Walmart actually has 2000 watt 110 volt portable electric heaters for sale on the website. I would think they would have 20 amp plugs.
plugs.
Craig, you have me going down the rabbit hole again. I see lots of references to this and I believe you but I cannot find a curve that shows this working. I see curves that show breakers holding at 1X rated current for 10,000 seconds, something like three hours, but the time scale doesn't continue. I cannot find the NEC code that states that or when it came to be a rule. Do you have that reference? I don't mean waste time on research, but if you have that, I'd like to see it. If not, I'm tapping out on household breakers.Breakers such as in an RV and at home are rated to handle 100% if the load is intermittent and 80% for continuous loads. For example if you plugged in a 1800W heater to a 15A breaker protected circuit with no other loads it will work for a while, and if it is turning off and on with the thermostat setting, it may work without ever tripping the breaker however, if it stays on (the heating element) continuously, the breaker will trip in time, right around 3 hours under test conditions.
Interesting questionCraig, you have me going down the rabbit hole again. I see lots of references to this and I believe you but I cannot find a curve that shows this working. I see curves that show breakers holding at 1X rated current for 10,000 seconds, something like three hours, but the time scale doesn't continue. I cannot find the NEC code that states that or when it came to be a rule. Do you have that reference? I don't mean waste time on research, but if you have that, I'd like to see it. If not, I'm tapping out on household breakers.