No power to microwave
We have a 2017 29mv , this weekend trip microwave would not work ( no power going to it) checked 20 amp breaker and it was not tripped (flipped it off and on) plugged microwave in to extension cord to 20 amp. Service at park pole and all was working great. Turned off both a/c units and still no power. Last trip out two weeks ago we lost power to it but it came back on with no reset to breaker. What can I check next?
|
|
|
08-13-2018, 11:10 AM
|
#2
|
Senior Member
Join Date: Jul 2011
Location: Long Island, NY
Posts: 1,402
|
Check outlet with GFI and make sure the GFI wasn't tripped. Push test and reset button.
__________________
2018 Jayco 28RLS
2012 F-250 6.2L 3.73
Equalizer Hitch
Yamaha 2400ISHC
|
|
|
08-13-2018, 11:18 AM
|
#3
|
Senior Member
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,109
|
Pull the receptacle from the wall/cabonet and check the wiring, some have been known to loosen.
__________________
DISNEY LOVERS
|
|
|
08-13-2018, 11:34 AM
|
#4
|
Senior Member
Join Date: Mar 2018
Location: Granbury
Posts: 829
|
You mentioned two air conditioners so you also have the power management system that sheds appliances when needed to keep you from overloading the 30 amp service your motorhome has.
If working correctly both air conditioners can run at the same time but other appliances may not.
It sounds like your problem could be the power management may be shedding the microwave but not returning power?
Were you running both the air conditioners when this happens? After power management sheds it takes a bit for power to come back after enough amps are again available.
__________________
2018 Greyhawk 29MVP
2018 Jeep 4 Door Rubicon Recon
Retired and Under New Management (See Spouse For Details)
|
|
|
08-13-2018, 12:59 PM
|
#5
|
Senior Member
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,863
|
Quote:
Originally Posted by cabinetmaker
You mentioned two air conditioners so you also have the power management system that sheds appliances when needed to keep you from overloading the 30 amp service your motorhome has.
If working correctly both air conditioners can run at the same time but other appliances may not.
It sounds like your problem could be the power management may be shedding the microwave but not returning power?
Were you running both the air conditioners when this happens? After power management sheds it takes a bit for power to come back after enough amps are again available.
|
I've been an electrician for 35 years and RV'ed for 18 and I've never heard of a "power shedding" device in any sub $500,000 motorhome. What is the brand and model number of this device?
|
|
|
08-13-2018, 01:05 PM
|
#6
|
Junior Member
Join Date: Dec 2016
Location: Stafford
Posts: 11
|
I think you are right, have power in wire behind breaker but not in same wire at outlet. Microwave not showing up when I scroll through power management device.
|
|
|
08-13-2018, 01:06 PM
|
#7
|
Senior Member
Join Date: Sep 2013
Location: South Texas
Posts: 7,217
|
Quote:
Originally Posted by Vicr
I've been an electrician for 35 years and RV'ed for 18 and I've never heard of a "power shedding" device in any sub $500,000 motorhome. What is the brand and model number of this device?
|
Believe it or not, the Greyhawks with 2 AC units have them. IIRC they're made by Progressive Dynamics. They keep these 30A units from throwing breakers between the 2 AC units and the other high draw devices like microwaves and electric water heaters. When there's a demand for power, the system will shed one of the AC units to provide enough power to whatever called for the demand. It will also shed other items to provide for both ACs to run.
__________________
-2018 Greyhawk 29MV
-2020 Jeep Wrangler Unlimited (JLU) (Primary Toad)
-1994 Jeep Wrangler YJ (Secondary Toad)
-2014 Jay Flight 28BHBE & Ram 2500 6.4L CC 4x4 (sold)
|
|
|
08-13-2018, 01:27 PM
|
#8
|
Senior Member
Join Date: Dec 2014
Location: FL
Posts: 11,281
|
Quote:
Originally Posted by Fuzzy
We have a 2017 29mv , this weekend trip microwave would not work ( no power going to it) checked 20 amp breaker and it was not tripped (flipped it off and on) plugged microwave in to extension cord to 20 amp. Service at park pole and all was working great. Turned off both a/c units and still no power. Last trip out two weeks ago we lost power to it but it came back on with no reset to breaker. What can I check next?
|
Did you PRESS the breaker to the off position? Those breakers need to be 'reset' after it trips by pressing it the off direction against spring pressure, not just moving/flipping to the off position. If you haven't already, give that a try. It's a common issue.
Please let us know...
EDIT: Oops! Thanks Grumpy. I missed that post by Fuzzy.
__________________
Sherm & Terry w/rescue Eydie (min Schnauzer) & Charley (std Poodle)
SOLD:2015 Jay Flight 27RLS, GY Endurance (E), Days: 102 '15, 90 '16, 80 '17, 161 '18, 365+ '20
SOLD: 2006 Ford F350 PSD, 4WD, CC, LB, SRW, Camper pkg., 375,000mi
Full timing: Some will think you're crazy, some will be envious, just enjoy the freedom!
|
|
|
08-13-2018, 01:29 PM
|
#9
|
Senior Member
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 16,109
|
Quote:
Originally Posted by oldmanAZ
Did you PRESS the breaker to the off position? Those breakers need to be 'reset' after it trips by pressing it the off direction against spring pressure, not just moving/flipping to the off position. If you haven't already, give that a try. It's a common issue.
Please let us know...
|
His last post...
Quote:
Originally Posted by Fuzzy
I think you are right, have power in wire behind breaker but not in same wire at outlet. Microwave not showing up when I scroll through power management device.
|
|
|
|
08-13-2018, 02:11 PM
|
#10
|
Senior Member
Join Date: Mar 2018
Location: Granbury
Posts: 829
|
Quote:
Originally Posted by Vicr
I've been an electrician for 35 years and RV'ed for 18 and I've never heard of a "power shedding" device in any sub $500,000 motorhome. What is the brand and model number of this device?
|
Vic...yes it’s a factory included feature of a Greyhawk 30 amp Service with 2 air conditioners option. Works great at controlling load and monitoring amps being used.
Here is a detailed description if you can read it sorry it’s small print.
|
|
|
08-13-2018, 08:08 PM
|
#11
|
Senior Member
Join Date: May 2017
Location: Kingman
Posts: 620
|
Quote:
Originally Posted by cabinetmaker
Vic...yes it’s a factory included feature of a Greyhawk 30 amp Service with 2 air conditioners option. Works great at controlling load and monitoring amps being used.
Here is a detailed description if you can read it sorry it’s small print.
|
It works exceptionally well in my 2017 GreyHawk w/2 A/Cs. A great feature I wouldn’t be without.
|
|
|
08-14-2018, 09:51 PM
|
#12
|
Member
Join Date: Aug 2014
Location: Allentown
Posts: 57
|
It looks like the power management feature comes on all Prestige 2018 and 2019 (saw on 31fsps). I was in a single ac 2018 with the PMS. I see pictures online for 2019 single AC that look like they have it too.
|
|
|
08-15-2018, 04:06 PM
|
#13
|
Senior Member
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,863
|
Quote:
Originally Posted by cabinetmaker
Vic...yes it’s a factory included feature of a Greyhawk 30 amp Service with 2 air conditioners option. Works great at controlling load and monitoring amps being used.
Here is a detailed description if you can read it sorry it’s small print.
|
Thanks for the information! I gotta have one of those!
|
|
|
08-28-2018, 10:03 AM
|
#14
|
Junior Member
Join Date: Dec 2016
Location: Stafford
Posts: 11
|
Update, found hot and common wires had melted together in breaker panel. Hot wire had burnt completely into! Repaired and all is good now.
|
|
|
08-29-2018, 09:05 PM
|
#15
|
Member
Join Date: Jun 2018
Location: Atlanta
Posts: 61
|
Quote:
Originally Posted by Fuzzy
Update, found hot and common wires had melted together in breaker panel. Hot wire had burnt completely into! Repaired and all is good now.
|
Any clues as to how this may have happened in such a young coach??
|
|
|
08-30-2018, 06:42 AM
|
#16
|
Junior Member
Join Date: Dec 2016
Location: Stafford
Posts: 11
|
No power to microwave
Looks as though both wires hot and common had been started to be stripped with a wire stripping tool and not had insulation removed (only scarred all way around) then stripped closer to the end of wire with insulation removed and connected to breaker and common bar. Wires where then pushed into the breaker panel box with cover and apparently rubbed on each other and over time arched.
|
|
|
09-05-2018, 12:50 PM
|
#17
|
Junior Member
Join Date: Oct 2016
Location: Knoxville
Posts: 6
|
I know this may sound way out there but please indulge me.
I have run into situations with microwave ovens that I could not understand.
Here it goes:
My mother-in law kept tripping a breaker that her microwave was connected to. So being an Electrical Engineer I figured I could fix this easy. Probably just a weak breaker. As a test only, mind you, I replaced the breaker with a 20 amp instead of the normal 15 amp breaker.
Several days later she called my wife and the 20 amp let go. Hmmm.
As soon as I reset it the microwave worked fine. Cooked me a free dinner and everything. Well, not that I wanted my mother-in-law to die in a microwave induced fire, I put a new 15 amp breaker in place of the 20 amp test breaker. Don't be concerned about the 20 amp test for I wired the place with 12 gauge wire myself. I don't like 14. People always overload them.
Ok, so now we have an intermittently tripping breaker. But the microwave works fine. So I tore into the wiring and found everything tight and secure.
hmmmm....
I told her not to use the microwave anymore. "Use the range for a while." I said receiving a very questionable look from her. She hadn't cooked on a range in years.
No tripping of the breaker was the result. Bought her a new microwave oven and haven't heard from her since. Turns out the magnetron tube in the microwave would intermittently short and pop the breaker.
Same thing happened at an apartment house I owned and I told the tenant to get rid of the microwave oven. She refused and moved. About a month later she called and said the same thing happened at her new apartment and that I was right. My head still hasn't stopped swelling.
If the shedding system works according to what I believe, it will shut down any device that has an overload condition on the system. I think you might want to move the microwave to a different circuit that isn't so controlled. You just might trip a breaker. Just a wild guess.
Please, do not let me know if this works. My hats don't fit as it is.
Walt
|
|
|
09-05-2018, 07:15 PM
|
#18
|
Junior Member
Join Date: Jun 2018
Location: Theodore
Posts: 6
|
Thats what happened to me
|
|
|
09-06-2018, 12:41 PM
|
#19
|
Member
Join Date: Dec 2017
Location: Kansas City
Posts: 64
|
check your converter...... sometimes if you had a power surge the breaker inside the converter will swell and the whole converter will go bad. Never a fun a thing.
|
|
|
09-13-2018, 01:09 PM
|
#20
|
Senior Member
Join Date: Apr 2016
Location: Fortuna Foothills
Posts: 1,863
|
Quote:
Originally Posted by JaycoChix89
check your converter...... sometimes if you had a power surge the breaker inside the converter will swell and the whole converter will go bad. Never a fun a thing.
|
In all my 35 years as an electrician I have never seen a swollen breaker. Please explain.
|
|
|
|