Quote:
Originally Posted by Jmooney View Post
I would not convert a 50 amp service down to a 30 amp cord. But you can convert a 30 amp service up to a 50 amp cord cant you?
Why not? I have 50A service (though it's not really necessary as I have the 2nd AC prep, but not the actual unit), and I imagine it's only a matter of time before I'm faced with a site that only has 30A service. I bought a dog bone at the dealer on delivery day specifically for that contingency, though I have yet to use it.

As long as you're not trying to pull too much amperage, you're okay right? And you'll trip the breaker at the post if you do try, right?
__________________

__________________


2014 Jay Flight 28 BHBE
2015 RAM 2500 6.4L HEMI, Tradesman 4x4, 3.73
Blue Ox SwayPro (BXW 1503)

Upgraded from an REI internal frame backpack and a Eureka 1/2 dome tent!
Camper_bob is offline   Reply With Quote
Old 04-25-2014, 04:17 PM   #22
Senior Member
 
Join Date: Jan 2014
Location: Aurora CO
Posts: 2,336
Quote:
Originally Posted by Camper_bob View Post
Why not? I have 50A service (though it's not really necessary as I have the 2nd AC prep, but not the actual unit), and I imagine it's only a matter of time before I'm faced with a site that only has 30A service. I bought a dog bone at the dealer on delivery day specifically for that contingency, though I have yet to use it.

As long as you're not trying to pull too much amperage, you're okay right? And you'll trip the breaker at the post if you do try, right?
I'm thinking its the end at which you are converting.


If your TT has 50 amp service, the master breaker inside will be rated at 50 amps

If you plug into 50 amp service, and convert down to a 30 amp cord, then pull 49 amps, neither breaker will blow, but the 30 amp cord will get very hot.

The other way: you plug into a 30 amp service, and convert up to a 50 amp cord. If you pull 30 amps, the breaker on the post will trip, but the cord will not have a problem....

No?
__________________

__________________
Jim & Kim from Colorado

2014 Eagle 30.5 RLS
2015 Dodge 3500HD SRW 6.7L
Click on my profile for Mods and notes
Jmooney is offline   Reply With Quote
Old 04-25-2014, 04:29 PM   #23
Senior Member
 
Join Date: Aug 2013
Posts: 201
Just be careful what you plug into. A true 20A adapter would have 1 of the terminals spun 90° so the adapters allow you to plug into a 15 A or a 20 A circuit. Outdoor plugs are most likely a GFCI which can take a true 20 A plug but might be wired on a 15 A circuit. I have a 20A GFCI receptical, but it is a true 20A circuit with 12 gauge wire to the panel and a 20A breaker. I have run my AC with no issues, but if you are running all kinds of other things in the TT when the AC turns on, you could have issues with too much voltage drop.

If you are using an adapter, be smart about it and realize there may be some restrictions.
__________________
Tim

2014 Whitehawk 33BHBS
Equilizer WDH
2014 F250 4X4 Crew Cab 6.2 l 3.73
2010 F150 4X4 Supercrew 4.6l 3.73 (traded in)
t2daniel is offline   Reply With Quote
Old 04-25-2014, 08:17 PM   #24
Senior Member
 
Join Date: Sep 2013
Location: South Texas
Posts: 4,190
Quote:
Originally Posted by Jmooney View Post
I'm thinking its the end at which you are converting.


If your TT has 50 amp service, the master breaker inside will be rated at 50 amps

If you plug into 50 amp service, and convert down to a 30 amp cord, then pull 49 amps, neither breaker will blow, but the 30 amp cord will get very hot.

The other way: you plug into a 30 amp service, and convert up to a 50 amp cord. If you pull 30 amps, the breaker on the post will trip, but the cord will not have a problem....

No?

Yeah, that sounds kind of right. Except that when you adapt 50 amp at the post down to a 30 amp plug, you actually only get 25 amps because the adapter only uses one side of the 50 amp service. At least that's the way I understand it. This would be an issue if a 30 amp rig pulls into a 50 amp only space, or a 50/30 where the 30 looks a little shady from too much use so you go into the 50 amp side because it's not as beat up. And if I'm correct, the bigger issue in that case is under-delivery of power rather than over loading the adapter.

But I don't have to worry about that because I have 50 amp service, so I can only go down.
__________________


2014 Jay Flight 28 BHBE
2015 RAM 2500 6.4L HEMI, Tradesman 4x4, 3.73
Blue Ox SwayPro (BXW 1503)

Upgraded from an REI internal frame backpack and a Eureka 1/2 dome tent!
Camper_bob is offline   Reply With Quote
Old 04-25-2014, 10:29 PM   #25
Senior Member
 
Join Date: Dec 2010
Location: North Idaho/Arizona
Posts: 5,303
Our trailer is 50 amp and when on the road I always use an adapter so I don't have to deal with the heavy 50 amp cord. I bought a 30 amp cord for travel and for the occasion when a 50 amp wasn't available.

Most people that have had trouble with a 15 or 20 amp hook up most likely are using too light of a cord. 25 or 50 ft of number 12 cord just won't do.
__________________
2011 Eagle 330RLTS with just about every option.
2017 Silverado 1500 4x4 5.3 with tow package.

I was born with nothing and I still have most of it left.
clutch is offline   Reply With Quote
Old 04-26-2014, 06:57 AM   #26
Senior Member
 
Join Date: Jan 2014
Location: Aurora CO
Posts: 2,336
Quote:
Originally Posted by Camper_bob View Post
Yeah, that sounds kind of right. Except that when you adapt 50 amp at the post down to a 30 amp plug, you actually only get 25 amps because the adapter only uses one side of the 50 amp service. At least that's the way I understand it. This would be an issue if a 30 amp rig pulls into a 50 amp only space, or a 50/30 where the 30 looks a little shady from too much use so you go into the 50 amp side because it's not as beat up. And if I'm correct, the bigger issue in that case is under-delivery of power rather than over loading the adapter.

But I don't have to worry about that because I have 50 amp service, so I can only go down.
I'm pretty sure that you have 50 amps on both legs.

So even though you have gone to a single phase, you still have 50 amps, and potentially pulling 50 amps through a 30 amp cord is never a good idea. The 30 amp wire becomes a " 30 amp fuse " if you will, just a very dangerous one.

The rule should be that the smallest wire used between post and power center dictate the largest service / breaker that you should connect too at the post.
__________________
Jim & Kim from Colorado

2014 Eagle 30.5 RLS
2015 Dodge 3500HD SRW 6.7L
Click on my profile for Mods and notes
Jmooney is offline   Reply With Quote
Old 04-26-2014, 07:53 AM   #27
Senior Member
 
Join Date: May 2010
Posts: 552
Quote:
Originally Posted by Camper_bob View Post
Yeah, that sounds kind of right. Except that when you adapt 50 amp at the post down to a 30 amp plug, you actually only get 25 amps because the adapter only uses one side of the 50 amp service. At least that's the way I understand it. This would be an issue if a 30 amp rig pulls into a 50 amp only space, or a 50/30 where the 30 looks a little shady from too much use so you go into the 50 amp side because it's not as beat up. And if I'm correct, the bigger issue in that case is under-delivery of power rather than over loading the adapter.

But I don't have to worry about that because I have 50 amp service, so I can only go down.
There are lots of misconceptions and lack of understanding about 50A service. 50A is actually 100A, two 120V legs each capable of supplying 50A. That's the reason 50A shore cords are made with 6ga cable. 30A cable is 10ga. There is no reason not to use a 30-50 adapter, but use the dogbone made by Marinco or Camco. The small "hockey puck" adapters are famous for burning up and taking the power cord with them. When you plug a 30A adapter into 50A service, you still have 50A available at the pedestal but the 30A breaker at your power panel will limit you to 30A. Contrary to popular belief, the pedestal is not going to try to "push" 50A into your rig.
If your trailer is set up for 50A and you use an adapter to plug a 30A cord into a 50A service because you don't want to wrestle a 50A cord then you are not protected. The safe way to do that would be to build a breakout box protected with a 30A breaker. Many people use ad adapter to plug their 30A rigs into 50A because the contacts on the 50A plugs are usually in better condition, and there is no problem in doing that.
I added a second 30A service to my trailer and use a breakout box plugged into the 50A outlet and nothing overheats.
__________________
2010 22FB(Ret)
2013 F250 XLT
I now have a Keystone Outback, but I try to help when I can.
---------------------
Bitter Gun Owner
Bitter Clinger
Armed Infidel
Bob Landry is offline   Reply With Quote
Old 04-26-2014, 09:30 AM   #28
Senior Member
 
Join Date: Aug 2013
Posts: 201
Quote:
Originally Posted by Bob Landry View Post
There are lots of misconceptions and lack of understanding about 50A service. 50A is actually 100A, two 120V legs each capable of supplying 50A. That's the reason 50A shore cords are made with 6ga cable. 30A cable is 10ga.
Bob,

Just for my understanding. When a trailer has a 50 A plug it is 50 A 220V (total of 50 A on each 110V leg)? The reason I ask is my 30 A in my White Hawk is 30 A 110 V. That is a huge step up from 30 A to 100 A!!
__________________
Tim

2014 Whitehawk 33BHBS
Equilizer WDH
2014 F250 4X4 Crew Cab 6.2 l 3.73
2010 F150 4X4 Supercrew 4.6l 3.73 (traded in)
t2daniel is offline   Reply With Quote
Old 04-26-2014, 10:01 AM   #29
Senior Member
 
Join Date: May 2010
Posts: 552
Quote:
Originally Posted by t2daniel View Post
Bob,

Just for my understanding. When a trailer has a 50 A plug it is 50 A 220V (total of 50 A on each 110V leg)? The reason I ask is my 30 A in my White Hawk is 30 A 110 V. That is a huge step up from 30 A to 100 A!!
That's correct, but 30A service consists of a single 120V leg, a neutral, and a safety ground. 50A service is two 120V legs each providing 50A, a neutral, and a safety ground, so it's two wire as opted to a single one. The 50A is wired with 6ga wire, thus allowing 50A per leg.
__________________
2010 22FB(Ret)
2013 F250 XLT
I now have a Keystone Outback, but I try to help when I can.
---------------------
Bitter Gun Owner
Bitter Clinger
Armed Infidel
Bob Landry is offline   Reply With Quote
Old 04-26-2014, 07:30 PM   #30
Lost in the Woods
 
Join Date: Jan 2014
Location: N/A
Posts: 567
Bob is correct. 30 amp service = 3600 watts vs. 50 amp service = 12,000 watts of power. Big difference. I recommend that everyone should study up on this somewhat in order to have a basic understanding of how RVs hook up to power as it isn't straight forward especially if you plan on using adapters. I think this is why Jayco says not to use adapters because one can get into trouble if one doesn't know what one is doing. I have just about all the common 50, 30 and 15/20 amp adapters going both ways and have used them all from time to time. I test the service I am about to hook to before hooking to it with a tester and a volt meter. I measure each hot leg to neutral and ground and if a 50 amp service I measure between each hot leg for 240 volts. Old camp grounds and State Parks are notorious for their power problems. But I have had problems at brand new RV parks as well with bad neutrals or grounds. I have a tester and plug in volt meter that I leave plugged in inside the camper so I can monitor it. It is amazing how much the voltage fluctuates and I have seen it get too low and too high.
__________________

wwsmith111 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia State Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -6. The time now is 06:43 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.