You mentioned a black button on the side you could push in a small amt. Try pushing in and turn counter clockwise. I think it is a fuse and the black button should come out with a fuse attached. Hope this helps.
__________________

__________________
2004 R vision Trail lite
2003 f 150 super crew
country boy is offline   Reply With Quote
Old 09-23-2015, 03:16 PM   #22
Senior Member
 
mike837go's Avatar
 
Join Date: May 2015
Location: Campbell Hall
Posts: 2,837
You say the blower moves enough air to activate the sail switch.


About 20 seconds after that is when the controller starts calling for ignition and then gas.


If the thing is operating that way, is seems to me, the controller board is the problem.


You say there is no clicking of the ignition system. But if your finger is on the gas solenoid, can you feel a single hit after the 20 seconds has elapsed? Check for 12v to the solenoid if you can't feel it open.


(I'm heading off to boondock until Tuesday in about 10 minutes)
__________________

__________________
TT 2015 19RD "TheJayco"
TV 2003 F-350 "Montblanc" - Housebroken chore truck


Sitting in The Cheap Seats.
And proud of it!
mike837go is offline   Reply With Quote
Old 09-23-2015, 03:37 PM   #23
Junior Member
 
Join Date: Sep 2015
Location: Poland
Posts: 4
Please check the 5amp fuse behide the black button as Country Boy suggested. This fuse should be power for the ignitor. If its blown the ingitor will not work nor will the gas valve open. No spark, no gas. Always replace with same size and style fuse. Good luck.
fireman is offline   Reply With Quote
Old 09-23-2015, 03:58 PM   #24
Member
 
Join Date: Aug 2015
Location: Davisburg
Posts: 48
Here is a photo of the "black button". It is located on the FRONT of the furnace (it's clearly visible when you take the louvered metal cover off the front when it is in the cabinet.) It is kitty-corner from the on-off rocker switch, up and to the right of the power switch. It is more of a rocker switch. It does not turn and doesn't toggle in or out when pushed. It does move a small amount in but springs back out the small amount. In the photo it is "out". It is only "in" when it is pushed in and held there. I think it is a circuit breaker of sorts. The button itself is about the size of a pencil eraser.
Attached Thumbnails
SAM_1114.JPG  
outrider is offline   Reply With Quote
Old 09-23-2015, 04:07 PM   #25
Member
 
Join Date: Aug 2015
Location: Davisburg
Posts: 48
Also, I did not say that the blower circulates enough air to activate the sail switch. The blower runs, but it doesn't seem to blow very much. As I already stated, it blows about as hard as if you exhaled after taking a deep breath. Someone already mentioned it should blow enough to hold a piece of paper straight out, which it does not. HOWEVER, taking the sail switch out of the mix and jumping the wires that went to the sail switch (thereby bypassing it) SHOULD have made the furnace start if that was the issue, regardless of if the blower is putting out enough air to close the sail switch OR if the sail switch were bad. We also, as already stated, did a continuity test on the switch with it engaged while it was out of the furnace, and it passed, the circuit completed with the switch engaged. Therefore, our deduction is that while the blower motor may not be putting out enough air, the sail switch should be ok, but there is some other issue here.
outrider is offline   Reply With Quote
Old 09-23-2015, 07:44 PM   #26
Member
 
Join Date: Aug 2015
Location: Davisburg
Posts: 48
Unless we come up with a solution to the issue, I think that we've decided that we're going to take the furnace unit in to the RV place and have diagnostics done on it. Doesn't mean we have to have anything fixed, but if they can at least tell us what needs to be replaced, it will be a start. We have looked up the prices for the parts we suspect might be an issue on ebay, so we will know if they're way out of line for the price for fixing it. It's $65 for the diagnostic and if we have anything fixed, that charge goes toward the cost, so we'll weigh things out and see what ends up cheapest. I have found the high limit switch, the sail switch, the circuit board and the gas valve. The gas valve is the only one I would probably have them do just because of not being 100% comfortable doing it. The other stuff is a piece of cake. Couple screws, couple wires to hook up.
outrider is offline   Reply With Quote
Old 09-24-2015, 08:15 AM   #27
Member
 
Join Date: Aug 2015
Location: La Crosse Va
Posts: 69
another thing you may check is the limit switch. It is a small switch on the side with 2 wires and is on the side of the firebox. If the furnace gets too hot it will trip , after a few uses it sometimes will not reset. try jumping it and see what happens.
__________________
2004 R vision Trail lite
2003 f 150 super crew
country boy is offline   Reply With Quote
Old 09-24-2015, 03:28 PM   #28
Member
 
Join Date: Aug 2015
Location: Davisburg
Posts: 48
Quote:
Originally Posted by country boy View Post
another thing you may check is the limit switch. It is a small switch on the side with 2 wires and is on the side of the firebox. If the furnace gets too hot it will trip , after a few uses it sometimes will not reset. try jumping it and see what happens.
By Jumping, do you mean "bypassing" the limit switch by disconnecting the two wires from it and hooking them together to complete the circuit? I've found where the limit switch is and actually had it out to look it over. It's pretty easy to get to with the entire furnace out of the cabinet.
outrider is offline   Reply With Quote
Old 09-24-2015, 03:46 PM   #29
Member
 
Join Date: Aug 2015
Location: La Crosse Va
Posts: 69
by pass it just for a test. Do not operate it for long without the limit switch.
__________________
2004 R vision Trail lite
2003 f 150 super crew
country boy is offline   Reply With Quote
Old 09-24-2015, 04:34 PM   #30
Member
 
Join Date: Aug 2015
Location: Davisburg
Posts: 48
Ok, I bypassed the limit switch AND the sail switch at the same time by removing the swtiches and using a couple small pieces of stranded electrical wire to jump from one connector to the other on each switch. Nada. Nothing but fan. No clicking. I'm thinking at this point, circuit board??? Wish there were a way to bypass that, but it's what sends the signal to light the flame.
__________________

outrider is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia State Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -6. The time now is 01:17 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.