Bernie Brassard
New Member
I have a 2007 32 ft Greyhawk. All 110 volt outlets normal except two in bedroom read 92 volts. Any ideas why this is possible. Breakers checked and gfci ok.
Test at the main breaker to verify that you have 120 volts to ground and 120 volts to neutral. Both sides if a 50 amp. Then test for voltage from neutral to the ground. It must be zero volts or very close to that. If everything tests good, turn your breaker off, verify no power, and pull out the receptacles. Most likely one has loose connection on the neutral. If it doesn’t test correct, check at the pedestal same checks. If it is ok, the last place is at the receptacle on the side of the RV that your cable attaches to.I have a 2007 32 ft Greyhawk. All 110 volt outlets normal except two in bedroom read 92 volts. Any ideas why this is possible. Breakers checked and gfci ok.