Generator/Inverter Specific Question.

Sifted through many posts about what folks use. My specific question is this: Will the Champion 3100/2800 run a 15k AC? I will not be using the microwave at the same time. Light, maybe tv or radio and A/C.

I'm not interested in spending 2k + on 2 Honda 2000's, I do have an opportunity to buy a used Honda 3000is, but the question remains the same, will it run a 15k A/C? The used Honda it needs a battery and runs rough, so I'm thinking that may not be cost effective vs a new or refurb unit from SuperGen.
__________________
Bob
Charlotte, NC
2020 28BHS
BobbyJayco is offline   Reply With Quote
Old 03-27-2018, 02:17 PM   #2
Senior Member
 
Join Date: Apr 2015
Location: Michigan
Posts: 2,650
You will have no problem running the a/c off either generator. If the Honda runs rough it probably needs a good carb cleaning or replacement, they get dunked up from sitting.
Sundancer330 is offline   Reply With Quote
Old 03-28-2018, 05:45 PM   #3
Junior Member
 
Join Date: Jul 2013
Location: Charlotte, NC
Posts: 7
Thanks Sundancer330
__________________
Bob
Charlotte, NC
2020 28BHS
BobbyJayco is offline   Reply With Quote
Old 03-28-2018, 05:50 PM   #4
Senior Member
 
Join Date: Jan 2018
Location: SW
Posts: 513
Quote:
Originally Posted by BobbyJayco View Post
Sifted through many posts about what folks use. My specific question is this: Will the Champion 3100/2800 run a 15k AC? I will not be using the microwave at the same time. Light, maybe tv or radio and A/C.

I'm not interested in spending 2k + on 2 Honda 2000's, I do have an opportunity to buy a used Honda 3000is, but the question remains the same, will it run a 15k A/C? The used Honda it needs a battery and runs rough, so I'm thinking that may not be cost effective vs a new or refurb unit from SuperGen.
I've done quite a bit of side-by-side testing of the Champion 3100 inverter generator, a paralleled pair of Honda EU2000i's and the Honda EU3000iS.

The Champion 3100 inverter generator produces more inrush current than a pair of paralleled Honda EU2000i's, and significantly more inrush current than the Honda EU3000iS. Inrush current is needed to "start" an RV a/c unit's compressor.

In plain-speak, this means a Champion 3100 inverter generator will have significantly more success starting/running 13,500 and 15,000 BTU RV a/c units than the Hondas.

In reality, the Honda EU3000iS typically struggles and fails (especially with the Eco mode on) starting/running quite a few 13,500 BTU a/c units---especially those with LRA's higher than 60 amps or so. Even Honda itself says the EU3000iS will only power more "efficient" 13,500 BTU a/c units. IMO, your chance of successfully (or consistently) powering a 15,000 BTU a/c unit with a Honda EU3000iS is very low.

Success (with any given generator) sometimes depends on the a/c unit. Dometic Brisk Air II 15,000 BTU a/c units are absolute power hogs. Even the Champion 3100 inverter generator can sometimes struggle starting this unit. The Coleman-Mach 15,000 BTU a/c units are generally more efficient, with lower LRA's. Your chance of successfully starting a Coleman-Mach a/c is higher.
CampNow is offline   Reply With Quote
Old 03-28-2018, 06:20 PM   #5
Site Team
 
Join Date: May 2017
Location: Connellsville
Posts: 22,707
Quote:
Originally Posted by CampNow View Post
I've done quite a bit of side-by-side testing of the Champion 3100 inverter generator, a paralleled pair of Honda EU2000i's and the Honda EU3000iS.

The Champion 3100 inverter generator produces more inrush current than a pair of paralleled Honda EU2000i's, and significantly more inrush current than the Honda EU3000iS. Inrush current is needed to "start" an RV a/c unit's compressor.

In plain-speak, this means a Champion 3100 inverter generator will have significantly more success starting/running 13,500 and 15,000 BTU RV a/c units than the Hondas.

In reality, the Honda EU3000iS typically struggles and fails (especially with the Eco mode on) starting/running quite a few 13,500 BTU a/c units---especially those with LRA's higher than 60 amps or so. Even Honda itself says the EU3000iS will only power more "efficient" 13,500 BTU a/c units. IMO, your chance of successfully (or consistently) powering a 15,000 BTU a/c unit with a Honda EU3000iS is very low.

Success (with any given generator) sometimes depends on the a/c unit. Dometic Brisk Air II 15,000 BTU a/c units are absolute power hogs. Even the Champion 3100 inverter generator can sometimes struggle starting this unit. The Coleman-Mach 15,000 BTU a/c units are generally more efficient, with lower LRA's. Your chance of successfully starting a Coleman-Mach a/c is higher.
I appreciate this post. Thank you.
Midnightmoon is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 10:02 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.