:46 PM   #14
Senior Member
 
Dustdevil's Avatar
 
Join Date: Mar 2016
Location: Orange County
Posts: 644
Quote:
Originally Posted by SmokerBill View Post
The opening and closing of the gas valve is controlled by voltage from the circuit board, which actuates the solenoid. Whether there's gas pressure or not wouldn't affect the state of the valve. It would be opened or closed depending on the presence of a control voltage. And if the control circuit is working properly, the valve would only open if the fan is running, and the sail switch has been actuated for a specific period of time.

A lack of propane pressure wouldn't "tell" the furnace control circuit anything. The only way the furnace would "know" there was no propane would be a case where the ignitor was actuated, and no heat was sensed by the flame sensor.

And if the flame sensor hasn't proven a flame after the ignition cycle, the control circuit will shut off the gas valve, requiring a reset (off/on) before the furnace is able to operate again.

I still see no way that propane, flowing through an already opened gas valve (which shouldn't be the case in a non-running furnace) could cause the blower to engage and the ignitor to activate.
OK. I understand all that. So, if that is supposed to work as you just outlined, then how is it possible the blower could start, and burner operate, simply by turning the gas pressure on? Especially if the system requires cycling power before the main gas valve will ever receive a command voltage to open again? Even if it is malfunctioning, this should not be possible unless there is some way the control "knows" there is either a presence or absence of propane.
__________________
2006 Jayco Seneca 34SS
2006 Jeep Wrangler Unlimited Rubicon Toad
Dustdevil is offline   Reply With Quote
Old 06-01-2016, 01:49 PM   #15
Senior Member
 
TWP723's Avatar
 
Join Date: Mar 2015
Location: Abingdon
Posts: 6,177
ghosts.
__________________
2013 Jayco Eagle 328 RLTS
2021 Keystone Montana 3121RL
2013 F350 6.7L 4x4 CCLB
W/Air Lift air bags (front & rear)
Equal-I-Zer™ WDH & B&W Companion
TWP723 is offline   Reply With Quote
Old 06-01-2016, 01:52 PM   #16
Senior Member
 
Dustdevil's Avatar
 
Join Date: Mar 2016
Location: Orange County
Posts: 644
Quote:
Originally Posted by TWP723 View Post
ghosts.
Hahaha!!! Better get an exorcist.
__________________
2006 Jayco Seneca 34SS
2006 Jeep Wrangler Unlimited Rubicon Toad
Dustdevil is offline   Reply With Quote
Old 06-01-2016, 08:21 PM   #17
Senior Member
 
SmokerBill's Avatar
 
Join Date: Sep 2010
Location: PNW
Posts: 5,195
Quote:
Originally Posted by Dustdevil View Post
OK. I understand all that. So, if that is supposed to work as you just outlined, then how is it possible the blower could start, and burner operate, simply by turning the gas pressure on? Especially if the system requires cycling power before the main gas valve will ever receive a command voltage to open again? Even if it is malfunctioning, this should not be possible unless there is some way the control "knows" there is either a presence or absence of propane.
I don't know. The OP, rustysheros, has never returned. Maybe he should explain the problem in more detail.
__________________
Bill
2011 Dodge Ram 1500 HEMI Quad Cab
2011 Jay Flight 26BH
SmokerBill is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 10:43 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.