And now, the moment of truth. It was time to start making the battery-side connections.
Before putting the false floor down in the bed, I mounted a positive busbar to the floor in there. I connected my 2 positive connections to the distribution system to it. I then mounted an on/off switch to the outside of the bed base so that I don't have to lift the mattress to turn off the system. This comes off of the busbar and that will feed into the battery/BMS connections.
It was pretty exciting to be able to put the false floor down and have the kids load in the batteries. For now, I'm still just focused on the 2 long lines of batteries and haven't yet worried about compression.
I mounted most of the rest of the hardware to a board, but my spacing here was pretty tight. I attached the catastrophic fuse, negative busbar, shunt, pre-charge controller from the BMS, and contactor (part of the pre-charge controller). I really need to get some pictures of this all and show the inter-connections. I set this into place under the bed where it'll go but hadn't secured it yet. I needed a placeholder for how long my battery cables needed to be.
So first, obligatory shot of the friend who came and sat with me while I did the work. He 100% was looking for the entertainment of me zapping myself. He was much disappointed.
Now, I apparently need to take a lot more pictures. But, what I did was- I took 16 of the batteries that I had previously top balanced and wired them in series. This gives me 304 ah at 48 volts. The negative comes off of one end and the positive off of the far end.
I double-checked the voltages in the BMS's cell voltage wires and came to find out that I had a battery upside down! Fortunately, no damage but it did mean that I had to tear down the whole pack, move batteries around, and build it back up. Fun times but fortunately I tested it before just blindly plugging it into the BMS.
And then it was time to start turning things on. This part was terrifying!
First up, the BMS. This was extra terrifying since I had previously burnt one up and know that they run $500 to replace. I surely didn't want to do that again. Simply plugging it in was hard on the heart. All went well- I had a moment of concern when the error light showed up, but this is its typical boot sequence.
I connected the laptop to the USB dongle and was able to verify that I was good. This is an older screenshot, but it looked exactly the same with some minor variance in the cell voltages:
Next, once that was all up and clean, I headed down into the hatch so that I could plug into the inverters and run Victron Connect so I could see what was going on.
I started with voltage at the busbar and it was showing a solid 50-something volts. Horray!
Loaded up Victron Connect and it wasn't showing the batteries. BOO! I shut them down, restarted them, did the classic IT things and had no change. Want to know what it was? I'm dumb, that's what it was- I have 2 battery disconnects for feeding power into the inverters and I had them OFF because I didn't want surprises as I was doing all of my wiring. DUH.
Turned them on and all looked pretty good!
I disconnected my shore power connection and the inverters hummed along nicely.
I tried the rear air conditioner and it roared to life!
I shut it down and tried the front air conditioner. After some brief reconfiguring of the inverters (I had been switching between parallel and split-phase during the troubleshooting with the generator), it roared to life, too!
I shut it back down and thought, OK- let's try this load assist feature. I went into VE. Bus System Configuration and enabled it and enabled the battery charger.
(Note, I've since updated the cutoff voltages for the load assist- though, that's a today job. Figure out the appropriate charging/discharging/cutoff voltages for the battery bank and get that configured in both VE. Bus and the BMS.)
I saved the settings and fired up the rear air conditioner- all excited for my new found load assist feature. And I tried the garage breaker. At nearly 11pm, well after my friends were asleep... well crap. Fortunately, they left the door unlocked for exactly this case. I sent my daughter in and I went about figuring out what was up.
Turns out, the battery charger portion was trying to pull too much power from the 15amp connection. If my math is right, it was:
2995.2 watts = 57.6 volts * 52 amps
2995.2 watts / 120 volts = 24.96 amps
Things get funny on a single-phase shore power connection with the dual inverters, so I don't think it was double that.
Once I dropped that 52 amps down to something like 8, everything hummed along nicely!
I was able to run both air conditions with the load assist supporting them on a 15 amp garage connection! And given that "funny" I mentioned, it was still trying to push some power back into the batteries.